Yes — a 40-year-old refrigerator can be a real power user, so you should measure its energy over a full day rather than judging by instantaneous watts [#15284523][#15467643] Refrigerators cycle on and off, and the thread gives examples around 1 kWh/day, about 2 kWh/24h, or even 0.4 kWh in 9 hours for an old 42-year-old unit; a worn door seal can also make an old fridge run much more often [#15467643][#15284523] A plug-in wattmeter is useful for checking appliances, but its accuracy is only approximate, so it is best used as a diagnostic tool rather than proof for a complaint [#15246577] Before blaming the fridge, switch off everything and watch the main meter; if it still moves, the thread suggests hidden loads or leakage in the wiring, and if you suspect the meter itself the utility can verify it [#15244604][#15244778][#15246577] The heater is also a strong suspect: one reply notes that a 5.5 kW instantaneous water heater can easily account for a large part of a bimonthly bill [#15244778]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 15244591
    justykacz
    Level 14  
    Posts: 195
    Rate: 25
    Greetings.

    We have a very high consumption of electricity, after a time of heavy sighing over the bill I took it upon myself to determine what is to blame.

    I have a few theories:

    1. Meter broken
    2. One tariff
    3. Old installation, old house, done very amateurishly
    4. Old refrigerator
    5. Someone plugged in, connection error

    I would like to figure out with your help what is the cause.

    The first thing I wanted to rule out is an old refrigerator. The refrigerator is 40 years old, very graceful, but it is on my target.

    According to your experience, how can such a thing be a current-consuming thing?

    I wanted to buy a wattmeter to determine this. The first better one on allegro is called dual tariff and I would like to know if I can measure on one tariff with such a thing? Does it have the option to program one tariff?

    Old refrigerator - High bills, old refrigerator and house, buying a wattmeter

    photo from user:

    http://allegro.pl/listing/user/listing.php?us_id=3518291

    Greetings.
  • ADVERTISEMENT
  • #2 15244604
    kozi966
    VIP Meritorious for electroda.pl
    Posts: 6922
    Help: 599
    Rate: 1288
    To begin with, disconnect all devices, literally all of them, and check if the meter is spinning (the main one).
    Then look for the culprits, if there are any.
  • ADVERTISEMENT
  • #3 15244638
    justykacz
    Level 14  
    Posts: 195
    Rate: 25
    Hmm it's an electronic meter how do I check if it flies? :) Something flashes?

    The problem is with this refrigerator, its not possible to unplug it because it will defrost, so I wanted to treat it with a wattmeter, since I'm already going to have this trouble. Maybe unplugging for a while to plug in this appliance should not cause me defrosting, but the risk is there.

    I'll provide a table of what we have at home, maybe tomorrow I'll be able to, to show more where we stand.


    We have a consumption of about 800kW for 5 people. Flow heater 5.5kW.
  • #4 15244649
    kozi966
    VIP Meritorious for electroda.pl
    Posts: 6922
    Help: 599
    Rate: 1288
    justykacz wrote:
    Hmm it's an electronic meter how do I check if it flies? Is something flashing?
    In that case, I add the digits (code 1.8.0 - you can see the total energy consumption).
    I don't know if it wouldn't be simpler to invite a metering electrician with equipment to the house....
  • #5 15244653
    krys06
    Level 29  
    Posts: 1179
    Help: 97
    Rate: 190
    And I would start with:
    - since the last electricity bill, I understand, is paid ---> report your doubts about the reading, and the reliability of the calculations to the Energy Provider.
    - of course, the 40-year-old refrigerator should be placed in the "museum of technology".
    - the "plugging in" of it must be ascertained , precisely by the Energy Provider.
    - you need to answer the question: since when, and by how much the bills have increased?
    - answering these questions , results in taking certain actions. I will add that even "old for those times", but efficient electrical installation of the house, certainly does not significantly inflate your energy bills!!!
    The purchase of unnecessary metering equipment...will not change your view of the current situation in any way.
    I would add, you should consider the following points:
    how many points of light there are in the house/apartment, how many watts/each bulb, how many outlets connected receivers during the day(refrigerators, washing machines, t.v., computers,etc)
    Apply a gradual transition to energy-saving type lighting. Costs are significant for a one-time replacement, but spread over time --->recovered by reduced bills precisely.
  • #6 15244678
    Anonymous
    Anonymous  
  • #7 15244738
    justykacz
    Level 14  
    Posts: 195
    Rate: 25
    I would invite someone I trust, but I don't know such a person. My esteemed mother spoke with an electrician who said that there are no such meters that when you plug between the plug and the outlet will check how many watts an appliance consumes ;) Now my mother every now and then asks when this wonderful device will come, as if she does not believe that actually such a thing who invented. I think for this reason as well as perhaps out of curiosity about how much electricity a Mesozoic refrigerator consumes, however, I will buy a wattmeter ;)


    Also, I repeat the question, will the two-tariff wattmeter I showed be able to calculate what I need at one tariff?

    Bill 500zł.

    The meter and yes it shows numbers in the form of 25040.4 kWh, does such a scale allow to observe, say, anomalies if I turned off everything, even those refrigerator of discord?

    As I understand it, even the most let's call it primitive installation dating back to the People's Republic of Poland should not affect the power consumption?

    Is the reminder from the supplier paid? If so, then approximately how much? Can they refuse such service?

    Should I move to the recently fashionable LED lighting? But is it an overrated thing and not much different from so-called energy-saving bulbs?

    I'm already preparing a table of what we have :)


    Hmm these 500zł seemed quite ok to me, given that we have this flow heater, only recently I began to change my mind that it does not necessarily have to be so ;)




    I'll add that the plug-in theory seems least likely to me. It was my grandmother who made this assumption, because from the pole that draws electricity to us they recently connected the lighting under the parking lot. To me it is improbable that by some strange coincidence we should pay for the parking lot streetlights, but what is on the list of theories :) .
  • #8 15244756
    omnibus111
    Level 15  
    Posts: 76
    Help: 11
    Rate: 46
    Once upon a time a friend had a similar problem.She was left alone in the apartment (blocks of apartments), and paid more than a neighbor with a husband and two children .After turning off what could be turned off the meter did not fool around too much.It turned out that at two points in the wall where the electrical system went were beaten metal pins to hang holy pictures.About 4 mb of carbon installation .After replacing the above-mentioned modest bills came.
  • ADVERTISEMENT
  • 5.5 kW water heater may explain high bills

    #9 15244760
    Anonymous
    Anonymous  
  • #10 15244766
    niewolno2
    Level 40  
    Posts: 4694
    Help: 630
    Rate: 1260
    Turning off the refrigerator for the time of checking the meter will not affect the possible thawing, you turn it off from the knob that probably located inside and then unplug it from the outlet. You turn off all appliances and watch the meter. As for the electrician/electricians who have a vague knowledge of metering devices, avoid them by a big bow.
  • Wall-mounted picture pins caused hidden wiring leakage

    #11 15244767
    Anonymous
    Anonymous  
  • 5.5 kW heater and meter checks explain high bills

    #12 15244771
    justykacz
    Level 14  
    Posts: 195
    Rate: 25
    omnibus111 wrote:
    About 4 mb of installation with carbonized .After replacing the aforementioned came modest bills.



    Haha, interesting :)


    I wonder if there's something in it, but not so much some supernatural forces, so to speak, but overconfidence in electricians as I mentioned above. Perhaps there is something in the connection of the heater. Maybe tomorrow I will cycle what we have there.


    Małolepszy wrote:
    The heater is 5.5kW, and that's not a lot and can run up a big bill. It depends on how much hot water you use, because if someone likes long and warm baths-showers then the bill is normal. 500zł is a monthly bill?


    For two months.

    I think you're right, as yet let's say I revel in the table I put together on short notice, I'm getting more and more of a feeling that the bills don't lie.

    Małolepszy wrote:
    What is the point of this reminder?


    Someone above wrote about the letter to the supplier that the bills "strangely" inflated. I have read in various places that people have misconfigured meters, not set up as they should be. Roughly speaking, I have in mind some routine meter check as a reminder :)



    Old refrigerator - High bills, old refrigerator and house, buying a wattmeter


    Of course, using a secluded place we do not rely on the help of a flashlight and there is lighting, in addition, there is also a corridor and lighting outside, but from an excess of excitement I forgot :D
  • ADVERTISEMENT
  • Measure the 5.5 kW heater before blaming refrigerator

    #13 15244778
    Anonymous
    Anonymous  
  • Heater test shows 0.4 meter-unit increase during bathing

    #14 15244786
    justykacz
    Level 14  
    Posts: 195
    Rate: 25
    That is, the longer you think about it, the circle of suspects does not narrow, but quite the opposite.

    From curiosities today I "measured" the consumption in this heater. Mom went to take a bath and the meter for 7 minutes of her bathing went from 25039.4 to 25039.8, then for 7 minutes without the heater it went to 25039.9, so it comes out so slightly messed up counting it per person came out 0.3 without the heater....
  • #15 15244925
    kortyleski
    Level 43  
    Posts: 12265
    Help: 957
    Rate: 3860
    However, it seems to me that such charges are perfectly normal. Hot water for washing, laundry. These few other appliances also draw some electricity. However, you will probably have to grit your teeth and pay....
  • Helpful post

    Check lighting, occasional loads, and meter leakage

    #16 15246577
    Maciej1387
    Level 15  
    Posts: 83
    Help: 9
    Rate: 25
    Dal me also with such appliances (heater 5.5kW, stove 2kW, 2 refrigerators, 2 TVs) this bill is not particularly striking. 250 zł per month is achievable, Just as the colleague above wrote, it is enough that there will be 2 more laundry done and already a dozen kWh will fly.
    What does not mean that you should not do anything to find savings. Such a wattmeter can give a picture of the power consumption of individual appliances, but one should bear in mind its rather debatable accuracy, and it will certainly not be a tool for any complaint.
    For my part, I can recommend taking a look at the lighting if "ordinary" incandescent bulbs are used in places where the light shines for a relatively long time (rooms, corridor). Such an incandescent bulb of, say, 60W in an hour will consume as much electricity as an LED of ~5-6 W (giving a similar amount of light) in 6 hours. You can already hit good LEDs at a price of PLN 10-20 so the tragedy is not and will pay for itself, depending on the lighting time, in about six months.
    Other than that, I turn my attention to devices used "occasionally". : hair dryer ~1kW , iron ~2kW, etc. also consume electricity and can affect a large fluctuation of bills in the month-to-month comparison.
    Checking the operation of the meter by disconnecting all devices from the electricity will allow to preliminarily exclude problems with escaping current into the wall through the "nail in the picture", after all, it is enough that such a nail touches only the phase conductor in the cable and does not have to cause tripping of the fuse, and the current will flow through the wall.
  • #17 15246792
    marcin55246
    Level 25  
    Posts: 918
    Help: 53
    Rate: 168
    At our place the old polar fridge(from 97) was causing bills for 350-400zl(~500kWh), after replacing it with a new one they dropped to 230-190zl(~270kWh). On the wattmeter it showed an intake of about 2kw/24h. The installation in the house, an old aluminum, two-wire system, saw the electrician in 1939, when it was put in place while it was still under the Germans.
  • #18 15246850
    omnibus111
    Level 15  
    Posts: 76
    Help: 11
    Rate: 46
    Returning to the subject of the above-mentioned meter , I use a similar one, for example, to check the washing machine for the efficiency (condition) of components during normal operation. Observing its indications, I can determine the damage, without dismantling the housing. Sometimes I prove to unbelievers that what is written on the plate describing the equipment is not quite true.
  • #19 15247064
    Anonymous
    Anonymous  
  • Test household consumption by monitoring the meter with everything unplugged

    #20 15248788
    vodiczka
    Level 43  
    Posts: 30276
    Help: 1185
    Rate: 4311
    justykacz wrote:
    For two months.
    With a fair amount of hot water consumption, this is almost a normal bill. Did the bills increase by leaps and bounds after the installation of the water heater or "for no reason" What is the difference between the bill from last year and now - for the same months.
    justykacz wrote:
    The problem is with this refrigerator, its not possible to unplug, because it will defrost
    Don't joke, You unplug EVERYTHING for 10 minutes and during that time watch if the LED in the meter blinks, if it blinks then every how many minutes or seconds. Give the result of the counter self-test :) .
  • #21 15248890
    djlukas
    Level 27  
    Posts: 1606
    Help: 94
    Rate: 266
    I for a family of four pay 220zł a month each. Wife is not working now so she is using appliances since morning. At my place, half of the bill is charged tv plasma 600W +ampli ~100W for a total of 700W about 8 g a day.
  • #22 15249662
    mychaj
    Level 35  
    Posts: 4742
    Help: 214
    Rate: 941
    A family of 4, gas water, about PLN130/month, PLN250 with an electric (5 people) heater does not seem much....
  • #23 15251155
    marcin55246
    Level 25  
    Posts: 918
    Help: 53
    Rate: 168
    Małolepszy wrote:
    But for what period?

    Some years, about 5-6 years from July (after replacement) the invoice is at 200PLN.
    Małolepszy wrote:
    On the new or old refrigerator?
    On the old one.
  • #24 15283278
    justykacz
    Level 14  
    Posts: 195
    Rate: 25
    Colleagues and friends!

    I give the results so far of playing with the wattmeter (I am in love with this device):

    grandma's TV including antenna - 40-50W
    our TV - 40W
    laptop 1 and 2 - about 30-35W (per head)
    microwave - 1050W
    bathroom stove - 1840W
    hair dryer - from 200W to 800W
    old oven - 2200W (he is not used at all, 1995 vintage out of curiosity I turned on)

    and queen - prehistoric refrigerator :) - 100-120W

    baby refrigerator this new, it didn't even start the meter, only when I opened it then 14W, I suspect she "freezes" every so often...

    sometimes in the outlet I have 217V ....
  • #25 15283547
    haneb
    Level 24  
    Posts: 657
    Help: 61
    Rate: 214
    Refrigerators had to be measured how much they consume in 24 hours because they cycle on.
    I have an old Polar that consumes 1kWh/day.
  • #26 15283588
    Anonymous
    Anonymous  
  • #27 15283865
    lukiiiii
    Level 29  
    Posts: 1468
    Help: 82
    Rate: 392
    At my place, an old refrigerator of Lithuanian origin once consumed 1.1 kWh per day. Refrigerators work in cycles, breaks between cycles last about 45min-1 hour.
  • #28 15284523
    Darom
    Electrician specialist
    Posts: 2779
    Help: 231
    Rate: 588
    Hello

    In the case of refrigerators, we do not measure its instantaneous power (what it draws at a given time), because it does not make sense.
    My recently purchased Samsung sometimes draws 0W, other times 15W, sometimes 40W, but once I caught it drawing 160W.

    By the way, taking advantage of the fact that some colleagues are confused by the units, I would like to remind you that power (that is, the rate at which energy is drawn) is measured in watts (W) or kilowatts (kW).

    The energy consumed is measured in kilowatt-hours (kWh). My refrigerator on a daily cycle consumes less than 0.6 kWh. In a monthly cycle it will be less than 20kWh.

    Large energy consumption of old refrigerators can have a trivial cause, such as damage to the door seal, through which warm air gets inside.

    sage
    -DAREK-.
  • Helpful post

    Smaller refrigerator matched old unit’s energy consumption

    #29 15467643
    kruskal
    Level 14  
    Posts: 81
    Help: 10
    Rate: 10
    Hello
    I did an experiment with a refrigerator that had been working without failure for more than 42 years. After transferring the contents to a smaller refrigerator (a small one with a capacity of about 1/3 of the old one), the energy consumption was almost identical and was about 0.4kwh for about 9 hours. The small refrigerator, which was several years old, consumed the same amount of energy because its unit turned on noticeably more often. In addition, it worked a little louder. I made the comparison over a period of hot weather over a week. I read the energy consumption from the meter for billing.

    The energy consumption stated in the post is entirely possible.
    Greetings
  • #30 15677440
    justykacz
    Level 14  
    Posts: 195
    Rate: 25
    Yes, I know dear ones that I should keep this old refrigerator for 24 hours, maybe someday :) Nevertheless, now that we have replaced the bulbs with LED ones, and some individuals including me do not run off to the purifier while washing ourselves the bills are much lower, they have gone below 300zł. Now it's 340zl, but that's during the period when the wood saw was on the go and the lawnmowers plus all the stuff titled "We're cleaning up for the summer," however, it's still perfect compared to the old days.
  • Topic summary

    LABEL_AI_GENERATED
    The discussion revolves around a user's concern about high electricity bills attributed to an old refrigerator, which is 40 years old. The user suspects various causes for the high consumption, including a faulty meter, outdated electrical installation, and the refrigerator itself. Several participants suggest using a wattmeter to measure the refrigerator's energy consumption, with discussions on its functionality and whether it can measure single tariff usage. The conversation also touches on the impact of other appliances, such as a 5.5 kW flow heater, and the importance of checking for issues like door seal damage in refrigerators. Users share personal experiences with energy consumption and suggest that replacing old appliances can lead to significant savings on electricity bills.