Best Location for Contactor: Input or Output Side of 2400VA 230V/115V Transformer?
300 6
  • #1 21681425
    Tom Blough
  • #2 21681426
    Rick Curl
  • #3 21681427
    Tom Blough
  • #4 21681428
    Rick Curl
  • #5 21681429
    Tom Blough
  • #6 21681430
    Cologne LED
  • Calling out plagiarism and account suspension
    #7 21681431
    Max Maxfield
For a CNC machine tool conversion using a 2400VA 230V/115V stepdown transformer powering servo motors, it is recommended to place the e-stop contactor on the input side of the transformer to cut power to the entire machine during an emergency. Although frequent cycling of the transformer is not harmful, the large inrush current at energization can cause premature wear of the contactor unless it is appropriately oversized. A 40A contactor is suggested for an estimated 10A steady-state input current. The e-stop also functions as a reset for the motion control processor, so consideration of the contactor's durability under repeated cycling is important.