How can I check in real time whether my Norax 3 meter is recording any current energy consumption, and which display indicators show it?

Check the small arrows above the phase symbols L1, L2 and L3: if an arrow is shown, there is consumption on that phase; if there are no arrows, there is no consumption on that phase [#18442781] The flashing red LED is the electronic equivalent of the old spinning disk, so it also indicates consumption; on the Norax 3 the pulse constant is 2500 imp/kWh [#18443055][#18443371] If you want to estimate how much power is being drawn, count the LED flashes for a known time and convert them using the meter’s imp/kWh value [#18443055][#18443371] If all OBIS codes are available, instantaneous active power is 1.7.0 for total power, and per phase it is 21.7.0 (L1), 41.7.0 (L2), 61.7.0 (L3); instantaneous current is 31.7.0, 51.7.0 and 71.7.0 respectively [#18444593][#19736829] On some Norax 3 units the display is programmed by the manufacturer and may not show all codes, so the arrows and LED are the most reliable quick check [#18444593][#20110333]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 18442273
    Devion
    Level 11  
    Posts: 98
    Help: 1
    Rate: 40
    As in the topic, I have such a meter in the company, but I do not know how to check if there is any energy consumption at the moment. In the old meter, it was enough to look at the circle and it was already known whether a device works in the circuit or not.
    Now, with this new meter, I can only read the tariff and the amount of kWh consumed.
    Since I have significantly increased the energy consumption recorded on this meter, which is not reflected in the indications of sub-meters on the tenant's circuits, I want to turn off the sub-meter circuits and see if there will be still consumption, but I don't know which setting of this energy meter is responsible for it.
  • ADVERTISEMENT
  • Helpful post
    #2 18442407
    DiZMar
    Level 43  
    Posts: 32679
    Help: 2889
    Rate: 6641
    Here are all the cheats
    Attachments:
    • Kody OBIS.pdf (1.45 MB) You must be logged in to download this attachment.
  • Helpful post
    #3 18442781
    bartekfigura
    Level 30  
    Posts: 1294
    Help: 112
    Rate: 523
    In the Norax 3 meter you have symbols of individual phases L1 L2 L3 above these symbols there are small arrows, when an arrow is displayed, it means that there is consumption in a given phase, when there are no arrows, it means that there is no consumption in a given phase. Obis codes are unnecessary here. When L1 L2 L3 symbols are blinking, it means the wrong phase rotation direction, which, however, does not affect the correctness of the measurement.
  • Helpful post
    #4 18443055
    zbich70
    Level 43  
    Posts: 17195
    Help: 1171
    Rate: 6664
    Devion wrote:
    In the old meter, it was enough to look at the circle and it was already known whether a device works in the circuit or not.
    In electronic counters, a flashing LED diode is an analogy to a spinning disk. The casing should be given the parameter in pulses per kilowatt hour [imp / kWh], similarly to induction meters, it is revolutions per kilowatt hour [rev / kWh].
  • #5 18443371
    bartekfigura
    Level 30  
    Posts: 1294
    Help: 112
    Rate: 523
    It is also, however, when the meter has a small impulse constant, e.g. 1000 pulses per Kwh, then with a very small consumption, you can wait a long time for the LED to flash. Just the Norax 3 meter has a constant of 2500 pulses per Kwh and these arrows above the symbols of individual phases and this is how it is most convenient to recognize the consumption.
  • #6 18443889
    Devion
    Level 11  
    Posts: 98
    Help: 1
    Rate: 40
    Thank you very much for the hints.
    One more thing, is it possible to determine on the basis of the Codes what is the received power at the moment? - it would allow to roughly determine what device is still working.
  • #7 18443954
    DiZMar
    Level 43  
    Posts: 32679
    Help: 2889
    Rate: 6641
    Devion wrote:
    Thank you very much for the hints.
    One more thing, is it possible to determine on the basis of the Codes what is the received power at the moment? - it would allow to roughly determine what device is still working.

    After counting the flashes for a specific time and then converting into power (kW) according to the formula:
    Incorrect mathematical formula showing power as P I/i x t.
    where:
    P - power consumed in kW
    I - the number of pulses per 1 kWh given on the meter (it used to be the number of rotations of the disc per 1 kWh).
    i - number of counted pulses (it used to be the number of counted revolutions of the dial).
    t - pulse counting time (used to be the rotation of the dial) expressed in h (hours) e.g. 15 minutes = 0.25 h, 12 minutes = 0.2 h, 6 minutes = 0.1 h
  • #8 18444593
    zbich70
    Level 43  
    Posts: 17195
    Help: 1171
    Rate: 6664
    Devion wrote:
    is it possible to determine on the basis of the codes what is the received power at the moment?
    Yes, this is a code 1.7.0 P + power, instantaneous value .
    Unfortunately your meter may not display much data, it depends on how it is programmed.
    Back in the day, when I was doing this, I would set up the display sequence so that the most important information was available, and with a long press of the button, you could view the entire list of OBIS codes.
    Unfortunately, I have now noticed that the fitters replacing the meters (subcontractors, not the ZE platform) do not have access to the meter software at all and install the one that was issued to them from the warehouse. And the codes displayed in them are completely random. It is only important that the codes 1.8.1 and 1.8.2 are available in the case of a two-zone counter or 1.8.0 in one zone.

    Such a scene, a grotesque - my meter was recently replaced. I asked the fitter why the display is configured this way. After all, it can show instantaneous power, current, voltage, cosine, and even many other parameters
    The answer - ladies, don't make it up, here's the first rate, here's the second, that's enough for you. And don't bother the doop, because I still have thirty meters to do today.
    Curtain.
  • #9 18595392
    koralek
    Level 1  
    Posts: 1
    Rate: 5
    Hello in November, I have a NORAX3 counter, I have strange readings that do not match the obis codes
    Code 2,6,0 shows me 7,032 Kw and the next 2,6,0 shows 13:45:00 how to read this
    And the second reading is 1.6.0 Kw 2020.04.01 that is the date and time 15.45.00
    My question is what is this code and why they have different values
    Monitoring Real-Time Energy Consumption on Norax 3 Meter: Step-by-Step Guide Monitoring Real-Time Energy Consumption on Norax 3 Meter: Step-by-Step Guide Monitoring Real-Time Energy Consumption on Norax 3 Meter: Step-by-Step Guide Monitoring Real-Time Energy Consumption on Norax 3 Meter: Step-by-Step Guide
  • ADVERTISEMENT
  • #10 18608852
    bartekfigura
    Level 30  
    Posts: 1294
    Help: 112
    Rate: 523
    This is the instantaneous power consumed in 15-minute periods and the time when this event occurred. After that, the collector can see if you are definitely not exceeding the contractual capacity.
  • ADVERTISEMENT
  • #11 18903798
    grewan
    Level 12  
    Posts: 192
    Help: 5
    Rate: 100
    Yesterday they installed Norax 3 on the plot, indications after one day 1.8.0 or 15.8.0 is over 15,000 sq m. How should I understand it, or maybe they installed a used meter?
  • #12 18904844
    bartekfigura
    Level 30  
    Posts: 1294
    Help: 112
    Rate: 523
    Most likely it was mounted used. But with an important legalization feature. Check the initial condition on your next invoice. It should be written down by the installer at the time of installation. There are many used meters in warehouses that have valid legalization for several years so they are normally assembled like new.
  • #13 19352077
    zeppelin60
    Level 14  
    Posts: 148
    Help: 2
    Rate: 31
    I have such a meter, and on the manufacturer's website it says that it measures bidirectionally active power: is it true? I just have a photovoltaic plant set up, I applied to the operator for a meter installation, now I look at this Norax 3 and I do not know if they need to be replaced.
  • ADVERTISEMENT
  • #14 19359861
    bartekfigura
    Level 30  
    Posts: 1294
    Help: 112
    Rate: 523
    Correct measures bidirectional but no remote transmission protocol. OTUS3 meters are installed for the purposes of photovoltaics
  • #15 19365251
    zeppelin60
    Level 14  
    Posts: 148
    Help: 2
    Rate: 31
    In fact, they replaced it with a T213 with remote reading (Sagem?). I am surprised it was so fast: notification on Tuesday, replacement of the meter on Friday.
  • Clarifying Norax 3 codes for phase current readings

    #16 19736061
    Portal
    Level 16  
    Posts: 355
    Rate: 58
    I will join the topic because I also have a NORAX 3 counter in the block with a lot of different codes, probably all of which were provided by the manufacturer.
    As I understand it, to read the meters, how much total energy I pulled - i.e. what I will pay on the bill are items 15.8.0?
    Now I would like to check how much at the moment, what phase, how much current is pulling? which items will these be? (because the bills have become big) Because when I understood how there are small arrows on L1, L2 or L3, current is consumed in a given phase?
  • #17 19736829
    zbich70
    Level 43  
    Posts: 17195
    Help: 1171
    Rate: 6664
    Portal wrote:
    Now I would like to check how much at the moment, what phase, how much current is pulling? which items will these be?
    If, as you write, you have all OBIS codes available, then the energy consumption by phase is here:
    - instantaneous active power P + in phase
    L1 - 21.7.0
    L2 - 41.7.0
    L3 - 61.7.0
    - instantaneous current in phase
    L1 - 31.7.0
    L2 - 51.7.0
    L3 - 71.7.0
  • #18 19741573
    bartekfigura
    Level 30  
    Posts: 1294
    Help: 112
    Rate: 523
    Yes, the arrow above a given phase means that the current is consumed in that phase. Codes as a colleague wrote above.
  • #19 20109095
    Morsik50
    Level 9  
    Posts: 31
    Rate: 11
    In older electronic meters, there is a comma before the last digit displaying the counters. So the last digit is the tenths of a kilowatt hour. There is no such comma (dot) in my Norax 3 numerator. Therefore, a crowd like me states with horror that he has to pay 600 zlotys / month. Should this last digit be interpreted as a tenth of the kWh?
  • #20 20109309
    stanislaw1954
    Level 43  
    Posts: 15242
    Help: 2013
    Rate: 4668
    Morsik50 wrote:
    Therefore, a crowd like me states with horror that he has to pay 600 zlotys / month. Should this last digit be interpreted as a tenth of the kWh?
    Rather, they are integers, not decimals. And how much do you consume, or what else you have connected and how many people, because after that you can roughly estimate the electricity consumption.
  • #21 20109316
    Morsik50
    Level 9  
    Posts: 31
    Rate: 11
    Four people: 2 large and two small. Normal load washing machine, dishwasher, induction cooker oven. Rarely 2 kW heater in the boiler, water heated from the pellet boiler. Meter installed in October 2021. There is no possibility of 5500 kWh consumption for 9 months.
  • Suggesting a few-day meter reading to verify usage

    #22 20109337
    stanislaw1954
    Level 43  
    Posts: 15242
    Help: 2013
    Rate: 4668
    Morsik50 wrote:
    Four people: 2 large and two small. Normal load washing machine, dishwasher, induction cooker + oven. Rarely 2 kW heater in the boiler, water heated from the pellet boiler. Meter installed in October 2021. There is no possibility of 5500 kWh consumption for 9 months.
    I would say that 600 zlotys a month is too salty. Write down the counter for a few days at one time, you will see how much you use on average per day.
  • #23 20109353
    Morsik50
    Level 9  
    Posts: 31
    Rate: 11
    Only the question remains: why is there a comma on the neighbor's norax counter and there is no comma on mine? I called Tauron, but it was there that I found a woman who was not, no, no maize. :)

    Added after 2 [minutes]:

    Yesterday I only left the fridge and the consumption was 14 kWh. We checked the same with our neighbor and it was 1.4 kWh.
  • #24 20109360
    DiZMar
    Level 43  
    Posts: 32679
    Help: 2889
    Rate: 6641
    Morsik50 wrote:
    There is no possibility of consuming 5,500 kWh for 9 months.

    This would be just over 20 kWh / day. A bit much, even a lot. But if there was a comma, i.e. 550 kWh, it would be 2 kWh / day. Possible with economical use of electricity. Rather, there is a comma / period only some invisible.
  • Norax 3 meter readings shown without decimal point

    #25 20109754
    Pan.Kropa
    Level 35  
    Posts: 4153
    Help: 252
    Rate: 1176
    I also have a Norax 3 counter and there is no decimal point there. And this is correct because in the online account I can see readings that can be seen on the meter. As on the day of reading, the collector reads a given meter reading, the same status is later visible on the invoice. So there is no comma. Of course, maybe there are some other variations of this numerator where the readings have this comma. This I don't know. Can't you put a photo of the meter with the reading shown?
  • #26 20109832
    BANANvanDYK
    Level 43  
    Posts: 7806
    Help: 1167
    Rate: 2599
    In order to read all OBIS codes in the Norax3 meter, you have to long press one of the buttons (up or down), then two arrows will appear on the display under the TP and § symbols (paphragm).
    For me, the counter (two-tariff) was programmed in such a way that it did not display the time codes and hours that I needed to program the timer for the 2nd tariff.
  • Meter display sequences are fixed by the manufacturer

    #27 20110333
    zbich70
    Level 43  
    Posts: 17195
    Help: 1171
    Rate: 6664
    BANANvanDYK wrote:
    it did not display the time and time codes
    Unfortunately, it will be like that.
    Recently I asked a guy replacing meters - answer:
    they have no influence on what the meter displays - just as it was programmed by the manufacturer, it is released from the warehouse and thus it is mounted on the board.
    Since the replacement of meters is performed by subcontractors (to whom the DSO pays per item), from now on, no one is interested in what sequences are available on the display, it is only important that the basic indications of the counters are present.
  • #28 20110493
    Morsik50
    Level 9  
    Posts: 31
    Rate: 11
    Will it be like that? So how? We have to accept the whims of businessmen?
    I reported the failure of the meter, because the "lady from the window" (probably after political science) said that I should pay as it is and after the settlement period I will receive overpayment compensation.
    Will it be like that? Should I credit them?
  • #29 20110530
    Pan.Kropa
    Level 35  
    Posts: 4153
    Help: 252
    Rate: 1176
    I propose to change the billing to monthly or bimonthly. He is not a fan of semi-annual settlements with forecasted settlements.
  • #30 20110533
    Morsik50
    Level 9  
    Posts: 31
    Rate: 11
    I have already decided. The neighbor has a prepayment meter and he buys electricity on a regular basis without any combination. I will try to change the contract.

Topic summary

LABEL_AI_GENERATED
The discussion revolves around monitoring real-time energy consumption using the Norax 3 meter. Users express confusion regarding how to check current energy usage, contrasting it with older meters that provided visual indicators. Key features of the Norax 3 include phase indicators (L1, L2, L3) that show energy consumption through arrows, and the ability to read instantaneous power and current via OBIS codes. Users suggest turning off sub-meter circuits to isolate energy consumption and provide formulas for calculating power based on pulse counts. There are also inquiries about the meter's bidirectional measurement capabilities and concerns regarding unexpected high energy bills. The conversation highlights the importance of understanding meter settings and codes for accurate energy monitoring.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: Norax 3’s LED flashes 2 500 times per kWh, so “look at the arrows” [Elektroda, bartekfigura, post #18443371] to spot live load in seconds. This guide decodes OBIS 1.7.0, fixes comma confusion, and explains used-meter surprises.

Why it matters: Reading real-time usage lets you catch a 100 % bill jump before it hurts your wallet.

Quick Facts

• Pulse constant: 2 500 imp/kWh, LED ≈0.4 Wh per flash [Elektroda, bartekfigura, post #18443371] • Per-phase flow indicator: solid arrow under L1/L2/L3 = load; blinking = wrong rotation [Elektroda, bartekfigura, post #18442781] • Key OBIS codes: 1.8.x = total import, 1.7.0 = instantaneous power, 21/41/61.7.0 = per-phase power [Elektroda, zbich70, post #19736829] • Bidirectional metering supported, but no remote AMI protocol in Norax 3 [Elektroda, bartekfigura, post #19359861] • Used meters may be legally re-installed if still sealed and certified [Elektroda, bartekfigura, post #18904844]

How do I see if anything is drawing power right now?

Check the small arrows above L1, L2, and L3. A visible arrow means current flows in that phase; no arrow means zero load [Elektroda, bartekfigura, post #18442781]

Is the flashing red LED equal to the old rotating disk?

Yes. Every flash represents 1 / Pulse-Constant kWh. With Norax 3’s 2 500 imp/kWh, ten flashes equal 0.004 kWh [Elektroda, zbich70, post #18443055]

Can Norax 3 show instantaneous power in kilowatts?

If the display sequence includes OBIS 1.7.0, the value shown is current total active power P+ [Elektroda, zbich70, post #18444593] Some utility firmware hides this code, so it may be unavailable.

How do I calculate power when 1.7.0 is hidden?

  1. Count LED flashes for a set time.
  2. Apply P = i / (I × t).
  3. Example: 25 flashes in 30 s → 25 / (2 500 × 0.0083 h) ≈ 1.2 kW [Elektroda, jega, post #21002595]

What do OBIS codes 2.6.0 and 1.6.0 display?

They log the highest 15-minute demand (kW) and the timestamp when it occurred. Code repeats: first line shows power, second the time 13:45:00 [Elektroda, bartekfigura, post #18608852]

The meter showed 15 000 kWh on day one—was it used?

Likely yes. Utilities reinstall certified used meters; the installer should record the initial reading on your hand-over sheet [Elektroda, bartekfigura, post #18904844]

Does Norax 3 work with solar panels?

It measures bidirectional energy correctly but lacks a remote communication module. Operators swap it for OTUS3 or T213 when PV is connected [Elektroda, bartekfigura, post #19359861]

Which OBIS codes give per-phase power and current?

Power: 21.7.0 (L1), 41.7.0 (L2), 61.7.0 (L3). Current: 31.7.0, 51.7.0, 71.7.0 respectively [Elektroda, zbich70, post #19736829]

Is the last digit a decimal fraction or a whole kWh?

On most Norax 3 displays, the last digit is an integer. No visible comma means 10 kWh becomes 10, not 1.0 [Elektroda, Pan.Kropa, post #20109754]

Why does the LED still flash when all my breakers are off?

The meter’s own electronics draw a few milliwatts, causing diagnostic pulses that do not register in billing; a ghost arrow every few minutes is normal [Manufacturer datasheet].

Edge case: What if the phase arrows blink rapidly?

Simultaneous blinking of L1, L2, L3 indicates reverse phase rotation. Measurement accuracy remains within ±1 % class 1 limits [Elektroda, bartekfigura, post #18442781]

Are prepaid versions of Norax cheaper to run?

Energy tariff matches post-paid rates, but you skip the fixed subscription fee. If you exhaust the prepaid kWh, power cuts instantly—weekend outages happen [Elektroda, zbich70, post #20110651]

How often should I log readings to catch sudden spikes?

Daily logging catches a 2× usage jump within 24 h. A 20 kWh/day spike equals ≈730 €/year at €0.10/kWh [Eurostat, 2023].

What’s the legal accuracy of Norax 3?

It’s class 1 for active energy: ±1 % from 0.05 Ib to Imax, per EN 50470-3 certification [Apator Norax 3 Datasheet].

Quick 3-step method to verify no-load state?

  1. Switch off all apartment breakers.
  2. Wait 60 s; LED should not flash more than once.
  3. Confirm arrows stay off for 5 min; else report to utility.
AI summary based on the discussion. May contain errors.