Tango Negro controller - controller settings, large combustion, not burning
siwekyhy 26094 12
How should I set a Tango Negro boiler controller and 4-way valve to reduce coal consumption and prevent poor burning/sintering?
There is no universal Tango Negro setting; start by keeping the boiler around 60°C, then tune the feeder, pause and blower values by watching the flame, while reducing coal use mainly by lowering the radiator supply temperature with the 4-way valve and keeping the return warmer [#16915566][#16917151] If sinters appear, the boiler temperature is too low for that coal, so raise the setpoint by about 10–15°C and check the burn again [#16915630] Lowering the temperature of water going to the radiators reduces heat demand and should reduce fuel consumption, but if the boiler runs too cold or at too low power, efficiency drops and it spends more time in maintenance [#16917151][#16921705] For a 200 m² uninsulated house, about 40 kg/day at your outdoor temperatures may still be normal, so some of the fuel use may simply come from the building’s heat demand [#16917062][#16921705]
  • #1 16915346
    siwekyhy
    Rate: 16
    For a month I have been using an eco-pea kiln for heating the house. Oven for coal mine 25 KW with "screw" feeder. Newly built house, closed, but without external insulation, only porotherm 25 brick, in the middle are already plaster tiles, prepared for painting. The furnace is used from 2007.
    At the time of finishing works there are used 10 radiators, rather small single, the two largest are double 120, the rest is a single max. 80 cm long. Radiators have throttled valves for adjustment. In addition, a floor-standing floor about 40 m2. For now, only central is activated without heating hot water.
    Tango negro driver. I do not know how to set up in a different way. At the beginning of the use I bought the cheapest eco-pea from the market. The furnace often extinguished itself, just the eco-pea was wet, now it has been dried a little earlier. It burned almost 50 kg per day at a furnace temperature of 50 degrees and the ash was a large bucket a day. The house is around 15 ~ 17 degrees with outdoor temperatures from -3 at night to 5 in the day.
    Currently I have been using better 27 KJ peas from the warehouse for a week. The four-way valve is set slightly in the "side of the radiators" after a few days of smoking there were large sinters on the hearth until it lifted the ring. The furnace reaches a much faster set temperature, it burns much better in the burner, the only thing I noticed is hard for him reach the temperature after the temperature drops during work, as it turns off the working time, the temperature goes up better and the furnace stands with elevated temperature. The pump is set in half for the second gear of four. Preset temperature 50 degrees. The furnace burns not much less because about 40 kg, it's probably too much. It seems to me that it did not burn coal. I have already cleaned the stove a few times, even there under the burner where there is a "chimney" from the fan.
    I am asking for advice on how to set up the controller and a 4-way valve to burn more coal and to burn less.
    Current furnace settings: Tango Negro model around 2007, I do not have a room controller, setting 50 degrees.
    PrA - feeder operation time - 8s
    PaU - feeder break time in working condition - 41s
    CdP - blower sustained in operation - 20 s
    PpO - the number of fuel feeds in maintenance - 6
    CoC - waiting time in maintenance - 21 min
    Ofs - blower speed in working condition 5
    Bpo - blower in maintenance 4
    Greetings.
  • #2 16915566
  • #3 16915609
    siwekyhy
    Rate: 16
    I know that there are no universal settings, but it would be good to base on something. Not one hour I "spent" in the boiler room over all this ... slowly I have enough ... Unfortunately, I do not live there every day the harder it is to set ... As for fuel, I doubt that now I bought dry fuel somewhere, I tried already in a few places "Krakow" and it's the same ...
    A house with a usable attic of about 200 m2. Height of the ground floor 2.85, attic height 2.65
  • #4 16915630
  • #5 16916915
    siwekyhy
    Rate: 16
    If I raise the temperature to, for example, 60 degrees, coal combustion will increase too. What will happen if I raise the temperature to 60 degrees but I turn the 4 way valve slightly towards the furnace return? Then the return will have a higher temperature the stove should not cool down any more, the radiators will only be slightly cooler so it should work? Burning should decrease a bit?
    Please send me some examples of checked settings, I will have something to "base" on
  • #6 16917062
    Sstalone
    Help: 72
    Rate: 398
    Combustion can be slightly reduced when the walls are heated. But 40 kg of coal 27 MJ / kg for a non-insulated house with an area 200 sq m at the temperatures you have given, it's probably the norm. Here you can look at the graph of energy demand for an insulated house with an area 200 sq m. Https://www.elektroda.pl/rtvforum/topic3388008-30.html#16860979
  • #7 16917108
    siwekyhy
    Rate: 16
    Maybe so, but at the moment, when there are no paintings I do not need as much as 17 degrees, there would be enough 10 in the house, and I would prefer that burning coal would be smaller, I do not live there ;) Is it possible to add a room controller to this Tango Negro controller? I looked at the back of the driver there is no such input ..
    Is what I wrote earlier about to change the valve more towards returning to the furnace reduce coal burning?
  • #8 16917129
  • #9 16917151
    Sstalone
    Help: 72
    Rate: 398
    As you lower the temperature of the water going out to the radiators, you reduce the energy consumption for heating, then the consumption of coal should fall. The problem may be the operation of the boiler at too low power, for example, as it externally is 10 degrees Celsius. :D
    If you have the option, try to reduce the temperature of the water leaving the radiators, at a constant temperature on the boiler, eg 60 degrees. Such operation may also require changing settings in the controller, because then the energy demand will decrease.
  • #10 16917194
  • Underfeeding fuel caused low burner temperature
    #11 16917993
    siwekyhy
    Rate: 16
    Radek3p
    As for the fuel you are right, I hear also from other users with worse and worse fuel. The house is definitely not warmed up. The house is on a hill around it is empty, it probably also gives you a blow by the wind.
    Simar boiler with a screw feeder, tango negro controller all from 2007. in the back there is no way out for a room controller.
    Today I changed my mind a little, gave too little fuel because it burned at the end of the day at the bottom of the burner and could not reach the temperature by this.
    Sstalone
    I am thinking about putting on thermostats for each radiator and adjust them for 2 or 3 because they go to full power.
    It will also analyze the given page by you.
  • #12 16920547
    siwekyhy
    Rate: 16
    Can large combustion also be caused by the fact that the boiler is more powerful than it should be?
    This one has 25 Kw and the project is 17 Kw. The house volume is about 850 m3
  • #13 16921705
    Sstalone
    Help: 72
    Rate: 398
    Demand in the project was calculated for the insulated house. Now that you have it uninsulated and the 25 kW boiler works at 50% of maximum power, the efficiency of combustion is not much worse. What else, if you reduced the heating temperature to 10 degrees, the boiler would work at 25% power and often in maintenance, combustion efficiency would drop. The same situation can occur after home insulation. If you intend to continuously smoke in a fuel boiler, you should not oversize the boiler. I advise you once again when replacing the boiler to determine the required power, because according to me 17 kW in a project for 200 sq m of an insulated house, unless it is too much ...
The discussion revolves around optimizing the settings of a Tango Negro controller for a Simar eco-pea kiln used for heating a newly built, uninsulated house. The user reports issues with coal combustion efficiency, experiencing frequent extinguishing of the fire and excessive ash production. Various responses suggest that proper fuel quality, temperature adjustments, and the potential for adding thermostatic controls to radiators could improve performance. The user is advised to monitor combustion closely and adjust the water temperature leaving the radiators to reduce coal consumption. Concerns are raised about the boiler's power being oversized for the house's heating needs, which may affect combustion efficiency.
TL;DR: Large sinters and high use (≈40 kg/day) on a 25 kW eco‑pea boiler in a 200 m² uninsulated home are typical; “Combustion can be slightly reduced when the walls are heated.” [Elektroda, Sstalone, post #16917062] Why it matters: This FAQ shows how to set Tango Negro controls and a 4‑way valve to cut fuel, stop clinkers, and stabilize temperature for new installs and uninsulated buildings.
How do I stop large sinters (clinkers) forming on the burner?
Increase the boiler setpoint by 10–15 °C, especially with higher‑calorific coal. Low furnace temperature with rich fuel promotes sintering. After raising the setpoint, check that the flame is stable and ash is friable, not fused. Adjust air only if the flame becomes too bright and hard. Keep the four‑way valve balancing radiator comfort separately from boiler protection. [Elektroda, 762302, post #16915630]
Is ~40 kg/day normal for a 200 m² uninsulated house?
Yes. For 27 MJ/kg eco‑pea and outdoor temperatures around −3 °C to +5 °C, ~40 kg/day is typical in an uninsulated 200 m² home. As walls and mass warm up, combustion can drop slightly. “Combustion can be slightly reduced when the walls are heated.” Consider finishing insulation to cut the baseline demand. [Elektroda, Sstalone, post #16917062]
Will setting the boiler to 60 °C raise consumption?
Not if you use the 4‑way valve to lower radiator supply temperature while keeping the boiler hot. Keep the boiler around 60 °C for clean combustion and use the mixing valve to match room demand. This often reduces cycling and overall fuel use once rooms stabilize. You may need to trim feed and air settings after this change. [Elektroda, Sstalone, post #16917151]
Should I turn the 4‑way valve more toward return to save coal?
Yes, if that lowers the supply temperature to radiators while maintaining a safe, hotter boiler circuit. Lower radiator water temperature reduces building heat demand. Keep boiler setpoint stable, then trim valve position for comfort. Re‑tune controller timings after any major valve change to maintain steady operation. [Elektroda, Sstalone, post #16917151]
Can I add a room thermostat to a Tango Negro controller from 2007?
In many 2007 Tango Negro units, there is no room‑thermostat input on the rear panel. Owners report no connector present, so add‑on room control is not supported on those models. Consider using TRVs on radiators to regulate room temperatures instead. [Elektroda, siwekyhy, post #16917993]
Why does wet eco‑pea coal make the boiler go out?
Wet eco‑pea burns poorly, cools the firebed, and can extinguish the flame. Drying the fuel before use restores stable burning and reduces stoppages. Keep the bunker and auger dry to prevent clumping and feed interruptions. If the fire wanes, check fuel moisture before changing controller timings. [Elektroda, siwekyhy, post #16915346]
What starting Tango Negro timings can I try before fine‑tuning?
Use the field‑tested baseline: feed 8 s, pause 41 s, blower sustain 20 s, maintenance feeds 6, maintenance wait 21 min, blower work speed 5, maintenance speed 4. Observe ash and flame for a day, then adjust feed and air in small steps. Log changes. [Elektroda, siwekyhy, post #16915346]
Is my 25 kW boiler oversized for this house, and does that waste fuel?
Oversizing pushes the boiler into low‑power or maintenance states, which lowers combustion efficiency. At very low room targets (e.g., 10 °C) or after deep insulation, efficiency can drop further. When replacing, size closely to the real heat load; 17 kW in the project may still be high. [Elektroda, Sstalone, post #16921705]
Can thermostatic radiator valves help if I only need about 10 °C inside?
Yes. Fit TRVs and set them around 2–3 to cap room temperatures while the boiler runs efficiently. This approach limits unnecessary radiator output when the building is unoccupied. It complements a fixed boiler setpoint strategy and reduces cycling. [Elektroda, siwekyhy, post #16917993]
Does fuel source and mixing different coals affect burning to ash?
Yes. Quality varies and sellers can misrepresent fuel. Different coals burn differently; you may need to adjust timings per batch. Mixing types sometimes prevents full burnout to ash. “You have to start observing the furnace work and modify it for your needs.” [Elektroda, 762302, post #16917129]
My site is windy and exposed—will that increase coal use?
Yes. An uninsulated house on a hill with strong wind exposure loses more heat through infiltration and surface convection, raising consumption. Expect higher use until you add exterior insulation and tighten the envelope. Fuel savings appear after the structure warms and leaks are reduced. [Elektroda, siwekyhy, post #16917993]
I reduced feed too much and the fire burned at the burner bottom—what now?
Increase feed slightly until the flame sits at the retort top and reaches setpoint reliably. Then trim air to keep a steady, bright‑orange flame. Recheck after several cycles. Under‑feeding causes the fire to sink and delays recovery. [Elektroda, siwekyhy, post #16917993]
What is “maintenance” mode and when does it hurt efficiency?
Maintenance mode keeps embers alive with periodic feeding and air when room demand is low. If you run at very low room targets or after insulation, the boiler may idle often, cutting efficiency. Adjust setpoints and valve mix to reduce idle time. [Elektroda, Sstalone, post #16921705]
Quick 3‑step how‑to: tune out sinters and stabilize heat
  1. Raise boiler setpoint by 10–15 °C to stop sinters.
  2. Leave boiler hot; lower radiator supply using the 4‑way valve.
  3. Observe ash and flame; adjust air in small steps until ash is loose. [Elektroda, 762302, post #16915630]
House volume is 850 m³—does that change my expectations?
Larger internal volume increases warm‑up energy and time. Expect higher initial consumption while the mass heats, then a slight reduction. Plan settings for steady operation rather than frequent starts. This helps stabilize temperature and improve burnout. [Elektroda, siwekyhy, post #16920547]