EN 50575 standard applicability for equipment wiring—does it cover non-building wire?
318 6
  • #1 21680121
    Daniel Beck
  • EN 50575 applies to cables in construction works
    #2 21680122
    Richard Gabric
  • #3 21680123
    Rick Curl
  • Valve box wiring may trigger EN 50575 scope concerns
    #4 21680124
    Daniel Beck
  • Recommend using wire that already meets ENxxxx
    #5 21680125
    Aubrey Kagan
  • #6 21680126
    Elizabeth Simon
  • #7 21680127
    Daniel Beck
The EN 50575 standard specifies fire and smoke reaction requirements for power, control, and communication cables used in construction works, primarily covering building wiring and civil engineering applications. It aims to limit fire spread and smoke generation in buildings. The standard generally does not apply to internal wiring within equipment but may apply to external cables connecting devices. A customer requested equipment wiring compliant with EN 50575, despite the wiring being 18AWG individual wires inside a valve box operating at 24VDC, which is not typically considered building wire. The contractor argued that since the valve box is mounted on a wall, it becomes part of the building structure, potentially extending the standard's applicability. This raises concerns about costly changes if the requirement is extended to all equipment wiring. It is recommended to obtain the exact standard from the customer, clarify applicable sections, and verify certification requirements with relevant authorities. Finding wire certified to UL, CE, and EN 50575 simultaneously may be challenging. Using certified cables for external wiring is a practical approach to meet such demands.