Calculation of the conductor cross-section - direct current DC, 12V

new_player 38448 6
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 18373658
    new_player
    Level 5  
    Hello users,

    I need to calculate the cross section of the DC conductors for 2 devices.
    Voltage 11-12.5V, DC
    The value of the current, if it ever flows like this - 30A. Nominal value 10-25A.

    Cable length in 1 device: 0.8m.
    Cable length in device 2: 0.5m.

    At the moment I have a 2.5mm ^ 2 cable, which I would like to use due to the small distance between the source and the receiver.

    While searching the forum, I found an online calculator available at:
    https://enterius.eu/wsparcie/kalkulator-przekrój-pirectow-led/
    In the link to the calculator available above, the 2.5mm ^ 2 cable fits, but nevertheless I would like to consult the forum.
  • ADVERTISEMENT
  • Helpful post
    #2 18373683
    daro31ie
    Automation specialist
    The 2.5 cable is perfectly suited to your application.
  • ADVERTISEMENT
  • #3 18373777
    new_player
    Level 5  
    daro31ie wrote:
    The 2.5 cable is perfectly suited to your application.


    For both devices?
    Cable length in the device 1: 0.8 m.
    Cable length in device 2: 0.5m.

    greetings
  • #4 18373945
    kierbedz4
    Level 36  
    For a current of 30A, the cable cross-section should be 4mm2. You can load a 2.5mm2 cable with a current of up to 20A
  • ADVERTISEMENT
  • #5 18375779
    teskot
    Level 37  
    There is no clear answer to the question, because we do not know what the acceptable voltage drops may be and how the cable is arranged and thus cooled. For copper, the resistance is 18m?xm / mm? and this formula should be used in such calculations.
  • ADVERTISEMENT
  • #6 19659891
    skautek
    Level 11  
    Hello!
    If I need to give a cable, e.g. 10mm², can I give e.g. 3x5mm² instead?
  • #7 19660686
    MietekFighter
    Level 20  
    You can give 2x5mm2. 3x5mm2 even more.

Topic summary

The discussion revolves around calculating the appropriate cross-section for DC conductors used in two devices operating at 11-12.5V with a maximum current of 30A. The user currently has a 2.5mm² cable, which is deemed suitable for currents up to 20A. However, for a 30A load, a 4mm² cable is recommended. The conversation highlights the importance of considering voltage drop and cable arrangement for accurate calculations. An online calculator was referenced for initial assessments.