Cable length and cross-section as well as selection of the inverter
sethir 55857 16
How should I choose the DC and AC cable cross-sections and inverter power for a 30 m ground-mounted PV run, and should the inverter be placed near the panels or the switchboard?
Put the inverter as close to the panels and the power supply as possible, and run the AC side to the switchboard instead of making the DC run unnecessarily long [#18073586] For the DC cable, the key issue is voltage drop; one reply suggests that 4 mm² or 6 mm² only changes the drop, while another calculated that for about 50 m at 20 A a 10 mm² Cu cable still gives more than 1.2% drop, and about 1% would require 16 mm² Cu [#18079589] [#18074532] Another calculation for your setup gave about 0.84% drop for the 4.6 kW inverter option and 0.67% for the 3.68 kW option, so the lower-power inverter eases the voltage-drop requirement [#18079542] Also check the module temperature coefficient and size the inverter for the worst-case open-circuit voltage at low temperature; one reply warned that 16 modules can reach 649.6 V at STC and even around 736 V at -25 °C, so the inverter input rating must cover that [#18073451] [#18073586] One suggestion was to use buried aluminum YAKY 4×16 mm² for the DC side and YAKY 5×16 mm² for the AC side if you want a robust, low-drop solution [#18071483]
  • #1 18070853
    sethir
    Rate: 21
    Conditions:
    - 30 meters from the table to the inverter - it will be routed in the ground, I want to put it in a 75mm corrugated pipe so that in the future, when expanding, I can pull an additional pair of cables.
    - 4mm? cable on modules - 16 modules contain a total of 38.4 meters of cable (2 × 1.2m per module according to the specification for the LR6-60HPH-315M module was supposed to be 2 × 0.3m)
    - 22 meters extra cable for leveling loops on the table etc.
    The above gives a total of 90.4 meters of solar cable, does it make sense to run the cable from the table to the inverter with a cross-section of 6mm? if the modules are connected with a 4mm? cable.
    A single-phase inverter will have 4.6 kW, which gives 20A (ENERGA should accept such inverters until October 14, 2019), the length of connection to the main switchboard is 20 meters. Is a wire with a cross-section of 4 mm2 (YDY 5 × 4 mm? sufficient) sufficient ;) or maybe 6 mm? ultimately from this line will also power the PHEV car charger.
    Is it better to use a 3.68 kW inverter with a generator power of 5040 W (16x315W) (oversizing approximately 33% and it will be easier to modernize the installation after October 15, 2019), or install 4.6 kW (oversizing approximately 6.5%)
    Thank you for the advice and best regards
  • #2 18071483
    ACCel
    Help: 24
    Rate: 217
    Want to bury your solar cable?
    After all, the most sensible is the aluminum YAKY 4 × 16mm?, even for DC. Unless you are over 600V.
    An earth cable in the ground (without a conduit) has better conditions than in a conduit. Of course, you can bury the Pechel just in case.
    On the AC side, the same aluminum YAKY 5 × 16mm?.
  • #3 18073451
    sethir
    Rate: 21
    Well, taking into account the Open Circuit Voltage = 40.6 V at STC conditions for 16 modules, I will have 649.6 V and the logic dictates that it should always be selected for the maximum possible conditions that arise. For NOCT at OCV I will have 606.40 V in the installation, and for maximum power from 497 to 539 V for STC, NOCT, respectively.
  • #4 18073586
    3301
    Help: 224
    Rate: 868
    You should also take into account the temperature coefficient (read from the catalog card) and count for the temperature of minus 25 degrees Celsius.
    for example for LR6-310 the coefficient equals (-0.286)
    and then at Uoc (-25) it will be 46V which at 16 mod. da 736V
    Added after 6 [minutes]:
    The inverter should be placed as close to the panels and the power supply as possible. AC lead.
  • #5 18074019
    sethir
    Rate: 21
    The fact, taking into account the temperature correction, these 736 can appear if it lights up well at -25C.
    The cable in this case at 50 meters is YKY 5 × 10mm? so that the drop is ~ 0.8%, or let go 20 meters to the place where the 5 × 10mm? inverter was planned and to the table of 30 meters 5 × 6mm?.
    How is the inverter secured against theft, e.g. by Fronius?
    I have a fenced area, the installation site will be monitored, but it can be different and I would not like to see an empty base in the morning.
  • #6 18074192
    ACCel
    Help: 24
    Rate: 217
    Copper YKY is several times more expensive than the aluminum YAKY 16mm?. Why overpay?
    You can try to secure the inverter with shear nuts.
  • #7 18074532
    3301
    Help: 224
    Rate: 868
    The cable in this case at 50 meters is YKY 5x10mm? so that the drop is less ~ 0.8%, or let go 20 meters to the place where the 5 × 10mm? inverter was planned and to the table of 30 meters 5 × 6mm?.
    At 20A, 50m, and a Cu conductor of 10mm?, the drop will be more than 1.2% as you want Mon. 1% is a Cu 16 wire.
  • #8 18079542
    sethir
    Rate: 21
    Generally, you should not create loops and some manufacturers recommend that you lay DC cables in their module installation instructions so that you do not create these induction loops. However, in the case of Longi Solar LR6-60HPH, I see in the manual that the recommended module connection creates a clear loop. This is how it is with these loops. Below is an excerpt about connections.
    Originally, I planned to pull the DC cables like this:
    And now, when I read the module manual, I don't know whether or not to eliminate this loop.
    However, I will go in the direction of: 30 m AROT 50mm + DC cables 4mm or 6mm2 (I wonder here again) and from the inverter to the 27m YDYp 5x10mm? switchgear. For 4.6 kW I have a decrease of 0.84% and for 3.68 kW 0.67%. I cling to these drops because I read somewhere that it should not be higher than 0.8%.
    I have to put a hoop in the 80 cm trench. Will this order of layering be OK: 10 cm of sand, 120mm? hoop, 10cm of sand, AROT with DC cables, 10 cm of soil, blue foil and earth?
    Are there to be two overvoltage limiters for installation on the ground with a length of 30m of DC cable from the table to the inverter? DEHN clearly indicates that if L> 10m then yes. The question arises from the information obtained from one of the installers that if the DC installation is not carried out in the building, it does not have to be two.
  • #9 18079589
    ACCel
    Help: 24
    Rate: 217
    4mm or 6mm is just a matter of voltage drop.
    YDYp are you sure? This is the wire in. Did you mean YKY?
    If you like to pay for 5x10mm? copper, who will forbid the rich? :D
    0.87% of 4.6 kW is about PLN 20 of energy per year ;)
    I would not put coats in the sand, after all, it is supposed to conduct the best to the ground.
  • #10 18079638
    PV_Albert
    Help: 11
    Rate: 117
    An interesting topic, because in the near future I will also be laying a cable for PV installations with a similar DC voltage.
    Is it not possible to lay two aluminum cables (to the ground) 2x16mm? (if they are at a good price), one for plus and one for minus?
    How will it cost you?
    It is worth making (anti) induction loops. It is true that it is hard to prove that it is worth it, but recently I experienced a discharge close to home, possibly direct because the bang was huge.
    Almost everything connected to the AC fell down. Only the fridge and the Wi-Fi router somehow survived.
    Of course, AC overvoltage protection with good grounding is done.
    On the roof of PV but disconnected inverter from AC and DC before storm.
    An anti-induction loop on the PV installation. I will not find out if this secured the panels.
  • #11 18079678
    sethir
    Rate: 21
    YDYp will be in the building from the inverter to the switching station, ultimately it will fly under the plaster and therefore it should be flat.
    In addition, I will add YKY to the table, but it will be either YKY 5x6 or 3x10, generally only to distribute power to the plot from there in the future.
    It is not about the volume of energy lost on the decline, but about the correct operation of the inverter, and more precisely its protections. I cannot locate it now, but I think Fronius confirmed on his forum that the voltage drop for proper functioning should not be greater than 0.8%.
    Why do I do the installation myself:
    - because when I asked the installers, I had to pay for the assembly on the ground and the connection to the building was to be organized by myself - and unfortunately they wanted a lot of money for this assembly
    - because there were proposals that a distance of 30 meters from the inverter to the table would suffice with one overvoltage limiter
    - because they did not have a 20x0 credit - I was able to buy the main components in the 20x0% system, i.e. the money I had to spend immediately remained in my pocket and I will be able to reinvest it
    - unfortunately, but no installer has checked what he will have to connect to - installation from the 70s, aluminum, burnt - this is the professional approach of PV installers
    - as I saw in my friends, connecting a 4.6 kW inverter in single phase to a 1.5mm? cable, sometimes 2.5mm? and a distance of 15 meters to the switchboard after the installation of powering sockets or lighting
    I have an electrician friend, but he made it clear to me that he doesn't have much free time and that PV is not his horse. I am also not surprised by the brigade entering the apartment building and after a month he charges n-thousand zlotys for the installation. But for example, ZK did me along with the removal of the measuring system, and I handle the rest as an electronics technician myself.
    Added after 3 [hours] 37 [minutes]:
    @PV_Albert it's more about the voltage that the cable insulation can withstand. The YAKY is 600V, so if you don't exceed it, it'll be OK. At my STC, I can achieve 649.60 Voc on 16 modules.
    If you parallelize the YAKY wires, more current will be able to flow and lower voltage drop will be achieved.
  • #12 19044070
    Radekkomis81
    Rate: 45
    <I have a question I'm about to decide which cable to supply to a 10kW inverter a ground mounted modular installation 120mb away from the switchgear
    please help
  • #13 19044453
    theo33
    Help: 78
    Rate: 321
    The voltage drop for Cu with a cross-section of 16 mm? is 0.82%
    or for Al 25mm it is 0.89%.
  • #14 19750740
    Stanlejoss
    Isn't it better to lay the solar cable in the ground and have a 0.5-1% drop on the DC side than have such a drop on the AC side?
    If the AC cable was laid in the ground, then such a drop on the AC side in the case of high density of the installation in the area, the voltage is reduced by 2V. In this case, is it not better to lay the DC cable in the ground and get as close as possible to the main switchboard?
  • #15 20157101
    Robinson74
    Rate: 159
    Stanlejoss wrote:
    In this case, is it not better to lay the DC cable in the ground and get as close to the main switchboard as possible?
    It is a pity that to this day no one has answered this question.
    I would also like to know if it is possible to drag DC cables in the ground from the panels to the house, over a length of several dozen meters.
    Studio Języka Angielskiego
    Piastowska 18, Krosno, 38-400
  • #16 20171470
    Stanlejoss
    Due to the lack of sufficient knowledge, I did what everyone says that it is better to pull AC than DC. Now I have contact with a technically well-versed electrician - if he gives a comprehensive answer, I will share it :)
✨ The discussion revolves around the optimal selection of cable length and cross-section for a solar installation, specifically addressing the connection from solar modules to an inverter located 30 meters away. Users debate the suitability of using 4mm² or 6mm² cables for both DC and AC connections, considering factors such as voltage drop, temperature coefficients, and the potential for future expansion. Recommendations include using aluminum YAKY cables for underground installation and ensuring that the inverter is placed close to the panels to minimize losses. The importance of adhering to voltage drop limits (ideally below 0.8%) for proper inverter operation is emphasized, along with considerations for securing the inverter against theft. The conversation also touches on the feasibility of burying DC cables and the implications of doing so on performance.
TL;DR: Plan for string Voc up to 736 V at −25°C; "The inverter should be placed as close to the panels and the power supply as possible." Keep DC short, target ≤1% voltage drop, and add DC SPDs if runs exceed 10 m. [Elektroda, 3301, post #18073586]
Why it matters: This FAQ helps DIYers and installers size cables, place inverters, and protect long PV runs to reduce trips, heat, and losses.
Should I run a long AC cable or a long DC cable from a ground‑mount to the house?
Keep DC runs short and place the inverter near the array and supply. Then run the longer AC feeder. "The inverter should be placed as close to the panels and the power supply as possible. AC lead." This reduces high‑voltage DC exposure and simplifies protection. [Elektroda, 3301, post #18073586]
What size AC cable for a 4.6 kW single‑phase inverter over about 50 m?
At about 20 A, a 50 m run in Cu 10 mm² drops more than 1.2%. Choose 16 mm² copper to hold near 1% drop. This supports proper inverter protection functions and limits nuisance trips. [Elektroda, 3301, post #18074532]
Is upgrading DC cable from 4 mm² to 6 mm² worth it?
Yes if you need lower voltage drop. Between 4 mm² and 6 mm², the only difference here is the drop. Upsizing helps on long strings or trench runs. It does not change module whip size limits. [Elektroda, ACCel, post #18079589]
Can I use aluminum YAKY on the DC side?
Yes, YAKY 4×16 mm² can be used on DC if your string voltage does not exceed about 600 V. Direct‑burial in soil offers better thermal conditions than conduit. If you prefer, bury a spare conduit for future pulls. [Elektroda, ACCel, post #18071483]
How high can my 16‑module string voltage go in cold weather?
Account for the temperature coefficient. Example: with −0.286%/°C, Voc at −25°C can reach about 736 V for 16 modules. Size the inverter and cable insulation accordingly to avoid over‑voltage. [Elektroda, 3301, post #18073586]
Is YDYp OK from inverter to an indoor switchboard, or should I use YKY?
Use YDYp indoors under plaster. For outdoor or underground runs, use YKY or another direct‑burial‑rated cable. "YDYp are you sure? This is the wire in. Did you mean YKY?" [Elektroda, ACCel, post #18079589]
Do I need corrugated conduit for underground PV cables?
Not strictly. Direct‑buried Earth cables have better thermal conditions than in corrugated conduit. You can bury a spare conduit as a contingency. This maintains cooling while preserving upgrade paths. [Elektroda, ACCel, post #18071483]
Do I really need two DC surge protectors for a 30 m string run?
Yes, install DC SPDs at both the array and inverter if the DC cable length exceeds about 10 m. This guidance is referenced from DEHN practice cited in the discussion. [Elektroda, sethir, post #18079542]
How should I route module leads to avoid induction loops?
Keep plus and minus close together and minimize loop area. Some manuals show loops; reduce exposed loops when possible. Manufacturers advise avoiding induction loops for better surge performance. [Elektroda, sethir, post #18079542]
How can I deter inverter theft on a ground‑mount?
Use shear nuts on mounting hardware to resist removal. Combine with fencing and monitoring for layered security. It’s a simple, low‑cost deterrent that installers commonly apply. [Elektroda, ACCel, post #18074192]
What feeder size works for ~10 kW when the inverter is ~120 m from the switchgear?
Approximate drops: Cu 16 mm² about 0.82%, Al 25 mm² about 0.89%. Select based on your drop target and budget. These values address long ground‑mount runs to the main board. [Elektroda, theo33, post #19044453]
Is paying for copper worth it given small voltage drops?
Not always. "0.87% of 4.6 kW is about PLN 20 of energy per year." Consider aluminum to save upfront cost. Invest savings in protection or monitoring if drop targets are still met. [Elektroda, ACCel, post #18079589]
Can I run DC cables in the ground for dozens of meters?
Yes, with appropriately rated cable and terminations. Direct‑buried aluminum YAKY is acceptable for DC if voltage rating is not exceeded. Avoid unnecessary conduit for thermal reasons. [Elektroda, ACCel, post #18071483]
How do I quickly size PV cables?
  1. Determine current and route length, then choose a drop target (e.g., ≤1%).
  2. Check if your chosen cross‑section meets the target (example: 20 A, 50 m needs Cu 16 mm² ≈1%).
  3. Verify insulation rating versus max Voc and ambient conditions. [Elektroda, 3301, post #18074532]
Should I pick a 3.68 kW inverter or 4.6 kW for a 5.04 kWp array?
A 3.68 kW unit gives ~33% DC/AC ratio; 4.6 kW yields ~6.5%. Choose based on grid acceptance rules and future upgrades. Either can work; weigh oversizing versus export or compliance constraints. [Elektroda, sethir, post #18070853]
What lightning‑related edge cases should I consider?
One user reported a near‑direct strike that ruined most AC‑connected devices. Maintain good AC overvoltage protection and minimize DC loop area. Disconnecting inverter DC/AC before storms also helped in that case. [Elektroda, PV_Albert, post #18079638]