Sizzling Electrical Outlet Issue: Troubleshooting & Repair Tips for Disturbing Noises

Przemon246 27561 13
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 17599437
    Przemon246
    Level 1  
    Hello,

    For some time now, my electrical outlet has started to make disturbing noises after plugging equipment into it. The connected equipment works but stops after a while. After unscrewing the socket housing, the following view appeared:

    Sizzling Electrical Outlet Issue: Troubleshooting & Repair Tips for Disturbing Noises

    Can you advise me what is wrong and how can I fix it?

    Regards
  • ADVERTISEMENT
  • #3 17599466
    kokapetyl
    Level 43  
    Przemon246 wrote:
    what's wrong and how can i fix it?

    Replacement socket.
    Since the "reset" is already done, it must be done correctly. TJ. the neutral wire first to the ground pin, and only to the socket contact (you have it the other way around), this bridge is to be made of a wire, not a string, or a cord, but terminated with a suitable tip.
  • ADVERTISEMENT
  • #4 17599487
    zadam64
    Level 39  
    Hello. This is due to burned, overheated aluminum wires. I propose to buy a new socket for replacement, turn off the electricity and start disassembling the old socket. Be careful not to make any sudden movements as aluminum cables are very brittle. Clean mechanically from tarnish. If it breaks, put the shortened cable on both cables of the connector and place them on the back, leading out two new cable sections in the appropriate colors.
    Brown - phase
    Blue - zero
    Connection in the same way as in the old socket. You have to think slowly about replacing the electrical wiring from aluminum to copper.
    It shouldn't sizzle anymore.
  • #5 17599501
    Plumpi
    Heating systems specialist
    Bad contact between the wires and the terminals.
    Overheated aluminum wires.
    Socket contacts overheated.
    Badly made zeroing circuit.

    How to repair?
    First, turn off the power.
    Replace the seat with a new one.
    Cut off burnt ends of aluminum wires.
    Strip these wires approx. 15 mm.
    Clean with fine sandpaper.
    Clamp the cable sleeves on them.
    Prepare 3 sections of copper wires 10 - 15 cm long in the following colors: blue, yellow-green, third phase color (black, brown or gray).
    Connect the stopped ends of the aluminum conductor with the new lengths of the copper conductor using terminal blocks.
    Blue and yellow-green wires are connected to the neutral wire, and one of the following colors to the phase wire: black, brown or gray.
    The ends of the copper wires are connected to the terminals in the new socket in accordance with the purpose of the individual terminals.

    The wires in the cubes should be connected in such a way that both screws press against the isolated ends of all wires, i.e. both the sleeve clamped on the aluminum wire and the copper wires. For this purpose, use a cube with a cross-section correspondingly larger than the cross-section of each conductor.
  • #6 17599755
    Adam-T
    Level 41  
    Plumpi wrote:
    Clamp the cable sleeves on them.

    What sleeves does the colleague mean? ?
    Plumpi wrote:
    We connect the blue and yellow-green wires to the neutral wire

    Such distribution is only in the switchgear, not in the socket. Like a pointer, someone wrote N to the "pin" and then the bridge to the socket contact.
    zadam64 wrote:
    Connection in the same way as in the old socket.

    Unfortunately, no, the N-ka in the old socket is incorrectly connected.
  • #7 17599890
    Plumpi
    Heating systems specialist
    Adam-T wrote:
    Plumpi wrote:
    Clamp the cable sleeves on them.

    What sleeves does the colleague mean? ?


    The most common ferrules for crimping stranded wires.
    https://dlaelektrykow.pl/10610-thickbox_defau...lejkowa-nieizolowana-ntn-610-100-szt-next.jpg
    I have been using this patent for aluminum conductors for many years. The connections that I made almost 20 years ago work without any problems to this day.


    Adam-T wrote:
    Plumpi wrote:
    We connect the blue and yellow-green wires to the neutral wire

    Such distribution is only in the switchgear, not in the socket. Like a pointer, someone wrote N to the "pin" and then the bridge to the socket contact.


    The method that I have described provides a much better galvanic connection of the protective pin with the neutral wire, and also protects the contact of the protective pin against overheating due to the flow of the operating current N.
    If you want to connect this way, the wire must be continuous between PE and N. Unfortunately, in most currently produced sockets it is not possible to screw the wire loop to the PE terminal so that the wire is connected to the N while maintaining continuity. Since in new equipment PE terminals are often more delicate than active conductor terminals, and it is often impossible to connect a wire loop while maintaining its continuity, it is wiser to perform zeroing as described above.
  • ADVERTISEMENT
  • #8 17600106
    Adam-T
    Level 41  
    Plumpi wrote:
    If you want to connect this way, the wire must be continuous between PE and N. Unfortunately, in most currently produced sockets it is not possible to screw the wire loop to the PE terminal so that the wire is connected to the N while maintaining continuity

    First of all, I do not want to connect like this (I do not have a problem), I have a TNS installation and I know how the "pin" in the socket in the TNC installation should be connected ;) secondly, with this loop (I have my opinion), I will not agree because if a vein will fit next to the screw, then the eyelet (loop) around this screw will fit. The problem may be the lack of a sufficient cable length.
    And then the author he shouldn't have to do it on his own, no kidding with the shock . Should call an electrician.
  • #9 17600258
    zadam64
    Level 39  
    Adam-T wrote:
    Plumpi wrote:
    Clamp the cable sleeves on them.

    What sleeves does the colleague mean? ?
    Plumpi wrote:
    We connect the blue and yellow-green wires to the neutral wire

    Such distribution is only in the switchgear, not in the socket. Like a pointer, someone wrote N to the "pin" and then the bridge to the socket contact.
    zadam64 wrote:
    Connection in the same way as in the old socket.

    Unfortunately, no, the N-ka in the old socket is incorrectly connected.

    And where is the customer to take the third cable in the installation from the times of the Polish People's Republic ui is yellow-green, it would be good in copper?

    Added after 4 [minutes]:

    Plumpi wrote:
    Adam-T wrote:
    Plumpi wrote:
    Clamp the cable sleeves on them.

    What sleeves does the colleague mean? ?


    The most common ferrules for crimping stranded wires.
    https://dlaelektrykow.pl/10610-thickbox_defau...lejkowa-nieizolowana-ntn-610-100-szt-next.jpg
    I have been using this patent for aluminum conductors for many years. The connections that I made almost 20 years ago work without any problems to this day.


    Plumpi wrote:
    We connect the blue and yellow-green wires to the neutral wire

    Such distribution is only in the switchgear, not in the socket. Like a pointer, someone wrote N to the "pin" and then the bridge to the socket contact.


    The method that I have described provides a much better galvanic connection of the protective pin with the neutral wire, and also protects the contact of the protective pin against overheating due to the flow of the operating current N.
    If you want to connect this way, the wire must be continuous between PE and N. Unfortunately, in the majority of currently produced sockets it is not possible to screw the wire loop to the PE terminal so that the wire is connected to the N while maintaining continuity. Since in new equipment PE terminals are often more delicate than active conductor terminals, and it is often impossible to connect a wire loop while maintaining its continuity, it is wiser to perform the zeroing as described. [/ Quote]
    Carve an eyelet for continuity on aluminum that is about 50 years old? Good luck.
  • #10 17600783
    Krzysztof Reszka
    Moderator of Electrical engineering
    zadam64 wrote:
    Blue - zero

    Are you sure buddy of that color?
    Plumpi wrote:
    We connect the blue and yellow-green wires to the neutral wire,

    Are you sure of these colors?
    zadam64 wrote:
    And where is the client to get the third cable in the installation from the times of the Polish People's Republic ui is yellow-green, it would be good in copper?

    Why does he need a third cable?
    Adam-T wrote:
    Such distribution is only in the switchgear, not in the socket. Like a pointer, someone wrote N to the "pin" and then the bridge to the socket contact.

    You are sure of such a combination. Justify it, buddy.
  • #11 17600963
    Plumpi
    Heating systems specialist
    Adam-T wrote:
    ... secondly, with this loop (I have my opinion), I will not agree because if a vein will fit next to the screw, then the eyelet (loop) around this screw will fit. The problem may be the lack of a sufficient cable length.


    The problem is not the length of the wires, because they can and even have to be extended, but the problem is that in the vast majority of sockets it is impossible to remove the screws, because they are covered with plastic and access with a screwdriver is through a hole smaller than the screw head, and the wires are introduced to the buttonholes.
    You probably still have ideas about old attachments from years ago. Nowadays it is difficult to find such accessories.

    https://elektrykadlakazdego.pl/wp-content/uploads/2015/03/GE_TNC_002.jpg

    http://elektrykapradnietyka.com/wp-content/uploads/2017/02/rys-8.jpg

    https://epstryk.pl/p/483/30007/simon-54-premi...aciski-srubowe-dgz2mz-01-48-simon-54-premium- contact-simon-socket-wylaczniki.html

    Not to mention the self-locking sockets

    http://www.elektro-partner.pl/sklep/celiane/067121/067121_t.JPG

    http://www.elektroonline.pl/img/media/12977
  • #12 17601437
    Adam-T
    Level 41  
    Krzysztof Reszka wrote:
    Justify it, buddy.

    I will quote here col kkas12
    Quote:
    This method is illustrated by the principle. first we protect, then we power up.
    So first a protective contact and then a working contact.

    Plumpi wrote:
    Nowadays it is difficult to find such accessories.

    Only one of the examples cited is double.
    My example
    https://photos05.redcart.pl/templates/images/...cts/4457/5f9789b133597d59e7d77c2aace7b4a9.jpg
    Still produced. Anyway, this dispute is nonsensical, so let it be that my friend is right and I am not.
    Regards.
  • ADVERTISEMENT
  • #13 17601772
    Anonymous
    Anonymous  
  • #14 17602895
    Krzysztof Reszka
    Moderator of Electrical engineering
    Adam-T wrote:
    Let me quote you kol kkas12
    Quote:
    This method is illustrated by the principle. first we protect, then we power up.
    So first a protective contact and then a working contact.

    Plumpi wrote:
    Nowadays it is difficult to find such accessories.

    Mate bad quote to this question, colleague Kkass meant something else.

    Krzysztof Reszka wrote:
    Adam-T wrote:
    Such distribution is only in the switchgear, not in the socket. Like a pointer, someone wrote N to the "pin" and then the bridge to the socket contact.
    You are sure of such a combination. Justify it, buddy.

    Buddy, remember the N conductor cannot be split again. So your advice to put the N wire on the pin and cross it to the terminal is wrong.
    Only the PEN conductor can be separated. In this case, it is a PEN that does not meet today's standards.

Topic summary

The discussion revolves around a user experiencing disturbing noises from an electrical outlet after plugging in equipment, which subsequently stops working. Responses highlight potential issues such as burnt or overheated aluminum wires, bad connections, and improperly wired sockets. Recommendations include replacing the socket, ensuring correct wiring connections (with emphasis on using copper wires), and cleaning or replacing burnt wire ends. The importance of safety precautions, such as turning off power before repairs, is also stressed. Some participants debate the correct wiring methods and the necessity of professional assistance for electrical work.