Gradual Pressure Increase in Buderus Logamax U042-24k Gas Boiler: Normal or Concerning?

Saskia1337 7395 6
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16807284
    Saskia1337
    Level 7  
    Welcome. For a year now, I have been the happy owner of a studio equipped with a heating system based on the heating of water by the Buderus Logamax U042-24k gas boiler. The heating circuit is not connected to any other circuit, yet from the very beginning it observes the gradual increase of the value indicated by the pressure gauge needle. When the plant was not in use (March to mid-October this year), the pressure slowly rose from 1.5 bar to 2.5 bar. Before the winter start-up, I reduced them to about 1.6 bar, draining about 1.5 liters of water. Since then, in two weeks, its value has increased to 2.1 bar.
    My questions are as follows:
    - Are such gradual increases normal in a new installation (from June 2016)?
    -If it is a closed circuit, the water is at the same temperature all the time, where does the pressure increase mentioned earlier, but quite significant, come from?
  • ADVERTISEMENT
  • Helpful post
    #2 16807436
    daro31ie
    Automation specialist
    Buddy, if the pressure rises even when the stove is not working, you must have a damaged valve allowing water from the network.
    Maybe it is not closed slightly?
  • ADVERTISEMENT
  • #3 16807665
    Saskia1337
    Level 7  
    In the meantime, I checked the meter reading. When the boiler pressure changed by 0.5 bar, only 0.0003 m3 "escaped" from the meter, so this is not it.
    I would like to add that the boiler is under warranty, so if we fail to come up with an easy solution, the service technician will have to deal with this problem.
  • ADVERTISEMENT
  • Helpful post
    #4 16807803
    daro31ie
    Automation specialist
    A colleague, a service technician will issue an invoice for such a diagnosis.
    Buddy, either the water gets into the system from an external source, or you have a damaged pressure gauge.
  • #5 16808097
    Saskia1337
    Level 7  
    Therefore, before calling a service technician, I prefer to spend a few moments and find out for yourself what the causes may be. As I understand all the hypotheses apart from the valve passing water from the network to the circulation, which can rather be excluded?

    Edit: the gauge is 100% functional.
  • Helpful post
    #6 16808700
    daro31ie
    Automation specialist
    Water pressure increases when we heat it up or it comes from another source.
    If you say that the pressure gauge and valve are ok, maybe you have a damaged diaphragm tank. This is where air under higher pressure can enter the system.
  • ADVERTISEMENT
  • #7 16828489
    Saskia1337
    Level 7  
    For posterity: remove the water release valve from the network, clean it, reinstall it and enjoy a working boiler. I am closing, thank the colleague above for the answers.

Topic summary

The discussion revolves around the gradual pressure increase observed in a Buderus Logamax U042-24k gas boiler, which has been noted by the owner since its installation in June 2016. The pressure gauge indicates a rise from 1.5 bar to 2.5 bar during periods of inactivity, prompting concerns about whether this is normal for a closed heating circuit. Responses suggest potential causes for the pressure increase, including a damaged valve allowing external water ingress, a malfunctioning pressure gauge, or issues with the diaphragm tank. The owner confirmed the gauge's functionality and expressed a preference to diagnose the issue before involving a service technician. Ultimately, a solution was proposed to clean and reinstall the water release valve from the network, which resolved the problem.
Summary generated by the language model.