How do I read a Rossweiner DE-10-MI004-PTB002 heat meter and calculate how much gas I used for heating from its readings?

The heat consumption is shown by the values marked in GJ, and you find usage by subtracting the earlier reading from the later one [#14641602][#14642158] In your example, 10.5860 GJ minus 0.5512 GJ gives 10.03 GJ, or about 10,035 MJ [#14642158] To estimate gas volume, divide that energy by your gas calorific value; with 31 MJ/m3, that is about 323.7 m3 of gas [#14642158] The 109% efficiency from the boiler leaflet is only catalog data, not a real constant for the whole season, so any gas conversion is only approximate [#14641978][#14642158] If the house has a common hot-water tank and no separate meter for domestic hot water, the calculation will not fully separate heating from hot-water use, and summer readings are the best way to estimate the hot-water share [#14644025][#14644252]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • Identifying heat consumption readings and estimating gas usage

    #1 14641088
    archellaos
    Level 9  
    Posts: 15
    Rate: 9
    Hello, I have a rossweiner DE-10-MI004-PTB002 heat one heat meter. I am completely green and I don't know which numbers indicate the heat consumption. He shares a house with a neighbor, we have 2 of them. He is at home and I am at home. I have a photo taken before the heating season and after and the numbers are different also some measurement is for sure. But which one and how do I calculate how much gas I used to heat the house on the basis of these numbers? Advice as you can.
    Attachments:
    • Reading Rossweiner DE-10-MI004-PTB002 Heat Meter: Guide to Understand Heat Consumption Numbers IMAG4061.jpg (1.31 MB) You must be logged in to download this attachment.
  • ADVERTISEMENT
  • #2 14641602
    piotr_boncza
    Level 29  
    Posts: 1058
    Help: 135
    Rate: 338
    Those marked with GJ.
  • ADVERTISEMENT
  • Helpful post
    #3 14641622
    eljarkos
    Level 21  
    Posts: 462
    Help: 46
    Rate: 104
    Here's the manual.
    Attachments:
    • COSMOHEAT_obsluga.pdf (132.76 KB) You must be logged in to download this attachment.
  • ADVERTISEMENT
  • #4 14641947
    archellaos
    Level 9  
    Posts: 15
    Rate: 9
    Thanks for the answer, and especially for the instructions, because that's what I was looking for. How to calculate now how much gas went to heat the house? I was looking in google but I did not find any specific solution. Add something, multiply?
  • ADVERTISEMENT
  • Calculating gas energy use from heat-meter readings and calorific value

    #6 14642109
    archellaos
    Level 9  
    Posts: 15
    Rate: 9
    I found on the website http://oferta.pgnig.pl/czy-jest-gaz-ziemny because we get gas from them, the gas values provided by them. "calorific value - not less than 31.0 MJ / m3 1)". We have a Brotje WBS 22C condensing furnace. According to this website http://www.ogrzewany.pl/product/Kociol-kondensacyjny-EcoTherm-Kompakt-WBS-22-E/?id=1779. The furnace appears to have an efficiency of 109%. The numbers from before the heating season are 0.5512 from October 21 and after - 10.5860 to April 8. According to this page, what you gave the formula to calculate is 31 MJ / (divided by 3600 seconds, i.e. an hour) 3600s = 8.6111 kWh from m3 of gas. And these 8.6111 kWh multiplied by 10.0348? I subtracted 0.5512 from this final value. I don't know if I understood correctly :-) . We also heat water with gas and boil it. I do not know if there is any division into gas used for heating utility water. Surely there is no meter by the gas stove.
    Attachments:
    • Reading Rossweiner DE-10-MI004-PTB002 Heat Meter: Guide to Understand Heat Consumption Numbers IMAG4678.jpg (1.46 MB) You must be logged in to download this attachment.
  • Helpful post
    #7 14642158
    eljarkos
    Level 21  
    Posts: 462
    Help: 46
    Rate: 104
    The heat consumption is: 10.586GJ - 0.5512GJ = 10.03GJ or 10,035 MJ
    10 035 MJ / 31 MJ = 323.7 m3 of gas. Efficiency above 100% will only be provided when several conditions are met, including at full load, with condensing boiler operation, which is not always the case. This is catalog data, not actual data. The conversion above is only approximate, not super accurate.
  • Helpful post

    Valid heat calculations require separate domestic hot-water metering

    #8 14644025
    piotr_boncza
    Level 29  
    Posts: 1058
    Help: 135
    Rate: 338
    Not enough data. If you have one storage tank in common and there is no third meter that would count the heat for heating domestic hot water, then any calculations do not make sense.

    Added after 4 [minutes]:

    eljarkos wrote:
    Efficiency above 100% will be only provided that a few conditions are met, including at full load, with condensing boiler operation, which is not always the case.

    You have data from a different matrix. With us, the highest efficiency and condensation occur at the lowest loads, and almost always with a properly performed installation. That's almost, it didn't happen this year, and the average annual number is a few days.
  • #9 14644144
    archellaos
    Level 9  
    Posts: 15
    Rate: 9
    I understand, but at least I know how much energy the heaters themselves used, and this already gives a resultant sum. Anyway, thanks for your interest and answer.
  • Helpful post

    Hot-water metering improves summer gas-cost allocation

    #10 14644252
    piotr_boncza
    Level 29  
    Posts: 1058
    Help: 135
    Rate: 338
    Heating water is sometimes a big part of the bill. In one family, two people use the shower briefly, in the other four people use a large bathtub. If you had at least a meter accounting for hot water consumption, you will determine the gas consumption and the distribution ratio during the summer, when the heating is turned off. There will of course be an error due to temperature differences among others, but you will be closer than now.
  • Questioning extra DHW disinfection cycles beyond weekly schedule

    #11 14645813
    archellaos
    Level 9  
    Posts: 15
    Rate: 9
    We'll do that too, thanks. I do not know if I can ask such a question on the same topic, namely. In the above-mentioned oven, a function is activated from time to time, which heats the water to about 60 degrees C, maybe a little more. He does it cyclically, that is, several times a day. I entered the specialist function and there saw a setting something like "tray cleaning"? I do not remember exactly. This function was set to 3, I did it to 1. In the further DHW settings I found it as if the main cleaning was done on Sundays. And here I am wondering what to do so that the stove does not heat this water to more than 60 degrees for these few minutes, and it does it only once a week. I know that the translators are not clear because I do not have a display in front of me, but maybe you know a little about it and maybe you know what I could do with it? This water heating is used to get rid of bacteria and viruses from the tank, and I am aware of this. The temperature is set to 45, because that's enough for me and the stove turns on between 8am to 9am and 6pm to 7pm and it's "exactly" to put it this way. But despite this, I "caught" him just heating the water on a weekday. Does the stove have any additional function of heating water constantly?
  • Helpful post
    #12 14646180
    piotr_boncza
    Level 29  
    Posts: 1058
    Help: 135
    Rate: 338
    It should have the tank thermal disinfection set. The main threat is legionella bacteria. I will not write anymore, because I have already done it several times. They reproduce perfectly up to 55 °. To knock them out, you need a minimum of 60 ° and the circulation is on, so that the temperature is reached in the entire volume of the reservoir and installation. After reaching this temperature, you open the taps, and most of all the showers, and disinfect the rest. In my opinion, and in a large part of the instructions, one such procedure a month is enough. I think it's over-zealous every day. Look in the settings, it should be changeable. It would be good if the time could be set so that there is no risk of burns to children and other unaware people.
  • #13 14646533
    eljarkos
    Level 21  
    Posts: 462
    Help: 46
    Rate: 104
    Refer to the manual for disabling this feature, and do it manually once a month at a convenient time.
  • #14 20501052
    misiekubot
    Level 9  
    Posts: 31
    Rate: 3
    Hello
    Can anyone recommend me a heat meter with wired M-BUS? It can also be a water meter; the device needs a protocol on the table to learn.

Topic summary

LABEL_AI_GENERATED
The discussion revolves around understanding the heat consumption readings from a Rossweiner DE-10-MI004-PTB002 heat meter. The user seeks clarification on which numbers indicate heat consumption and how to calculate gas usage for heating. Responses highlight that the relevant readings are marked with GJ, and the calorific value of gas is crucial for calculations. The user provides specific data from their heating system, including a Brotje WBS 22C condensing furnace with an efficiency of 109%. Calculations are discussed, leading to an approximate gas consumption of 323.7 m³ based on the difference in heat meter readings. The conversation also touches on the importance of accounting for hot water heating and the potential need for additional meters for accurate billing. Additionally, there are inquiries about the furnace's water heating settings and recommendations for managing thermal disinfection to prevent bacteria growth.
AI summary based on the discussion. May contain errors.