Choosing the Right Wire Thickness for 2 KV Boiler: 1.5mm, 2.5mm, or Thicker?

piter3173 44890 9
Best answers LABEL_AI_GENERATED

What cable cross-section should I use to connect a 2 kW boiler?

A 1.5 mm² copper cable is enough for a 2 kW boiler, because 2 kW at 230 V is about 10 A [#3037341] The detailed calculation given in the thread says that with a 1.5 mm² cable over a 10 m total run, the losses are small and the cable should heat only slightly [#3038091] If the cable run is longer, using 2.5 mm² is fine and will not do any harm, since it reduces resistance and heating [#3037583]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 3037330
    piter3173
    Level 11  
    Posts: 11
    Rate: 7
    Who can help me :I want to connect a 2 kW boiler and I need to run a cable but I don't know what kind of cable should be 1.5 or 2.5 mm, or maybe thicker who can help me?
  • ADVERTISEMENT
  • Helpful post
    #2 3037341
    Jerzy Węglorz
    Level 39  
    Posts: 3447
    Help: 501
    Rate: 451
    2kW is a current of up to 10A, so 1.5mm? copper is enough.
  • ADVERTISEMENT
  • #3 3037353
    piter3173
    Level 11  
    Posts: 11
    Rate: 7
    And for the bulbs 3 times 100 volts is 0.75 kW enough in this case? For this boiler the 1.5 will be enough, as it will be running all the time? Greetings
  • ADVERTISEMENT
  • #4 3037583
    robokop
    VIP Meritorious for electroda.pl
    Posts: 29412
    Help: 1763
    Rate: 6372
    If it's a longer section then you can give 2.5mm² to the boiler, it won't do any harm - current flowing in a conductor of some resistance causes heat to build up in it, i.e. a loss.
  • #5 3038091
    Jerzy Węglorz
    Level 39  
    Posts: 3447
    Help: 501
    Rate: 451
    When designing the installation, it is assumed that the current density in copper conductors in the loaded section may be 6 - 10A / mm? constantly, and in the sections loaded occasionally, but for a short time, it should not exceed 16A / mm?. The load depends on the quality of the insulation and cooling conditions, moreover - e.g. in pipes where several pairs of wires are flying together - there should be a lower load, while in an overhead installation, where the wires are hanging apart from each other and are well cooled, higher densities can be assumed.
    The copper resistance is 0.0175 Ohm * mm? / m, so a cable with a cross-section of 1.5mm? and a length of 10m (2x5m) has a resistance of 0.116 ohms, i.e. the current flow of 8.7A to the 2kW / 230V boiler will generate 8.8W of power in it, which in such a section should not heat the cable by more than 1 degree Celsius above the ambient temperature, the start power is 8.8 / 2000 = 0.44% of the supplied power.
    Do you already know how it is designed?
  • #6 16537499
    boruurob
    Level 12  
    Posts: 229
    Rate: 97
    I'm going to go off topic. I don't quite understand these calculations.

    I have a 2.1 kW/230 V boiler, 2 m long cable. What cross-section should it be? As of today I have it connected with 0.75 mm², but the wire heats up quite a bit.
  • #7 16537516
    sp4msu
    Level 20  
    Posts: 492
    Help: 21
    Rate: 53
    1.5 mm² will suffice .
    This is stated in the post above .
  • #8 16537603
    retrofood
    VIP Meritorious for electroda.pl
    Posts: 31317
    Help: 1140
    Rate: 4798
    boruurob wrote:
    For today I have 0.75mm2 connected but the cable heats up quite well.

    Are you playing with grenades too? You are brave. Just don't cry after you burn up the hut.
  • ADVERTISEMENT
  • Thicker wire is always the safer choice

    #9 21886106
    jackowskipatryk1982
    Level 2  
    Posts: 2
    I don't understand the question, is 1.5 enough????
    I can understand people who have no knowledge at all and are trying to do something on their own. But to ask if 1.5 mm is enough, when you know that 2.5 mm is better, and the difference in buying a section of a few metres is a few zlotys on the whole wire, is asking for trouble. A thicker wire will always be a better wire, a little supply is better than not enough.
    Revised[T.M.]
  • #10 21886119
    Topolski Mirosław
    Moderator of Electrical engineering
    Posts: 7163
    Help: 355
    Rate: 1624
    The socket circuits are 3x2.5 mm² wire, while the lighting circuits are 3x1.5 mm² and that concludes the discussion.
    The topic is closed.

Topic summary

LABEL_AI_GENERATED
The discussion concerns selecting the proper copper cable cross-section for a 2 kW boiler on 230 V. The initial advice states that the load is about 10 A, so 1.5 mm² copper is sufficient. Another response notes that for a longer cable run, 2.5 mm² can be used without harm because lower resistance reduces heating and power loss. A more detailed explanation estimates current density and cable losses, concluding that a 1.5 mm² cable over a short distance should not overheat significantly. Later comments reinforce that 1.5 mm² is enough for the boiler, while 3x2.5 mm² is standard for socket circuits and 3x1.5 mm² for lighting circuits.
AI summary based on the discussion. May contain errors.