Burning Smell from Socket in Block of Flats: Identifying Defective Sockets & Potential Risks
slonkoo 37878 11
How can I tell which socket is defective when a kitchen outlet smells and gets warm under kettle load, and is it safe to wait before repairs?
No, you should not just replace the “smelly” socket or wait a week; stop using these sockets and call an electrician immediately to test the installation. An electrician should take proper measurements because the problem may be in the wiring or connections, not only the visible socket [#16795185] The smell and warming are consistent with a loose or bad connection under load, and in old block wiring the issue can affect other sockets as well, so the whole installation should be checked, especially heavily loaded outlets like the oven, boiler, or washing machine [#16795339][#16795429][#16795486] Do not try to combine or rework the sockets yourself, because old “zeroing”/protective arrangements can make them dangerous and there is a real risk of electric shock [#16795189] Several replies also warned that this kind of sparking installation can lead to fire and damage to the wall or wallpaper, so it should be treated as urgent [#16795429][#16795486]
  • #1 16795169
    slonkoo
    I live in a large block of flats and the sockets have already been burned. Now, however, I have a strange problem. When I turn on the electric kettle in the kitchen, I can feel the smell in the room clearly coming from one of the sockets. In addition, the socket is warm for a moment. However, on the same socket you can not see even a trace of burning, the equipment connected to it works properly. Of course, now I have nothing to connect to. The question - which of these sockets is really defective, is it enough to replace it "smelly" or also in the kitchen? Could something "burn deeper" have been burning (since there are no traces on the socket itself). Do I have to replace it immediately or can it wait a week? (assuming I will not use the kettle), because I do not have time to deal with the electrics. I will add that there is wallpaper on the wall. And I'm afraid for the safety of other equipment at home.
  • #2 16795185
    bearq
    Help: 414
    Rate: 1612
    Probably replacement of the socket will not do anything, call an electrician who will take the appropriate measurements, everything will be corrected and corrected.
  • #3 16795189
    750kV
    Help: 240
    Rate: 713
    Do not try anything alone as a beginner! If it is still an old block, where there was a "zeroing" of the protective pins in the sockets, you risk being electrocuted and an electrician needed immediately! Do not use any of these sockets and do not combine anything!
  • #4 16795339
    kosmos99
    Help: 338
    Rate: 820
    Probably the power supply is made "jumps" from the socket to the socket. The problem is in this socket where you can smell it, the wires are not solidly connected with each other and thus this situation with a heavy load like a kettle.
  • #5 16795429
    MonikaMarcin
    Help: 32
    Rate: 103
    It's a smelly nest that "does" a splitter.
    I wonder if there is no outflow to other sockets yet.
    And while visiting an electrician, I suggest that he also look at other sockets.
    Especially those heavily loaded (oven, boiler, washing machine, etc.)
    Do not risk this "week". If the pipe breaks, you call a specialist right away.
    Greetings.
  • #6 16795461
    slonkoo
    Once an electrician who exchanged a socket stated that in these blocks circuits are so arranged that through the socket in a small room virtually electricity flows from the whole apartment and that is why they are so often spoiled.
    When there was a shortage many years ago in this socket, turning on the TV in a large room also caused it to spark.
    The problem is that I really do not have time or the ability to go shopping, buy sockets ... I have a very important exam in a few days (really really). Assuming that we will not include anything incriminating until that time, it may endure it somehow.
    Unless you have to order an electrician from Łódź (I live in Chojny on the border with Dąbrowa) who could come and fix it, with its sockets and measuring devices. etc. Searching for yourself takes a long time, and often a person with little competence comes. I would like to add that the extension cables are connected directly to the sockets (the electrician cuts off the plug and wires connecting directly to the socket) and I would like it to be done this time. There is also a need for a small help in moving the sofa, for which there is this contact (it is enough to move it slightly away from the wall). But for a man it's a pit, I have a big problem with it.
    I still have a question outside the competition. In the case described (probably there is no ground in the socket, the cable connected directly to the socket), it makes sense to buy a surge protector to the computer. Of course, I will lose the guarantee on it, cutting off the plug, but if in case of what she has a chance to work properly, protecting the computer. The previous electrician claimed that yes (but how much did he have in common with the electrics, I do not know). Although he exchanged these sockets and extension cords with his eyes closed.
    And, if someone decided to do it, I could also order the extension lead to the socket (as described above) in a large room. Now there are some devices like modem, TV decoder, and this extension has too few sockets. It is true that the "distributor" is included, but it is such a makeshift.
  • #7 16795486
    MonikaMarcin
    Help: 32
    Rate: 103
    As I thought.
    It's easy to count that in these nests we have min. 6 veins each (3L + 3N).
    (colleagues have not forgotten about the EP, but at 99% in such blocks it is missing ;-) )
    I wonder how it is connected.
    Probably under the nest, because very shallow cans have been placed long ago, so the cubes do not fit.
    There is not much space on the surface.
    Cables from extension cords are cables and 100% of the ends are not soldered or without sleeves!
    It must "burn"!
    slonkoo wrote:
    and often a person who is not very competent.
    Or a few zlotys more for professional repair,
    or tens of thousands on losses after a fire !!!
    I will not mention life!
    A NECESSARY REVIEW OF THE ENTIRE INSTALLATION !!! (possibly modernization)
  • #8 16795495
    slonkoo
    But once, when the extension cords were normally connected to the socket, failures occurred more often than now. The reason is that unfolding the couch causes pulling the plug connected to the socket and "loosening" the socket after a certain time. This is a narrow room, so every centimeter is worth its weight in gold, so the couch can not be moved away from the wall to a safe distance. Anyway, even when she was removed, after some time she spontaneously moved back. So if the cable is connected traditionally, it's only with a very flat plug - I used to look for a week after the stores and I did not find one. Hence, such solutions. And if it's connected, I do not know exactly. The electrician cuts off the plug, removes part of the plastic protection, ejects these cables and connects them to the "hole" in the wall, connecting them with the cables located there. He puts a normal socket on it. The cable from the extension cable comes out at the bottom of the contact, and you can theoretically also turn on the contact.
  • #9 16795498
    MonikaMarcin
    Help: 32
    Rate: 103
    I also advise you to handle devices requiring grounding carefully,
    using sockets with a protective pin.
    The blasting earthing contact in the socket is a disaster.
    Added after 6 [minutes]:
    slonkoo wrote:
    Hence, such solutions. The cable from the extension leads out from under the contact, and a normal socket is placed on it.
    I do not deny such an extension cord connection.
    The only condition is that the connection will be made correctly.
    Since nothing can be connected to this socket (normal plug), it should be removed
    and mount the box in which there is space for professional attachment of the installation.
  • #10 16795515
    slonkoo
    And you can answer, is there any sense in buying this surge protector? Is it still not possible to work with such an installation.
    And I repeat the question, would anyone from Łódź be interested in the review and repair?
  • #11 16795575
    MonikaMarcin
    Help: 32
    Rate: 103
    A bit far ;-)
    The strip - a slat, but a "sparkling" installation is a greater threat.
    Both for devices and, above all, for you.
    First a professional visit and then additional security.
    But with an efficient installation, the strip can come in handy.
  • Asking about wall wiring material and fuse rating
    #12 16796032
The discussion revolves around a burning smell emanating from a socket in a block of flats when an electric kettle is used. Users advise against attempting repairs without professional help due to the risk of electrocution and potential fire hazards. It is suggested that the socket in question is likely defective, possibly due to poor connections or deeper wiring issues. The importance of having an electrician inspect not only the problematic socket but also other heavily loaded sockets is emphasized. Users express concern about the safety of the electrical installation, particularly in older buildings where wiring standards may be inadequate. Immediate action is recommended rather than delaying repairs, as the risks of fire and equipment damage are significant.
TL;DR: Burning smell + warm outlet = upstream loose connection, not just the kettle; one faceplate may hide "min. 6 veins (3L + 3N)." "A NECESSARY REVIEW OF THE ENTIRE INSTALLATION!!!" [Elektroda, MonikaMarcin, post #16795486]
Why it matters: Smoldering joints can ignite wallpaper and damage appliances before any scorch marks appear; stop use and call an electrician now.
How do I identify the defective socket when the smell is in a different room?
In jump-fed flats, current to several rooms can pass through a single outlet. A loose or undersized joint in the smelly outlet heats up when the kettle loads the circuit elsewhere. That smell pinpoints the weak connection. Stop using those outlets and book diagnostics. [Elektroda, kosmos99, post #16795339]
Is it safe to wait a week if I stop using the kettle?
No. “Do not use any of these sockets and do not combine anything!” Heating can continue with other loads, and ignition can occur without visible charring. Turn off the affected circuit and call an electrician immediately. [Elektroda, 750kV, post #16795189]
What immediate steps should I take to stay safe?
  1. Switch off the breaker for the affected circuit and unplug devices.
  2. Keep combustibles (like wallpaper) clear and ventilate the area.
  3. Book a licensed electrician for inspection and measurements before re‑energizing. “An electrician [is] needed immediately!” [Elektroda, 750kV, post #16795189]
Will swapping only the smelly outlet fix the problem?
Not reliably. A technician must test, tighten, and, if needed, re-terminate or re-route jump connections. Simple replacement leaves hidden high-resistance points that overheat under load. Get measurements and corrections, not just hardware swaps. [Elektroda, bearq, post #16795185]
Could the problem be deeper in the wall box?
Yes. Old shallow boxes and multiple conductors behind a faceplate restrict space. Poorly secured or unsleeved wire ends increase resistance and heat under load. “It must ‘burn’!” A professional re-termination in a proper box is required. [Elektroda, MonikaMarcin, post #16795486]
Why does the kettle trigger a smell in a bedroom outlet?
High-watt loads like a kettle stress weak upstream joints. In jump wiring, that upstream outlet carries the kettle’s current, so its loose joint heats and emits odor even if the kettle plugs in elsewhere. [Elektroda, kosmos99, post #16795339]
Is hardwiring an extension lead behind the outlet acceptable?
Only if done correctly inside a proper box with compliant terminations. Barely fitting multiple cables under a socket leads to overheating and failure. If the faceplate can’t accept a normal plug, install a junction box and route a fixed socket strip. [Elektroda, MonikaMarcin, post #16795498]
Will a surge‑protector strip save my PC on this wiring?
No. A power strip cannot compensate for a sparking or loose installation. Fix the installation first, then add surge protection as supplemental defense. “First a professional visit and then additional security.” [Elektroda, MonikaMarcin, post #16795575]
Does missing protective earth change what I can plug in?
Yes. Devices needing grounding must use sockets with a protective pin. A damaged or “blasting” earthing contact is hazardous, potentially energizing metal cases. Do not use ungrounded or suspect sockets. [Elektroda, MonikaMarcin, post #16795498]
How many conductors might be under a single faceplate here?
Expect at least “min. 6 veins (3L + 3N)” when outlets feed extensions and downstream sockets. Cramming that into a shallow box increases the chance of bad terminations and heat rise. Schedule a modernization review. [Elektroda, MonikaMarcin, post #16795486]
Are extra‑flat plugs a good workaround behind a tight sofa?
Yes. Use a certified extra‑flat 16 A plug to prevent plug strain instead of hardwiring extensions. This reduces loosening and repeated sparking when furniture moves. [Elektroda, 465208, post #16796032]
Can one faulty outlet affect the whole flat?
Yes. In some flats, “electricity flows from the whole apartment” through upstream outlets; past faults caused sparking when other rooms’ TVs turned on. One weak joint can cascade issues. [Elektroda, slonkoo, post #16795461]
Who should I call and what should they check?
Call a qualified electrician who brings measuring equipment. Ask for a full installation review and tighten/renew terminations, focusing on heavy-load points like oven, boiler, and washer outlets. [Elektroda, MonikaMarcin, post #16795429]
What does “zeroing” mean here, and why is it risky?
It refers to old practice bonding the protective pin to the neutral within the socket. In aging systems, faults can expose you to shock. An immediate professional check is necessary before use. [Elektroda, 750kV, post #16795189]