Running 12V from Switchboard to LED Strips: Distance and Switch Compatibility
wecia91 13224 28
Can I power LED strips at 12V from a switchboard over several meters through wall switches, and are ordinary light switches suitable for that?
Do not run the 12V feed from the switchboard through long wall-switch circuits as the main solution; the lower voltage means higher current, so you must expect voltage drop and larger cable cross-sections [#15579276] If the power supplies must stay in the switchboard, a better approach is to switch the 230V primary side with the wall switches or use a relay/controller rated for the load, rather than putting ordinary switches directly in the 12V secondary circuit [#15575690][#15576590][#15580099] Exact strip type and wattage matter, because the installation could be around 96W for 20 m of 5050 white strip at 4.8 W/m or 288W for RGB at 14.4 W/m, and that changes the required supply and wiring [#15580376] One reply also notes that some switching power supplies do not like having no load on the secondary side, which is another reason not to assume a 12V-side switching scheme will always work [#15579276] For this kind of setup, 24V strips with DIN-rail PSUs were suggested to reduce voltage-drop problems and heating [#15580376]
  • Checking 12 V voltage drop and switch compatibility
    #1 15575665
    wecia91
    Rate: 228
    Hello, I am preparing an electrical installation to connect LED strips in two suspended ceilings in the living room and kitchen. The suspended ceiling contractor noted that there would be no place to hide the power supplies under the ceilings. I thought that I would install one power supply common for two ceilings in the switchboard. I have about 5 m to the first switch and from it about 3 m to the ceiling, the distance to the second switch is 9 m and to the ceiling 3 m. Will I light up the LED strips on the ceilings by running 12v from the switchboard through two circuits to the switches? Can I use traditional light switches for this?
  • #2 15575690
    piotrek22101
    Help: 695
    Rate: 1421
    Hello. Will the power supplies be constantly under voltage? It should not be like that. The switch in each room should switch on the voltage to the power supply, 12V from the power supply directly to the LEDs.
  • #3 15576590
    kasprzyk
    Electrician specialist
    Help: 354
    Rate: 671
    How powerful will these LEDs be?
    As my friend writes, you should interrupt the primary 230V side of the power supply with the switch, not the secondary side.
  • Ventilate 100 W supplies and account for voltage drop
    #4 15576821
    polaklbn
    Help: 55
    Rate: 162
    The layout is very simple.
    We don`t know what power the power supplies will have, but you must remember that they will emit heat, so they must be placed in a well-ventilated place.
    Assuming that there will be illuminated structures on the ceilings, there will most likely be two 100W power supplies.
    When it comes to connection, you should control the power supply through the connector so that it is not constantly powered.
    Additionally, you must remember about the voltage drop in the case of a long connection between the power supply and the receiver.
  • #5 15577761
    e-sparks
    Help: 77
    Rate: 216
    kasprzyk wrote:
    you should interrupt the primary side of the 230V power supply with the switch, not the secondary side.
    Complete nonsense, it`s as if you ordered the transformer powering the estate to be turned off on the primary side in order to turn off the lights.
  • Switch the 230 V primary and specify strip wattage
    #6 15577863
    kasprzyk
    Help: 354
    Rate: 671
    wow! e-sparks You, my mentor, can make an accurate comparison - bravo, you ;)
    wecia91 - I ask again, what strength do you have these sections of tape?
  • #7 15577878
    e-sparks
    Help: 77
    Rate: 216
    kasprzyk wrote:
    Bravo, you
    Thank you :oops:
  • #8 15577944
    Zbigniew 400
    Help: 283
    Rate: 794
    In the case of switching power supplies, it is even more advantageous to switch on the voltage of 12V.
  • Switching 12 V avoids burned 230 V switch contacts
    #9 15578096
    kasprzyk
    Help: 354
    Rate: 671
    Great, what switches does your friend recommend? - let`s assume a 200W LED strip, for a living room it`s not much, the topic here concerns the bathroom: https://www.elektroda.pl/rtvforum/topic3186142.html maybe your friend can advise what to do with burning contacts of the switch on the 230V side, will it be better on 12?
  • #10 15578199
    Zbigniew 400
    Help: 283
    Rate: 794
    Dear Colleague. Contact strength you recommend when turning on the switching power supply
    200W /capacitive load/ ?
  • #11 15578205
    kasprzyk
    Help: 354
    Rate: 671
    I asked you and ?
  • #12 15578208
    Zbigniew 400
    Help: 283
    Rate: 794
    A good relay solves the problem.
    Added after 1 [minute]:
    Possibly IGBT.
  • #13 15578259
    kasprzyk
    Help: 354
    Rate: 671
    So we come back to the question of what the power of the tapes used will be. By nature, the lighting of the living room or kitchen is not 5W tape sections, even if it is not the primary light source.
    I suggest waiting behind the interested person.
  • #14 15578281
    CYRUS2
    Help: 1241
    Rate: 3535
    Let your friend justify it.
    The computer is not turned off on the primary side
    The TV is not turned off on the primary side.
  • #15 15578316
    Łukasz-O
    Admin of electroenergetics
    Help: 654
    Rate: 4292
    That`s right, but the computer and TV are not part of the installation.
  • #16 15578456
    retrofood
    Help: 1140
    Rate: 4798
    kasprzyk wrote:
    So we come back to the question of what will be the power of the tapes used,
    It`s written. 200W.
    But they don`t have circuit breakers.
  • Primary-side switching causes relay and switch failures
    #17 15578662
    Zbigniew 400
    Help: 283
    Rate: 794
    What do the regulations say about switching on power supplies for light sources at home?
    Switching on switching power supplies on the primary side (surge current, capacity) with ordinary switches does not improve durability.
    I have a case of switching on a switching power supply for LED /2m/, 5W. The switch and relay in the occupancy sensor need to be replaced regularly.
    Turning on the fluorescent lamp (2 x 36W) with an RM 84/16A relay for resistance exhausted him within a month. Only replacing it with R15 solved the problem.
    CYRUS2 wrote:
    "retrofood"
    It`s written. 200W.
    But they have stand-by switches, but they are not used. Too frequent use wears them down.
  • #18 15578774
    CYRUS2
    Help: 1241
    Rate: 3535
    Such an installation is a SELV installation.
    Show the regulation requiring the installation of a switch for the SELV source.
    They have dedicated circuits separate circuit breakers . There is no dedicated circuit here.
    Still no one has provided a regulation or technical justification for the need for a switch on the 230V side.
  • Questions 230 V switching requirement for a 200 W load
    #19 15578878
    retrofood
    Help: 1140
    Rate: 4798
    Do not mix. My post referred to the computer and TV.
    Calculate the current at a power of 200W.
  • Separate switches and transistor control for 12V LED loads
    #20 15578902
    Zbigniew 400
    Help: 283
    Rate: 794
    Dear moderator.
    Who at home powers a 200W LED from one switch.
    If we have divided circuits, either separate power supplies or switches in the 12V circuit.
    Turning on the capacitive load is not conducive to durability, at high currents you can use transistors (in a 12V circuit).
    In my house, a 5 x 5W chandelier
    Single lamps up to 12W.
    LED strip 5m, approx. 15W.
    Each circuit has a separate switch.
  • #21 15578966
    retrofood
    Help: 1140
    Rate: 4798
    Zbigniew 400 wrote:
    Dear moderator.
    And who wrote in the first post:
    I feel like it`s not me.
    Especially since my discussion with Col. CYRUS2 concerns a slightly different issue.
  • Clarifying whether to switch 230V input or 12V output under regulations
    #22 15578978
    Zbigniew 400
    Help: 283
    Rate: 794
    That is, two ceilings and two switches in a 12V circuit.
    But there is still no answer to the question whether the power supply should be turned off at 230V or whether the power supply can be turned off in the 12V circuit. What the regulations say.
    In the case of a smart home, the relays turn on the load on the contacts (voltage before or after the power supply) and the switches give a logical signal, not at the 230V level.
  • Low-voltage switching requires larger cables and load-compatible supplies
    #23 15579276
    ArturAVS
    Moderator
    Help: 2303
    Rate: 7832
    Zbigniew 400 wrote:
    But there is still no answer to the question whether the power supply should be turned off at 230V or whether the power supply should be turned off in the 12V circuit.
    Technically, it doesn`t matter. However, there are power supplies (converters) that cannot work without a load on the secondary side. This disqualifies them from being used when the connector is on the secondary side.
    Second thing; as we know, for the same power, higher currents flow in circuits with lower voltage. When installing the power supply in a switchboard, this means the need to use larger cable cross-sections.
    Zbigniew 400 wrote:
    In the case of a smart home, the relays turn on the load on the contacts /voltage before or after the power supply/ and the switches give a logical signal, not at the 230V level
    Not necessarily.
  • One PSU for three separately switched LED strip runs
    #24 15579518
    wecia91
    Rate: 228
    Hello friends, I`m sorry I didn`t respond earlier, but I had a sudden, urgent trip and no Internet access. I`m giving you some data, so on the living room ceiling there are about 15-20 mb of tape, on the living room wall 15 mb and on the kitchen ceiling 10 mb of tape, unfortunately I don`t know what type of LED and how many watts (the forum is Polish-language, so the measurements are too). I was thinking about using one power supply in the switchboard and there will be two switches, one in the kitchen and one two-key switch in the living room, to switch on the ceiling and wall separately. Switches from the Opel frame system. That`s all I know at the moment. Can I do this or do I have to control the switches of 3 independent power supplies in the switchboard?
  • #25 15579811
    Zbigniew 400
    Help: 283
    Rate: 794
    Maybe someone with theoretical and practical knowledge will compare the durability of a flush-mounted switch
    230V/10A when switching on a 60W switching power supply on the primary and secondary sides?
  • Use inrush-rated relay contacts for 60W power-supply switching
    #26 15580099
    CYRUS2
    Help: 1241
    Rate: 3535
    Correct.
    This question is only for the manufacturer - the power supply and the switch.
    It`s not as simple as you think.
    The 12V power supply behaves "nasty" when connected to 230V. .
    There are Inrush relays with contacts specifically for higher switching currents.
  • Choose 24 V strips and DIN-rail Mean Well supplies
    #27 15580376
    kasprzyk
    Help: 354
    Rate: 671
    Buddy, you need to know exactly what the target strips will be, this is the basis for properly preparing the installation for this lighting. Currently, white 5050 LEDs are often installed, approximately 4.8W/1m = 96W at 20 meters. It is also possible that the customer will want RGB strips, for the same section it will be 14.4W x20 = 288W. However, in this situation there will be a different connection method - the power supply/power supplies will be permanently connected to 230V, the controller will be responsible for on/off, dimming, etc. .so there will be no problem with the life of the switches discussed here.
    Personally, when power supplies must be placed in the switchboard, I use 24V tapes, and Meanwell din rail power supplies with the possibility of adjusting the output voltage. I try to minimize the possibility of subsequent problems with voltage drops, uniform light distribution, and heating of the tape elements (appropriate number of connection points for longer sections)
    Most manufacturers, e.g. of twilight/motion sensors, specify the maximum contact load, here is an example:
    and they certainly inform whether LED sources can be connected.
    http://www.fif.com.pl/pub/File/download/INSTR...0ruchu/elFF%20DR-04%20inst%20D141120%20PL.pdf
    I am curious whether the parameters shown above are also available in the descriptions of electrical equipment manufacturers.
  • #28 15580424
    Zbigniew 400
    Help: 283
    Rate: 794
    This 150W is theoretical, powering the 20W power supply from the detector results in sticking of the contacts in the detector after 2 years. I always use an intermediate relay /R 15/.
  • #29 15580479
    kasprzyk
    Help: 354
    Rate: 671
    You may be right, but on the other hand, what is wrong is that they provide values that have nothing to do with reality - on the discussed detector I have about 60W of "mesh" on the LEDs - I prefer to play it safe, so I limited it to a level below half the power they declare - in this case At the moment it works for about a year.
The discussion revolves around the installation of LED strips powered by a single 12V power supply located in a switchboard, with concerns about the distance to the switches and compatibility with traditional light switches. Participants emphasize the importance of switching the primary side of the power supply rather than the secondary side to avoid issues with inrush current and contact wear. They highlight the need to consider the power rating of the LED strips, potential voltage drop over long distances, and the necessity of using appropriately rated switches or relays to ensure durability. The conversation also touches on the advantages of using 24V systems and specific brands like Meanwell for power supplies, as well as the importance of proper installation practices to mitigate heating and ensure uniform light distribution.
TL;DR: A 200 W 12 V strip draws about 16.7 A, so 1 mm² wire over 9 m will drop ~0.3 V (2.5 %) [IEC 60228]. "Switch on the voltage of 12 V" [Elektroda, Zbigniew 400, post #15577944] Size cables and pick the correct side to switch. Why it matters: Correct design prevents dim LEDs, welded contacts and fire-risk downtime.
• Max voltage drop for LED strips: ≤0.6 V (5 %) at 12 V [LightingEurope, 2020] • 5050 60 LED/m white strip load: 4.8 W / m [Datasheet, 2023] • Inrush current of a 200 W SMPS: up to 40 A for 1 ms [Mean Well, 2021] • 1 mm² Cu conductor resistance: 0.018 Ω / m [IEC 60228] • Typical 10 A AC switch is rated ≤3 A DC continuous [Schneider, 2022]
Can I feed two ceilings from one 12 V power supply located in the switchboard?
Yes, if the supply can cover the total wattage and cables meet voltage-drop limits. For 40 m of 4.8 W/m tape you need ≈192 W and 16 A. Use ≥2×2.5 mm² to keep drop below 5 % over 9 m [IEC 60228].
What cable cross-section should I run for 12 V at 15–17 A?
A 2.5 mm² twin cable gives 0.007 Ω/m. Over 9 m the round-trip resistance is 0.126 Ω, causing 2.1 V drop at 17 A—too high. Double up or step to 4 mm² to halve the loss [IEC 60228].
Should the wall switch break 230 V or 12 V?
Break the 12 V side when current is ≤10 A. High inrush on 230 V SMPS (up to 40 A) erodes contacts [Mean Well, 2021]. Forum users report longer switch life on the secondary side [Elektroda, kasprzyk, post #15578096]
Are standard household switches safe on 12 V DC?
Only if their DC rating covers your current. A 10 A AC switch often carries just 3 A DC continuously [Schneider, 2022]. Exceeding this risks contact welding [Elektroda, Zbigniew 400, post #15578662]
How much voltage drop can LED strips tolerate?
Keep total drop under 0.6 V (≈5 %) to avoid visible dimming [LightingEurope, 2020]. Split long runs every 5 m or feed both ends to stay within limit.
What happens if an SMPS runs with no load?
Some converters need a minimum load; without it they hunt and overheat. Check datasheet—many budget 12 V/100 W units specify ≥10 % load [Mean Well, 2021].
Is using several smaller supplies better than one large unit?
Multiple supplies reduce wire size and segment failures. Three 75 W units near each ceiling cut cable current and voltage drop by two-thirds [IEC 60228]. However, cost and maintenance rise.
How do I calculate total power for my strips?
  1. Measure length in metres.
  2. Multiply by strip wattage per metre (e.g., 4.8 W).
  3. Add 20 % headroom. Example: 25 m × 4.8 W = 120 W; choose ≥150 W supply.
What is inrush current and why worry?
When you energise a 200 W SMPS, capacitors draw up to 40 A for 1 ms [Mean Well, 2021]. Small switches or relays can pit or weld—edge case: occupancy sensor relay failed in one month [Elektroda, Zbigniew 400, post #15578662]
Why did my wall switch weld closed after a year?
Capacitive inrush from the PSU exceeded its DC rating. "Turning on the capacitive load is not conducive to durability" [Elektroda, Zbigniew 400, post #15578902] Upgrade to an inrush-rated relay or SSR.
Is a dedicated SELV switch required by regulation?
No EU or PL regulation mandates a switch on the SELV side, but designers add one for maintenance and energy savings [Elektroda, CYRUS2, post #15578774]
How to mount the power supply safely in the switchboard?
  1. Leave ≥30 mm clearance above DIN PSU for airflow.
  2. Earth the metal case and provide 6 A MCB protection.
  3. Label the SELV outputs clearly. These steps meet IEC 62368 heat and segregation rules [IEC 62368].