How can I lower the Termet Silver boiler’s minimum heating temperature for underfloor heating to around 25–30°C?
Set the Termet Silver into its reduced temperature range for floor heating, which is 25–55°C, by changing parameter P02 from 0 to 1 in the service menu [#16763277][#16763993] Enter programming mode by holding K4 and K6 for about 3 seconds until the parameter number flashes, select P02 with K5/K6, then press K3 to edit the value, set it to 1, confirm again with K3, and exit with K4 [#16763993] This mode is specifically intended for floor heating, so it avoids the normal 40–80°C range [#16763277] If the installation also has radiators or mixed circuits, then a mixing system with a three-way valve is needed for the floor loop [#16795804]
  • #1 16763115
    wojczarek
    I have a request to people who will be familiar with this, namely I have a bifunctional Termet Silwer stove the lowest temperature I can set on the stove is 40 degrees and this is too much because I have only floor heating, what can I do in such a situation to lower the temperature to around 30-25stopni
  • #2 16763223
    1repcaK
    Help: 52
    Rate: 123
    Read about three-way valves.
  • #3 16763231
    jacekwwy
    Level 19  
    Help: 39
    Rate: 108
    40 degrees is the "homicide" for the stove, it's best if the temperature for the stove is at least 60 degrees. So you set the stove at a minimum of 60 degrees and some regulator would be useful for the floor-tile, which will reduce the temperature to, for example: 20-30 degrees
  • #4 16763277
    okifaro
    Rate: 11
    Colleagues are just writing to write ....
    - Silver boiler has two temperature ranges in which it works: standard 40-80C and reduced 25-55C, parameter to be set in the service menu
    - instructions on how to do it: https://www.elektroda.pl/rtvforum/topic3296047.html
  • #5 16763278
    mod22
    Help: 130
    Rate: 312
    You set the furnace at a higher temperature and strips with a mixing system and a three-way valve are used for the flooring. This is the basis.
  • #6 16763993
  • #7 16795434
    wojczarek
    Okifaro, thank you for your help regarding the temperature on the stove as the only one you can see on gas stoves, because the stove can actually be switched to floor heating, the rest of the colleagues know that they are calling, but they do not know very well in which church, thank you all ??? ???????????
  • Condensing boiler supports 25–55°C floor heating mode
    #8 16795804
    BUCKS
    Help: 536
    Rate: 1087
    The forum reads different people, so you have to stigmatize nonsense so as not to mislead others.
    The thread is about the Termet Silver boiler, which is a gas condensing boiler.
    And condensing boilers in principle like low temperatures and in the case of radiators, they most like the return temperature of about 30 degrees, because then they have the highest efficiency.
    The condensing boiler likes condensate, the more its boiler has more efficiency, and because it is made of durable materials, this condensate does not harm him.
    Due to the preference for low temperatures, condensing boilers are recommended for floor-standing and as he wrote okifaro and pitrel The Termet Silver boiler has a reduced temperature mode of 25-55 dedicated to floor heating.
    Otherwise, it looks like the old "traditional" boilers, which are basically withdrawn from use and rarely buy such a new one. I have an atmospheric boiler (open combustion chamber) for a dozen or so years, and the boiler will prefer a higher temperature, although the setting range is 35-82 degrees. At lower temperatures of 35-50 degrees, the boiler will also work, but due to the increased amount of condensate, which accelerates corrosion and agony of the boiler, this is not recommended. Then, wanting to use such a boiler near the floor pan, additional mixing valves are obligatory.
    The thread's author would also have to have valves if he had the installation of mixed heaters + floor-standing, but if he has 100% of the floor, it will go without mixers, etc.
    I would ask you to keep the minimum level on the forum and not give advice that indicates that their author has no mastered basics about condensing boilers.
    Although I do not use a condensing boiler, I know these basics, so I would not write such nonsense.
  • #9 16797851
    mod22
    Help: 130
    Rate: 312
    A mass of gibberish and nothing about. Read what the author asked for. This is not about explaining how a condensing boiler works because everyone knows it.
  • #10 16797977
    BUCKS
    Help: 536
    Rate: 1087
    Read what I wrote, because reading comprehension is probably your weakness.
    Well, the forum is reading various people looking for knowledge, so you have to stigmatize posts containing nonsense so that others do not duplicate the same nonsense.
    Since you know how the condensing boiler works, why did you write nonsense, that the boiler is to be set to a higher temperature, since the author has 100% of floor heating, he sets a reduced range of 25-55 degrees instead of 40-80 degrees on the boiler and has a problem with the head.
  • #11 16802895
    mod22
    Help: 130
    Rate: 312
    Because I did not read what exactly the boiler model is and I wrote it from the machine. And in this thread, you're right. There is still the problem of adding additional "traditional" radiators (and to the way I know life probably will eventually come) that need more than 20 few degrees, in which case the need is to use a mixing system for the floor-standing. Greetings.
  • #12 17421416
    wojczarek
    Subject closed positively
    The oven is set to the floor range and after the subject
The discussion revolves around adjusting the temperature settings of a Termet Silwer bifunctional stove, specifically lowering the floor heating temperature from the minimum of 40°C to a more suitable range of 25-30°C. Several users suggest utilizing a three-way valve and a mixing system to achieve the desired temperature. It is noted that the Termet Silwer boiler has two operational temperature ranges: a standard range of 40-80°C and a reduced range of 25-55°C, which can be set in the service menu. Users provide detailed instructions on how to access and change the settings to the reduced range, emphasizing the efficiency of condensing boilers at lower temperatures. The conversation concludes positively, confirming that the stove can be successfully set to the appropriate floor heating range.
TL;DR: To drop below 40°C, switch Termet Silver to reduced mode by changing P02 from 0 to 1 — "set parameter P02 to 1." This unlocks lower setpoints for underfloor heating without external mixers. [Elektroda, Anonymous, post #16763993]
Why it matters: This FAQ helps Termet Silver owners with 100% floor heating quickly unlock safe 25–35°C supply temps without extra hardware.
How do I lower the Termet Silver’s floor heating temperature below 40°C?
Enter the service menu and switch to the reduced temperature range by setting parameter P02 from 0 to 1. This enables setpoints below 40°C suited to underfloor heating. “Set parameter P02 to 1.” [Elektroda, Anonymous, post #16763993]
What temperature ranges does the Termet Silver support?
It offers two space-heating ranges: standard 40–80°C and reduced 25–55°C dedicated to floor systems. Select the reduced range for 25–35°C floor supply targets in mild weather. [Elektroda, okifaro, post #16763277]
How do I change P02 to enable the reduced range?
Three-step How-To:
  1. Hold buttons K4 and K6 for ~3 seconds until the parameter number flashes.
  2. Use K5/K6 to select P02, press K3, set value to 1 with K5/K6.
  3. Press K3 to save, K4 to exit programming. Default P02 is 0. [Elektroda, Anonymous, post #16763993]
Do I need a three‑way mixing valve for 100% underfloor with this boiler?
No, not if you use the boiler’s reduced 25–55°C range. Mixing sets are essential when combining floor loops with higher‑temperature radiators on the same system. [Elektroda, BUCKS, post #16795804]
What if I plan to add radiators later?
Keep the boiler’s floor range for UFH and add a manifold with a mixing system and three‑way valve for the floor circuit. Radiators can run hotter; the mixer protects the floor loops. [Elektroda, mod22, post #16802895]
Is running 60°C on a condensing boiler efficient?
No. Higher flow temperatures reduce condensing and waste energy. As one expert put it, running 60°C is “throwing money away.” Lower returns around 30°C maximize efficiency. [Elektroda, Anonymous, post #16763993]
Why do condensing boilers prefer low return temperatures?
They condense water vapor in flue gases, reclaiming latent heat. Cooler return water (about 30°C) keeps the heat exchanger in condensing mode longer, boosting seasonal efficiency. [Elektroda, BUCKS, post #16795804]
What buttons control programming on the Termet Silver?
Left of display: K1 (upper), K2 (lower). Bottom row: K3 (left), K4 (right). Right of display: K5 (upper), K6 (lower). Use them to enter, adjust, save, and exit parameters. [Elektroda, Anonymous, post #16763993]
Will switching to reduced mode actually fix my too‑hot floors?
Yes. The thread author confirmed success after setting the boiler to the floor (reduced) range. This allowed lower supply temperatures and stable comfort. [Elektroda, wojczarek, post #17421416]
What is a three‑way valve in floor heating?
It’s a mixing valve that blends hot boiler water with cooler return water to achieve the lower supply temperature needed by underfloor circuits when other emitters need higher temps. [Elektroda, mod22, post #16763278]
Can I damage the boiler by running low temperatures?
No, not for a condensing gas boiler. It is designed for low‑temperature operation and benefits from cooler returns, unlike older non‑condensing units. [Elektroda, BUCKS, post #16795804]
What if P02 doesn’t change or the menu won’t open?
Recheck the button sequence and hold time. Start by holding K4 and K6 for ~3 seconds until the parameter number flashes, then proceed to P02. [Elektroda, Anonymous, post #16763993]