Fuse Protection & Maximum Power for 80m Extension Cord with 5x6mm^2 Cross Section

solek558 25488 3
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16452409
    solek558
    Level 8  
    Hello
    I am asking what fuse should be protected extension cord with a length of 80 m and cross section of 5x6mm^2 . And what can be the maximum power of the device connected through this extension cord.
    Greetings.
  • ADVERTISEMENT
  • #2 16452603
    wzielonymgaju18
    Level 18  
    The long-term load capacity of this cable is 34-40A, depending on the laying conditions. So the optimal fuse to guarantee the safety of continuous operation is 32A, so the maximum power of a three-phase device is 12.8kW, and a single-phase device is 7.4kW
  • ADVERTISEMENT
  • #3 16452619
    kkas12
    Level 43  
    Load capacity is load capacity and IPZ at its end does not at all go with it.
    Also, an extension cord with a length of more than fifty meters is a failure.
  • #4 16452626
    Strumien swiadomosci swia
    Level 43  
    wzielonymgaju18 wrote:
    Thus, the optimal fuse to guarantee the safety of continuous operation is 32A, so the maximum power of a three-phase device is 12.8kW, and a single-phase device is 7.4kW



    Kolego 22kW at 32A. Secondly you need to measure the IPZ as you have what or limit the current to 16-25A.