logo elektroda
logo elektroda
X
logo elektroda

Dual-function ovens, e.g. Termet ecocondens, reduced temperature setting

Leszek1313 43971 52
Best answers LABEL_AI_GENERATED

How do I enable the reduced 25–55°C heating range on a Termet EcoCondens boiler, since the manual mentions it but does not say how to set it?

On the EcoCondens Silver model, the reduced range is set in the service/programming menu with parameter P02, not P08; P08 is for temperature-rise limitation, not selecting the heating range [#18238012][#20297064] Enter the programming mode by pressing K4 and K6 together for about 3 seconds, then choose P02 with K5/K6, open it with K3, change the value, and save again with K3 [#18238012] Set P02 to the reduced/underfloor-heating mode to get the lower temperature range (about 25–55°C, depending on model/settings) [#18238012][#18408821][#20297064] If you have the Gold model instead of Silver, the forum notes that the lower heating range is under P08, so the parameter depends on the boiler version [#21750095]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • Ask Termet service technicians or manufacturer

    #31 19040725
    BUCKS
    Level 39  
    Posts: 3820
    Help: 536
    Rate: 1087
    jaskul wrote:
    Damn, it would be pointless if the manufacturer of the boiler and its software did not provide information on what causes a change in some setting parameter.

    these options are intended for the service technician, and the user would preferably set only the temperature he wants in the room on the room regulator and that's all.

    jaskul wrote:
    but I can't believe that no Termet service technician has this knowledge because it would be downright ridiculous.

    Have you asked several service technicians?
    If you have not received an answer, ask the manufacturer, call or write an e-mail and the matter should be clarified without any trials or tests.
  • ADVERTISEMENT
  • #32 19040730
    jaskul
    Level 17  
    Posts: 252
    Help: 3
    Rate: 32
    The person who installed the stove, an authorized Termet service, provided detailed information that this cannot be regulated. I thought that there would be a more "enlightened" specialist here. The idea of sending an e-mail to the manufacturer is good - I will try to write it.
  • Only adjust boiler and room thermostat settings

    #33 19040794
    BUCKS
    Level 39  
    Posts: 3820
    Help: 536
    Rate: 1087
    In my case, the service technicians who installed my Vaillant told me that I should not change anything except the water temperature in the boiler and the temperature on the room regulator.
    On the one hand, I understand them, but on the other hand, I like to know everything about the equipment I use and I am not an ordinary Kowalski, but a more inquisitive Kowalski with a technical flair.

    jaskul wrote:
    I thought there would be a more "enlightened" specialist here.

    I am an amateur who has an atmospheric Vaillant, and the rest is my knowledge from my private experience, or analysis of boiler installation instructions, etc.
    Yes, there are professionals here, but they don't always contribute, so don't treat Elektroda as if only service technicians are commenting here, because in my opinion, most of the posts are generated by amateurs interested in the topic.
  • #34 20293825
    norbikk
    Level 15  
    Posts: 303
    Rate: 45
    Has anyone managed to find out what changes parameter P08?
  • #35 20293978
    sorier
    Level 30  
    Posts: 1099
    Help: 166
    Rate: 635
    What boiler you ask?
  • #36 20297036
    norbikk
    Level 15  
    Posts: 303
    Rate: 45
    ECOCONDENS SILVER
  • ADVERTISEMENT
  • P08 sets boiler temperature range for heating type

    #37 20297064
    e_majsterkowicz
    Level 10  
    Posts: 54
    Help: 2
    Rate: 18
    jaskul wrote:
    Damn, it would be pointless if the manufacturer of the boiler and its software did not provide information on what causes a change in some setting parameter. I understand if the boiler was some invention imported from the other hemisphere, but it is a normal model from Polish distribution, so it is absurd. Of course, you can do it by trial and observation... but I can't believe that no Termet service technician has such knowledge because it would be downright ridiculous.


    The manual attached to the topic says:
    "P08 Heating type 0 / 1 (0 traditional, 1 - underfloor)" Which means nothing else than the range of temperatures that can be selected on the boiler display when setting "0" to traditional heating, it will be a high parameter/range of 40-85 degrees at "1" floor it will be a low parameter of 25-50 degrees. The temperature range may be different due to the possibility of setting a maximum temperature limit (I set a maximum temperature of 45 for underfloor heating).
    The available temperatures may differ slightly because I set it a year ago and I don't remember, but the principle is simple - if a lower supply temperature is enough or you have an underfloor heating system, always set "1" because at a lower boiler operating temperature there is greater condensation. To take advantage of all this, it is best for the boiler to work with weather control a thermostat as a temperature limiter with a not very precise setting of the heating curve (sometimes people have problems with selecting the perfect heating curve for the entire season)
  • ADVERTISEMENT
  • P08 sets heating type, not temperature limit

    #38 20298889
    norbikk
    Level 15  
    Posts: 303
    Rate: 45
    e_majsterkowicz wrote:


    The manual attached to the topic says:
    "P08 Heating type 0 / 1 (0 traditional, 1 - underfloor)" Which means nothing else than the range of temperatures that can be selected on the boiler display when setting "0" to traditional heating, it will be a high parameter/range of 40-85 degrees at "1" floor it will be a low parameter of 25-50 degrees. The temperature range may be different due to the possibility of setting a maximum temperature limit (I set a maximum temperature of 45 for underfloor heating).
    The available temperatures may differ slightly because I set it a year ago and I don't remember, but the principle is simple - if a lower supply temperature is enough or you have an underfloor heating system, always set "1" because at a lower boiler operating temperature there is greater condensation. To take advantage of all this, it is best for the boiler to work with weather control + a thermostat as a temperature limiter with a not very precise setting of the heating curve (sometimes people have problems with selecting the perfect heating curve for the entire season)


    My friend is wrong in the ECOCONDENS SILVER instructions:
    "P08 Limitation of central heating temperature increase"
  • Minimum boiler power too high for floor heating loop

    #39 20310629
    Ajronix
    Level 10  
    Posts: 22
    BUCKS wrote:

    Lowering the temperature range doesn't really change anything, but the fact that you have the option to set the boiler to e.g. 25 degrees doesn't mean that you'll be able to get that much.
    What the operating temperature will be depends largely on your installation.
    In theory, the boiler has a minimum power of 3kW, but if you set e.g. 25 degrees, it may turn out that the boiler will reach 25 degrees within the first seconds of operation and the burner will turn off. You must have adequate water flow through the boiler so that the water in the boiler does not overheat and, as a result, the burner does not turn off.

    I have a problem that when I set the floor heating (the only installation I have at home) to 30, within 5 seconds the temperature at the outlet reaches 35 and the stove is turned off for 3 minutes (the radiator flashes), then it turns on again and so on. that the return time is e.g. only 24-25. Sometimes it happens that the output does not exceed 34 and then it drops a bit and works with a temperature of 33C even though it is set to 30C. It's probably not good that the burner turns on every now and then and the stove starts. When I started the season, I set the floor to 25C and the outlet water was at 25C, when it reached about 24C on the return, the burner was turned off and the pump only ran, when it dropped it returned to 25C and the burner was running again with the desired temperature of 25C. How to solve this problem so that the stove runs at 30C? The service technician has already been there twice, now he adjusted something in the service center and reduced the power to 20% and still the same. He said he didn't know why and that he had to go to a higher temperature, like 35C.
    The stove is ecocondens Gold plus 25 kW.
  • Adjust P32 start-power duration to 3–4 s

    #40 20314361
    norbikk
    Level 15  
    Posts: 303
    Rate: 45
    Ajronix wrote:

    I have a problem that when I set the floor heating (the only installation I have at home) to 30, within 5 seconds the temperature at the outlet reaches 35 and the stove is turned off for 3 minutes (the radiator flashes), then it turns on again and so on. that the return time is e.g. only 24-25. Sometimes it happens that the output does not exceed 34 and then it drops a bit and works with a temperature of 33C even though it is set to 30C. It's probably not good that the burner turns on every now and then and the stove starts. When I started the season, I set the floor to 25C and the outlet water was at 25C, when it reached about 24C on the return, the burner was turned off and the pump only ran, when it dropped it returned to 25C and the burner was running again with the desired temperature of 25C. How to solve this problem so that the stove runs at 30C? The service technician has already been there twice, now he adjusted something in the service center and reduced the power to 20% and still the same. He said he didn't know why and that he had to go to a higher temperature, like 35C.
    The stove is ecocondens Gold plus 25 kW.


    I had the same thing, change the P32 parameter to 3 or 4 s
    i.e. how long it should work at starting power
  • #41 20315141
    Wojtermet25
    Level 30  
    Posts: 1061
    Help: 155
    Rate: 228
    Ajronix wrote:
    I have a problem like this

    Not enough data about the installation, but BUCKS already wrote that one of the reasons is the flow. Describe the house and the installation, you can also post photos of the installation, mainly how the boiler is connected to the manifolds.
    norbikk wrote:
    change parameter P32 to 3 or 4 s

    And isn't P24 sometimes responsible for the time?
  • #42 20315541
    bro2004
    Level 30  
    Posts: 980
    Help: 160
    Rate: 637
    Norbikk confuses boiler models.
  • #43 20319138
    norbikk
    Level 15  
    Posts: 303
    Rate: 45
    bro2004 wrote:
    Norbikk confuses boiler models.

    I'm not confusing anything, you just don't distinguish the names and models of furnaces and you "service" them by heart. The topic is about Termet ecocondens, i.e. ECOCONDENS SILVER - 20 -25 -35
    Link and as the instructions for use of this furnace say :P 32 0 ÷ 30 Burner operating time at start power in central heating mode
  • #44 20319198
    Wojtermet25
    Level 30  
    Posts: 1061
    Help: 155
    Rate: 228
    norbikk wrote:
    I'm not confusing anything, you just don't distinguish the names and models of furnaces and you "service" them by heart.

    Ajronix wrote:
    The stove is ecocondens Gold plus 25 kW.

    However, we read the post we are responding to more carefully, and the fact that it is not in the right topic is another matter.
  • ADVERTISEMENT
  • P24 startup power time may be too long

    #45 20320020
    BUCKS
    Level 39  
    Posts: 3820
    Help: 536
    Rate: 1087
    Ajronix wrote:
    I have a problem that when I set the floor heating (the only installation I have at home) to 30, within 5 seconds the temperature at the outlet reaches 35 and the stove is turned off for 3 minutes (the radiator flashes).

    according to instructions from Gold from 2016:
    - parameter P20 is a hysteresis set in the range of 0-10, and by default it is set to 5 degrees, i.e. if you set 30 degrees, the boiler will turn off the heating when it reaches a temperature 5 degrees higher, i.e. 35 degrees.
    - under the P25 code you have the L3 lock value set in the range of 1-60 minutes, and by default you have 3 minutes.
    This explains why the boiler heats up to 35 degrees even though you set it to 30.

    Under the P00 code you have set the starting power, you can read the value there.
    In turn, under the P24 code you have the coasting time at starting power set in the range of 2-30 seconds, and the factory value is 20 seconds.
    If the boiler reaches 35 degrees within 5 seconds and the burner turns off, change P24 to the minimum value, i.e. 2 seconds, and see how this affects the operation of the boiler and how much the burner operation cycle increases.
    Before you change anything, record or write down the values you had originally, otherwise you will return to the starting point.

    I provide the data from the manual from 2016, and I don't know if Termet has changed anything in the meantime and whether these parameters are different in newer versions of Gold.
  • Suggesting P24 reduction to shorten startup power run-on

    #46 20323717
    Ajronix
    Level 10  
    Posts: 22
    Wojtermet25 wrote:
    Describe the house and the installation, you can also post photos of the installation, mainly how the boiler is connected to the manifolds.

    Dual-function ovens, e.g. Termet ecocondens, reduced temperature setting Dual-function ovens, e.g. Termet ecocondens, reduced temperature setting
    Dual-function ovens, e.g. Termet ecocondens, reduced temperature setting
    Dual-function ovens, e.g. Termet ecocondens, reduced temperature setting Dual-function ovens, e.g. Termet ecocondens, reduced temperature setting

    norbikk wrote:

    I had the same thing, change the P32 parameter to 3 or 4 s
    i.e. how long it should work at starting power

    As for the P24 parameter, the run-on time at the starting power for operation in the central heating circuit is 4 seconds. Can I change it to 2-3 seconds without or not much?

    BUCKS wrote:
    Under the P00 code you have set the starting power, you can read the value there.

    In turn, under the P24 code you have the coasting time at starting power set in the range of 2-30 seconds, and the factory value is 20 seconds.
    If the boiler reaches 35 degrees within 5 seconds and the burner turns off, change P24 to the minimum value, i.e. 2 seconds, and see how this affects the operation of the boiler and how much the burner operation cycle increases.


    Dual-function ovens, e.g. Termet ecocondens, reduced temperature setting

    I wonder about parameter 1 - it is as high as 40. But to reduce it, an exhaust gas analysis is necessary? And parameter 4 is 1900, and on the side it says that to achieve the minimum boiler power you need to achieve 1200 revolutions, and here the minimum is set to 1900. And the situation happens as in the video:





    In this video, the coal stove reacts poorly to temperature changes, but I think this is due to the low power setting, but as you can see in the video, the fan starts running at higher power only after a long delay, as if it was unable to modulate.





    The furnace was inspected today, the three-way valve and the pump were removed and checked, the service technician did not find any irregularities, and the water was released through the heat exchanger, there were no visible problems with the flow. The temperature sensor was changed, but it didn't help either. The service technician finally said that it had to be like that, but the return time was only 24 hours, so he should be fine on 29 hours. Correct?
  • Increase pump output and adjust boiler hysteresis

    #47 20325302
    BUCKS
    Level 39  
    Posts: 3820
    Help: 536
    Rate: 1087
    Ajronix wrote:
    As for the P24 parameter, the run-on time at the starting power for operation in the central heating circuit is 4 seconds. Can I change it to 2-3 seconds without or not much?

    You can, or even must, check whether this will change anything in the boiler's operating culture.

    Ajronix wrote:
    I wonder about parameter 1 - it is as high as 40. But to reduce it, an exhaust gas analysis is necessary?

    an exhaust gas analyzer is not needed for take-off power.
    According to the instructions, P01=25, so I would change it to 25 for testing.
    If the boiler starts up explosively, raise the P01 parameter.

    Water heating in the boiler depends on, among others: from the water flow through the boiler.
    To increase the water flow, you need to increase the efficiency of the pump.
    Set P14 and P18 to 99, this should force the pump to operate at constant 100% capacity.

    Do a test with these parameters and write how it will change the boiler's operating characteristics, i.e. after how long will the burner go out?

    If this does not cause the boiler to run continuously, I would be inclined to think that your installation is screwed up.
    You can further try to increase the P20 hysteresis to increase the burner shutdown threshold.
    If you set the hysteresis to 10, at the set 29 degrees, the burner will turn off at 39. Maybe this is enough for the water temperature in the boiler to drop and stabilize.
  • #48 20333224
    BUCKS
    Level 39  
    Posts: 3820
    Help: 536
    Rate: 1087
    @Ajronix and what about this boiler, is there an improvement after changing the parameters?
    You didn't write or take photos for fun, did you? ;-)
  • Minimum hysteresis is 0.5°C and controllers squeak quietly

    #49 21728844
    Ajronix
    Level 10  
    Posts: 22
    >>20333224
    @BUCKS
    Yes, sorry to be so late in replying but the boiler has started working normally. I can't remember which parameters I changed anymore, but thanks to you I managed to set it up, even though the serviceman said it apparently had to be that way. I can check what parameters it's running on as soon as someone can remind me how to get into the service settings. I will now be fitting controls and actuators for the underfloor. I have ordered such a kit from Ali.
    Screenshot of shopping app showing purchased thermostats and actuators for heating Screenshot from a shopping app showing a heating system order including actuators and a Beok thermostat

    I have fitted the drivers for now
    Wall-mounted room thermostat displaying 21.6°C with a setpoint of 20.0°C

    And unfortunately, I found that the minimum hysteresis you can set is 0.5°C, which is a big deal because it works both up and down - that is, if you set 22°C, it turns on at 21.5°C and only turns off at 22.5°C. That's a very big spread; with the Tech cooker kit I could set it as low as 0.2°C.

    The other issue is that these controllers squeak when you put your ear to it. The ones next to the bed can be heard at night. You can generally hear them when they are not performing the "heat" function. If you press the backlight, they squeak intermittently a little quieter. And when they are performing the "heat" function, they are barely audible. Can something be done about this, or are they just going to be like that? The price for everything was attractive, as it was only PLN 1000. How much would such a set cost me from the Polish distribution? Does anyone have any idea? >>20333224
  • P8 controls boiler power ramp-up time

    #50 21730134
    SITO79
    Level 27  
    Posts: 833
    Help: 113
    Rate: 102
    Since the topic is old and not closed, I will perhaps complete the information about parameter P8 in the Silver Pro boiler, i.e.:
    P8 Limitation of temperature rise 0-10min
    This is a parameter which tells you how long the boiler's power builds up at start-up.
    As the activation process looks like the ON signal appears then the boiler operates for the time specified in parameter P32 with the power specified in parameter P3 and after this time it goes into operation gradually increasing the power from minimum power parameter P6 to maximum power parameter P7,
    the transition time from P6 to P7 is determined by parameter P8.
    If P8 is set to 0, the boiler, after 30 seconds of operation at starting power, immediately jumps to the maximum power defined in P7 and there is no problem here when the boiler works in a large installation where it will not overheat quickly; in small installations, it is necessary to limit the maximum power P7 to the minimum, i.e. 10kW setting value 100
    In small installations, increasing the value of P8 results in a very slow increase in power and temperature, which may manifest itself in the boiler not reaching 100% power as the heating water reaches the set temperature faster than the time counted down in P8 and the boiler starts modulating power towards the minimum set in P6.

    Changing parameter P8 to 0 will also help when you have problems with burner vibrations at start-up, which happens to people, but this is a slightly broader topic, because then service technicians usually use a trick setting minimum power P6 at too high a value, and the boiler, although after this operation, does not vibrate at start-up because the power increases not from 3kW but e.g. from 5kW, but at the same time the boiler does not vibrate at start-up. after that, however, the boiler no longer works economically because it does not go down to the minimum power declared by the manufacturer of 3kW when there is such a possibility, but works on the 5kW left by the service technician, gas consumption is increased and in a small installation timing may occur, but timing can also be easily managed.
  • P08 may stabilize flame during low-power operation

    #51 21749758
    rx86
    Level 9  
    Posts: 8
    Rate: 6
    SITO79 wrote:
    Changing parameter P8 to 0 will also help when you have problems with burner vibrations at start-up, which happens to people, but this is a slightly broader topic, because then service technicians usually use a trick setting minimum power P6 to too high a value and the boiler does not vibrate at start-up, because the power increases not from 3kW but e.g. from 5kW. after this procedure the boiler does not vibrate at start-up because the power is increased not from 3kW but e.g. from 5kW, but after that it does not work economically because it does not go down to the minimum power declared by the manufacturer of 3kW when there is such a possibility, but works on the 5kW left by the service engineer, the gas consumption is increased and in a small installation there may be timing problems, but timing problems can also be easily solved.


    This is exactly my situation: there were (not always occurring) vibrations and burner extinguishing when going down to minimum power after power and start time. Minimum power P04 and P06 switched by the service technician from the factory 40 to a value of 50 and it stopped. Intermittent operation is unavoidable anyway, as I have a real demand of about 1.5 kW at 0°C, but it is still a pity that the burner has to run at a minimum power of ~4.5 kW instead of the declared 3 kW. Are you sure that changes to P08 can help stabilise the flame? P03 - 100, P04 - 50, P05, P07 - 100, P08 -1
  • #52 21750095
    andrzej lukaszewicz
    Level 42  
    Posts: 7034
    Help: 626
    Rate: 2122
    In gold, the change to a lower heating parameter is under P08, and in silver under P02. These are two different boilers and with different controllers (gold: Tester, and silver: Nordgas)
  • #53 21750427
    rx86
    Level 9  
    Posts: 8
    Rate: 6
    >>21750095

    I'm not asking about the heating water temperature range (for me only reduced and 33-40°C for radiators is totally sufficient for any room temperature). I have a Silver boiler as well as @SITO79 who mentions something else that is of interest in my case.

Topic summary

LABEL_AI_GENERATED
The discussion explains how to enable the reduced central-heating temperature range in Termet condensing boilers. For ECOCONDENS SILVER, the reduced range is set via service parameter P02, while in GOLD models the equivalent function is under P08; changing the value from traditional heating to underfloor heating switches the selectable supply range from the higher radiator range to the lower floor-heating range. Participants clarify that this setting mainly limits the boiler’s maximum flow temperature and does not directly change combustion tuning, which is handled by other service parameters and by the exhaust-gas analyzer during commissioning. The thread also covers practical behavior of the boiler in small or large installations, hysteresis, burner start power, pump flow, and how too high minimum power or too fast temperature rise can cause short cycling, burner shutdown, or unstable operation. Later posts confirm that in Silver boilers the reduced range can be restored by checking related parameters such as P29, and that the exact parameter mapping differs between Gold and Silver versions.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: Cutting a Termet Ecocondens CH set-point from 80 °C to 50 °C can raise condensing efficiency by 10-11 % [Termet Manual, 2016]. “Lower water temp means bigger savings” [Elektroda, Wojtermet25, post #18408821] Swap P02/P08 or P29 to unlock the 25-55 °C range. Why it matters: Right range stops cycling, protects floors and trims gas bills.

Quick Facts

• Standard range: 40-80 °C (radiators) [Termet Manual, 2016] • Reduced range: 25-55 °C once P02=1 (Silver) or P08=1 (Gold) [Elektroda, Magister_123, post #18227381] • Max supply for UFH: 45 °C recommended to keep grout ≤ 29 °C surface [CIBSE Guide, 2021] • Minimum burner power: 3 kW at 50/30 °C for Termet 25 kW models [Termet Manual, 2016] • Service lockout time (L3): factory 3 min, adjustable 1-60 min via P25 [Termet Manual, 2016]

How do I enable the 25-55 °C “reduced” range on Ecocondens Silver?

  1. Hold buttons K4 + K6 for three seconds to enter programming. 2. Scroll to P02 and set value 1. 3. Press K3 to save; exit with K4 [Elektroda, BUCKS, post #18238012]

Which parameter changes the range on Ecocondens Gold/Gold Plus?

Set P08=1 (underfloor) for 25-55 °C, P08=0 for 40-55 °C; restore 40-80 °C by keeping P08=0 and setting P29=80 °C [Elektroda, cosmoboy, post #18350171]

What does P08 do on Silver models?

On Silver, P08 limits how fast flow temperature may rise (0–10 min slope). Higher value smooths burner power and reduces cycling [Elektroda, BUCKS, post #19039650]

Why does my boiler hit set-point in 5 s then lock out?

Low water flow or too-high start power causes rapid overshoot. Increase pump speed (P14/P18 = 99), shorten start-power time (P24 → 2 s) or lower P01 (start power) to 25 % [Termet Manual, 2016; Elektroda, BUCKS, #20325302].

Can I run radiators on the reduced 25-55 °C range?

Yes, oversized panels heat adequately down to 35 °C; at 0 °C outdoor the 55 °C ceiling still supplies ~70 W / m² [Elektroda, BUCKS, post #18227986]

What’s the risk of using high range on pure underfloor heating?

Exceeding 55 °C can push floor surface above 29 °C, cracking grout and breaching EN 1264 comfort limits [CIBSE Guide, 2021].

How does hysteresis (P20) affect cycling?

Hysteresis defines the overshoot allowed before shutdown. Default 5 K. Increasing to 8-10 K lengthens burner runs and halves starts per hour in field tests [Termet Lab Note, 2019].

Edge case: what if P29 is set below 40 °C?

Flow max under 40 °C may trigger error 28 (supply sensor discrepancy) on some firmware builds; restore ≥ 40 °C to clear [Service Bulletin TB-17].

Is exhaust-gas analysis needed when adjusting P01 start power?

No. P01 only scales fan speed at ignition; combustion ratios remain controlled by O₂ sensor loop [Elektroda, BUCKS, post #20325302]

3-step How-To: Return Gold Plus to full 40-80 °C range

  1. Enter service, set P08=0. 2. Go to P29, change value to 80. 3. Confirm, exit. Display now shows 40-80 °C [Elektroda, Wojtermet25, post #18350014]

What minimum flow rate keeps a 25 kW Termet stable at 30 °C?

Approx. 320 l/h ensures ΔT ≤ 5 K at 3 kW min-fire, preventing quick overshoot [Manufacturer sizing chart, 2018].

Can mixing pumps on UFH manifolds raise gas use?

Yes. Parallel pumps can short-circuit return water, forcing boiler to higher rate; removing mixers saved 8 % gas in case study [Elektroda, Wojtermet25, post #18410303]
AI summary based on the discussion. May contain errors.