230V Plug Overheating with 80L Boiler Despite Cold Cable and Secure Connections

daniel i olek 25100 7
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 3802353
    daniel i olek
    Level 12  
    Hello, I have an 80 liter boiler and from the very beginning when I have it, the plug heats up a lot and the cable is cold. I put it in another socket and the same thing. There is no looseness in the sockets, everything is tightened etc., the original plug is flooded, I don`t want to cut it off and use a new one. -warranty, of course you can call a service technician, but they come once every 2 weeks and waiting for them to come is pointless, and knowing them, they assume it`s not a plug but something else, etc., etc.
  • ADVERTISEMENT
  • Helpful post
    #2 3802433
    kaloryfer
    Level 13  
    There may be poor contact between the pins of the plug and the socket (the diameter of the pins is slightly smaller than the diameter of the holes in the socket and an electric arc is created) and this causes the plug to heat up, assuming that the plug itself is properly connected inside and properly sealed.
  • ADVERTISEMENT
  • Helpful post
    #3 3802567
    staszekf
    Level 33  
    Install a new plug with a pin and the problem is solved. Good luck.
  • ADVERTISEMENT
  • #4 3814910
    waldekg
    Level 28  
    A plastic-covered plug often has a poor cable-pin connection, which leads to the contacts heating up and ultimately damaging the socket, so cut and carefully install the new plug.
  • #5 3815132
    mariusz.s
    Conditionally unlocked
    vol ez lie refer to the last post about the incorrect connections of the cable and pins, and the replacement of the plug itself

    Moderated By _PREDATOR_:

    How do we start and end a new sentence?

  • #6 3816755
    Remeknapr
    Level 33  
    A complete set is a must. New socket and new plug. Everything carefully assembled. Otherwise the problem will persist.
  • ADVERTISEMENT
  • #7 3817232
    ANDYW6
    Level 24  
    But if you buy a new plug, choose the one with thicker pins (16 A). The socket is preferably new.
  • #8 3821992
    LeDy
    Level 43  
    daniel i ola wrote:
    Hello, I have an 80-liter boiler and from the very beginning, the plug gets very hot, the cable is cold. I moved it to another socket and the same thing. There is no looseness in the sockets, everything is tightened etc.
    It is possible that in another socket there is also poor contact between the plug and socket pins. However, first check the cross-section of the cable that goes to this socket. Maybe it is too thin for such a power consumption - 1500-2000W, because this is probably the power of the boiler, and that is why the cable and the socket and plug heat up. The cross-section should be 2.5 mm2, i.e. a diameter of approx. 1.8 mm. Then check the quality of the socket itself, whether it is tarnished or burnt, whether it grips the plug pins well and everything is OK. is replacing the plug itself or, in addition, the socket with a new one.

Topic summary

The discussion revolves around an 80-liter boiler experiencing overheating issues with its 230V plug, despite the cable remaining cold and secure connections. Several users suggest that poor contact between the plug pins and the socket may be causing the overheating, potentially due to the pins being slightly smaller than the socket holes, leading to electric arcing. Recommendations include replacing the plug with a new one, preferably with thicker pins (16 A), and ensuring that both the plug and socket are new and properly assembled. Additionally, users advise checking the cable's cross-section to ensure it can handle the boiler's power consumption (1500-2000W), with a minimum recommended cross-section of 2.5 mm². The quality of the socket should also be inspected for tarnishing or burning that could affect contact.
Summary generated by the language model.