Hi Joe,I pulled up an old danfoss vsd manual that I had for a HVAC drive fc102 1-90 kw. Not sure obviously which one you have but the screenshot below suggest that the terminals that you mentioned are correct at least for this drive.
I hope you can see the screenshot above and the values of resistance shown. Using the ptc wired via the digital input method, a closed circuit from terminal 10 through the thermistor and back to terminal 33. Any termistor value below 800ohms is seen as healthy temperature and a value somewhere between 800ohms and 2.7 kohms will be seen as unhealthy and cause the drive to stop. Does this help?