  • #1 17494404
    lisu24
    Level 9  
    Hello
    I will start with the fact that I am a layman in the subject and I do not know anything about it, but to the point. I have a coal and wood stove, an open system with an overflow vessel. I keep dripping water from this blue-cap valve. Can anyone tell what the reason could be, or will replacing this valve solve the problem?

    Water Dripping from Safety Valve on Coal & Wood Stove (Open System): Possible Reasons & Fixes
  • ADVERTISEMENT
  • #2 17494743
    piracik
    VIP Meritorious for electroda.pl
    No air pre-pressure in the expansion vessel. A white pot.
    You have to turn off the cold water supply, turn on the hot water tap and pump air into the canister until the pressure gauge shows 3 bars and the tap water stops flowing.
  • #3 17495154
    lisu24
    Level 9  
    I combined the white canister in all ways, pumped 2 bars then 3 bars and the dripping did not stop. What I noticed, the hotter the water in the canister, the less dripping is. other cause?
  • ADVERTISEMENT
  • #4 17495197
    Edzien
    Level 9  
    Lisu24, I have the same problem, but on an open circuit.
    It just dripped from time to time, especially when it was "horny".
    I bought a new one for about PLN 20 and replaced it, the problem repeated again.
    I don't have much time to rummage, I put the bucket in and it drips like that for a month.
    But I join the topic.
  • #5 17495214
    darek.jacek
    Level 13  
    Why an open circuit safety valve?
  • ADVERTISEMENT
  • #6 17495251
    lisu24
    Level 9  
    I also have an open system, I have the same patent (a bucket of this dripping can fill up in a few days). If not the valve, what could be the problem?
  • #7 17495316
    piracik
    VIP Meritorious for electroda.pl
    You write about an open system but a CO system. You are dripping from the DHW valve!
    lisu24 wrote:
    if not the valve, what can be the problem?

    Did you do what I wrote? There is no improvement?
  • #8 17495570
    Edzien
    Level 9  
    Piracik is correct, the safety valve is leaking on the water supply system to the boiler (heat exchanger) - i.e. in the DHW system.
    Maybe you know what the reason is?
  • #9 17495612
    lisu24
    Level 9  
    piracik wrote:
    You write about an open system but a CO system. You are dripping from the DHW valve!
    lisu24 wrote:
    if not the valve, what can be the problem?

    Did you do what I wrote? There is no improvement?

    I did, the dripping continued.
  • #10 17495620
    goldzik15
    Level 16  
    Do you have a pressure gauge somewhere on cold water? Put on the inflation gun without draining the water and what pressure will show. Do you have a reducer at the entrance or your own well?
  • #11 17495671
    piracik
    VIP Meritorious for electroda.pl
    If you have done exactly as described and it is still dripping, it may mean that the liquid has been flowing for so long that the valve has become covered with limescale and needs to be replaced
  • #12 17495715
    roman 18
    Level 24  
    Colleagues, if it drips for a long time, the safety valve will have to be replaced (Piracik is right). But if it drips after replacing the valve, the diaphragm cap must be replaced because the diaphragm in it is broken. To check it, press the valve in the air pumping vessel, if there is water, it should be replaced. greetings.
  • #13 17496236
    lisu24
    Level 9  
    goldzik15 wrote:
    Do you have a pressure gauge somewhere on cold water? Put on the inflating gun without draining the water and what pressure will show. Do you have a reducer at the entrance or your own well?

    I do not have any manometer that would show the pressure in the network, I can only check the temperature, the water is from the water supply network, I have two valves on the supply.
    As for the vessel, when you press the valve, only air escapes, water does not appear.
    If I want to replace the valve, should I first drain all the water from the tank (250l)? How to do it correctly?
  • #14 17496331
    roman 18
    Level 24  
    Buddy, you don't need to drain the water at all, turn off the boiler feed valve (cold), but remember to keep the hot water taps closed, then turn the safety valve hood to release the pressure. To be sure, you can use another person to hold a vessel under this valve, because when you unscrew the valve, the water may flow a little, but it will be without pressure and quite lazily, then you screw in a new valve and the problem is over. greetings.
  • #15 17496402
    MANTA20E
    Level 16  
    Hello

    I noticed that you are raving about a primitive DHW safety valve ...

    Our colleague "lisu24" did not write how old this installation is ....
    After some time of use, this valve will start to leak anyway ... probably from old age ..

    Buddy "lisu24" tomorrow to the plumbing store for a new safety valve and a small roll of Teflon tape to seal the thread.

    Before replacing the valve, do not forget to first shut off the water supply to the tank and then release the pressure from it by emptying it of water.

    From what you can see in the photo you posted, it is a standard safety valve, rather 1/2 inch in size and water discharge pressure from 4 to 5 kg / cm2 ....

    Well, unless your domestic water pressure is higher ... then you need a valve above 5 kg / cm2
  • #16 17496448
    Homo_toxicus
    Level 26  
    What is the pressure of this valve (?) And is it screwed into the boiler connection?

    I have the impression that we are looking at a picture of a boiler with two coils and a valve screwed into a stub pipe. If this valve protects the boiler against pressure build-up in this way, dripping while heating may be normal, apart from the "interesting solution". :-)
  • #17 17496470
    MANTA20E
    Level 16  
    roman 18 wrote:
    Colleagues, if it drips for a long time, the safety valve will have to be replaced (Piracik is right). But if it drips after replacing the valve, the diaphragm cap must be replaced because the diaphragm in it is broken. To check it, press the valve in the air pumping vessel, if there is water, it should be replaced. greetings.


    To my friend "roman18" .........

    What does "gingerbread for the windmill" etc ... etc ....
    I propose to recall ANOTHER what the diaphragm tank connected to the DHW tank is for ...

    In the case that "lisu24" described it is unnecessary ...
  • #18 17496476
    Homo_toxicus
    Level 26  
    MANTA20E wrote:
    .... I suggest you to remember ANOTHER what the diaphragm tank connected to the DHW tank is for ...


    We don't really know where that white diaphragm reservoir is plugged in.
  • #19 17496549
    MANTA20E
    Level 16  
    Hello
    To my friend "Homo_toxicus"

    In the case of CO installations in an open system, what we deal with in the case of my colleague "Lisu24", diaphragm pressure vessels are not used ... (the name says an open system - read - without pressure)

    We attach the DHW tank to this system, in which we already have the pressure of the water supply network ... and then ... by heating the water with the CO stove in this tank, we increase the pressure in the DOMESTIC HOT WATER (DHW) system.
    To overcome the so-called arrows in the pipes after opening the DHW tap, we use equalizing tanks with an airbag.

    So at our very nice friend "Lisu24" there is no other option for the existence of this diaphragm tank ....
  • #20 17496560
    lisu24
    Level 9  
    The tank with valves was installed less than 2 years ago, the valve drips regardless of whether the water is heated or not (I would say that the more the water cools, the more it drips) the tank has one coil. The expansion vessel is pulled up with the lowest pipe to the tank drain valve .

    Water Dripping from Safety Valve on Coal & Wood Stove (Open System): Possible Reasons & Fixes Water Dripping from Safety Valve on Coal & Wood Stove (Open System): Possible Reasons & Fixes
  • #21 17496583
    Homo_toxicus
    Level 26  
    MANTA20E wrote:
    .... In CO installations in an open system, which is what we deal with in the case of my colleague "Lisu24", diaphragm pressure vessels are not used .... (the name says an open system - read - without pressure) ....


    I return my honor :-) . I wrote too quickly :-)
  • #22 17496599
    roman 18
    Level 24  
    My mantana, read carefully and understanding what other people write, or stay silent. Greetings.
  • #23 17496622
    MANTA20E
    Level 16  
    Hello
    Buddy "lisu24", do not worry about the discussions that were created here on the forum ...
    As I wrote earlier, slide for a new safety valve and that's it ...

    It will definitely take care of your problem.
    You still have to take into account the quality of the currently sold products, since your installation is only 2 years old, maybe you got a crap ..... in the form of a valve ...
    In my case regarding the BZ valve it was like this:
    the first valve installed in 1999 (it lived until the end of the tank's life)
    the next one in 2010 after replacing the tank with a double-walled ...
    another one in 2015
    and now another one in 2017 to the same tank ...

    So we have a picture of the quality of the hydraulic components ...... in relation to modern technical thought ...
    It is going to break pretty quickly so you have to get another one .....

    greetings
  • #24 17496643
    lisu24
    Level 9  
    Ok, now I am repeating the question whether I have to drain all the water from the tank or do I just turn off the water supply and can I turn it off?
  • #25 17496653
    MANTA20E
    Level 16  
    roman 18 wrote:
    My mantana, read carefully and understanding what other people write, or stay silent. Greetings.


    Hello
    No offense ... read with understanding ...
    You suggested to your buddy replace the expansion tank too early ...


    greetings
  • #26 17496666
    grzmak
    Level 11  
    I had the same story. For me, the pressure in the water supply system is too high. The expansion vessel did not help. I had 5.5 bar in the network. I put on the reducer, pressure 2.5 bar and forgot the dripping. Check the water pressure in the network.
  • #27 17496673
    roman 18
    Level 24  
    Buddy lisu24, two hours ago I wrote how to do it. Buddy, you still do not read the mantana with caution, I wrote that when the water flies with a valve, it must be replaced. Greetings.
  • #28 17496720
    MANTA20E
    Level 16  
    Hello

    As one of our colleagues said before, you don't need to drain all the water from the tank .....

    Question:
    Will you do it yourself ... do you have someone to help ...

    First, cut off the water supply to the tank, then unscrew the lowest taps to release the pressure, when the water stops flowing from them, close them.

    Option one: you do it yourself ... unfortunately you have to empty the water tank to the level of the valve you want to replace ....,

    Option two: with the help of another person ---

    you unscrew the valve and your assistant blocks the water leak from the tank with his hand / cloth / or something else at hand ... unfortunately ...
    Remember that the valve must be previously prepared for screwing, wound with Teflon, etc.
  • #29 17496759
    lisu24
    Level 9  
    grzmak wrote:
    I had the same story. For me, the pressure in the water supply system is too high. The expansion vessel did not help. I had 5.5 bar in the network. I put on the reducer, pressure 2.5 bar and forgot the dripping. Check the water pressure in the network.

    How do I check the power pressure? I have a tap at the beginning of the power supply and the water from it is flying very strongly as it decontaminates it.
  • ADVERTISEMENT
  • #30 17496767
    BrodowskiG
    Level 22  
    There are three options:
    -high network pressure .... install a reducer
    -problems with the expansion vessel ... a damaged membrane (the water will fly through the valve when the air is released) or bad air pressure (inflate without water pressure and check the vent.with low air pressure, you can give the water pressure and measure what is in the network and it should be air pressure when there is no water pressure)
    - defective safety valve (replace ... with the appropriate pressure)
    and you make a doctorate out of it.

Topic summary

Water dripping from the safety valve of a coal and wood stove in an open system can be attributed to several factors, including insufficient air pre-pressure in the expansion vessel, high water supply pressure, or a defective safety valve. Users suggested checking the pressure in the water supply system, as excessive pressure (noted as high as 5.5 bar) can lead to leaks. If the valve has been leaking for an extended period, it may need replacement due to wear or limescale buildup. When replacing the valve, it is not necessary to drain the entire tank; instead, shut off the water supply and release pressure by opening taps. A pressure reducer may also be installed to mitigate high supply pressure issues.