[Solved] Induction Hob Wiring: 5x2.5 or 4x2.5 Wire Type, Heat Resistance for Oven Placement - Advice

Mrozan 24753 19
Best answers

What type of cable should I use to connect an induction hob with an oven installed underneath it, and do I need a heat-resistant cable because of the temperature between them?

Use a normal flexible appliance cable, preferably H07RN-F, with 2.5 mm² conductors; a fireproof cable is not needed because the temperature between the hob and oven should not be dangerously high, and standard cable is rated for 70°C [#16970599][#16970601][#16972293] If the hob is already wired with 5x2.5 in the wall, that is enough for the hob, and a separate 4x2.5 flexible cable can be used for the oven connection where needed [#16970601][#16972408] Make the connection in a proper cooker connection box or terminal strip with good clamping rather than a loose cube; one reply also said Wago is acceptable, but the thread favored solid, well-secured terminals [#16972646][#16972293][#16972408]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16967900
    Mrozan
    Level 9  
    Posts: 7
    Rate: 7
    Hello, as in the subject, I do not mean cross-section because I know that I have to give 5x2.5 and that's really enough 4x2.5 because my motherboard uses only 2 phases, but I have a problem because I will have an oven under the plate and I wonder if the cord OW or maybe some fireproof one because between the plate and the oven (how it will be running) it will be quite high temperature, please advise, thank you in advance, greetings Krzysiek
  • ADVERTISEMENT
  • #2 16968332
    mawerix123
    Level 39  
    Posts: 4143
    Help: 482
    Rate: 949
    Why do you need a fireproof cable :?: furniture you have non-flammable :?:
    At what high temperature you talk over the oven :?: I have a furniture board above the oven and, despite several years of operation, it has not burned. The oven throws warm air into the front.
  • ADVERTISEMENT
  • #3 16970566
    Mrozan
    Level 9  
    Posts: 7
    Rate: 7
    Hello, I mean that I do not know what will be the remperatura there, i.e. the guest makes me furniture and we assemble the oven to the bottom and induction hob and I want to connect the plate only I do not know what the temperature will be between the plate and the oven. ....? such free space as there will be in this space, etc., and therefore I do not know if it is OMY, OWY or OW wire, does it matter? please help
  • ADVERTISEMENT
  • #4 16970579
    icosie
    Level 34  
    Posts: 1908
    Help: 298
    Rate: 239
    I would suggest an electrician, because this is not just about the cable, but also about the protection in the switchgear with over-current circuit breakers.

    We do not know the power, we do not know the network layout, it's hard to do something. Because we will find that non-flammable, and they will still ignite as it will be badly made.

    greetings
  • #5 16970591
    Mrozan
    Level 9  
    Posts: 7
    Rate: 7
    New apartment, wires in the wall 5x2,5, no other changes I will not do, but thanks.
  • Helpful post
    #6 16970599
    MARCIN.SLASK
    Home appliances specialist
    Posts: 11851
    Help: 1030
    Rate: 2632
    I usually use H07RN-F. It is not cheap (4 * 2.5mm? approx. 5.50 PLN / m, 5 * 2.5mm? approx. 6.50 PLN / m). Prices in supermarkets can be twice as large. But once a decent cable is used, well connected (cable terminals to the ends of individual wires, good quality terminal strip).
    A better cable is not needed. This one is durable, flexible (it fits nicely behind the furniture, in the event of removing the equipment there are no problems that YDY holds it rigidly).
  • #7 16970601
    icosie
    Level 34  
    Posts: 1908
    Help: 298
    Rate: 239
    In this case, the usual 5x2.5mm is properly connected to the board. You do not need a non-flammable, because the usual one has the right operating temperature (70 ° C), and there should be no more around the oven.

    It does not make sense to use 4x2,5mm, because if you have to replace the plate, you will have to make a new cable.

    Plus the board should probably be mounted immediately to the cable from the wall, without sockets and connectors, but I can be wrong.
  • ADVERTISEMENT
  • #8 16970618
    zein
    Level 10  
    Posts: 115
    Rate: 23
    First of all, the standard clearly states that every such device must be connected with a flexible cable, the old OWY etc. after the new H07RN-F. Sometimes 5x ... will be cheaper than 4x ... because it is a bit less popular, I recommend definitely wholesalers than castoramy etc.
  • #9 16970713
    kkas12
    Level 43  
    Posts: 17356
    Help: 1073
    Rate: 4262
    Today, most producers of plates and ovens equip them with a power cord.
    If the motherboard is / can be powered with one phase and the producer on the plug's cable does not mount it under any circumstances, it should not be mounted.

    The same power supply to the board should be made with a 5x4mm2 cable.
    However, if the board requires two phases, it does not mean that the remaining free phase can be used to supply the oven. These are two separate receivers that need to be powered by two separate circuits.

    However, it may turn out that the manufacturer has produced a "combine" in which the oven joins the stove and the stove is fed with three phases and that it requires only two phases for proper operation.
    In such and only such a case, the free phase can be used to supply the oven.

    And if the device is connected to the network without a socket connection, the use of an RCD switch is not required.
    Of course, if the TN system.
    If the TT is the RCD, it should be used as much as possible.
  • #10 16970980
    MARCIN.SLASK
    Home appliances specialist
    Posts: 11851
    Help: 1030
    Rate: 2632
    kkas12 wrote:


    The same power supply to the board should be made with a 5x4mm2 cable.
    However, if the board requires two phases, it does not mean that the remaining free phase can be used to supply the oven. These are two separate receivers that need to be powered by two separate circuits.


    There is no need to overdo it with 5 * 4mm?. As we connect on 3 phases, the max current on any phase will not be bigger than 16A, it will calmly 5 * 2.5mm? will be enough. 4mm? we use, for example, a board with a maximum power of 7600W, we use one phase.
    These devices are designed so as not to exceed 16A on one phase. As we have an oven and plate set, two phases are for the plate and one phase for the oven. Sometimes the oven has a total power of heaters above 3800W, but then the electronics cyclically switches the heaters to evenly heat, but not to exceed the current of 16A.
  • #11 16971079
    kkas12
    Level 43  
    Posts: 17356
    Help: 1073
    Rate: 4262
    Yes, I am not talking about what is today, but what is tomorrow.
    And then it may turn out that today's oversizing of the cross-section tomorrow will result in the lack of another thread with the appeal: Save, but no forging goes into play.
  • #12 16971643
    mawerix123
    Level 39  
    Posts: 4143
    Help: 482
    Rate: 949
    Gentlemen, maybe a little exaggerating the author does not put a wire from the switchgear to the junction box and he just wants to choose TYPE wires between this can and the board.

    icosie wrote:
    We do not know the power, we do not know the network layout, it's hard to do something. Because we will find that non-flammable, and they will still ignite as it will be badly made.


    And why do you need this data for choosing the type of wire :?:

    Mrozan wrote:
    I just do not know what the temperature will be between the plate and the oven .....?


    No worries it will not be dangerously high. You can choose the cable proposed in post # 6.
  • #13 16971693
    MARCIN.SLASK
    Home appliances specialist
    Posts: 11851
    Help: 1030
    Rate: 2632
    kkas12 wrote:
    Yes, I am not talking about what is today, but what is tomorrow.
    And then it may turn out that today's oversizing of the cross-section tomorrow will result in the lack of another thread with the appeal: Save, but no forging goes into play.


    Yes. You're right. I thought you were writing about a piece of cable from the can to the disc / oven. From the switchgear to the box should go 5 * 4mm?. But then 5 * 2.5mm? is enough for an oven / ceramic / induction hob.
  • #14 16972279
    Mrozan
    Level 9  
    Posts: 7
    Rate: 7
    Hi, I bought Amica
    Connection to 400 V 2N power supply, 230 V connection, * 230 V connection required 32 A protection
    Connection power [W]: 7400
    Control: Sensor
    Used cooking zones:
    18.0 cm induction booster box (1.2 / 1.4 kW)
    22.0 cm induction booster box (2.0 / 2.5 kW)
    18.0 cm induction booster box (1.2 / 1.4 kW)
    22.0 cm induction booster box (2.0 / 2.5 kW)

    there is no conversation about the oven because it is on 230V and has a separate socket,
    and what about the 5x4mm cable is probably a slight exaggeration as in the wall I have 5x2,5 what's the sense ???
    Gentlemen, I mean only that I have no idea what the temperature will be between the oven and the plate and I'm afraid that if the wife starts the oven at 200C for example 2h is the temperature between these devices will not be too high, I am not a furniture designer, etc., best regards
    PS instead of ankle I wanted to use WAGO connectors ???
  • #15 16972293
    zein
    Level 10  
    Posts: 115
    Rate: 23
    Everything will be ok with the temperature.

    Wago is also ok

    Connect with a 2.5mm2 flexible cable.
  • #16 16972408
    kkas12
    Level 43  
    Posts: 17356
    Help: 1073
    Rate: 4262
    Mrozan wrote:
    and what about the 5x4mm cable is probably a slight exaggeration as in the wall I have 5x2,5 what's the sense ???
    After all, it is clear from my statements that when I wrote about the 4mm2 cross section, I meant what was in the wall.
    And you can use 4x2,5mm2 to connect the oven.
    Wago yes, but to the links.
    Only why are there cans mounted both n / t and ip / t, which are used to connect such receivers as the cooker. They have the advantage that (at least in theory) they make it impossible to pull out the wire when ejecting the device from the body.
    It should be remembered that the protective vein was longer than the others, both in the can and in the oven, because if for some reasons the cables were torn out, it is to lose the continuity as the last one.
  • #17 16972583
    Mrozan
    Level 9  
    Posts: 7
    Rate: 7
    kkas12
    I have p / t but there is a 5x2.5 wire terminated with the cheapest cube and nothing is blinded, so you can tear it out very easily, and as for the weight you can use it like I have a wire on the wall and a cable ...?
  • #18 16972627
    MARCIN.SLASK
    Home appliances specialist
    Posts: 11851
    Help: 1030
    Rate: 2632
    I saw new installations made by electricians from the cooperative, where it was 4 * 1.5mm?. I do not know who picked it up ...

    Buy a solid 4mm? strip (hard, strong material, the right amount of metal about 5-7 PLN), 2.5mm? insulated terminals (or not) on individual wires (about 8-10gr / pc) so that the cables are properly clamped in the strip. WAGO I would give up. I only use them in lighting circuits. Here you have high currents and the proper contact of the connection must be.
  • Helpful post
    #19 16972646
    Łukasz-O
    Admin of electroenergetics
    Posts: 21783
    Help: 654
    Rate: 4278
    It has long used cans, typically for connecting discs:
    link
    Induction Hob Wiring: 5x2.5 or 4x2.5 Wire Type, Heat Resistance for Oven Placement - Advice
    It comes in a normal installation box, has clamps, a holder for fixing the receiver's power cord and a hole from the bottom.
  • #20 17004536
    Mrozan
    Level 9  
    Posts: 7
    Rate: 7
    Hello, thank you very much for all the help but after counting it would make me around 40-50 zlotys and the electrician with papers connected me for 90 zlotys with a cable and concealment guarantee, so I recommend looking for a cheap electrician, but thank you again for your help.

    subject to be closed.

Topic summary

✨ The discussion revolves around the appropriate wiring for an induction hob and oven installation, specifically whether to use 5x2.5 or 4x2.5 wire types, considering heat resistance due to proximity to the oven. The original poster expresses concern about potential high temperatures between the induction hob and the oven, seeking advice on suitable wire types (OW, OWY, or fireproof). Responses suggest using H07RN-F flexible cable, which is durable and suitable for high temperatures, with 5x2.5mm being adequate for the setup. Experts recommend consulting an electrician for proper installation and emphasize the importance of using the correct wire gauge to prevent overheating and ensure safety. The discussion also touches on the necessity of separate circuits for the oven and hob if they require different phases.
Generated by the language model.

FAQ

TL;DR: Use a flexible H07RN‑F cable and size for approx. 70°C service; “the usual one has the right operating temperature (70°C).” Keep oven and hob on separate circuits unless the unit is designed otherwise. [Elektroda, icosie, post #16970601]

Why it matters: This prevents overheated wiring, nuisance trips, and costly rework when replacing or upgrading appliances.

Who this is for: DIYers and installers wiring an induction hob above an oven, choosing cable type, size, connectors, and protection.

Quick Facts

What wire type should I use between the junction box and an induction hob?

Use a flexible cable, such as H07RN‑F. Standards and installers favor flexible cords for appliance connections because they tolerate movement and routing behind cabinets. Buy from a wholesaler rather than a big-box store for better availability and pricing. [Elektroda, zein, post #16970618]

Is 5×2.5 mm² or 4×2.5 mm² enough for an induction hob?

Run a 5×2.5 mm² flexible cable to the hob. It covers typical multi‑phase hookup and simplifies future replacements. Using 4‑core limits options if you change appliances later, forcing a re-cable. “It does not make sense to use 4×2.5 mm².” [Elektroda, icosie, post #16970601]

Will heat from an oven under the hob damage the cable?

No. Behind a properly installed oven and hob, temperatures remain below typical cable ratings. Experienced installers report it “will not be dangerously high.” Route the flex cleanly between the units and avoid direct contact with hot surfaces. [Elektroda, mawerix123, post #16971643]

Can I power the oven from the spare phase feeding a two‑phase hob?

Treat hob and oven as two separate receivers on two separate circuits. Only combined factory‑designed units may share phases internally. Otherwise, do not repurpose a free phase from the hob feed for the oven. [Elektroda, kkas12, post #16970713]

Do I need an RCD/GFCI if I hardwire the hob?

In TN systems, a hardwired connection does not mandate an RCD. In TT systems, use RCD protection. Follow your local supply system rules and manufacturer instructions. When unsure, consult a licensed electrician. [Elektroda, kkas12, post #16970713]

What current should I expect per phase on a multi‑phase hob?

Designs keep each phase at or below about 16 A. A 3‑phase connection spreads load so any phase stays within that current, aiding breaker coordination and cable sizing. [Elektroda, MARCIN.SLASK, post #16970980]

Are WAGO (spring) connectors OK for hob connections?

They can be used, and several installers report success. If you choose them, select the correct series and rating, and mount inside an enclosure rated for the location. “Wago is also ok.” [Elektroda, zein, post #16972293]

When should I avoid spring connectors and use a screw terminal strip instead?

For higher currents and heat-prone areas, prefer a solid screw terminal strip and crimped ferrules for strong, low-resistance joints. Poor contacts cause overheating and failures. “Here you have high currents and the proper contact of the connection must be.” [Elektroda, MARCIN.SLASK, post #16972627]

What is H07RN‑F cable?

It’s a heavy‑duty, flexible rubber‑sheathed cable suited for appliances. Installers favor it for durability, flexibility behind cabinets, and robust insulation. It routes neatly and avoids the stiffness of rigid YDY building wire. [Elektroda, MARCIN.SLASK, post #16970599]

How do I hardwire an induction hob with a junction box?

  1. Install a dedicated hob junction box with integrated clamps and cord strain relief.
  2. Terminate the flexible cable with crimp ferrules and connect L/N/PE to the internal clamps.
  3. Secure the cord in the holder, close the box, and connect the hob per its diagram. [Elektroda, Łukasz-O, post #16972646]

Should I use a socket or hardwire the hob?

Hardwire directly to the supply using a flexible cable and an appropriate junction box. Many hobs are intended for direct connection without a plug-and-socket interface, reducing weak points. [Elektroda, icosie, post #16970601]

What breaker size does a 7.4 kW, 230 V hob need?

Follow the nameplate. For the cited Amica 7.4 kW model, the manufacturer requires 32 A protection at 230 V. Always match the wiring diagram that comes with the appliance. [Elektroda, Mrozan, post #16972279]

Do new hobs and ovens include a power cord from the factory?

Many modern appliances arrive with a fitted power cord. If a cord or plug is not supplied, do not add one unless the manufacturer permits it. [Elektroda, kkas12, post #16970713]

How should I route and secure the protective earth (PE) conductor?

Make the PE conductor slightly longer in both the junction box and the appliance cavity. If tension pulls on the cable, PE stays connected last, preserving earthing until the end. [Elektroda, kkas12, post #16972408]

What if my wall feed is only 4×1.5 mm² from a previous install?

Do not reuse undersized circuits. High current loads need adequate section and secure terminations. Upgrade the circuit and use a quality terminal strip and ferrules to avoid overheating. [Elektroda, MARCIN.SLASK, post #16972627]

Is hiring a licensed electrician worth it for this job?

Yes. A licensed electrician can supply the correct cable, conceal routing, and provide a workmanship guarantee at modest cost, saving time and risk. [Elektroda, Mrozan, post #17004536]
Generated by the language model.