Dual-function ovens, e.g. Termet ecocondens, reduced temperature setting

Leszek1313 38394 49
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #31 19040725
    BUCKS
    Level 39  
    jaskul wrote:
    Damn, it would be pointless if the manufacturer of the boiler and its software did not provide information on what causes a change in some setting parameter.

    these options are intended for the service technician, and the user would preferably set only the temperature he wants in the room on the room regulator and that's all.

    jaskul wrote:
    but I can't believe that no Termet service technician has this knowledge because it would be downright ridiculous.

    Have you asked several service technicians?
    If you have not received an answer, ask the manufacturer, call or write an e-mail and the matter should be clarified without any trials or tests.
  • ADVERTISEMENT
  • #32 19040730
    jaskul
    Level 17  
    The person who installed the stove, an authorized Termet service, provided detailed information that this cannot be regulated. I thought that there would be a more "enlightened" specialist here. The idea of sending an e-mail to the manufacturer is good - I will try to write it.
  • #33 19040794
    BUCKS
    Level 39  
    In my case, the service technicians who installed my Vaillant told me that I should not change anything except the water temperature in the boiler and the temperature on the room regulator.
    On the one hand, I understand them, but on the other hand, I like to know everything about the equipment I use and I am not an ordinary Kowalski, but a more inquisitive Kowalski with a technical flair.

    jaskul wrote:
    I thought there would be a more "enlightened" specialist here.

    I am an amateur who has an atmospheric Vaillant, and the rest is my knowledge from my private experience, or analysis of boiler installation instructions, etc.
    Yes, there are professionals here, but they don't always contribute, so don't treat Elektroda as if only service technicians are commenting here, because in my opinion, most of the posts are generated by amateurs interested in the topic.
  • #34 20293825
    norbikk
    Level 15  
    Has anyone managed to find out what changes parameter P08?
  • ADVERTISEMENT
  • #37 20297064
    e_majsterkowicz
    Level 10  
    jaskul wrote:
    Damn, it would be pointless if the manufacturer of the boiler and its software did not provide information on what causes a change in some setting parameter. I understand if the boiler was some invention imported from the other hemisphere, but it is a normal model from Polish distribution, so it is absurd. Of course, you can do it by trial and observation... but I can't believe that no Termet service technician has such knowledge because it would be downright ridiculous.


    The manual attached to the topic says:
    "P08 Heating type 0 / 1 (0 traditional, 1 - underfloor)" Which means nothing else than the range of temperatures that can be selected on the boiler display when setting "0" to traditional heating, it will be a high parameter/range of 40-85 degrees at "1" floor it will be a low parameter of 25-50 degrees. The temperature range may be different due to the possibility of setting a maximum temperature limit (I set a maximum temperature of 45 for underfloor heating).
    The available temperatures may differ slightly because I set it a year ago and I don't remember, but the principle is simple - if a lower supply temperature is enough or you have an underfloor heating system, always set "1" because at a lower boiler operating temperature there is greater condensation. To take advantage of all this, it is best for the boiler to work with weather control a thermostat as a temperature limiter with a not very precise setting of the heating curve (sometimes people have problems with selecting the perfect heating curve for the entire season)
  • #38 20298889
    norbikk
    Level 15  
    e_majsterkowicz wrote:


    The manual attached to the topic says:
    "P08 Heating type 0 / 1 (0 traditional, 1 - underfloor)" Which means nothing else than the range of temperatures that can be selected on the boiler display when setting "0" to traditional heating, it will be a high parameter/range of 40-85 degrees at "1" floor it will be a low parameter of 25-50 degrees. The temperature range may be different due to the possibility of setting a maximum temperature limit (I set a maximum temperature of 45 for underfloor heating).
    The available temperatures may differ slightly because I set it a year ago and I don't remember, but the principle is simple - if a lower supply temperature is enough or you have an underfloor heating system, always set "1" because at a lower boiler operating temperature there is greater condensation. To take advantage of all this, it is best for the boiler to work with weather control + a thermostat as a temperature limiter with a not very precise setting of the heating curve (sometimes people have problems with selecting the perfect heating curve for the entire season)


    My friend is wrong in the ECOCONDENS SILVER instructions:
    "P08 Limitation of central heating temperature increase"
  • #39 20310629
    Ajronix
    Level 10  
    BUCKS wrote:

    Lowering the temperature range doesn't really change anything, but the fact that you have the option to set the boiler to e.g. 25 degrees doesn't mean that you'll be able to get that much.
    What the operating temperature will be depends largely on your installation.
    In theory, the boiler has a minimum power of 3kW, but if you set e.g. 25 degrees, it may turn out that the boiler will reach 25 degrees within the first seconds of operation and the burner will turn off. You must have adequate water flow through the boiler so that the water in the boiler does not overheat and, as a result, the burner does not turn off.

    I have a problem that when I set the floor heating (the only installation I have at home) to 30, within 5 seconds the temperature at the outlet reaches 35 and the stove is turned off for 3 minutes (the radiator flashes), then it turns on again and so on. that the return time is e.g. only 24-25. Sometimes it happens that the output does not exceed 34 and then it drops a bit and works with a temperature of 33C even though it is set to 30C. It's probably not good that the burner turns on every now and then and the stove starts. When I started the season, I set the floor to 25C and the outlet water was at 25C, when it reached about 24C on the return, the burner was turned off and the pump only ran, when it dropped it returned to 25C and the burner was running again with the desired temperature of 25C. How to solve this problem so that the stove runs at 30C? The service technician has already been there twice, now he adjusted something in the service center and reduced the power to 20% and still the same. He said he didn't know why and that he had to go to a higher temperature, like 35C.
    The stove is ecocondens Gold plus 25 kW.
  • ADVERTISEMENT
  • #40 20314361
    norbikk
    Level 15  
    Ajronix wrote:

    I have a problem that when I set the floor heating (the only installation I have at home) to 30, within 5 seconds the temperature at the outlet reaches 35 and the stove is turned off for 3 minutes (the radiator flashes), then it turns on again and so on. that the return time is e.g. only 24-25. Sometimes it happens that the output does not exceed 34 and then it drops a bit and works with a temperature of 33C even though it is set to 30C. It's probably not good that the burner turns on every now and then and the stove starts. When I started the season, I set the floor to 25C and the outlet water was at 25C, when it reached about 24C on the return, the burner was turned off and the pump only ran, when it dropped it returned to 25C and the burner was running again with the desired temperature of 25C. How to solve this problem so that the stove runs at 30C? The service technician has already been there twice, now he adjusted something in the service center and reduced the power to 20% and still the same. He said he didn't know why and that he had to go to a higher temperature, like 35C.
    The stove is ecocondens Gold plus 25 kW.


    I had the same thing, change the P32 parameter to 3 or 4 s
    i.e. how long it should work at starting power
  • #41 20315141
    Wojtermet25
    Level 30  
    Ajronix wrote:
    I have a problem like this

    Not enough data about the installation, but BUCKS already wrote that one of the reasons is the flow. Describe the house and the installation, you can also post photos of the installation, mainly how the boiler is connected to the manifolds.
    norbikk wrote:
    change parameter P32 to 3 or 4 s

    And isn't P24 sometimes responsible for the time?
  • #42 20315541
    bro2004
    Level 30  
    Norbikk confuses boiler models.
  • #43 20319138
    norbikk
    Level 15  
    bro2004 wrote:
    Norbikk confuses boiler models.

    I'm not confusing anything, you just don't distinguish the names and models of furnaces and you "service" them by heart. The topic is about Termet ecocondens, i.e. ECOCONDENS SILVER - 20 -25 -35
    Link and as the instructions for use of this furnace say :P 32 0 ÷ 30 Burner operating time at start power in central heating mode
  • #44 20319198
    Wojtermet25
    Level 30  
    norbikk wrote:
    I'm not confusing anything, you just don't distinguish the names and models of furnaces and you "service" them by heart.

    Ajronix wrote:
    The stove is ecocondens Gold plus 25 kW.

    However, we read the post we are responding to more carefully, and the fact that it is not in the right topic is another matter.
  • #45 20320020
    BUCKS
    Level 39  
    Ajronix wrote:
    I have a problem that when I set the floor heating (the only installation I have at home) to 30, within 5 seconds the temperature at the outlet reaches 35 and the stove is turned off for 3 minutes (the radiator flashes).

    according to instructions from Gold from 2016:
    - parameter P20 is a hysteresis set in the range of 0-10, and by default it is set to 5 degrees, i.e. if you set 30 degrees, the boiler will turn off the heating when it reaches a temperature 5 degrees higher, i.e. 35 degrees.
    - under the P25 code you have the L3 lock value set in the range of 1-60 minutes, and by default you have 3 minutes.
    This explains why the boiler heats up to 35 degrees even though you set it to 30.

    Under the P00 code you have set the starting power, you can read the value there.
    In turn, under the P24 code you have the coasting time at starting power set in the range of 2-30 seconds, and the factory value is 20 seconds.
    If the boiler reaches 35 degrees within 5 seconds and the burner turns off, change P24 to the minimum value, i.e. 2 seconds, and see how this affects the operation of the boiler and how much the burner operation cycle increases.
    Before you change anything, record or write down the values you had originally, otherwise you will return to the starting point.

    I provide the data from the manual from 2016, and I don't know if Termet has changed anything in the meantime and whether these parameters are different in newer versions of Gold.
  • #46 20323717
    Ajronix
    Level 10  
    Wojtermet25 wrote:
    Describe the house and the installation, you can also post photos of the installation, mainly how the boiler is connected to the manifolds.

    Dual-function ovens, e.g. Termet ecocondens, reduced temperature setting Dual-function ovens, e.g. Termet ecocondens, reduced temperature setting
    Dual-function ovens, e.g. Termet ecocondens, reduced temperature setting
    Dual-function ovens, e.g. Termet ecocondens, reduced temperature setting Dual-function ovens, e.g. Termet ecocondens, reduced temperature setting

    norbikk wrote:

    I had the same thing, change the P32 parameter to 3 or 4 s
    i.e. how long it should work at starting power

    As for the P24 parameter, the run-on time at the starting power for operation in the central heating circuit is 4 seconds. Can I change it to 2-3 seconds without or not much?

    BUCKS wrote:
    Under the P00 code you have set the starting power, you can read the value there.

    In turn, under the P24 code you have the coasting time at starting power set in the range of 2-30 seconds, and the factory value is 20 seconds.
    If the boiler reaches 35 degrees within 5 seconds and the burner turns off, change P24 to the minimum value, i.e. 2 seconds, and see how this affects the operation of the boiler and how much the burner operation cycle increases.


    Dual-function ovens, e.g. Termet ecocondens, reduced temperature setting

    I wonder about parameter 1 - it is as high as 40. But to reduce it, an exhaust gas analysis is necessary? And parameter 4 is 1900, and on the side it says that to achieve the minimum boiler power you need to achieve 1200 revolutions, and here the minimum is set to 1900. And the situation happens as in the video:





    In this video, the coal stove reacts poorly to temperature changes, but I think this is due to the low power setting, but as you can see in the video, the fan starts running at higher power only after a long delay, as if it was unable to modulate.





    The furnace was inspected today, the three-way valve and the pump were removed and checked, the service technician did not find any irregularities, and the water was released through the heat exchanger, there were no visible problems with the flow. The temperature sensor was changed, but it didn't help either. The service technician finally said that it had to be like that, but the return time was only 24 hours, so he should be fine on 29 hours. Correct?
  • ADVERTISEMENT
  • #47 20325302
    BUCKS
    Level 39  
    Ajronix wrote:
    As for the P24 parameter, the run-on time at the starting power for operation in the central heating circuit is 4 seconds. Can I change it to 2-3 seconds without or not much?

    You can, or even must, check whether this will change anything in the boiler's operating culture.

    Ajronix wrote:
    I wonder about parameter 1 - it is as high as 40. But to reduce it, an exhaust gas analysis is necessary?

    an exhaust gas analyzer is not needed for take-off power.
    According to the instructions, P01=25, so I would change it to 25 for testing.
    If the boiler starts up explosively, raise the P01 parameter.

    Water heating in the boiler depends on, among others: from the water flow through the boiler.
    To increase the water flow, you need to increase the efficiency of the pump.
    Set P14 and P18 to 99, this should force the pump to operate at constant 100% capacity.

    Do a test with these parameters and write how it will change the boiler's operating characteristics, i.e. after how long will the burner go out?

    If this does not cause the boiler to run continuously, I would be inclined to think that your installation is screwed up.
    You can further try to increase the P20 hysteresis to increase the burner shutdown threshold.
    If you set the hysteresis to 10, at the set 29 degrees, the burner will turn off at 39. Maybe this is enough for the water temperature in the boiler to drop and stabilize.
  • #48 20333224
    BUCKS
    Level 39  
    @Ajronix and what about this boiler, is there an improvement after changing the parameters?
    You didn't write or take photos for fun, did you? ;-)
  • #49 21728844
    Ajronix
    Level 10  
    >>20333224
    @BUCKS
    Yes, sorry to be so late in replying but the boiler has started working normally. I can't remember which parameters I changed anymore, but thanks to you I managed to set it up, even though the serviceman said it apparently had to be that way. I can check what parameters it's running on as soon as someone can remind me how to get into the service settings. I will now be fitting controls and actuators for the underfloor. I have ordered such a kit from Ali.
    Screenshot of shopping app showing purchased thermostats and actuators for heating Screenshot from a shopping app showing a heating system order including actuators and a Beok thermostat

    I have fitted the drivers for now
    Wall-mounted room thermostat displaying 21.6°C with a setpoint of 20.0°C

    And unfortunately, I found that the minimum hysteresis you can set is 0.5°C, which is a big deal because it works both up and down - that is, if you set 22°C, it turns on at 21.5°C and only turns off at 22.5°C. That's a very big spread; with the Tech cooker kit I could set it as low as 0.2°C.

    The other issue is that these controllers squeak when you put your ear to it. The ones next to the bed can be heard at night. You can generally hear them when they are not performing the "heat" function. If you press the backlight, they squeak intermittently a little quieter. And when they are performing the "heat" function, they are barely audible. Can something be done about this, or are they just going to be like that? The price for everything was attractive, as it was only PLN 1000. How much would such a set cost me from the Polish distribution? Does anyone have any idea? >>20333224
  • #50 21730134
    SITO79
    Level 27  
    Since the topic is old and not closed, I will perhaps complete the information about parameter P8 in the Silver Pro boiler, i.e.:
    P8 Limitation of temperature rise 0-10min
    This is a parameter which tells you how long the boiler's power builds up at start-up.
    As the activation process looks like the ON signal appears then the boiler operates for the time specified in parameter P32 with the power specified in parameter P3 and after this time it goes into operation gradually increasing the power from minimum power parameter P6 to maximum power parameter P7,
    the transition time from P6 to P7 is determined by parameter P8.
    If P8 is set to 0, the boiler, after 30 seconds of operation at starting power, immediately jumps to the maximum power defined in P7 and there is no problem here when the boiler works in a large installation where it will not overheat quickly; in small installations, it is necessary to limit the maximum power P7 to the minimum, i.e. 10kW setting value 100
    In small installations, increasing the value of P8 results in a very slow increase in power and temperature, which may manifest itself in the boiler not reaching 100% power as the heating water reaches the set temperature faster than the time counted down in P8 and the boiler starts modulating power towards the minimum set in P6.

    Changing parameter P8 to 0 will also help when you have problems with burner vibrations at start-up, which happens to people, but this is a slightly broader topic, because then service technicians usually use a trick setting minimum power P6 at too high a value, and the boiler, although after this operation, does not vibrate at start-up because the power increases not from 3kW but e.g. from 5kW, but at the same time the boiler does not vibrate at start-up. after that, however, the boiler no longer works economically because it does not go down to the minimum power declared by the manufacturer of 3kW when there is such a possibility, but works on the 5kW left by the service technician, gas consumption is increased and in a small installation timing may occur, but timing can also be easily managed.

Topic summary

The discussion revolves around setting the reduced temperature range for the Termet ecocondens dual-function oven, specifically how to adjust the heating parameters for optimal performance. Users share insights on changing parameters in the service menu, particularly P02 and P08, to achieve lower temperature settings suitable for underfloor heating. The conversation highlights the importance of understanding the heating system's configuration, whether it involves underfloor heating or radiators, and the implications of temperature settings on efficiency and comfort. Users emphasize the need for practical testing to find the right balance between comfort and boiler operation, as well as the potential for increased gas consumption with certain configurations. The discussion also touches on the limitations of the boiler's design and the necessity of consulting service technicians for specific adjustments.