Connecting the inverter to the network / selecting the cable type.
Szczurek.1891 34611 11
Can I use 3x6 mm² cable instead of 10 AWG/10 mm² for a 20 m single-phase connection between my 4.5 kW inverter and the meter/house without overheating?
Yes, 3x6 mm² cable is enough for this setup, and 10 mm² is likely overkill and more expensive [#16207572][#16209521][#16208336] For a 4.5 kW inverter on a single-phase installation with 6 kW allocation, one reply says a 6 mm² cable will go 30 m calmly without heating [#16209521] Another calculation for 40 m total suggests about 2.6% voltage drop on 6 mm² versus 1.6% on 10 mm², so 10 mm² only reduces losses if you want extra margin [#16208504] The general recommendation in the thread is to use 3x6 mm² 450/750 V if you want the cheaper, easier-to-lay option [#16207572]
  • #1 16207495
    Szczurek.1891
    Rate: 8
    I almost started my PV installation but I have some concerns about the cable connecting the inverter with the meter. Currently, the cable is 2.5mm.
    The instruction recommends 10 AWG which translates into a 5.3 mm2 cable round it to 6mm2.
    I have to route two wires. From the meter to the inverter and from the inverter to power the house. connection also at the place of the meter.
    I wanted to give 5x6mm2 one wire. Two wires from the meter and two to power the house. I'm afraid of overheating the cable and hence greater failure rate.
    So I put on two separate wires. One from the meter to the inverter and the other from the inverter to power the house and I have the choice:
    YDYp 3x6mm2 450 / 750V cable
    or
    YLY cable 3x6mm2 0.6 / 1kV
    I will add that sometimes I download from the network about 4.5-5.5kW 2.5kW 2kW kettle and the rest of the house 1kW.
    The wire speaks because it is cheaper and easier to lay. The cable is stable. In this case, I focus only on the experience of colleagues.
  • #2 16207572
    Tech132
    Help: 97
    Rate: 392
    Give 3x6mm2 450 / 750V for sure enough.
  • #3 16207634
    Szczurek.1891
    Rate: 8
    I am just afraid that it will not overheat because I forgot to add that the distance between the inverter and the meter is 20 meters.
  • #4 16207647
    Tech132
    Help: 97
    Rate: 392
    What power allocation do you have and what inverter power?
  • #5 16207717
    Szczurek.1891
    Rate: 8
    Single-phase installation and power allocation from ZE is 6kW. 4.5kW inverter.
  • #6 16207728
    Tech132
    Help: 97
    Rate: 392
    All you need is a cable with such power.
  • #7 16207964
    3301
    Help: 224
    Rate: 869
    You have a total of 40mb and the voltage drop will be around 2% and it is 4.6V, admittedly such a drop is permissible, but to reduce losses I would use a cross-section of 10 because who knows, maybe you will add panels.
  • #8 16208336
    Tech132
    Help: 97
    Rate: 392
    Let's not exaggerate 10mm2 is an exaggeration over a distance of 20m, why cost it.
  • #9 16208504
    rafbid
    Help: 153
    Rate: 418
    At 40mb and 10mm2 the voltage drop will be 1.6% or 3.68 V
    at 6mm2 the voltage drop will be 2.6% or 5.98 V
    We do not know, for example, the rigidity of the network.
  • #10 16208663
    Szczurek.1891
    Rate: 8
    In fact, the distance to small does not belong. Of course, I'm still trying to break it off. Giving a 6mm2 wire spectrum wire that it will be more convenient to lay than 10mm2 the more that I have to give two. There is also a visual difference. 10mm2 is already a big diameter.
    prose
    Level 36  
    Help: 173
    Rate: 850
    I have 4 mm? phase and Pv power for 1 phase 3 kw is enough and 4.5 kW to the meter will calmly go 30 m and nothing is heating, convert to 5 A 1 mm?. If you give 6 mm? it will be with a higher and thicker don't waste money.
  • #12 16210783
    Szczurek.1891
    Rate: 8
    Thank you for clarification and help. I preferred to consult with colleagues more familiar with the topic than to test myself. It is also not an art to advise on minimum or maximum parameters and cost cutting. Or in the worst case, drown the money and in a month do everything again. Thanks again to everyone for their comments.
The discussion revolves around selecting the appropriate cable type for connecting a photovoltaic (PV) inverter to the meter, with concerns about overheating and voltage drop over a distance of 20 meters. The user initially considers using a 2.5mm cable but is advised to use a 3x6mm2 cable rated for 450/750V or 0.6/1kV. The power allocation is 6kW with a 4.5kW inverter, and various responses suggest that a 6mm2 cable is sufficient, although some recommend a larger 10mm2 cable to minimize voltage drop, especially if additional panels are added in the future. The user expresses a preference for the 6mm2 cable due to ease of installation and cost considerations, while also acknowledging the importance of consulting knowledgeable colleagues before making a final decision.