Title: Combining 7-10 KVA UPS, Bacterial Modules & Photovoltaic Panels: Is it Efficient?

Doom 14886 45
Best answers

How can I connect a 7–10 kVA UPS to my existing on-grid microinverters so the house stays powered during outages, and is this a sensible solution?

A standard 7–10 kVA UPS is not a good way to combine with on-grid microinverters; the thread recommends a hybrid or off-grid inverter with battery input instead, plus a proper automatic transfer/contacting scheme that disconnects the utility during outages [#19636206][#19636463][#19638392] On-grid microinverters must not be allowed to feed the utility when mains fails, so the installation needs a certified transfer switch or automatic contactor to cut off the operator side; otherwise backfeeding is dangerous [#19636334][#19639098] A simple UPS-only arrangement is problematic because microinverters need AC to run, but when the backup source changes state or synchronization is lost they may shut down, and a normal UPS may not tolerate being fed from the PV side [#19639098][#19640452] For emergency power, the practical options discussed were to power only selected circuits through the UPS/off-grid inverter, or move to a hybrid inverter that can prioritize PV, battery, and grid automatically [#19639110][#19639501] The overall conclusion was that a full house solution with PV backup is possible, but it is expensive and easier to do with a hybrid/off-grid design than by forcing a conventional UPS into the role [#19638392]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #31 19639446
    bestboy21
    Level 40  
    kosmos99 wrote:
    The three-phase ongrid inverter will not be excited by the voltage from a single-phase UPS or Offgrid


    It's just about powering the house in the event of a blackout ;) .
    So we preventively cut off the network and put UPS on the house.
    I didn't understand what it was at first either

    Such an on-grid mixed with an off-grid island. rotfl.
  • ADVERTISEMENT
  • #32 19639448
    kosmos99
    Level 38  
    bestboy21 wrote:
    So we preventively cut off the network and put UPS on the house.

    Wouldn't it be better to power your home with a UPS all the time?
    Then the ATS will not be needed.
    Of course UPS or off with the right power.
  • #33 19639451
    bestboy21
    Level 40  
    kosmos99 wrote:
    bestboy21 wrote:
    So we preventively cut off the network and put UPS on the house.

    Wouldn't it be better to power your home all the time via a UPS?


    Better but 4 times more expensive.
  • #34 19639452
    kosmos99
    Level 38  
    Why? If it's the same UPS. Even better for the battery, because their state of charge will be monitored all the time.
  • ADVERTISEMENT
  • #35 19639459
    bestboy21
    Level 40  
    kosmos99 wrote:
    Why? If it's the same UPS. Even better for the battery, because their state of charge will be monitored all the time.


    If this UPS was to work as on-line, it would have to transfer all the power (and God forbid 3 phases), here we are entering industrial UPSs, you can ... everything is possible.
  • ADVERTISEMENT
  • #36 19639501
    kosmos99
    Level 38  
    See post (1) from the author's topic:

    Doom wrote:
    I'm thinking about connecting a 7-10 KVA UPS


    Added after 3 [minutes]:

    Therefore, cost-effectively, offgrid may be better.

    And it is best to separate current-consuming circuits that do not have to work in the event of a power failure from the network. Then 5kVA single phase should be enough.
  • #37 19639513
    bestboy21
    Level 40  
    kosmos99 wrote:
    See post (1) from the author's topic:

    Doom wrote:
    I'm thinking about connecting a 7-10 KVA UPS


    Added after 3 [minutes]:

    Therefore, off-grid may be better off-grid.

    And it is best to separate current-consuming circuits that do not have to work in the event of a power failure from the network. Then 5kVA single phase should be enough.


    This is some solution.
  • #38 19640377
    Doom
    Level 18  
    Everything is ok, but one detail is still missing for the PV to work when the power supply from the grid fails. Therefore, the UPS cannot be fully separated and could theoretically power the grid together with the PV during a power outage, which is why automatic backup switches are needed. With the cost of PV and UPS, the cost of switches is small. In general, I want to have a plan to know what to complete successively to build a fairly reliable system. I can also buy a few panels and add a classic off-grid, but what will it give? The point is to use all the elements of the current infrastructure and build something that will work efficiently and reliably. If the hybrid inverter can handle it, then ok, I can use it, if a separate charge regulator and a separate converter will be better, it's also ok. If you have any idea or even specific devices that can be nicely customized, I will gladly take your advice :-) I'll just add that I don't live there, so the system must be autonomous, I'm preparing this house to live there when I'm tired of working in corporate. Heating is only electric, both central heating and DHW, I heat it up to about 10 degrees in winter, so that nothing freezes or moldy - that's why I installed PV. Electricity costs in the amount of PLN 800-1000 per month in the winter knocked down. That is why I want PV to supply the grid with surpluses, in the winter PV alone will not be able to afford heating, so it will draw on surpluses from the summer. in September alone, I have about 600 kWh worked out, and there is only a fridge + a small CCTV server. So about 400 kWh will be available. Even if I fire 2 radiators of 2kw each, it will be a bit of a drag, they will not go all the time to the max, but always.
  • #39 19640399
    kosmos99
    Level 38  
    Doom wrote:
    Everything is ok, but one detail is still missing for the PV to work when the power supply from the grid fails.


    It's a linden with microwaves, because they are probably under the panels and we don't have any DC voltage pulled out anywhere.
    With a standard inverter, you could think about replacing it with a hybrid one, or switching panels to Offgrid. Now there is no way to bite it too much.
  • #40 19640437
    Doom
    Level 18  
    Well, that's why I wanted to use switches to disconnect the panels from the mains and connect them to the "internal network" with a UPS / inverter that will simulate the voltage from the supplier. In general, this was the idea for the UPS to power the whole house, i.e. it was connected between the supplier and the receivers. The switches would switch PV from pre-UPS to UPS and vice versa. But then the UPS will not charge from the PV. Only problems ;-) Therefore, the PV could be connected before and after the UPS, but I don't know if the UPS can be powered by the electricity it produces from the batteries.
  • #41 19640452
    kosmos99
    Level 38  
    Doom wrote:
    that's why I wanted to use switches to disconnect the panels from the mains and connect them to the "internal network" with a UPS / inverter that will simulate the voltage from the supplier.


    This will be rather difficult, if at all possible to implement. Even if the microwaves wake up, they will probably damage the UPS, because it will then get voltage at its output.
    The only way out, but also rather difficult to implement, is to disconnect the panels in front of the microwaves and put them on offgrid.
  • #42 19640483
    Doom
    Level 18  
    Well, it will be easier to buy additional 4-8 panels for off-grid and charge the batteries also from microwaves if there is power from the network. In case of failure, disconnect the on-grid and the network from the provider. That is, give a hybrid inverter and connect the network and ongrid as input, then we lose charging from microwaves in the event of a failure, but there will be additional panels that will charge the batteries anyway.

    Which batteries are best to use and how to count them to be enough?
  • #43 19640598
    kosmos99
    Level 38  
    Doom wrote:
    Well, it will be easier to buy additional 4-8 panels for off-grid and charge the batteries also from microwaves if there is power from the network.


    Approx. Only the inverter must have this option to select charging hours.

    Doom wrote:
    In case of failure, disconnect the on-grid and the network from the provider.


    There's no need. You power ongrid before offgrid, i.e. it will turn itself off and on without collision.

    Doom wrote:
    So give a hybrid inverter and connect the network and ongrid as input


    Only the network, if there is sun, you will indirectly use ongrid, which will then work for this network.

    Doom wrote:
    in case of failure but there will be additional panels that will charge the batteries anyway.


    You will use these panels all the time, because the offgrid will continuously supply the loads.

    Doom wrote:
    Which batteries are best to use and how to count them to be enough?


    It depends on the length of the emergency operation, the capacity of the panels and the load. After discharging the batteries to the offgrid input, the generator can be switched on, in addition to powering the loads, it will also charge the batteries.

    I plan to use a Growatt inverter, 2kWp panels and AGM batteries, initially 4 pieces 100Ah. If it's ok, I'll add another 4.
    For batteries of this type, when it comes to service life, temperature and lack of deep discharge are very important. For a temperature of 20C and buffer operation, it is 12 years, but at 40C it is only 3 years, i.e. the battery loses 40% of its capacity. The same is true for discharge cycles. At 100% discharge we have only 300 cycles, 50% 500, and at 30% already 1300.
    Therefore, I will try to discharge them to a maximum of 20% during normal operation and up to 50% in an emergency. There will be no warehouse from this huge one, but the power from the panels will be used. There are also gel and lithium batteries, but the price of the latter is five times higher and they can be discharged much deeper and more often. Overall, they seem to be the most profitable. But I don't want to spend too much right now.
  • #44 20264130
    piotr360
    Level 1  
    Old topic but still relevant?
    I have it like that:
    1. mechanical switch utility or UPS. (unfortunately the break is less than a second but it's there)
    2. Afore solar inverter (single phase - up to 3 phase I don't have UPS)
    3 UPS sinline 1200 VA (pure sine)
    4. Afore smartblocker between the UPS and the inverter - makes sure that the inverter only produces as much as the household consumption and the voltage does not increase)

    The UPS works without load, so on a small battery (2x7Ah) it works for over 6 hours. It is only used to "synchronize" the inverter with the grid (UPS). As there is no "sun", it discharges quickly even in the light itself. I plan to add a "charger" to the batteries outside of the UPS to continuously charge the batteries from solar power. Then it could walk away from the power grid (from dawn to dusk) and not just 6 hours. I had to add an additional load to the output of the UPS to smooth the sine, I experimentally reduced it to a 5 W incandescent bulb.

    I tried with a fideltronik 3000VA UPS and an external MB4821 battery but it does not give a sine (steps) and the Afore inverter does not recognize it as a network. It does not generate electricity as if there is no power at all. A separate battery module was to be powered from an inverter on the other side of the smartblocker. The battery module has output only from the battery (constant current), but the problem is the lack of sine at the output.

    These are experiments, not normal operation of the mains. People who do not have the appropriate knowledge (those with knowledge too) may be at risk, including the loss of their lives and the lives of bystanders. I advise home electricians against such experiments.
  • ADVERTISEMENT
  • #45 20264189
    Doom
    Level 18  
    I've done it like this for now:

    Power supply from the mains + microinverters are connected to the disconnector - on the network side, the disconnector is connected to the power supply of the DELL 8KW UPS, the ups is connected as the power supply of the house installation. What does it give me? The surplus goes to the network and is later returned at night. When I have a power outage from the mains, the house still works normally - the UPS supports the whole thing - the panels do not produce. It's not a perfect solution, but it's good enough for now. I also have a generator that I will want to connect via an automatic switch + several batteries charged directly from other panels with a 2500KW full sine constant power inverter.
  • #46 20612924
    tomekp15
    Level 12  
    Hello,
    I'm digging up some old stuff, but I'm having the same dilemma.

    The solution is Victron Multiplus II, but only if the PV installation is reported to the ZE.

    If I did not want to report the PV installation to the ZE, I only have off-grid.
    The problem is that I want to use Enphase microinverters that I would like to plug into the emergency power supply of the house, e.g. Sinus converter. In microinverters I set the network profile to Zero Export and in theory everything works and I am separated from the ZE grid. But in practice, the Zero Export mode needs time to measure and analyze before it lowers PV production, so some excess energy will be delivered to the output of the inverter or UPS for a short time anyway, i.e. there will be a momentary higher voltage.

    The question is, are there any emergency power devices that have protection against short-term power supply to the output?

Topic summary

✨ The discussion revolves around the integration of a 7-10 KVA UPS with existing photovoltaic (PV) panels and the potential use of bacterial modules for home energy management. The user seeks advice on the feasibility and efficiency of this setup, particularly in maintaining power supply during outages. Key points include the importance of adhering to safety regulations when connecting to on-grid systems, the potential for using off-grid inverters for better energy management, and the necessity of automatic switches to prevent backfeeding into the grid during power failures. Participants emphasize the need for a hybrid system that can utilize both grid and solar energy effectively, while also considering the costs and technical challenges associated with battery storage and inverter configurations. The conversation highlights various solutions, including the use of automatic transfer switches (ATS), hybrid inverters, and the importance of energy storage management.
Generated by the language model.

FAQ

TL;DR: A 10 kVA online UPS can draw ≈600 W at idle, and “there is no cosmic possibility that reverse voltage will appear” [bestboy21, 19636334]. Use a certified ATS to island the house and consider a hybrid inverter for higher round-trip efficiency. Why it matters: incorrect wiring can trip micro-inverters and violate grid-safety rules.

Quick Facts

• Idle draw 10 kVA UPS: 500–800 W [Eaton Spec, 2023] • Victron MultiPlus II change-over: 15–20 ms [Victron, 2023] • ENS relay (Ziehl UFR1001E): €250, trips <0.2 s [Ziehl Price, 2023] • 48 V bank, 4 × 100 Ah AGM = 9.6 kWh gross, 5 kWh usable at 50 % DoD [kosmos99, 19639147] • AGM cycle life: 300 (100 % DoD) to 1 300 (30 % DoD) [kosmos99, 19640598]

1. Is it legal to connect a UPS directly to an on-grid micro-inverter system?

Not without certified islanding protection. Polish and EU rules forbid feeding private power back to a dead grid. A UPS wired “guerrilla-style” breaches safety law and can endanger linemen [bestboy21, 19636206]. Use a certified automatic transfer switch (ATS) or an ENS relay that opens all poles when grid voltage disappears.

2. How should I wire the automatic transfer switch to avoid back-feeding the grid?

Place the ATS upstream of the UPS. Pole 1 connects utility + micro-inverters, pole 2 connects UPS/hybrid output. The common goes to the house board. When utility fails, the ATS drops pole 1 within 0.2 s and closes pole 2, isolating the property [bestboy21, 19636334].

3. Will micro-inverters stay online when powered by a UPS during blackout?

Rarely. UPS voltage often drifts above 250 VAC with light load, forcing micro-inverters to trip under EN 50549 limits [wilk125, 19639098]. They also need frequency synchronisation that many UPS units fail to provide.

4. Is a hybrid (off-grid) inverter more efficient than a large UPS for backup?

Yes. Hybrid inverters operate at 92–96 % round-trip efficiency and idle at <30 W, while online UPS units idle at 500–800 W [Eaton Spec, 2023]. Hybrids also integrate MPPT charging and ATS logic [kosmos99, 19638748].

5. How big should my battery bank be to ride through a 12-hour, 1 kW load?

You need 12 kWh usable. With AGM at 50 % depth-of-discharge, install ≈24 kWh gross: eight 12 V × 200 Ah or sixteen 12 V × 100 Ah batteries in a 48 V string [kosmos99, 19639147].

6. Which battery chemistry offers best lifecycle cost?

LiFePO₄ costs ≈2 000 €/10 kWh but gives 3 000–6 000 cycles at 80 % DoD. AGM costs ≈1 300 €/10 kWh yet falls to 500 cycles at 50 % DoD [kosmos99, 19640598]. Over 10 years, LiFePO₄ usually wins despite higher entry price (“Battery Cost Comparison”, 2023).

7. What happens if PV export briefly exceeds UPS load capacity?

Line voltage spikes; if it climbs above 253 VAC for 0.2 s the UPS may shut down or micro-inverters disconnect, causing a brown-out cascade [EN 50549; wilk125, 19639098].

8. How much does a 10 kVA UPS cost in Poland?

Users report 12–15 k PLN for refurbished datacentre units [Doom, 19636256]. New industrial models start around 25 k PLN (“UPS Cennik”, 2023).

9. Three-step safe changeover procedure (How-To)

  1. Open the main breaker and verify zero voltage with a tester. 2. Switch ATS to “Generator/UPS” and start the inverter. 3. Re-energise critical circuits only; log voltage and frequency for 2 minutes to confirm stability [Elektroda consensus].

10. What certified devices disconnect PV from the grid automatically?

ENS relays such as Ziehl UFR1001E or ComAp MainsPro meet DIN V VDE V 0126-1-1 and cut both phases within 200 ms when voltage/frequency deviate [Ziehl Manual, 2023].

11. Can I let a petrol generator charge the same batteries?

Yes, route the generator into the AC-in of a hybrid inverter set to “Gen” mode. It will prioritise load then charge the 48 V bank at up to 80 A according to model specs [kosmos99, 19639147].

12. Does running the whole house permanently through a UPS hurt battery life?

Online UPS keeps batteries float-charged; with AGM at 20 °C float life reaches 12 years, but high ambient (40 °C) cuts it to three [kosmos99, 19640598]. Keep UPS in a cool room and exercise batteries monthly.

13. How much will certified ATS + hybrid inverter + 10 kWh LiFePO₄ cost?

Approx. €250 ENS relay + €1 800 5 kW hybrid inverter + €2 000 LiFePO₄ bank equals €4 050 (≈18 k PLN) [Ziehl Price 2023; Victron, 2023; “LiFePO4 Market”, 2023].

14. Why do micro-inverters sometimes out-produce string inverters on cloudy days?

Module-level MPPT lets each panel harvest low irradiance earlier and recover faster after voltage trips, giving up to 20 % extra yield under shading [Doom, 19638821]. Expert quote: “They start much earlier and, after a restart, produce again within minutes.” [Doom, 19638821]
Generated by the language model.