Why is my CORAX 3 meter showing much higher electricity consumption than my appliance estimate, especially with LED and other nonlinear loads?

A CORAX 3 can overreport with low, nonlinear loads, but the thread does not prove a universal meter defect; the practical advice is to verify the installation and compare it against a calibrated external meter or a utility inspection [#17737035][#19490295][#19521087] One user with the same meter reported much higher readings than a PAFAL submeter, for example Corax 13 kWh versus PAFAL 5 kWh, with the biggest gaps in winter months [#17736669] Other replies say small loads around 10% of the meter range and nonlinear receivers can cause large errors, especially LED lamps, chargers, and switch-mode power supplies [#17737035][#19244583] Before blaming the meter, disconnect all receivers and see whether it still turns, then have an electrician check for hidden consumption, insulation faults, and impedance issues [#19490295] If the mismatch remains, ask the utility for an expert test; one recommendation is a class-A power-quality meter such as a calibrated FLUKE 435-II, whose measurements should be considered in a dispute [#19521087][#19521320]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16346950
    3d0
    Level 10  
    Posts: 52
    Rate: 14
    Hello. In my new apartment I noticed a strange growing trend in energy consumption readings, which I decided to investigate. Interestingly, in the meantime, subsequent residents on the forum of our estate began to report an identical problem, so something must be for a thing ...

    This is the history of my invoices (month / kWh consumption):
    Sep-16 || 140
    Oct-16 || 279
    Nov-16 || 469
    Dec-16 || 437
    Jan-17 || 569
    Feb-17 || 478


    Even without measurements, I can not understand what can generate an increase from 140kWh to 570kWh if half of the equipment goes the same day and the other half can differ by up to 50% and here comes 400% (Sep vs Jan). OK in the winter, "the light is on" longer, but these bulbs have a maximum of 5W, so even if they all went all day, they generate little more.

    For one week I wrote down the values from the meter three times a day (morning / noon / evening) to see if it coincides with the FV and when the consumption is the highest. There were no strange deviations and the morning / night was minimal and the main part dialed the hourly range 17-23. We cook a lot (x2 oven, induction, kitchen equipment) and the TV is plasma, so the elevated value seems to be OK.

    Everything is right up to the point where I wrote down and summarized the values from the nameplates of each electrical equipment. broken down into equipment that goes 24 hours a day (fridge, intercom, fans, etc.) and the one switched on temporarily (light bulbs, oven, TV). According to my estimates, the consumption should be 60% lower. Most of the equipment meets the A +++ standard and the lighting is 100% LED, the total value of which, including LED strips, is ~ 500W.

    The installation is based on electronic 3-phase counters CORAX 3 (APATOR) from 2016.
    http://www.apator.com/uploads/files/Produkty/...-prim-1/pl-00045-2016-norax-3-corax-3prim.pdf

    There is an acrt mass on the network. about how the counters distort up to 600% but usually there are no meters, how it was measured, etc., so my post, because I know that the measurement values are important, not the Internet legends :) most often the wine falls on the LED bulbs (1-3W) or on the A +++ equipment and ill-adapted transducers in meters, but the question is whether anyone has been in contact with this particular device or has it and could make some measurement?
  • ADVERTISEMENT
  • #2 16347791
    polaklbn
    Level 24  
    Posts: 594
    Help: 55
    Rate: 162
    The Riso measurement is indicated here, whether the current is not flowing into the abyss.
    The case can be reported to ZE and the counter will be sent to the lab (you will be charged for the negative result). Equipment in A +++ class can also work as D, depending on the work program. If you moved in August 2016, you could have forecasted invoices until January 2017 - hence the change.
  • ADVERTISEMENT
  • #3 16349230
    3d0
    Level 10  
    Posts: 52
    Rate: 14
    I do not know what the cost of such a measurement is (I will find out) but the question is whether someone with this particular model / company actually had such a problem before and there is a chance that the result will be positive? Because as I understand it is not a flaw of the assembly and the defect of the device, in this case the damaged had to be a whole series since so many people observed a similar effect.

    The general question is whether the construction of the meter itself can actually affect the reading for specific devices.
    btw: on the estate next to a similar complaint, the Apator meter was exchanged for smartEMU 3

    As for forecasting, this could have been the case, although the seller gave information that he had counted the counters at the end of the month from the beginning. The installation is adapted to automatic readings, but for some reason the team goes on a monthly basis and writes down.
  • Helpful post
    #4 16349963
    polaklbn
    Level 24  
    Posts: 594
    Help: 55
    Rate: 162
    There are many MV switch-disconnectors controlled remotely and yet the fitters drive and check their position. It does not matter.

    I also have coraxa and I did not notice such a situation.
    On the forum, it is not possible to give more advice in this case than to review the installation or to advertise the situation in the EC.
  • #5 16351308
    3d0
    Level 10  
    Posts: 52
    Rate: 14
    polaklbn wrote:
    I also have coraxa and I did not notice such a situation.

    Thanks, that's what I meant. Because an individual may be affected by a defect always but sometimes it happens that a particular company will apply other solutions and this may later affect performance and accuracy (generally speaking about each equipment).
  • #6 17051452
    Vein
    Level 22  
    Posts: 743
    Help: 1
    Rate: 51
    So for information, from month to month, with the same use of the house, the increase in the cost of electricity by 50%. To make it from 100 to 150 PLN, I jumped the cost from 500 to 800 PLN ...
  • #7 17052231
    zbich70
    Level 43  
    Posts: 17195
    Help: 1171
    Rate: 6664
    3d0 wrote:
    In my new apartment, I noticed a strange growing trend in energy consumption readings

    Two questions:
    1. Are these "estimates", i.e. calculation of energy consumption based on previous periods?
    2. When writing "my new flat," do you mean a new place just put into service or from the secondary market?
  • ADVERTISEMENT
  • #8 17052485
    Vein
    Level 22  
    Posts: 743
    Help: 1
    Rate: 51
    @ zbich70 you will let me describe my case, it is not my respect for me, only the monthly reading (this is how it is written on the invoice), the building is still in my possession, however, 4 months ago, continuous use has begun.
  • #9 17736669
    piotr-611
    Level 7  
    Posts: 5
    Rate: 10
    Hello! I have exactly the same problem with the CORAX 3 counter. I even used 1000 kWh once. There were gentlemen out of control and said that the meter is ok, you just need to turn off the charger from the phones ... The peak of consumption is about January - February, and the smallest consumption June - July
    (I 2018 -1000kWh IV 2018 - 300 kWh and 2019 - 800 kWh). Recently, I set myself a PAFAL 16EC3gr sub-count and compared the indications. CORAX indicates a lot more than PAFAL, almost the second. For example, Corax - 13 kWh, PAFAL - 5 kWh !!! Weird....
    I wonder what was the continuation of the CORAX 3 counter history?
  • #11 17737122
    piotr-611
    Level 7  
    Posts: 5
    Rate: 10
    Thank you for your response. That explains a lot, especially the great differences between the indications between my sub-meter and the supplier's counter. Just what to do to not be harmed by very high bills? Currently, I do not have high-power receivers that are used frequently.

    Greetings!
  • ADVERTISEMENT
  • #12 17738605
    student11
    Level 21  
    Posts: 687
    Help: 14
    Rate: 28
    Hello,

    My parents got to pay PLN 200 max. Now PLN 2,500. WG Elektrownia consumed 5400kWh and when I was at home (computer + router + tv) they consumed 1800kWh for 6 months. They have this meter just.
  • #13 17742605
    zworecki
    Level 11  
    Posts: 4
    Rate: 4
    I have overstated consumption after replacing the meter. Counter indication as below.
    I disconnected everything at home and connected the devices separately:
    - nothing -> 0W
    - traditional 375W bulb -> 368W
    - LED Osram 20W bulb -> 19W
    - noname 50W LED illuminator -> 96W
    - 50W curling iron -> 210W
    - 40W straightener -> 120W
    - electronic water pump ECO 25W -> 100W
  • #14 17742778
    zbich70
    Level 43  
    Posts: 17195
    Help: 1171
    Rate: 6664
    zworecki wrote:
    I became the victim of this scam. Why the victim? I disconnected everything at home and connected the devices separately:
    - nothing -> 0W
    - traditional 375W bulb -> 368W
    - LED Osram 20W bulb -> 19W
    - noname 50W LED illuminator -> 96W
    - 50W curling iron -> 210W
    - 40W straightener -> 120W
    - electronic water pump ECO 25W -> 100W

    I recently discovered a perpetuum mobile while sitting on the toilet. Well, the wife bought a hair dryer - I look and I do not believe - on the cardboard written that the power of the hot air stream (dry watts) is 2100W , but only 1500 Watts from the network. Energy saving 25% ... Miracles, miracles are announced .... :D
  • Measured loads show nameplate wattage is overstated

    #15 17751874
    zworecki
    Level 11  
    Posts: 4
    Rate: 4
    Turns out the meter is OK, and the overcharged power consumption is the light in the basement that someone forgot about ... for a month
    Immediately improve the post above, because I went after the producer and I should not.

    Yes, out of curiosity, I measured:
    Curler "50W" current graph:
    /// 100mV -> 1A ///
    CORAX 3 Energy Meter: Investigating Rising Consumption Trend in New Apartment (Month/kWh)

    During heating, the value changed, but I tried to take a drop along with the meter reading.
    So the 50W according to the oscilloscope is 96W. The counter showed 87W. It is possible that I did not read at the same time.

    45W straightener:

    CORAX 3 Energy Meter: Investigating Rising Consumption Trend in New Apartment (Month/kWh)

    Calculated 270W. 260W counter.

    The whole house in one phase with all lamps, computers, water pumps turned on:

    CORAX 3 Energy Meter: Investigating Rising Consumption Trend in New Apartment (Month/kWh)

    Calculated 1.05kW. Counter: 970W

    I have yet done the LED illuminator test no name but I have not saved a screenshot from the oscillation. The massacre is more heater than a lamp.

    Generally, the conclusion is that the values given on the rating plates are some fake ....
  • Suggests unplugging everything to test for meter creep

    #16 19244502
    Tbodzio
    Level 2  
    Posts: 4
    Rate: 3
    I also have CORAX 3 and an inflated January reading of 2021. I have a real settlement and I gave the last meter reading (earlier and now always downhill) 4800kWh - the collector came for me (apparently it goes every month), the energa office confirms by phone that what he read after me it was always less than I gave about a week before him. Well, I gave 4800 on January 3 and he read 5665kWh on January 12, 2021. 865kWh in 9 days !!!!! ???? What would I have to have connected? I read the meter on February 7, 2021 and it turned out that I have 6147.4kWh (almost 1200kWh) and the bill is over PLN 900. I feel like crying because I am aware that I am not able to "consume so much electricity in a month. My average kWh consumption is 250 - super max 500 per month. So ... they advised me that I could turn off all devices from the sockets on 30 minutes and see if the meter starts. If it does not move, I do not have a chance and pay. 865kWh in 10 days !!! ??? there are no such home appliances in my opinion 1200kWh in a month when from 5 years never was> 500kWh Any ideas?
  • #17 19244583
    kortyleski
    Level 43  
    Posts: 12265
    Help: 957
    Rate: 3859
    None. On the one hand, in each device a converter without a filter, so the current waveform is significantly different from a sine wave, on the other hand, a meter that cannot correctly measure the distorted waveform. Surprisingly, the old ones with the shield were doing very well.
    The new ZE scam in white gloves has come.
  • Plan to measure appliance loads with a plug-in submeter

    #18 19246865
    Tbodzio
    Level 2  
    Posts: 4
    Rate: 3
    Today, i.e. 10/02/2021, I thought to myself - if I already pay 1000 PLN per month of electricity, for about 1300kWh, even if I pay 200 more for the replacement / expertise of the meter (because it probably works properly and these phone chargers suddenly turn to me took ...) then I will have a new one :) because I assume the old one won't come back. What for? In the meantime, I will measure with an ordinary single-phase sub-meter to the socket, how much is consumed in the daily cycle (I already know that the 24kW central heating furnace and accompanying pumps are about 90 PLN per month). In 7-10 days I will have my main receipts measured:
    - Bake; - fridge; telemedia in the living room (amplifier, TV, decoder, sobwoofer, which never works); then possibly an oven and an induction hob (but it's for two days because I cook and bake little) and a dishwasher + washing machine, I'm not going to measure lighting.
    I still can't believe and I wonder how suddenly my demand increased by 120% (not to be confused with 20% - 100% + 120% :) ).
    Cry and pay, that's the philosophy of ZE.
  • #19 19473063
    PPP
    Level 14  
    Posts: 183
    Rate: 4
    I confirm the problem for me 1300 kWh where in previous periods I had 400kwh nothing new has come. I have an increase in both tariffs
  • Paid the bill after concluding a legal fight is futile

    #20 19478881
    Tbodzio
    Level 2  
    Posts: 4
    Rate: 3
    I have already paid. After I measured (almost) every day for a month and everything was ok ... it left me to think that they cheated me once (probably for the second time in 10 years) and there is no point in digging with the horse. I do not like to let go but I am not interested in a looong fight (maybe years) for 600-700 zlotys and with no greater chances of winning. They will make an expert opinion, say that everything is done and goodbye after the case and I will be left with the court costs. I have no other advice, unfortunately, how to pay it to these "gentlemen".
  • Check for afternoon load and verify meter readings

    #21 19490295
    Slawek9022
    Level 7  
    Posts: 23
    Rate: 4
    I can advise you to disconnect all receivers and check for any afternoon electricity. A vector should appear on the numerator along with the energy demand. Later check the meter reading with the invoices if it is correct or if the readings are not estimated. If this is not possible, call an electrician to check the installation and perform measurements. Installation from insulation to impedance. Electricity meters fail very rarely, I would look for errors in readings or in receivers at home.
  • #22 19521087
    ronwald
    Level 27  
    Posts: 876
    Help: 85
    Rate: 68
    Here it will help to check the energy measurement with a class A power quality meter with the current calibration, eg FLUKE 435-II. Measurements of this class with a meter must be taken into account by the Energy Seller.
  • #23 19521177
    Slawek9022
    Level 7  
    Posts: 23
    Rate: 4
    Analyzer for 50 thousand. Only the service will cost, the easiest way to report it to the power company will come and check the measuring system if it measures well, you will get a printout from their device, if the meter is in the measurement accuracy class, the standard is /- 2%. Examination for about PLN 150. This is the easiest way
  • Fluke meter can calculate monthly energy losses

    #24 19521320
    ronwald
    Level 27  
    Posts: 876
    Help: 85
    Rate: 68
    Without exaggerating with those 50,000 PLN, you can buy it for 23,000 PLN net. Yes, such a measurement costs money
    FLUK has the valuable advantage that it has an energy loss calculator, in addition to checking the energy meter, it will show the quantitative parameters of energy losses and inform what is the cause. Calculates energy losses for the month, quarter, year, etc.
    With large bills and you don't know why, it's worth doing such research.
  • Suspected meter mix-up with photovoltaic register codes

    #25 21240988
    Anonymous
    Level 1  
  • Recommend external meter verification before reporting fault

    #26 21241509
    ronwald
    Level 27  
    Posts: 876
    Help: 85
    Rate: 68
    Before notifying the 'District' that your meter is not working, you should have your electricity measured by an external company that provides electrical metering services. Of course, they should have a class A meter, e.g. FLUKE 435, and have a current calibration of the measuring equipment. For your information, I saved a farmer from paying PLN 72,000 to ENERGA. The energy meter was charging 10 times energy consumption. After 6 months, ENERGA recognised the complaint and checked the energy meter at its own expense. One more remark, when replacing the meter, draw up a protocol, in which the state of the meter with the date and its serial number is written down by a commission.
  • Meter replaced after PGE detected abnormal readings

    #27 21242127
    Anonymous
    Level 1  
  • Sustained 14.63 kW draw explains high readings

    #28 21242496
    =Grzegorz=
    Level 26  
    Posts: 729
    Help: 73
    Rate: 445
    Mass replacement of counters with remote - this is true.
    Using 15.8.0 registers interchangeably with 1.8.0 registers - this is also true and common practice just needs to be done well.
    The use of used counters is also a practice.

    In your case there is some doubt about the contractual power of 11kW with 20A protection (behind the meter probably max 16A per circuit) and according to the letter you provided on PW you were drawing for a long time (more than an hour) almost 15kW (14.63kW) non-stop with short breaks for many days.

    To your detriment is the fact that this was during October/November/December.
  • 14.43 kW peak nearly trips 20A fuses

    #29 21243591
    Anonymous
    Level 1  

Topic summary

LABEL_AI_GENERATED
The discussion revolves around the CORAX 3 energy meter, with users reporting a significant increase in energy consumption readings in their apartments. The original poster noted a rise from 140 kWh in September to 570 kWh by January, prompting an investigation into potential causes. Other users shared similar experiences, suggesting issues with the meter's accuracy, particularly with nonlinear loads affecting readings. Suggestions included checking the installation, reporting to the energy company, and using external measurement devices for verification. Some users mentioned the Apator meter and smartEMU 3 as alternatives. The conversation highlighted the importance of accurate meter readings and the potential for faulty equipment or incorrect installation to lead to inflated bills.
AI summary based on the discussion. May contain errors.