elpapiotr wrote: Give the YDY 5 x 4 mm? cable for peace of conscience
Not for the peace of conscience, it is only to be.
Assuming that someone can install a full induction cooker with four burners, eg Bosch, it has almost 10 kW, and the oven is 2 kW, so we have 12 kW. Thus, the current is about 24 A. / For the abbreviation power in kW x 2 = current in A with three-phase power supply /.
Often, induction hobs are powered by only two phases? from the third power the oven.
It is assumed that for 2.5 mm? it is 16 A - that is not enough.
Even if we buy an economical plate, which will have only 6 kW + 2 kW oven, we still have 8 x 2 = 16 A, i.e. on the border.
ps. I omit thermal conditions and styrofoam.
Moderated By Łukasz-O: If the oven and induction hob are separate receivers, they should not be supplied from one circuit.