    Can I use the ROP-01 radio receiver to switch lights on and off in an existing installation with the current switch?
  • ADVERTISEMENT
  • #2 13945476
    azibik
    Level 32  
    Posts: 1950
    Help: 82
    Rate: 322
    Replace the switch with a staircase switch and treat the relay from the ROP as a second staircase switch
  • #3 13949643
    tapis
    Level 12  
    Posts: 103
    Help: 1
    Rate: 7
    In the box where the switch is, there is only the phase wire and the wire from the lamp, there is no neutral wire. :cry:
  • ADVERTISEMENT
  • #4 13955478
    tapis
    Level 12  
    Posts: 103
    Help: 1
    Rate: 7
    So the current wiring is not suitable?

    greetings.
  • #5 13956916
    azibik
    Level 32  
    Posts: 1950
    Help: 82
    Rate: 322
    The neutral wire is in the box above if there is a typical installation.
  • ADVERTISEMENT
  • #6 13963187
    tapis
    Level 12  
    Posts: 103
    Help: 1
    Rate: 7
    OK, I already have 3 wires in the box, phase, neutral and the wire from the lamp, how do I connect the ROP-01 radio receiver to a regular bistable switch? According to the schematic Link I am supposed to use terminals 12, 11, 14.

    salutation.
  • ADVERTISEMENT
  • #7 13964425
    azibik
    Level 32  
    Posts: 1950
    Help: 82
    Rate: 322
    Can you pull another wire from the switch to the box ?
  • #8 13966822
    tapis
    Level 12  
    Posts: 103
    Help: 1
    Rate: 7
    Yes, no problem, I can add another cable, but won't there be too many of these cables?

    greetings.
  • #9 13967195
    azibik
    Level 32  
    Posts: 1950
    Help: 82
    Rate: 322
    Pull one more cable,replace the switch with a staircase switch and treat the relay as a staircase switch,search for the diagram on googlle.
  • #10 13973522
    retrofood
    VIP Meritorious for electroda.pl
    Posts: 31317
    Help: 1140
    Rate: 4785
    azibik wrote:
    Pull another cable,


    These are not cables, they are wires. If you don't want to see posts in the bin, please keep the nomenclature correct.