I will not agree. While 8A for 1mm² may be acceptable in some circumstances for 230VAC installations, it means nothing. Following this lead, 10mm² would allow for a continuous load of 80A, and this has nothing to do with the permissible values. What counts above all is the allowable voltage drop on the cable, regardless of the power dissipated on it. 0.5V at 230V is nothing but at 12V it becomes significant.
Let's assume that we drop 0.5V on a given section of the cable, a 12V installation powered by batteries. The battery has 11.5V, 11V on the inverter and there is already a cut-off, so we do not have the full capacity of the battery available.