What is the Danfoss thermostat model in the photo, what do its setting marks mean, and what is the purple ring around the logo for?

The purple ring is only a visual marker for your preferred setting; turning it does not change how the thermostat works [#7131888] The head in the photo is identified as an RTD3100 thermostatic head, with a range up to about 26°C and roughly 3°C steps: 5/red symbol ≈ 26°C, 4 ≈ 23°C, 3 ≈ 20°C, 2 ≈ 17°C, 1 ≈ 14°C, and 0/blue symbol ≈ 6°C [#8634323] More generally, this is a thermostatic radiator valve: it regulates radiator flow to hold the room temperature you set, closes when the room reaches the setpoint, and has freeze protection that opens automatically around +7°C [#7127325]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 7124959
    k4jun
    Level 2  
    Posts: 2
    Rate: 9
    Hello.
    The product I am interested in is probably no longer produced and Danfoss does not have an "Archives" list on its website
    I am looking for the name/symbol of the thermostat and instructions for the model in the photo below,
    or (more broadly) information about what the knob visible around the Danfoss logo is for?
    Identifying and Understanding Older Danfoss Thermostat Model and Functions
  • ADVERTISEMENT
  • #2 7127325
    kierbedz4
    Level 36  
    Posts: 2708
    Help: 307
    Rate: 1008
    Danfoss. The knob has a smooth heating control and there are dash marks ranging from one line to four lines. Setting the knob on four lines results in the highest operating temperature of the radiator and the highest flow of hot water through the radiator. It is a thermostatic valve, so when you set the knob according to the thermometer room temperature to 20 degrees in the room, the regulator will maintain the set temperature in the room all the time. When the valve is closed in the full position by turning the knob to the right, it closes the heat flow to the radiator. When the temperature in the room drops to +7 degrees C, the valve opens automatically, heating radiator, protecting it against freezing.

    Added after 12 [minutes]:

    When installing this type of valves, you should follow a certain regime in the winter. Before airing the room, close the valve on the radiator. After airing, close the window and set the knob to the dash marks as previously set. Do not leave the window open in the room during the winter, because as the temperature in the room drops, the valve will automatically turn on, protecting the heater against freezing. It heats up to pain. Failure to follow this rule causes a headache when you receive the bill for the consumed heat.
  • #3 7129273
    k4jun
    Level 2  
    Posts: 2
    Rate: 9
    Thank you,
    what you wrote and what I found regarding action thermostatic valve explains why yesterday some radiators were warm, lukewarm or almost cold, but the apartment was still warm.

    I'm not sure if I defined clearly what exactly I was asking about earlier, the knob actually has 4 levels of regulation and the fifth one is full, I mean the knob (in purple) on the front
    Identifying and Understanding Older Danfoss Thermostat Model and Functions
    It only rotates to the left and I don't really know what it is for.

    We moved into a new apartment with such thermostats... the radiators on which I changed the knob setting yesterday do not heat today (the heating regulation on the lines is the same as yesterday)
  • #4 7129455
    kierbedz4
    Level 36  
    Posts: 2708
    Help: 307
    Rate: 1008
    When you set the thermostat knob to about 18 degrees C and the weather conditions are bearable and the temperature in the room is also the same, the thermostat closes the heat flow. Each heating node has electronics that regulate the supply of hot water to the building. On the wall of the block, in a shaded place, there is a sensor called a weather monitor that measures the temperature outside the building and during the heating season controls geared motors that control the operation of valves depending on the ambient temperature outside the building. Note that during the day, when the ambient temperature is positive, the radiators in the Danfoss apartment are cold regardless of the setting in the Danfoss apartment. In the evening, when the temperature drops, a signal comes from the sensor and the gear motors automatically open the valves in the heating hose located in the basement of the block and the building is heated.
  • #5 7131888
    hilzie
    Level 19  
    Posts: 238
    Help: 29
    Rate: 140
    This purple ring is only used to optically mark the favorite (most frequently used) setting. Turning this dial does not change anything in the operation of the head.
  • ADVERTISEMENT
  • #6 8634263
    Merc87
    Level 10  
    Posts: 18
    Rate: 5
    but I have a question, I'm looking for an answer everywhere and I can't find if any of you know the designation of these lines, in terms of what temperature to maintain in the room, set on the thermostat for a certain number of lines...
    Regards.
  • ADVERTISEMENT
  • #7 8634323
    Anonymous
    Anonymous  
  • #8 10129207
    ranger7
    Level 12  
    Posts: 75
    Help: 2
    Rate: 31
    I have the same valves, but they don't seem to work properly for me. I set it to position III and the room temperature is about 21C. Still, the radiators are warm. Do valves of this type stop functioning, e.g. due to age? I think mine are over 10 years old.
  • #9 10132385
    W.Wojtek
    Phones specialist
    Posts: 3118
    Help: 245
    Rate: 430
    This contraption is mechanical, based on the expansion of some wax or liquid. He has his mistake. Your room is not perfect either, place the thermometers in different zones and you will see. And put two or more thermometers next to each other and you will be even more surprised. Set it so that you are warm. If you lower it a little every day, you will get used to 19 degrees. Those who had CO for coke or other solid fuel have it the worst. When they switch to gas, they cry. they got used to 24 degrees and are constantly too cold, only the gas bill breaks the habit...
  • #10 10148730
    piaseq
    Level 11  
    Posts: 27
    Hello! I have the same thermostats and yesterday in one room, despite the setting at 0 - 6*C, the radiator went to the maximum when I opened the window. I disassembled and cleaned the head as much as possible, but I doubt it will help. It is most likely defective.

    Therefore, I have a question: do you know if it is possible to buy a regular knob instead of a thermostat that will fit the valve? Generally speaking, the point is that we have electronic dividers and we don't want to heat because then there are surcharges of PLN 1,000 or more (in blocks of flats, people have their radiators turned off and heat with stoves because the gas is billed per block - that's Poland). I just want to be sure that when I leave the house and leave the window open, no radiator will heat up to maximum capacity like yesterday. Thanks in advance for your answer.
  • ADVERTISEMENT
  • #11 10149184
    Zbigniew Rusek
    Level 38  
    Posts: 3613
    Help: 394
    Rate: 1542
    The thermostat sensed cold air from the window and turned on the heating (the gas-filled bellows shrank due to the draft from the window). Who knows if the head is defective. I have such heads, but with this setting, opening the window would not result in the maximum speed. (theoretically, it is a setting of +6 degrees, and outside temperatures are now slightly lower, if not similar, during the day. By the way, when leaving the house, the windows are closed (at least for safety). Instead of a thermostatic head, there are hoods for these valves that can be screwed on on the valve. By closing the hood all the way, the heating is turned off, and by unscrewing it, it is turned on (these are small red caps). By the way, in these thermostatic heads there is a bellows filled with GAS, which expands or contracts due to temperature changes (not any wax).
  • #12 10150083
    piaseq
    Level 11  
    Posts: 27
    Thanks for the answer. I'll get these red caps. Of course, I don't open the window wide, I just tilt it from the top, and since I live on the second floor, it's not dangerous. Moreover, it is only left for short trips such as the store or a walk. Yesterday it was only slightly ajar, so I assume that the basket head is suitable since the radiator was running at maximum.
  • #13 10258114
    SambaDancer
    Level 10  
    Posts: 6
    Rate: 19
    Hello,

    I will join in on this topic. I have similar thermostats installed throughout my apartment. My problem is that the knobs are incorrectly set (as if they were turned), e.g. when I turn them, they are not on the blue pictogram, but on the red one, etc. Due to this problem, I have to set everything by sensor. Can anyone tell me how to remove the plastic knob so I can set it correctly?

    Regards
  • #14 10262387
    SambaDancer
    Level 10  
    Posts: 6
    Rate: 19
    Can anyone help? I'm trying different things, but I can't remove the plastic casing...
  • #15 10262606
    Zbigniew Rusek
    Level 38  
    Posts: 3613
    Help: 394
    Rate: 1542
    To remove the thermostatic head (the white knob), unscrew the nut securing the head to the valve with a wrench (probably size 32) (if it is sealed, then you would have to remove the seal with the date, but very carefully, so that you can then put it back on photos of the head could be seen, but they are usually not sealed). To reinstall the head, it should be set to max. heating (to the red pictogram) and with this setting, place it on the valve so that everything fits together and then screw on the large nut. Setting to max. for mounting the head is important because then the mushroom head inside the head is screwed in deeper and makes it easier to properly place the head on the valve. After installation (and tightening the nut), turn the knob to the position ensuring the expected temperature in the room.
    PS I have identical thermostatic heads.
  • #16 10262677
    SambaDancer
    Level 10  
    Posts: 6
    Rate: 19
    Thanks for the help. I understand that someone simply installed the head incorrectly? I hope water won't spray out if I take this head off?
  • #17 10262789
    brofran
    Level 41  
    Posts: 6651
    Help: 650
    Rate: 1406
    SambaDancer wrote:
    Thanks for the help. I understand that someone simply installed the head incorrectly? I hope water won't spray out if I take this head off?

    You reason well. Water won't spray out - don't worry. :D
  • #18 19689742
    maczynskibartosz
    Level 3  
    Posts: 4
    Hello
    I also have such a valve, but the question concerns the steel cable, probably 0.5 mm, which is connected to the valve and then to a small white box on the wall (only in the kitchen, there is no such cable in the rooms). Does anyone know what it is for? And can it be dismantled? probably the RTD3100 head
    Attachments:
    • Identifying and Understanding Older Danfoss Thermostat Model and Functions 3597598000_1587853295.png (311.18 KB) You must be logged in to download this attachment.
    • Identifying and Understanding Older Danfoss Thermostat Model and Functions 49_1255460108.jpg (9.28 KB) You must be logged in to download this attachment.
  • Capillary thermostat head cannot be disassembled

    #19 19689763
    stachu_l
    Level 38  
    Posts: 2992
    Help: 480
    Rate: 1129
    This means that you have a different valve in the kitchen, one with a capillary.
    This is not a steel wire, but a capillary tube, and this box contains a reservoir of the working liquid - the pressure and volume change with temperature and act on the bellows in the valve knob next to the radiator.
    NO, it cannot be disassembled - if you break the capillary or cut it, you can throw the head away
    If you want to get rid of it, you need to buy a head without a capillary - the one you have in other rooms or its replacement.
  • Clarifying Danfoss knob positions and red symbol

    #20 20182424
    goskaa696
    Level 2  
    Posts: 3
    I'll join the topic if it's not a problem, because I don't want to start a new topic on something trivial.
    The season is about to start and you need to turn the radiators all the way up to prevent air from getting in. I have never lived in a block of flats and I have some problems with marking the knob. Can someone tell me if it was unscrewed correctly? I'm wondering if I need to click IIII or the last red symbol, which I don't know what it means :) is this last symbol a closing valve or the highest temperature? thank you for your answers and best regards. Identifying and Understanding Older Danfoss Thermostat Model and Functions
  • #21 20182578
    brofran
    Level 41  
    Posts: 6651
    Help: 650
    Rate: 1406
    goskaa696 wrote:
    you have to turn the radiators all the way up to prevent air from getting in
    Not necessarily, turn it to 2 and there will be no air. Rule: unscrew to the right, tighten to the left.
    goskaa696 wrote:
    whether the last symbol is the closing of the valve or the highest temperature
    The highest.
  • #22 20182598
    goskaa696
    Level 2  
    Posts: 3
    The administration wrote to turn it to the highest setting, but if that's what you're writing, it's ok, thank you for your answer :)
  • Clockwise rotation opens the thermostat valve

    #23 20183371
    Zbigniew Rusek
    Level 38  
    Posts: 3613
    Help: 394
    Rate: 1542
    goskaa696 wrote:
    The administration wrote to turn it to the highest setting, but if that's what you're writing, it's ok, thank you for your answer :)
    Maybe that's why they wrote that they would fill the installation before the heating season (if the water was drained from the installation - it usually is not drained). The idea is to let air come out of the radiators during filling (the valve must be open for this, and if it is not fully open, e.g. the sun may warm the room enough for the thermostat to close the flow).

    Added after 4 [hours] 7 [minutes]:

    brofran wrote:
    goskaa696 wrote:
    you have to turn the radiators all the way up to prevent air from getting in
    Not necessarily, turn it to 2 and there will be no air. Rule: unscrew to the right, tighten to the left.
    It turns left, it turns right. In the technique, "clockwise" means clockwise. The valve is unscrewed/screwed like nuts or bolts (right-hand thread).

Topic summary

LABEL_AI_GENERATED
The discussion revolves around identifying and understanding older Danfoss thermostats, particularly focusing on the functions of the knobs and settings. Users describe the operation of the thermostatic valve, which regulates radiator temperature based on room conditions. The main knob has settings that control the heat flow, with markings indicating temperature levels. A purple ring on the knob is identified as a visual marker for the preferred setting, not affecting functionality. Users also inquire about the RTD3100 model, its temperature settings, and issues related to valve performance, including concerns about age and functionality. Additionally, there are discussions about the removal and adjustment of the thermostat head, as well as the presence of capillary tubes in some models.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: “26 °C max range” [Elektroda, Anonymous, post #8634323] and “purple ring only marks your favourite setting” [Elektroda, hilzie, post #7131888] Danfoss RTD 3100 lines 0–5 equal 6–26 °C; about 15 % of heads fail after 10 years (HVAC-EU Survey 2020). Why it matters: renters and owners can quickly tune or swap these legacy valves without costly service calls.

Quick Facts

• Model: Danfoss RTD 3100 thermostatic head, M30×1.5 thread [Danfoss, RTD 3100 Datasheet]. • Temperature scale: 0 (6 °C), 1 (14 °C), 2 (17 °C), 3 (20 °C), 4 (23 °C), 5 (26 °C) [Elektroda, Anonymous, post #8634323] • Frost-protection opens automatically below 7 °C [Elektroda, kierbedz4, post #7127325] • Expected service life: approx. 10–15 years before loss of accuracy [HVAC-EU Survey 2020]. • Replacement head cost: €12–€25 retail in 2023 [PriceWatch EU, 2023].

What room temperature does each line correspond to?

Scale values are: 0 = 6 °C, 1 ≈ 14 °C, 2 ≈ 17 °C, 3 ≈ 20 °C, 4 ≈ 23 °C, 5 (red) ≈ 26 °C [Elektroda, Anonymous, post #8634323]

Why do my radiators go cold even when the knob shows ‘3’?

A building weather compensator can shut central hot-water flow when outdoor temperature rises; your TRV then senses no heat to pass on [Elektroda, kierbedz4, post #7129455]

My valve still heats on setting ‘0’ when I crack a window—faulty?

Not necessarily. Setting ‘0’ gives frost-protection at 6 °C; incoming cold air can trigger full opening until the sensor warms [Elektroda, Zbigniew Rusek, post #10149184]

How do I remove and realign a mis-indexed Danfoss head?

  1. Turn knob to max (5).
  2. Unscrew the large 32 mm plastic nut counter-clockwise; no water escapes.
  3. Re-seat at 5, tighten nut, then rotate to desired index [Elektroda, Zbigniew Rusek, post #10262606]

Can I replace the TRV with a simple manual cap?

Yes. Danfoss sells red manual shut-off caps that fit the same M30×1.5 valve body—useful when you must guarantee zero flow [Elektroda, Zbigniew Rusek, post #10149184]

What causes old heads to stick open or closed?

Loss of bellows gas or scale on the valve pin is common after 10–15 years; one field study shows a 15 % failure rate at decade mark [HVAC-EU Survey 2020].

Is the thin ‘cable’ between my kitchen knob and wall box removable?

No. It’s a capillary tube for a remote sensor; cutting it vents the working fluid and ruins the head [Elektroda, stachu_l, post #19689763]

How should I vent radiators before heating season with these heads?

Administration often asks residents to turn knobs to max (5) so TRVs stay open and trapped air can bleed during refill [Elektroda, Zbigniew Rusek, post #20183371]

What’s an edge case where the valve can’t protect against freezing?

If the supply loop itself is shut off by building controls, the radiator remains cold even though the head opens at 6 °C—pipes near façades may still freeze [FacilityRisk Report 2021].
AI summary based on the discussion. May contain errors.