[Solved] Changing the power supply from 1 phase to 3, apartment in a block of flats, old
Suszoczarny16 16245 16
How can I convert an old apartment in a block of flats from single-phase to three-phase power for a 7.8 kW electric cooker, and who has to replace the wiring from the meter to the flat?
You cannot just ask the utility to "turn on" three phases at the meter; first get written consent from the housing cooperative/association to use the staircase riser and other common areas, then apply to the utility for increased power and 3-phase connection conditions [#18611545][#18613546][#18615707] The utility will issue the connection conditions and may require a notification of installation readiness / technical-condition statement before connecting the meter [#18611588] The internal installation is your electrician’s responsibility, and the cable from the meter to the apartment is at your expense; the cooperative may also replace the pre-meter section or charge you part of the cost [#18611545][#18611588] In this case the existing equipment in the photos is described as very old and in terrible condition, so the WLZ/riser and the apartment switchboard likely need replacement too [#18611545][#18612690] A typical recommendation was to use a WLZ around 5x6 mm², install a larger main switchboard, and add separate circuits for the cooker and kitchen appliances [#18612690]
  • #1 18611113
    Suszoczarny16
    Hello, here is my problem :)
    Apartment in a block of flats, top floor, I bought an electric cooker. BEKO FSE57300GX max power consumption 7.8kW.
    I want 3 phases ;) I called SM* they said to send an application and I can do what I want because I will pay anyway.
    Walking around the cage I checked the wires and they look like in the pictures.
    Changing the power supply from 1 phase to 3, apartment in a block of flats, old Changing the power supply from 1 phase to 3, apartment in a block of flats, old Changing the power supply from 1 phase to 3, apartment in a block of flats, old
    1 - a can in the apartment.
    2- here ZE** connects the meter.
    3- hatch with wires on the floor below (there is a seal on my floor so I didn't want to touch it yet because I don't know the subject).
    Looking at picture no. 3 I can see correctly that 3 phases are released in this vertical on the cage? and it is enough for me to report the need for 3 phases in my apartment to the ZE and they will connect it on my floor? (where the seal is) and I will be able to run the cables from the meter with 3 phases?
    Is it somehow different and I will have to push another wire there (we are talking about those tubes from which the wires come out, picture No. 3) and pull it to my meter? :crazyeyes:
    I hope all is well with the post.
    *Power company.
    **Housing Association.
  • #2 18611176
    CYRUS2
    Help: 1241
    Rate: 3530
    Suszoczarny16 wrote:
    I want 3 phases ;) I called SM* they said to send the application and I can do what I want because I will pay anyway.
    There are 3 phases in the riser, but the cooperative has not written whether it will allow connection to this riser.
    And all I have to do is report the need for 3 phases in my apartment to ZE and they will connect it on my floor? (where the seal is) and I will be able to run the cables from the meter with 3 phases?
    You have to write to the energy utility about new connection conditions and a new power allocation.
    It is possible that under the conditions of the Energy Regulatory Office, it will demand that the installation in the premises be replaced with TN-S. (separate PE conductor).
  • #3 18611207
    opornik7
    Electrician specialist
    Help: 316
    Rate: 1568
    Not for new conditions, but for an increase in power.
    It's out of the question. Energy does not deal with such "little things". It's up to the electrician to do the work.
    By the way, crap from photo No. 1 to be disposed of.
  • #4 18611212
    Suszoczarny16
    Oh, so they can answer me that they don't let me connect to it, okay, so the worst case is that I will have to squeeze another wire myself.
    But if SM** agrees to connect to the riser in the cage, then ZE* will connect 3 phases to the meter and leave me some wire so that I can pull it to the apartment myself or what? (picture no. 2). Because 2 wires enter the meter and 2 come out. They will pull this wire there or will it be my cost?
    The switchboard in the apartment will be new, on Sy
    I confirm :D
  • #5 18611247
    opornik7
    Help: 316
    Rate: 1568
    le if SM** agrees to connect to the riser in the cage, the ZE* will connect 3 phases to the meter and leave me some wire so that I can pull it to the apartment myself or what? (picture no. 2). Because 2 wires enter the meter and 2 come out. They will pull this wire there or will it be my cost?
    Power engineering has nothing to do with internal installation, It's the problem of the cooperative and yours. If the cooperative tells you to replace the headlights, your electrician must do it. If there is an exchange of wlz-tu, it would be good if it had a cross-section that would take into account the future needs of all recipients connected to it. In this case, you can take a "share" from the cooperative, but the cooperative can do it and charge you some % of the costs. From the meter to the apartment is your cost.
  • #6 18611494
    CYRUS2
    Help: 1241
    Rate: 3530
    I have other experiences.
  • #7 18611523
    Suszoczarny16
    So the seal that is placed on my floor vertically on the staircase is the property of SM, right? and electricians from SM will have info. about that right? (it's about photo No. 3) because the photo comes from the floor below, my box is sealed ;)
    And will ZE have any info. about what is in a given block (thickness and number of wires), what is the connection power I can afford?
    bartekfigura
    Level 30  
    Help: 112
    Rate: 524
    The installation is in such a terrible condition that when applying for new connection conditions, you will probably have to replace the cable from the ZK next to the building, because this one, despite the fact that there are 3 phases, is old and the cross-section is too small. The installation is subject to acceptance, so before they connect the meter, they will check whether you have done it in accordance with the conditions. First, you also need to obtain the consent of the cooperative to work in generally accessible places, i.e. in the staircase. And then put everything back to its original state. Direct the first steps to the ZE, submit an application, wait for the connection conditions, show the electrician these conditions, let him do everything in accordance with the conditions ...
  • #9 18611578
    Suszoczarny16
    bartekfigura wrote:
    Direct the first steps to the ZE submit the application wait for the connection conditions
    All right, I'm going to deal with the ZE tomorrow, and we're waiting for the sequel ;)
    I am not closing the topic yet because I may need your help regarding this matter :)
    Thank you for today and I'll get back to you when I get the info. from ZE. Regards :D
  • #10 18611588
    Jacek1l
    Help: 7
    Rate: 71
    From my experience - first for permission to SM, it will be known whether SM has any requirements for the replacement of WLZ. After the consent of SM to ZE for power increase and 3f counter. It varies with administrators, but most likely you replace the wires from the pre-meter protection to the meter under the supervision of SM at your own expense, or MS will replace, but also at your expense, from the meter to the security in the apartment at your expense. ZE (Tauron) is not interested in what is behind the meter, because they require the "Notification of readiness of the installation to be connected, Statement on the technical condition of the installation" where there is a statement on the technical condition of the installation and the person signed under the statement takes responsibility.
    Regards
  • #11 18612056
    opornik7
    Help: 316
    Rate: 1568
    Jacek1l wrote:
    ZE (Tauron) is not interested in what is behind the meter because they require the "Notification of installation readiness for connection
    What's more, in this case, the power industry is not interested in what is in front of the meter up to the exploitation limit, and this is most likely in the cable connector or on the stand/console terminals when powered by an overhead connection.
    Jacek1l
    Help: 7
    Rate: 71
    Slightly off topic, but related.
    In the above case, the author probably "enters" the apartment, so the renovation of the installation is easier than if you already live there, secondly, the aluminum is asking for replacement, thirdly, he probably calculated the costs of changing from 1 to 3 phases in general costs.
    But - in my opinion (and I know such cases too), changing the power supply from 1 to 3 phases in buildings where there is already copper with appropriate cross-sections in the apartment is not necessarily an expense that must be incurred when buying a cooker or hob, whether ceramic or induction.
    I have an Amica 601IE3.464TaYKDpOg(XxL) cooker with a connection power of 10.5 kW since November 2011, and from the beginning of using the cooker it "managed" to overload the s301 b16A fuse maybe 4, max 5 times for a family of 4 with two children when cooking daily . Single-phase installation, so that two circuits go to the kitchen and on one there is a stove and lighting under the furniture, on the other the rest.
    The author probably enters the apartment and there is no problem with such modernizations, but if someone already lives and wants, for example, to "transition" from gas to electricity and heard in the store that it must have 3 phases because the stove or hob is at 3f and draws a lot of electricity and the fuses will not withstand a the costs of changing the installation are more than the purchase price of the equipment, so I say: buy a cooker, if it is possible without major "damage" to pull a separate cable from the fuses to the cooker, pull it and use it, you'll see what will happen, maybe changing to 3f is not necessary at all.
    tajan123
    Everything in the picture is in terrible condition. Absolutely to be replaced.
    -Wlz for flat usually 5x6mm²
    Then this pseudo-switchgear in the apartment is better to give a larger min 2x12 and, as the renovation of subsequent rooms, lead new circuits to individual rooms and fill new boxes
    - I don't know what the kitchen looks like, but if you want to lead the cable under the stove (5x2.5), then immediately add a few circuits to the countertop for the dishwasher, fridge, etc. If the tiles are new, you can run them behind the cabinets in invisible places.
    I have carried out such upgrades many times. Replacing the WLZ, setting up a new main switchgear and a circuit for the cooker is about PLN 2-3k with the material, but I would advise you to replace the installations and make more circuits in the kitchen right away, but you know other costs
    CYRUS2
    Help: 1241
    Rate: 3530
    There's no need to go to the cooperative.
    He must obtain connection conditions from the ZE for the power he wants.
    How much power will give ZE - is not known.
    Moderated By Topolski Mirosław:
    Knowledge and experience is important not my point of view.
    3.1.11. Don't post messages that add nothing to the discussion. They are misleading, dangerous or do not solve the user's problem.
    opornik7
    Help: 316
    Rate: 1568
    You are wrong again. He has to go to ZE with a piece of paper from the cooperative. Don't mislead people.
    Szyszkownik Kilkujadek
    Level 37  
    Help: 211
    Rate: 1014
    Just like it is possible that an asteroid will hit the Earth tomorrow.
    Well, it's just the opposite. First SM, then ZE.
  • #17 20053314
    Suszoczarny16
    The idea of changing the connection was abandoned. The dishwasher and washing machine work at night, only the fuse box has been changed.
The discussion revolves around the user's intention to upgrade their apartment's electrical supply from a single-phase to a three-phase system to accommodate a BEKO FSE57300GX electric cooker with a maximum power consumption of 7.8 kW. Participants highlight the necessity of obtaining permission from the housing cooperative (SM) before contacting the energy utility (ZE) for connection conditions. Concerns are raised about the existing wiring's condition, with suggestions that it may need replacement to meet regulatory standards. The user is advised to ensure that the installation complies with the Energy Regulatory Office's requirements and to prepare for potential costs associated with upgrading the wiring from the meter to the apartment. The conversation concludes with the user deciding to abandon the connection change, opting instead to manage their appliances with the existing setup.
TL;DR: Upgrading flats to 3‑phase often uses WLZ 5×6 mm², and "Everything in the picture is in terrible condition. Absolutely to be replaced." Budget PLN 2–3k for WLZ + main switchgear + cooker circuit. [Elektroda, tajan123, post #18612690]
Why it matters: For apartment owners moving from 1‑phase to 3‑phase for electric cooking, this FAQ clarifies approvals, scope, and realistic costs.
Do I really need 3‑phase for an electric cooker, or can single‑phase work?
Not always. One user runs an Amica 10.5 kW cooker on single‑phase. A B16 breaker tripped only 4–5 times over years. Use a dedicated cooker circuit and separate kitchen circuits to spread load. "Buy a cooker, pull a separate cable, use it… maybe changing to 3f is not necessary." Evaluate your usage before upgrading. [Elektroda, Jacek1l, post #18612324]
Who must approve work in the staircase or riser before I talk to ZE?
Your housing association (SM). Get written permission first and follow their requirements. After SM consent, apply to the power utility (ZE) for a power increase and a 3‑phase meter. SM may require work under their supervision. [Elektroda, Jacek1l, post #18611588]
What does ZE actually check when switching to 3‑phase?
ZE focuses on paperwork, not your internal wiring. They require a Notification of readiness and a Statement on the technical condition. The person who signs assumes responsibility for the installation behind the meter. [Elektroda, Jacek1l, post #18611588]
Who pulls and pays for cabling from the meter to my apartment?
You do. The utility does not handle internal installations. From the meter to the apartment is your scope and cost, often under SM oversight in common areas. [Elektroda, opornik7, post #18611247]
Can SM refuse connection to the 3‑phase riser even if it exists?
Yes. A riser can carry three phases, but SM decides on access. They can deny a new connection or require upgrades before approval. [Elektroda, CYRUS2, post #18611176]
What WLZ size and main switchboard should I plan for a modern upgrade?
Plan WLZ 5×6 mm² to the flat and replace old gear. Use a larger main switchboard (min 2×12 modules) to add circuits as rooms are renovated. Replace visibly degraded equipment. [Elektroda, tajan123, post #18612690]
Which kitchen circuits should I add during the upgrade?
Run a cooker feed (e.g., 5×2.5 mm² as suggested) and add separate countertop circuits for dishwasher, fridge, and other loads. Route behind cabinets if tiles are new to avoid rework. [Elektroda, tajan123, post #18612690]
What’s a realistic budget for WLZ + main switchboard + cooker circuit?
Expect roughly PLN 2–3k including materials for WLZ replacement, a new main switchboard, and a cooker circuit. Full‑room rewires increase costs but improve safety and capacity. [Elektroda, tajan123, post #18612690]
How do I apply to increase power and get a 3‑phase meter?
  1. Obtain SM permission for works in common areas and any WLZ changes.
  2. Apply to ZE for a power increase and 3‑phase meter; await connection conditions.
  3. Have a licensed electrician do the works and file the readiness and condition statements. [Elektroda, Jacek1l, post #18611588]
Will ZE leave spare cable for me to pull to the apartment?
No. ZE does not supply or pull internal cabling. You or your contractor provide and install cables from the meter to the apartment at your cost. [Elektroda, opornik7, post #18611247]
My building has old aluminum wiring. What should I expect under new conditions?
Expect required replacements. You may need a new cable from the building’s connector (ZK). ZE will only connect the meter after acceptance checks against their conditions. Secure SM consent for staircase works and show your electrician ZE’s conditions. [Elektroda, bartekfigura, post #18611545]
Where does the utility’s responsibility typically end?
At the exploitation limit. ZE is not concerned with what is in front of the meter up to that point, often at the building connector or stand terminals. [Elektroda, opornik7, post #18612056]
Will ZE force me to convert to TN‑S with a separate PE conductor?
Edge case: Under connection conditions, ZE may ask for TN‑S. Plan for a separate PE conductor if required by issued conditions. [Elektroda, CYRUS2, post #18611176]
If the WLZ is replaced, how should it be sized and who pays?
Choose a cross‑section that covers future needs of all connected recipients. SM may coordinate the replacement and charge you a share. From the meter to your flat remains your cost. [Elektroda, opornik7, post #18611247]
Can I avoid a 3‑phase upgrade by shifting loads and modernizing the fuse box?
Yes. One outcome was to abandon the change, replace the fuse box, and run heavy appliances at night. Load management can defer a 3‑phase upgrade. [Elektroda, Suszoczarny16, post #20053314]