Thanks for replying,
I have MCCB data as follows:
MCCB Rating = 40 Amps (i.e. Maximum Continuous Ampere Rating at 40 degree C)
Thermal Range = 32 - 40 Amps
Magnetic Range = 200 - 400 Amps (i.e. Instantaneous Pickup Range)
Horizontal axis = Multiple of current setting (i.e. Multiples of 40 Amps - Breaker Rating).
Based on this info, what will be the maximum instantaneous fault clearing time (secs)?
I came up with:
1) 5.5 secs corresponds to 10X (400 Amps)
2) 4.6 secs corresponds to 9X (360 Amps)
which one of the above two values in (secs) are close to being correct or else?
Note: Not to confuse you regarding 9X (360 Amps) value I choose in the graph.
I selected 9X because I selected this MCCB to protect a Motor whose Lock Rotor Current = 143 Amps, the Service Factor of this Motor is 1.0, therefore I used 360 Amps magnetic setting > (2.5 X LRC) = 357. 5 Amps.
Regards