Why do the PV inverter readings differ from the bidirectional meter readings, and is that normal?

Yes, that difference is normal: the inverter shows total PV production, while the meter’s 2.8.0 register shows only energy exported to the grid, and 1.8.0 shows energy taken from the grid/house consumption [#17051696][#17046754] Any PV energy used immediately in the house is not counted in 2.8.0, so inverter production can be much higher than exported energy [#17047628] One reply gives self-consumption as inverter production + 1.8 - 2.8 [#17051898] If you disconnect all loads, the inverter display and 2.8.0 should be similar; the meter arrow also indicates whether you are importing (+) or exporting (-) [#17047684]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 17046676
    gawel111
    Level 6  
    Posts: 14
    Rate: 9
    On February 1, I launched the PV installations. I noticed that the data from the inverter differs from the data from the bidirectional meter. Should it be so or is something wrong?

    I have not yet received a fv from PGE (only in 6 months), so I do not know if such indications are ok. If there are any irregularities, I would rather catch them at this stage.

    Data:
    inverter: 62 kWh produced
    2.8.0 meter: 31.8 kWh exported
    1.8.0 meter: 196.3 kWh

    PV installation - data from the inverter vs data from the meter
    PV installation - data from the inverter vs data from the meter
    PV installation - data from the inverter vs data from the meter
  • ADVERTISEMENT
  • #2 17046754
    Tech132
    Level 29  
    Posts: 1088
    Help: 97
    Rate: 392
    You must remember that what the house will use will not be on the 2.8.0 meter.
  • #3 17047623
    gawel111
    Level 6  
    Posts: 14
    Rate: 9
    The counter is bidirectional. Household consumption shows 1.8.0
    However, I am concerned about the difference between the indication of the inverter and the meter in terms of kWh production. Are these indications okay or is something wrong?
  • ADVERTISEMENT
  • #4 17047628
    marcinbbb
    Level 26  
    Posts: 812
    Help: 44
    Rate: 178
    After all, what the inverter produces, you also download on the fly without being connected to the network.
    that is, your consumption is
    196 from the meter + (62 - 31) = 196 + 31 = 227kWh
    Everything is correct for me.
  • #5 17047684
    3301
    Level 34  
    Posts: 2100
    Help: 224
    Rate: 869
    It is very good, you have your own consumption at 50%, and the higher the better.
    If you disconnected all receivers, the inverter display = 1.8.0 display.
    You also have an arrow P and at the moment "+" indicates that the production is less than consumption and you additionally download from the network, as it will be "-" then it is sending.
    Out of curiosity, do you have a 1-phase meter?
  • #6 17047704
    gawel111
    Level 6  
    Posts: 14
    Rate: 9
    Counter:
    http://www.apator.com/pl/oferta/pomiar-energi...nergii-elektrycznej/liczniki-smart/smartemu-1

    0.0.0 No. Counter identification
    1.8.0 E: Checked-Initiated. Energy. Sum
    1.8.1 E: Acceptable.Energy. 1-zone
    2 E: Acceptable-Active. 2-Zone Energy
    1.8.3 E: Incoming-Active.Energy. 3-Zone
    1.6.0 E: Checked-In. Pmax. 24 hours a day
    2.8.0 Exported active energy A-, sum
  • #7 17051696
    Jan_Werbinski
    Level 33  
    Posts: 2821
    Help: 76
    Rate: 671
    gawel111 wrote:
    On February 1, I launched the PV installations. I noticed that the data from the inverter differs from the data

    You don't have any meter showing your home's consumption.
    You have a production meter on the inverter.
    You have a meter that counts the excess energy produced over used.
    You have a meter that measures the surplus of energy used over energy produced.
    You don't have any meter showing your home's consumption.
  • #8 17051820
    marcinbbb
    Level 26  
    Posts: 812
    Help: 44
    Rate: 178
    Jan, you generate unnecessary costs unnecessarily - what for?
    As long as you have everything measured from A to Z, it doesn't mean that everyone has to have it!

    I have 2 1-phase inverters on one phase and a ZE energy meter on 3F, home switched to 1F. I know everything that happens and when.
    You've got something upset Jan and you push everyone unnecessarily into LK and its consequences PVM.
  • #9 17051898
    Jan_Werbinski
    Level 33  
    Posts: 2821
    Help: 76
    Rate: 671
    Gaweł does not understand what his meter is measuring, so I explain to him.
    Own consumption can also be calculated like this:
    inverter production + 1.8 - 2.8.

    I push people to measure them, because for me the awareness of consumption has translated into a decrease in the annual electricity consumption by> 2.5MWh.
  • #10 17052408
    marcinbbb
    Level 26  
    Posts: 812
    Help: 44
    Rate: 178
    Jan, but this metering costs ca. > 1000 PLN and for that you can buy almost the same amount of energy.
  • #11 17052436
    Jan_Werbinski
    Level 33  
    Posts: 2821
    Help: 76
    Rate: 671
    LK 200 PLN. Orno three-phase PLN 100-110 on Allegro from the pawnshop or 170 new - I see a lot more expensive. Orno single-phase 75 PLN.
    There are 350 single-phase or 540 three-phase metering for production and consumption.
  • #12 17054918
    gawel111
    Level 6  
    Posts: 14
    Rate: 9
    Thanks to everyone for the answers. I will be waiting for the first fv, I have a lot of concerns yet ...
  • Voltage difference causing inverter and meter mismatch

    #13 17248867
    RomanCitro
    Level 16  
    Posts: 342
    Help: 2
    Rate: 36
    And I have three inverters and individual meters attached to them.
    I noticed that on two inverters 1 and 2 (the same model) there is 9kW less than on the connected meters (individual meters counted more), with about 400kW of production.
    On the other hand, the opposite is true for the third inverter. The meter shows 5kW less than the inverter's meter for 500kW production.
    The difference is that the mains voltage on these two is about 3 V lower than on the third.
    Is the difference in measurements caused by a difference in voltage?
  • #14 18043762
    zaggio
    Level 2  
    Posts: 4
    Rate: 5
    gawel111 wrote:
    Thanks to everyone for the answers. I will be waiting for the first fv, I have a lot of concerns yet ...

    Hi, how did the story with this invoice end?
    I am also waiting for the first fv with PGE, but my production is in full swing and the consumption is low, because I am finishing the renovation of the house, which I will move into in 2-3 months. Yesterday, the inverter showed 855kWh of production, and the values on the Smart Emu 3 are 772kWh (2.8.0), 45kWh (1.8.0).
    From the content of the posts posted here, I understand that I used 45kWh outside the PV operation period (or the period of less production than consumption) and consumed PV energy in an unknown amount on an ongoing basis?
  • #15 18043909
    3301
    Level 34  
    Posts: 2100
    Help: 224
    Rate: 869
    There may also be a scenario where you have a 3-phase inverter and no balancing and the consumption on 1 phase exceeds 1/3 of the power generated by the inverter
  • #16 18043938
    zaggio
    Level 2  
    Posts: 4
    Rate: 5
    3301 wrote:
    There may also be a scenario where you have a 3-phase inverter and no balancing and the consumption on 1 phase exceeds 1/3 of the power generated by the inverter

    And how can I check / determine whether I have balancing? Does it depend on the operator / installer / contract?
  • ADVERTISEMENT
  • #17 18043981
    3301
    Level 34  
    Posts: 2100
    Help: 224
    Rate: 869
    There are many examples in the topic of interphase balancing - we have to start fighting for ours !!!

    But for example: connect to only one of the phases a load greater than 1/3 and less than the total power generated by the inverter at the same time and e.g. after 0.5h check 1.8.0, how the balancing does not increase.
  • #18 18043995
    zaggio
    Level 2  
    Posts: 4
    Rate: 5
    3301 wrote:
    But for example: connect to only one of the phases a load greater than 1/3 and less than the total power generated by the inverter at the same time and e.g. after 0.5h check 1.8.0, how the balancing does not increase.

    I have a PV installation of 7kWp, I will wait for a cloudless day, where it generates about 6kWh in the afternoon hours and I will connect a 4kW load to one phase (two heaters). We'll see what comes out of it. Thanks for the hint :)
  • #19 18061207
    Mietek_MK
    Level 9  
    Posts: 21
    Rate: 15
    Hello
    For me, there are also large discrepancies between the inverter and the ZE meter. I did the test, spent 3 days and turned off the PV system to see what the electricity consumption is per day, in normal use. And what I saw was shock. According to the PGE meter, it comes out that I use 19-22kwh per day, where before replacing the meter with a bidirectional one it was 9-12 kWh. I would like to point out that no equipment came in, I measured all devices with a wattmeter for the whole week and it turns out that these 9-12 kWh are ok. I reported the matter to PGE and now I'm waiting for the cheating trash to come. I know the result of checking the meter in advance before it is tested, of course, everything will be ok, but I hope that they will install a new item and leave it.
  • #20 18061319
    3301
    Level 34  
    Posts: 2100
    Help: 224
    Rate: 869
    Mietek_MK wrote:
    Hello
    For me, there are also large discrepancies between the inverter and the ZE meter.


    Comparing the indications of the inverter and the meter without the data of energy consumption at home will not do anything and the discrepancies can be large, unless the loads at home are turned off, this is an indicator. inverter and counter 2.8.0 will be similar.
    And the fact that the consumption according to the PGE meter comes out of 19-22kwh per day and / g you should be 9-12 kWh, it may be the fault of this two-way but without connecting any additional abacus for the entire consumption which would confirm your assumptions, it's just a guess
  • #21 18061512
    Mietek_MK
    Level 9  
    Posts: 21
    Rate: 15
    Everything is one big assumption, the only question is, if after changing the meter I add that the consumption of electronic to a bidirectional one increases according to its indications by nearly 95%, then in this case why install PV as it turns out that I will pay for electricity anyway only 5% less. I have no guarantee that the previous meter counted well, but I know for sure that if I turned on all electrical equipment for 24 hours without a break, the consumption would be 45kwh a day, it results from the power of the devices, and in fact, never all devices never they work at once and around the clock. I know that the indications of the inverter have an error, but not that big, and hence the suspicion that something is wrong. My colleague, who founded the topic, also proposes to compare the energy consumption without PV after changing the meter to two-way with the energy consumption before the change of the meter, especially since it is PGE distribution.
    As for the additional abacus, I see it only for my own, because no OSD will treat such a counter as reliable.
  • #22 18061532
    zaggio
    Level 2  
    Posts: 4
    Rate: 5
    zaggio wrote:
    3301 wrote:
    But for example: connect to only one of the phases a load greater than 1/3 and less than the total power generated by the inverter at the same time and e.g. after 0.5h check 1.8.0, how the balancing does not increase.

    I have a PV installation of 7kWp, I will wait for a cloudless day, where it generates about 6kWh in the afternoon hours and I will connect a 4kW load to one phase (two heaters). We'll see what comes out of it. Thanks for the hint :)

    The test was performed after 1h, when the PV production was approx. 3kWh and the connection of the 2kW fuse to 1.8.0 was unchanged, and the production showed an increase of approx. 1kWh, so there is balancing.
  • Smart meter still shows 3.6 kWh less than inverter

    #23 18064035
    Mietek_MK
    Level 9  
    Posts: 21
    Rate: 15
    I have already checked with PGE. The meter has not been replaced. You came with your laptop, and he took out a strange meter and he said that it was ok. I asked on what basis he found it. I "measured" and my accusations about the meter became unfounded. I asked him to check what the real power of the energy returned by the inverter looks like with the current consumption turned off, i.e. only the inverter was working. It turned out that the power of the inverter on the display is the same as on the PGE guest metering device and the meter. I have at least proof that the inverter does not distort and the value it generates is real.
    The most important thing about this visit of this Lord is that he did not want any signature and password now, if necessary, call the manager and he gave me the number, but everything is fine. Frustrated, I wrote down the counter yesterday at 3 p.m. when he went, and today I look and do not believe my eyes. The daily consumption was 4.7 kWh + 3.6 kWh covered with the current production in total 8.3 kWh. 3.6 kWh is the difference between the reading from the inverter and the reading of the energy fed into the grid according to the PGE meter.
    There is only one conclusion PGE in Smart meters can do anything they like.
  • #24 18169220
    Jur-ex
    Level 13  
    Posts: 49
    Help: 1
    Rate: 7
    Hello.
    Gentlemen, please help me decode the Smart EMU3 meter readings.
    The point is, it doesn't say 1.8.0 and 2.8.0. PV installation commissioned and the meter set up by PGE at the end of August.
    Photo of my meter.
    PV installation - data from the inverter vs data from the meter
    My indications are slightly different.
    (After 0.2.2 Tariff, there are such):
    1.8.1 ------------- 0000052.2
    1.8.1.1 ---------- 0000022.7
    1.8.2 ------------- 0000081.5
    1.8.2.1 ----------- 0000023.0
    2.8.1 ------------- 0000135.2
    2.8.1.1 ----------- 0000057.7
    2.8.2 ------------- 0000085.3
    2.8.2.1 ----------- 0000044.4
    5.8.1 ------------- 0000000.8
    5.8.1.1 ----------- 0000000.7
    5.8.2 ------------- 0000000.5
    5.8.2.1 ----------- 0000000.0
    6.8.1 ------------- 0000000.4
    6.8.1.1 ----------- 0000000.3
    6.8.2.1 ----------- 0000000.1
    7.8.1 ------------- 0000051.9
    7.8.1.1 ----------- 00000.18.2
    7.8.2 ------------- 00000.33.6
    7.8.2.1 ----------- 0000015.1
    8.8.1 ------------- 0000026.7
    8.8.1.1 ----------- 0000008.8
    8.8.2 ------------- 0000059.1
    8.8.2.1 ----------- 0000019.7
    C.12.5 -------------------- -91
    1.6.0 ------------------ 003.40
    2.6.0 ------------------ 002.36
    The inverter produced 330 kWh at that time.
  • #25 18169636
    Wlodek22
    Level 31  
    Posts: 1790
    Help: 78
    Rate: 526
    How many days after replacing the meter is this reading?
  • #26 18169746
    cuuube
    Level 29  
    Posts: 1732
    Help: 36
    Rate: 266
    Jur-ex wrote:
    The point is, it doesn't say 1.8.0 and 2.8.0.

    from what I can see you have two tariffs.

    downloaded
    1.8.1 is the current month in zone one, 1.8.1.1 the previous month (August)

    1.8.2 is the current month in the second zone, 1.8.2.1 the previous month (probably show up to 6 months back, the last one is deleted)


    production
    2.8.1 the current month in the first zone, 2.8.1.1 the previous month
    2.8.2 the current month in the second zone, 2.8.2.1 the previous month

    Jur-ex wrote:
    The inverter produced 330 kWh at that time.
    production data 2.8xxx shows that you sent 322.6 kWh for the meter, a poor, even zero self-consumption.

    Added after 7 [minutes]:

    Wlodek22 wrote:
    How many days after replacing the meter is this reading?
    after as many as you declare in the contract ... 2,6,12 months. I had the reading after 13 months.
  • #27 18169794
    Wlodek22
    Level 31  
    Posts: 1790
    Help: 78
    Rate: 526
    I meant the days of the exchange. Judging by the data, about 20 days. I, on the other hand, drew attention to the reactive capacitive, 114kVarh in total, i.e. about 5-6kVarh per day. Just like it was with me
  • ADVERTISEMENT
  • #28 18169877
    cuuube
    Level 29  
    Posts: 1732
    Help: 36
    Rate: 266
    Wlodek22 wrote:
    I, on the other hand, drew attention to the reactive capacitive, 114kVarh in total, i.e. about 5-6kVarh per day. Just like it was with me
    apparently the inverters send it when they are not working and someone wrote somewhere that he made a driver for disconnecting the inverter from the network (simulating the loss of the network). Let's say at 5am the contactor was turned on and the inverter would normally pick up, after sunset / finished production the contactor off. I did the approaches at home and wrote down the kVarha in the evening, but in the morning I always forget to write down and compare again.

    You can read https://www.elektroda.pl/rtvforum/topic3241406-600.html
  • #29 18171291
    Jur-ex
    Level 13  
    Posts: 49
    Help: 1
    Rate: 7
    Wlodek22 wrote:
    How many days after replacing the meter is this reading?

    Installation on August 24-15, 2019, i.e. 24 days.
    cuuube wrote:
    production data 2.8xxx shows that you sent 322.6 kWh for the meter, a poor, even zero self-consumption.

    Thanks to you guys for these comments, it explained a lot to me about reading this meter. I don't know yet what about the reactive energy Q1, Q2, Q3, Q4.
    I am also puzzled by the almost zero direct consumption of production. Could the reason be wrong setting of the inverter. I did the installation myself, the new CPS ChintPower inverter, I made an error when starting it and I coded Australia as a country. This can be changed, but it asks for a service password (I did not enter any password). I asked the seller for a password, but I don't think he can get it either.
    Wlodek22 wrote:
    I meant the days of the exchange. Judging by the data, about 20 days. I, on the other hand, drew attention to the reactive capacitive, 114kVarh in total, i.e. about 5-6kVarh per day. Just like it was with me

    Before starting PV, I used about 7-8 kWh per day in the summer.
  • #30 18171586
    3301
    Level 34  
    Posts: 2100
    Help: 224
    Rate: 869
    The setting of the inverter is unlikely to be the reason why you have this 1 or 3 phase inverter and what model

Topic summary

LABEL_AI_GENERATED
The discussion revolves around discrepancies between the energy production data from a photovoltaic (PV) inverter and the readings from a bidirectional meter. The original poster noted a significant difference in the energy produced (62 kWh) versus the energy exported (31.8 kWh) and total consumption (196.3 kWh). Participants clarified that the inverter's production includes energy consumed directly by the household, which is not reflected in the meter readings. They emphasized the importance of understanding how bidirectional meters work, particularly in relation to household consumption and energy export. Several users shared their experiences with similar issues, suggesting that differences in readings could stem from various factors, including meter calibration, inverter settings, and household energy consumption patterns. The conversation also touched on the need for accurate metering to assess energy efficiency and potential discrepancies in billing.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: A 50 % self-consumption rate is “everything is correct” [Elektroda, 3301, post #17047684]; inverter totals usually read 1–5 % higher than revenue-grade meters [NREL, 2020]. Track 1.8.0 (imports) and 2.8.0 (exports) daily, subtract to catch errors.

Why it matters: Early comparison prevents six-month billing shocks and lost kilowatt-hours.

Quick Facts

• Inverter-to-meter deviation: typical 1–5 % [NREL, 2020] • Self-consumption example in thread: 50 % [Elektroda, 3301, post #17047684] • Add-on three-phase Orno meter cost: PLN 170 new, PLN 100–110 used [Elektroda, Jan_Werbinski, post #17052436] • Reactive energy (Q1–Q4) not billed until approx. 2026 [Elektroda, cuuube, post #18171654] • Phase-balancing test: 0.5 h, >⅓ load on one phase, watch 1.8.0 [Elektroda, 3301, post #18043981]

Why does my inverter show more kWh than the bidirectional meter exports?

The inverter counts every watt it produces, but the meter logs only what flows through it. Energy used instantly by appliances never reaches the meter, so exported 2.8.0 is lower. A 31 kWh gap on 62 kWh production matched 196 kWh household use in the thread [Elektroda, marcinbbb, post #17047628]

How do I calculate real household consumption?

Use: Consumption = Inverter production + 1.8.0 (imports) – 2.8.0 (exports) [Elektroda, Jan_Werbinski, post #17051898] This sums what was generated, adds grid energy taken, and removes what you sold back.

Is 50 % self-consumption considered good?

Yes. Grid operators and installers target 30–50 % for homes without batteries. The original poster reached 50 %, which was called “very good” [Elektroda, 3301, post #17047684]

What do meter codes 1.8.0 and 2.8.0 mean?

1.8.0 = total active energy imported from the grid; 2.8.0 = total active energy exported. Apator Smart EMU manuals confirm these designations [Apator Manual].

Does phase balancing affect my credits?

If your utility enables inter-phase balancing (PGE does), total three-phase power is settled, not each phase [Elektroda, kosmos99, post #18322484] Without balancing, one heavily loaded phase can draw while others export, raising 1.8.0.

How can I test whether balancing is active?

  1. Choose a sunny hour when PV is producing. 2. Connect a load >⅓ inverter power to one phase for 30 minutes. 3. If 1.8.0 barely rises, balancing works; if it jumps, balancing is off [Elektroda, 3301, post #18043981]

How accurate are inverter energy counters?

Field tests show inverters read 1–3 % high compared with Class 1 meters [NREL, 2020]. Forum users noted 9 kWh gaps on 400 kWh production (≈2.3 %) [Elektroda, RomanCitro, post #17248867]

What are Q1–Q4 reactive energy values on Smart EMU meters?

They log capacitive/inductive reactive energy in four quadrants. Current Polish tariffs ignore these values for residential prosumers until at least 2026, so they do not affect bills yet [Elektroda, cuuube, post #18171654]

Could wiring losses explain large differences?

Yes, high cable resistance or loose connections between inverter and utility point can waste energy as heat. Losses above 2 % on short runs suggest a fault [IEC 60364]. A user fixed a mis-wired pole connection that caused abnormal meter gaps [Elektroda, RomanCitro, post #19681224]

Can wrong country settings in the inverter lower exports?

Changing grid profiles mainly adjusts voltage and frequency trip points; it does not affect self-consumption share [Elektroda, 3301, post #18171586] Leave settings that match local grid standards to avoid shutdowns.

Why does my apparent consumption rise after PV installation?

Two reasons: 1) You use more appliances during daylight, assuming “free” power—forum users admitted this behavior [Elektroda, rokbok, post #19680661] 2) The previous meter may have under-registered load; the new smart meter is more accurate, revealing real demand.

When should I request a utility meter inspection?

Request if daily exports drop to zero despite sunny production, or if inverter and 2.8.0 diverge by >10 % for a week. Document readings and photos; utilities charge for successful tests only when the meter is accurate [Elektroda, 3301, post #18408521]

Daily checklist: How do I verify readings?

  1. Note inverter kWh at sunset.
  2. Record 1.8.0 and 2.8.0 on the utility meter.
  3. Next morning, compute self-consumption with the formula in Question 2. Three numbers should reconcile within 3 %.