Determining Correct Wire Cross-Section for 12V 10A, 2 Meter Installation

arturmt26 40005 5
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 12394474
    arturmt26
    Level 10  
    The subject of the post is the question: what wire cross-section should be for a 12V 10A installation, 2 meters long.
    Thank you for your help.
  • ADVERTISEMENT
  • Helpful post
    #2 12394632
    Sołtys_Elbląga
    Level 31  
    If you give 1.5 mm it will be perfect.
  • ADVERTISEMENT
  • Helpful post
    #3 12394644
    ladamaniac
    Level 40  
    Continuous or instantaneous load, wire loose or bundled? 4 to 6 A per 1 mm? is assumed. I would recommend 2.5mm?, since this length will not add up to much of the cost.
  • ADVERTISEMENT
  • #4 12394794
    Quarz
    Level 43  
    Sołtys_Elbląga wrote:
    If you give 1.5 mm it will be perfect.
    If it is a copper wire, it will have a voltage drop of almost 0.5V (from the source to the receiver):
    ?U = (2 o 2m / (56 (m / (? o mm? ;) ) o 1.5mm? ;) ) o 10A = 0.476190 ... V
    ignoring the power losses in such a 'conductor'.
  • ADVERTISEMENT
  • #5 12394800
    arturmt26
    Level 10  
    Rather continuous work for me - two hours of work followed by an hour of break and the cycle repeats itself all over again. Free-lying cable.
  • Helpful post
    #6 12394804
    Quarz
    Level 43  
    arturmt26 wrote:
    [p] P. rather continuous flare because as for [space] I have two hours of work, then an hour of break, and the cycle repeats itself. Free-lying cable.
    Look up...