Why Did 3 Pole Breaker Trip but 90A Time Delay Fuses Didn’t Blow on 50HP Motor?

12 7
ADVERTISEMENT
  • #1 21683279
    Christopher Moya
    Anonymous  
  • ADVERTISEMENT
  • #2 21683280
    Elizabeth Simon
    Anonymous  
  • ADVERTISEMENT
  • #3 21683281
    Christopher Moya
    Anonymous  
  • #4 21683282
    Elizabeth Simon
    Anonymous  
  • ADVERTISEMENT
  • #5 21683283
    Christopher Moya
    Anonymous  
  • #6 21683284
    Elizabeth Simon
    Anonymous  
  • ADVERTISEMENT
  • #7 21683285
    colin adam
    Anonymous  
  • #8 21683286
    FauxN Cotton
    Anonymous  

Topic summary

A 50HP, three-phase, 480VAC industrial compressor motor rated at 80A experiences immediate main breaker trips upon startup. The system includes a 175A three-pole circuit breaker and a disconnect switch with three 90A time delay fuses. Despite a detected phase-to-phase short in the motor, the 90A time delay fuses did not blow, and the motor overload protection did not trip, leading to the breaker tripping first. Time delay fuses can tolerate currents up to twice their rating for a duration, allowing a faster-acting breaker to trip before fuse operation. The fuse rating and type may be inappropriate for the motor's startup and fault conditions. Recommendations include reviewing trip curves for both fuses and breakers to understand coordination and consulting the motor/compressor manufacturer for proper fuse specifications. Fast-acting fuses are not necessarily suitable without knowing the motor's startup current and fault characteristics.