    who can help me, I want to connect a 2 kv boiler and I have to run a cable, but I do not know what 1.5 or 2.5 mm should be, or maybe a thicker one who will help me
  • ADVERTISEMENT
  • Helpful post
    #2 3037341
    Jerzy Węglorz
    Level 39  
    2kW is a current of up to 10A, so 1.5mm? copper is enough.
  • ADVERTISEMENT
  • #3 3037353
    piter3173
    Level 11  
    and for the bulb 3 times 100v, 0.75kw is enough in this case? for this boiler, these 1.5 will be enough because it will be working all the time? Regards
  • ADVERTISEMENT
  • #4 3037583
    robokop
    VIP Meritorious for electroda.pl
    If you can add 2.5mm2 to the boiler for a longer distance, it will not hurt - the current flowing in the conductor with some resistance causes it to emit heat, i.e. a loss.
  • #5 3038091
    Jerzy Węglorz
    Level 39  
    When designing the installation, it is assumed that the current density in copper conductors in the loaded section may be 6 - 10A / mm? constantly, and in the sections loaded occasionally, but for a short time, it should not exceed 16A / mm?. The load depends on the quality of the insulation and cooling conditions, moreover - e.g. in pipes where several pairs of wires are flying together - there should be a lower load, while in an overhead installation, where the wires are hanging apart from each other and are well cooled, higher densities can be assumed.
    The copper resistance is 0.0175 Ohm * mm? / m, so a cable with a cross-section of 1.5mm? and a length of 10m (2x5m) has a resistance of 0.116 ohms, i.e. the current flow of 8.7A to the 2kW / 230V boiler will generate 8.8W of power in it, which in such a section should not heat the cable by more than 1 degree Celsius above the ambient temperature, the start power is 8.8 / 2000 = 0.44% of the supplied power.
    Do you already know how it is designed?
  • ADVERTISEMENT
  • #6 16537499
    boruurob
    Level 12  
    I will step on the topic. I do not really understand these calculations.

    I have a 2.1kW / 230V boiler, 2m long cable. What cross-section should be? For today I have 0.75mm2 connected but the cable heats up quite well.
  • #7 16537516
    sp4msu
    Level 20  
    1.5 mm2 is more than enough.
    This is the post above.
  • #8 16537603
    retrofood
    VIP Meritorious for electroda.pl
    boruurob wrote:
    For today I have 0.75mm2 connected but the cable heats up quite well.

    Are you playing with grenades too? You are brave. Just don't cry after you burn up the hut.

Topic summary

The discussion revolves around selecting the appropriate wire thickness for connecting a 2 kW boiler. Responses indicate that a 1.5 mm² copper wire is generally sufficient for this application, as it can handle currents up to 10A without significant heating. However, some participants suggest that using a 2.5 mm² wire may be beneficial for longer distances to reduce heat loss due to resistance. The conversation also touches on the importance of considering current density and cable length in the installation design, with recommendations for maintaining safe operating temperatures.