How much air should I put in a 300 L galvanized hydrophore tank, and what pressure should the pump switch on and off at?

Set the air cushion to about 150–170 kPa (1.5–1.7 bar) with the tank drained: turn the pump off, run water out until air starts escaping, close the outlet, then inflate the tank and turn the pump back on [#17549178] A commonly suggested switch setting was about 1.5 bar cut-in and 3.5–4 bar cut-out, and another reply reported a 2.2/4.2 bar setting on a similar system [#17548980] If you need about 1.5 bar at a tap on the second floor, the pump should start around 270 kPa because the height loss is about 1.2 bar for roughly 12 m [#17549208] The air cushion mainly changes how much water you get between pump starts; it does not by itself fix weak delivery to the upper floor [#17550253] If the upper floor pressure is still poor, check for undersized or clogged pipes, valves, or filters [#17549400]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 17548726
    Majcher123456
    Level 7  
    Posts: 20
    Rate: 33
    I have a galvanized tank 300l 0.5MPa. How much air to fill when it should turn on and off...
  • ADVERTISEMENT
  • #2 17548980
    stanislaw1954
    Level 43  
    Posts: 15245
    Help: 2013
    Rate: 4673
    Majcher123456 wrote:
    I have a 300l 5at galvanized tank
    I'm guessing it's the hydrophore tank.
    Majcher123456 wrote:
    How much air
    When it is empty, you do not need to fill it with air, just turn on the pump and fill the tank with the outlet valve closed. You can possibly finish the air earlier by 1 -1.5 atm.
    Majcher123456 wrote:
    when should it turn on and off...
    It depends on your preferences, but the recommended switch-on is the one with which, for example, a washing machine will work properly, so 1.5 atm, and the switch-off can be, for example, 3.5 atm, 4, atm
  • ADVERTISEMENT
  • #3 17548983
    mczapski
    Level 40  
    Posts: 6249
    Help: 468
    Rate: 1658
    So add where you intend to use this tank and under what conditions.
  • #4 17549081
    Majcher123456
    Level 7  
    Posts: 20
    Rate: 33
    I have a hydrophore in the basement, water will be taken to the first floor

    Added after 2 [minutes]:

    I have a hydrophore and a tank in the basement and the water will be collected on the first and second floor

    Added after 35 [minutes]:

    I have such a tank Galvanized Tank 300L 0.5MPa: Air Fill Quantity & On/Off Cycle Guidance
  • ADVERTISEMENT
  • #5 17549154
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    Do you have a water gauge?
    At what pressure does the pump start and at what pressure does it stop?
  • #6 17549168
    Majcher123456
    Level 7  
    Posts: 20
    Rate: 33
    Pressure valve lower 2.2 upper 42
  • ADVERTISEMENT
  • #7 17549174
    stanislaw1954
    Level 43  
    Posts: 15245
    Help: 2013
    Rate: 4673
    Majcher123456 wrote:
    Pressure valve lower 2.2 upper 42
    And what is that pressure valve
  • #8 17549178
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    You can do this:
    Turn off the pump
    Run water until you hear air escaping.
    Close the water outlet
    Inflate air to approximately 150-170 kPa
    Turn on the pump.
  • #9 17549181
    Majcher123456
    Level 7  
    Posts: 20
    Rate: 33
    Pressure switch 2.2-4.2
  • #10 17549193
    stanislaw1954
    Level 43  
    Posts: 15245
    Help: 2013
    Rate: 4673
    piracik wrote:
    You can do this:
    Turn off the pump
    Run water until you hear air escaping.
    Close the water outlet
    Inflate air to about 1.5 - 1.7 bar
    Turn on the pump.
    And you can justify it, because according to my knowledge, you can finish the air at any time (no matter what pressure is currently in the hydrophore), as long as the compressor "could do it". but what kind of compressor is it that won't make a pressure of several atm.?
  • #11 17549202
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    The justification is quite simple.
    To ensure that we use the maximum capacity of the hydrophore
    we need to set the pump to turn on when the mirror is already quite low, but not against the background low so that the air escapes from it.
    You can pump it up to the stick, but either we will get a small amount of water between starts, or for some time after pumping, before switching on the pump, it will shoot air from the taps, and by the way all the crap torn off the walls of the pipes.

    If we give half a bar of reserve until the air starts to escape, we are sure that the pump will be able to turn on and replenish the water before the outflow pipe is uncovered.
  • #12 17549203
    Majcher123456
    Level 7  
    Posts: 20
    Rate: 33
    I want to know how much air to fill and how to set the pump activation so that the water flows to the 2nd floor, because when the pump is activated, water flows like blood from the nose ...
  • #13 17549208
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    two floors of approx. 3m each plus ground floor and basement.
    Together you have 12m or 1.2bar
    If you want 1.5 bar at the top tap, the pump must start at 270 kPa
  • #14 17549222
    stanislaw1954
    Level 43  
    Posts: 15245
    Help: 2013
    Rate: 4673
    Majcher123456 wrote:
    I want to know how much air to fill and how to set the pump activation so that the water flows to the 2nd floor, because when the pump is activated, water flows like blood from the nose ...
    It can be seen from this that the problem is more with the on / off setting than with the lack of air.
    Why do you not want to tell the AUTHOR what your current setting is, because everyone who thinks knows that the problem of the 2nd floor is only - counting from the basement ceiling, something more than 5 m, so about 0.5 atm.
  • #15 17549387
    Majcher123456
    Level 7  
    Posts: 20
    Rate: 33
    The problem is with my parents at home as far as I know it's always been like this. air 2.4, he enjoined 2.4 was on and 5.0 was off measure ok. But recently there was something weak pressure completely drained the water and air pumped 2.4 and set the lower switch to 3.0 to make it faster he enjoined . But even if I unscrew the faucet on the 1st floor where it is first demolition water and is about to turn on the pump (3.2) it's a disaster
  • #16 17549400
    stanislaw1954
    Level 43  
    Posts: 15245
    Help: 2013
    Rate: 4673
    Sections too thin, or clogged pipes or valve.
    300 kPa in the basement, the storey above should be almost the same, so the cause lies somewhere else.
    Or are there filters?
  • #17 17549411
    Majcher123456
    Level 7  
    Posts: 20
    Rate: 33
    Mr. Stanislaw, and how to fill it with air correctly from the beginning and when to turn it on and off so that it was ok and I will continue to check
  • #18 17549468
    Krzys55
    Level 28  
    Posts: 1146
    Help: 89
    Rate: 303
    piracik wrote:
    You can do this:
    Turn off the pump
    Run water until you hear air escaping.
    Close the water outlet
    Inflate air to about 150-170kPa
    Turn on the pump.
    This is a bad hint, because if the air has not been finished for a long time and there is too little of it, you will never hear it, because it will not escape. You can finish with excess, and what will be too much will flow through the tap and the situation will stabilize. Pressure on 2 bar, off 400 kPa will be ok.
  • #19 17549486
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    So just add a point that if the water stops flowing, pump until it shoots, then close the valve and continue according to the list: /
    If we inflate it with excess, it can still shoot air for a week.
  • #20 17549581
    Krzys55
    Level 28  
    Posts: 1146
    Help: 89
    Rate: 303
    piracik wrote:
    If we inflate it with excess, it can still shoot air for a week.
    too much doesn't mean too much. Your phrase "until he shoots" is also overkill.
  • #21 17549605
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    If you paid a minimum of attention, you would notice that it "shoots" is 50 kPa lower than turning on the pump. So not an excess, but a safe stock.
  • #22 17549857
    wojtek1234321
    Level 36  
    Posts: 3554
    Help: 306
    Rate: 1133
    I remember that we used to have a 300 liter hydrophore, the rest of the installation was typical everywhere. I remember that to determine the amount of water in the hydrophore there was a small tap somewhere on 1/3 of the tank height and a pressure on/off switch nearby at the same height, hydrophore without "additional pumping" of air. The first filling or replenishment of the hydrophore in the event of a power failure and when too much water "went down" consisted in opening this tap, when the water level was raised by the pump to the level of the tap and it started to flow, it was enough to close it and the pump did the rest. She added enough water to get the pressure right. In the past, it seems to me that all these solutions were simpler, more user-friendly.
  • #23 17550253
    stanislaw1954
    Level 43  
    Posts: 15245
    Help: 2013
    Rate: 4673
    Majcher123456 wrote:
    how to fill it with air correctly from the beginning and when to turn it on and off so that it was ok
    There were questions about the tank here
    piracik wrote:
    Do you have a water gauge?
    They were also about setting the pumps on and off. So far I have only learned:
    Majcher123456 wrote:
    Pressure switch 2.2-4.2
    And this, I think, even in a two-story house, should be enough. And why does it not reach the upper floor (or very poorly)? The amount of air in the hydrophore, although also important, is "only" responsible for the amount of water drawn in one pump cycle.
  • #24 17566168
    telta
    Level 10  
    Posts: 19
    Help: 1
    Rate: 5
    So you have 3 floors. Pressure is one thing - old pipes, popular flexible hoses, etc., which reduces the cross section - but the amount of water taken from the tank between pump starts is important. It may be worth replacing the tank with a larger one. I have a ground floor and a first floor and the tank has almost 500 liters and with about 1.7 atm on the first floor, the pump turns on every 30 liters to a maximum of 3.5 atm pumping from 22 meters.
  • #25 17566264
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    Hydrophore 500 l and only 30 liters of water?
    You have too little air cushion.
  • #26 17566279
    stanislaw1954
    Level 43  
    Posts: 15245
    Help: 2013
    Rate: 4673
    It doesn't seem very effective to me either. From the 300 l tank, at the setting of 1.5 - 3.5 (maybe around 4) atm, with the initial boost of air, you can take about 6 buckets of water (10-12 l) or ~ 60-70 l.
  • #27 17569068
    telta
    Level 10  
    Posts: 19
    Help: 1
    Rate: 5
    That's true, but I need to have a water reserve if the electricity goes off. Then a small 1kw generator, compressors and you can bid.
  • #28 17569071
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    telta wrote:
    but I need to have a water reserve if the electricity goes out

    It's amazing how well you deceive yourself.
    With this small pillow you use 2x more electricity than you could.

    The motor at start can draw 6x the rated current.
    It is better to start the engine once every 1x5 min than 5x1 min.

    The next topic is changing the water in the tank.
    With such a small difference, it will not be replaced too often, which can lead to the development of all kinds of creatures.

Topic summary

LABEL_AI_GENERATED
The discussion revolves around the optimal air fill quantity and pump activation settings for a 300L galvanized hydrophore tank operating at 0.5MPa. Users suggest that the tank should be filled with air to approximately 150-170 kPa (1.5 atm) when the pump is off, and it should activate at around 270 kPa to ensure adequate water pressure reaches upper floors. The importance of maintaining a sufficient air cushion to prevent frequent pump cycling and ensure effective water delivery is emphasized. Various users share their experiences with pressure settings, indicating that a lower pressure setting for activation (around 2.2-3.0 atm) can lead to better performance, while also noting potential issues with pipe sizes and water flow rates.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: A 300 L hydrophore preset to 2.2–4.2 bar stores about 60–70 L of usable water per cycle ["safe stock", Elektroda, stanislaw1954, #17566279]. Keep an air cushion 0.5 bar below cut-in to avoid air spitting [Elektroda, piracik, post #17549202]

Why it matters: Correct air charge maximises draw-off volume, protects the pump, and ensures steady pressure on upper floors.

Quick Facts

• Tank size discussed: 300 L, rated 0.5 MPa (5 bar) [Elektroda, Majcher123456, post #17548726] • Typical cut-in/out: 1.5–3.5 bar for two-storey supply [Elektroda, stanislaw1954, post #17548980] • Pre-charge air: 1.5–1.7 bar (0.15–0.17 MPa) [Elektroda, piracik, post #17549178] • Pressure loss per metre height: ≈0.1 bar/m (hydraulic rule of thumb, Grundfos Tech) • Usable water per 300 L tank at 2.2–4.2 bar: 60–70 L [Elektroda, stanislaw1954, post #17566279]

How much air should I pump into a 300 L galvanized hydrophore?

Pump until the tank shows 1.5–1.7 bar with the water drained and pump off. This gives a 0.5 bar margin below a 2.2 bar cut-in and prevents air discharge through taps [Elektroda, piracik, post #17549178]

What cut-in and cut-out pressures suit a two-storey house?

Set cut-in to 2.2 bar and cut-out to 4.2 bar. At 2.2 bar you have 1.0 bar at second-floor taps after 12 m lift; 4.2 bar stays below the 0.5 MPa tank rating [Elektroda, Majcher123456, #17549168; Elektroda, piracik, #17549208].

Why does water ‘flow like blood from the nose’ when the pump starts?

Low flow signals clogged pipes or undersized lines. With 3.0 bar cut-in, pressure at the first floor should still be about 2.5 bar. If it is not, check filters, valves, or rusty pipe restrictions [Elektroda, stanislaw1954, post #17549400]

Does too much air hurt the system?

Yes. Excess air reduces draw-off volume and can keep taps spitting air for days until dissolved. Short cycling also doubles motor starts and energy peaks [Elektroda, piracik, post #17549486]

What happens if air is too low?

An undersized cushion means the pump starts every few litres, causing frequent 6× inrush currents, overheating, and premature switch wear—an edge-case failure many owners overlook [Elektroda, piracik, post #17569071]

How do I recharge air from scratch?

  1. Switch off pump and open a tap until flow stops. 2. Close tap and inflate through the Schrader valve to 1.6 bar. 3. Power pump, then verify cut-in/out. This 3-step routine restores design volume [Elektroda, piracik, post #17549178]

How much water should I get per cycle from a 300 L tank?

With 2.2–4.2 bar settings and proper air, expect 60–70 L before the pump restarts—about six 10-L buckets [Elektroda, stanislaw1954, post #17566279]

Can I run higher than 4.5 bar to improve top-floor flow?

Avoid it. The tank is rated 0.5 MPa (5 bar). Keeping at least 10 % safety margin prevents seam fatigue. Boosting line pressure is safer with a secondary booster pump [Elektroda, Majcher123456, post #17548726]

Is a larger tank worth it for three floors?

A 500 L tank doubles reserve but needs a bigger air cushion; otherwise only 30 L discharges, wasting energy [Elektroda, telta, #17566168; Elektroda, piracik, #17566264].

How often should I check the air cushion?

Test quarterly or after long power cuts. Air dissolves at ≈1 % per month in steel tanks; early checks prevent short cycling [Grundfos Tech].