Nie, dziękuję Przekieruj mnie tammechagodzillakontra wrote:So again. Specifically. Three groups of single-phase microinverters, approx. 3 kWp each group. Distance about 30m. What diameter ground cable 5 x how many?
prose wrote:ACCel wrote:But the 5x6 is only copper, which is expensive. Aluminum 5x10 is more profitable.
Aluminum is not used in Pv installations for many reasons, and the difference between 4 mm? and 6 mm? of copper is about PLN 2 per meter.
ACCel wrote:Looking at Allegro, the YAKY 5x10 is cheaper than the YKY 5x4, so why overpay?
likwidatorr1 wrote:Thank you very muchI understand that if connected to the network, it will be in accordance with the standards and regulations?
hindoos wrote:I have never pulled the wire through the conduit (only cables), are the trays left or is there a patent for this?
TL;DR: For a 9 kWp, 3-phase micro-inverter string (≈13 A/phase), a 30 m run in 5 × 4 mm² Cu keeps voltage drop < 1.5 % [Elektroda, theo33, post #17736371] “Aluminium is not used in PV installations” [Elektroda, prose, post #17775838] Go copper unless Al price wins.
Why it matters: Right-sized conductors stop nuisance trips at 253 V and avoid needless cable spend.
• Anti-islanding trip: 253 V AC phase-neutral (EN 50549-1) [EN50549, 2020] • Design voltage-drop limit (AC side): ≤ 3 % [IEC60364, 2020] • Calculated cable current: 9 kWp ÷ 400 V = ≈ 13 A/phase [Elektroda, theo33, post #17736371] • Cu price gap: 5 × 6 mm² vs 5 × 4 mm² ≈ 2 PLN/m [Elektroda, prose, post #17775838] • Typical main breaker for ≤ 16 kW: C25 [Elektroda, grzegorz dob., post #17775810]