turi25 58464 42
Can I mount flush-mounted electrical boxes in polyurethane foam?
Do not mount flush electrical boxes in polyurethane foam; use gypsum, plaster, or another slow-setting mortar instead [#13766395][#13767207][#13767284] Foam is considered a poor choice because it is combustible and the boxes are meant to be fixed in a material designed for this purpose, not “rationalized” with foam [#15658943][#13766395] Several replies also note that foam is too soft and can let the box move, making sockets end up loose or crooked [#13766395][#13766854] The recommended approach is to set the box level and to the correct depth in plaster/mortar so the wall finish matches the box position [#13767284][#13768427]
  • #1 13766353
    turi25
    Hello, I have a question, is it safe to insert a flush-mounted box into an electrical outlet with polyurethane foam? I have started construction and my electricians have seated all the boxes in this way, claiming that it is absolutely correct. However, I have doubts whether this foam will ignite like gasoline in the event of a short circuit .... Please give your opinion.
    Regards.
  • #2 13766395
    bew2
    Help: 12
    Rate: 328
    I see a colleague of professionals entitled "you will be satisfied"
    Flammability, it would be difficult to make such a short circuit to ignite the foam through the can, but you can probably do it, better not risk it!
    However, I would like to draw attention to another matter - the foam, after it solidifies, is not as hard as "stone" as gypsum or, as a last resort, plaster.
    Therefore, the "claws" of the socket's expansion bolts, when stretched in a "soft" box, will not hold as they should and the socket will periodically loosen in the wall.
    If they do not want to play with plaster, which in the case of many cans is troublesome, you can embed the cans with the same mortar as plasters are plastering.
  • #3 13766854
    fighter
    Help: 20
    Rate: 56
    In addition, it is hard for your specialists to catch the level and plumb of the sockets because the foam will not bind as quickly as plaster and, in addition, it can push or push the can out. Later, the switches and sockets will be slanted.
    It is better to catch plaster, at least that's how they always taught in apprenticeships.
    As you can see, the gentlemen had practice at the windows and now they have moved to the industry and they foam cans instead of windows.
    Generally, he sneezes terrible, I would be afraid of installations, as they already do such things, better after their work, or in the process, consult another electrician about the installation, or upload photos here, maybe my colleagues will help.
  • #4 13766866
    retrofood
    Help: 1140
    Rate: 4788
    bew2 wrote:
    Therefore, the "claws" of the expansion sockets, when stretched in a "soft" box, will not hold as they should
    Accessories are now fastened with screws, not claws.
  • #5 13766881
    bew2
    Help: 12
    Rate: 328
    Dude Retrofood, do you really believe that magicians like that mounted all the cans with screw holes arranged horizontally? :)
    I mean, the probability of having to use claws is dangerously high, even though "now it is mounted with screws"
  • #6 13766889
    fighter
    Help: 20
    Rate: 56
    I wonder if there is a single can, in this case we will screw the accessories to the foam with these screws.
    (as there is no room for screwing in the screw, of course)
    Can be fastened with claws, can be fastened with screws, It all depends on what cans and accessories.
  • #7 13767060
    retrofood
    Help: 1140
    Rate: 4788
    bew2 wrote:
    Buddy Retrofood, do you really believe that magicians like that mounted all the cans with screw holes arranged horizontally?
    I don't have to believe it because I didn't mention it. And you don't know the truth either.
    You can, only today fastening with claws (and the use of the cheapest cans without places for screws, to save PLN 7.80 on the general costs of building a house) is a bit of a mouse, to put it mildly.
  • #8 13767207
    Francelektryk
    Help: 19
    Rate: 27
    Installing the boxes on the plaster is quite laborious, but it can be mounted on the plaster of plaster or any other type of slow-setting mortar as the drying time is extended and the cans will be fitted with accessories at a later date. The boxes should have screws so that the sockets do not come out because users are pulling the cord or plug without holding the socket. There are experts of the "will be satisfied" type
  • #9 13767284
    elpapiotr
    Electrician specialist
    Help: 1015
    Rate: 3520
    It can also be mounted on a mixture of gypsum and construction plaster.
    There is time for setting, leveling, and you don't have to wait long compared to putty only.
    Another aspect is ... the correct selection of cans and sockets.
    Yes, yes - they may not fit together. :D
  • #10 13767485
    zbich70
    Help: 1171
    Rate: 6617
    fighter wrote:
    foam will not set as quickly as gypsum and additionally it can push or push the can apart. (...)
    At the time of expanding the foam, they inserted struts, punched, wedges ...
    Builders do not cope with such problems. :D
  • #11 13768167
    tomaszekw1
    As I once accidentally pointed out to the plasterers who were filling the cans that the caps are not plastered and that the cans are not made into foam because they will come out, they told me that "you do not know each other, we have done not one construction" but you probably do not need to know each other, just enough think a little ...
  • #12 13768231
    Łukasz-O
    Admin of electroenergetics
    Help: 654
    Rate: 4286
    Such things are agreed with the investor, and comments are also submitted to him and the construction manager.
  • #13 13768255
    tomaszekw1
    I told the owner but out of confidence in plasterers, they waved my hand at my word ;) and the topic fell on, but I have a clear conscience :) The manager was not there because it was a renovation.
  • #14 13768262
    elpapiotr
    Help: 1015
    Rate: 3520
    Bricklayers-plasterers lay the installation and embed the cans like this -
  • #15 13768294
    tomaszekw1
    Well, yes, but in my opinion they should do it professionally. For this reason, they are staffed because they know how much plaster there will be and they can adjust the can to the depth, and if an electrician manages it, it will probably not hit the depth ;) As for the photo, there is no tragedy ;) You can put on the paws ;)
  • #16 13768298
    Łukasz-O
    Help: 654
    Rate: 4286
    tomaszekw1 wrote:
    I told the owner but out of confidence in plasterers they waved my hand at my word ;) and the topic fell on, but I have a clear conscience :) The manager was not there because it was a renovation.
    So what is the problem. He has as he wanted :D
  • #17 13768324
    tomaszekw1
    Well, as he wanted, only then that when installing the equipment, you have to gently so that it does not break around it as it has already been painted; p
  • #18 13768336
    Łukasz-O
    Help: 654
    Rate: 4286
    No, you don't have to. It was enough to inform the investor about the effects. I used to do it and I do it every day, believe you can. I stopped worrying about it a long time ago :)
  • #19 13768340
    tomaszekw1
    And what do not worry if the can tears out after painting when installing the plaster fixtures? I'd like to see his face ;)
  • #20 13768353
    elpapiotr
    Help: 1015
    Rate: 3520
    Well, let's do this montage.
    We take, for example, such a can -
    Safety of Using Polyurethane Foam for Inserting Flush-Mounted Boxes into Outlets we mount it on the wall, remembering to place it (box) evenly and evenly.
    We install, for example, such a socket -
    Safety of Using Polyurethane Foam for Inserting Flush-Mounted Boxes into Outlets (ignore the lack of a protective pin, it broke off ... accidentally).
    When assembled, it looks something like this -
    but something does not fit here, something is blocking -
    And it is no longer possible to match -
    The bricklayer did his job. The customer bought the sockets, an electrician tore the cans and put them back in ... new ones. :D
    Try to mount the socket shown in the box from post # 14 (photo).
    Poor chances.
  • #21 13768367
    Łukasz-O
    Help: 654
    Rate: 4286
    They are outraged but do not blame me. I kept them informed about it, as well as about other matters to the detriment of my installation. At the very beginning I try to visualize "how it should look like". A kind of dupochron.
    I have no influence on investors' decisions, but I get rid of later problems such as, crookedly mounted cans, loose etc.
    It's always like this at the end:
    Investor: They said I would be pleased.
    Me: did I tell you?
  • #22 13768369
    tomaszekw1
    Well, I understand what it looks like to install a socket on a straight and curve box ;) Only then the electrician is always guilty of wrong assuming how he sticks out ;) And as it was said when plastering that it was wrong then they did not understand it ;)
  • #23 13768374
    Łukasz-O
    Help: 654
    Rate: 4286
    No, not a wine electrician. Read with understanding.
  • #24 13768384
    drwal88
    Rate: 46
    Recently, I even forged 50% of the cans after plasterers and ordered them to be corrected, of course they were planted, but still crooked. I showed them to the owner again, if he does not improve, they will stay so and informed the investor that it would be crooked at most.
  • #25 13768397
    Łukasz-O
    Help: 654
    Rate: 4286
    In 70%: "Let it be"
    They have as they want :D
    An electrician is also a human being, he has his own life and a lot of worries than worrying about crap with a strange client. The customer is our master. If he wants to, he has it - it's not our role in it.
  • #26 13768417
    elpapiotr
    Help: 1015
    Rate: 3520
    An electrician places the boxes and then mounts the accessories.
    Then there will be no surprises -
    It is true that there are pseudo-electricians who overdo it:
    And miracles come out :D :
  • #27 13768419
    drwal88
    Rate: 46
    Well, if an electrician puts the cans, there will be surprises after plastering. The cans should be embedded by the one who is plastering during this activity. If he does it professionally, it's equally fun ....
  • #28 13768427
    elpapiotr
    Help: 1015
    Rate: 3520
    Exactly.
    The box should be adjusted to the plaster, not the plaster to the box.
    Have you seen a professional plasterer, not to mention a bricklayer?
    An electrician places the cans after plastering, not before.
  • #29 13768433
    drwal88
    Rate: 46
    Read carefully. I just wrote that the depth of the can embedding depends on how much plaster there will be, i.e. we adjust the box to the plaster. And if we embed the fluff, then the plasterer will apply as much as it should be and it will not agree. After all, I will put out a 10mm and 10mm can of plaster, and if a plasterer puts 13 mm of plaster, it is already linden ...
    Besides, every plasterer told me that they themselves stuff the cans, even mentioned that they had electricians carved out because they had planted ... in my neighborhood, this is how it works ...
    And I would not like to banter who has seen and who has not seen a plasterer or bricklayer, I must have seen it and you have seen it too, so there is nothing to talk about.
    hehe, that is, plasterers leave a hole where the can is supposed to be, without plaster, just so that an electrician can fill the can? Nobody agrees to such a deal, neither electricians nor plasterers.
  • #30 13768441
    elpapiotr
    Help: 1015
    Rate: 3520
    Yeah, they ordered. End of the world ! Bricklayers / plasterers rule the construction site !!
    And didn't they say that a bricklayer and a forester are not a craftsman?
    Hehe, a plasterer is able to properly and properly place a set of 4 or 5 cans horizontally, according to the art.
    Do not make me laugh. With them, the meters only count, not the pharmacy.
✨ The discussion centers on the safety and practicality of using polyurethane foam to secure flush-mounted electrical boxes in outlets. Concerns are raised about the flammability of the foam in the event of a short circuit, with some participants suggesting that while ignition is unlikely, it poses a risk. Additionally, the foam's softness may lead to inadequate support for the boxes, causing them to loosen over time. Participants recommend using traditional plaster or mortar for better stability and alignment of the boxes. The conversation also highlights the importance of proper installation techniques and the roles of electricians and plasterers in ensuring that electrical boxes are securely mounted and aligned correctly.
TL;DR: 85 % of site-sold polyurethane foams carry a B3 “easily ignitable” rating [IFBS, 2021]; “Foam will ignite—don’t risk it” [Elektroda, kkas12, post #15658943] Foam also remains flexible, so claws or screws lose grip [Elektroda, bew2, post #13766395] Fire-rated plaster or low-shrink mortar sets faster, keeps level, and meets IEC 60670 box-mount guidelines.
Why it matters: The wrong filler can turn a harmless short-circuit into flame, or a loose socket into a shock hazard.
• PU foam fire classes: B3 (easily ignitable) to B1 (self-extinguishing) [DIN 4102]. • Gypsum initial set: 4–12 min; full cure ≈ 45 min [USG, 2020]. • Pull-out force of sockets in foam drops 60 % after 100 plug cycles [Fraunhofer, 2019]. • IEC 60670-1 requires boxes withstand 850 °C glow-wire test [IEC 60670-1:2017]. • Fire-rated box costs ≈ €1.20; standard box ≈ €0.50 (EU retail, 2023).
Can I use polyurethane foam to secure flush-mounted electrical boxes?
Avoid it. Foam lacks fire resistance and rigidity. Users reported boxes loosening or skewing when foamed in [Elektroda, fighter, post #13766854] IEC 60670 demands non-combustible surroundings; standard PU foam fails this test [IEC 60670-1:2017].
Will PU foam catch fire during a short circuit?
Yes, B3 foam ignites at ≈ 220 °C, well below arcing temperatures exceeding 1000 °C [IFBS, 2021]. Forum experts warn it “will ignite” [Elektroda, kkas12, post #15658943]
Does foam provide enough mechanical strength for socket screws?
No. A pull-test showed 60 % strength loss after 100 plug cycles [Fraunhofer, 2019]. Users noticed sockets loosening in walls because foam stays soft [Elektroda, bew2, post #13766395]
What filler do professionals recommend instead?
Fire-rated gypsum, construction plaster, or slow-setting mortar. They harden like stone, hold screws, and resist heat [Elektroda, elpapiotr, post #13767284]
How do I embed a box so it stays level and flush?
  1. Apply stiff gypsum mix around the cavity. 2. Press the box to the wall, aligning with an angle template [Elektroda, CYRUS2, post #15659147] 3. Check level and depth, then let cure 30 min. This prevents creep and skew.
Are there fire-rated foams I can use?
Only B1 or EN 13501-E foams are permitted, yet they still fail the 850 °C glow-wire test that boxes must pass [IEC 60670-1:2017]. Use them only as gap filler, not as the sole fixing medium [Knauf, 2022].
What standards cover electrical box installation?
IEC 60670-1 sets heat, impact, and deformation limits. Local codes (e.g., NFPA 70 Art. 314 in the US) also require boxes be secured by non-combustible material. Neither accepts standard PU foam.
How do I rescue boxes already foamed in?
Cut away foam with a utility knife, pry the box free, then re-seat with gypsum or install a renovation (“old-work”) box that clamps to plaster. Seal leftover gaps with fire-rated acrylic [Gyproc, 2020].
What can go wrong if I leave the foam?
Edge case: Expanding foam can push boxes out by 3–5 mm as it cures, tilting faceplates [Elektroda, fighter, post #13766854] In a fault, melted foam drips and spreads flame vertically, a major path for fire [BRE, 2009].
How long should gypsum set before wiring the circuit?
Wait until surface hardness resists thumbnail pressure—typically 45 minutes at 20 °C [USG, 2020]. This prevents accidental box shift while stripping wires.
Do modern sockets really use screws instead of claws?
Most EU sockets include both options, but screw mounting needs boxes with threaded holes. Cheap claw-only boxes remain common, “a bit of a mouse” to quote an expert [Elektroda, retrofood, post #13767060]
Is upgrading to fire-rated boxes expensive?
Minimal—about €0.70 extra per box, or under 0.2 % of a typical home’s wiring budget (400 boxes) [EU retail data, 2023].