logo elektroda
logo elektroda
X
logo elektroda

Why doesn’t a 30mA RCD trip with an N–PE short on an unloaded socket?

mariusz.bartoszek 59938 18
Best answers LABEL_AI_GENERATED

Will a 30 mA RCD trip if I short neutral to PE at an unloaded socket?

Not necessarily: a 30 mA RCD trips only when the N-PE short creates enough residual current, so a truly unloaded, isolated socket may not trip it [#7563496][#7568138] If there is other load on the same installation, the neutral can sit at a different potential because of voltage drop, and the N-PE short can create an equalizing current that may exceed 30 mA and trip the RCD even though that socket itself is unloaded [#7563428][#7564325][#7564496] The circuit does not have to be loaded right at the socket; it is enough that current is flowing elsewhere on the same neutral path [#7563428][#7564496] In a symmetrically loaded 3-phase network it may not trip [#7564496] The exact result depends on where the N/PE split is and on the network layout [#7564496]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 7563027
    mariusz.bartoszek
    Level 10  
    Posts: 5
    Rate: 1
    I searched a lot of information on the Internet, including forum, I also asked a lot of people but I did not get a clear answer. If we have a single socket on one circuit, protected by a 30mA residual current circuit breaker and I short the N and PE wire together, will the switch switch off the contacts? There is no device connected to the outlet and we make a short circuit through a wire or a light bulb. We did such an experiment at work and the switch did not turn off, but apparently in many situations such a short circuit turned off the differential. After the N and PE conductors have the ground potential, where would the current flow in them after a short-circuit. And if there were two sockets (protected by a differential), one loaded and the other not, and in unloaded we would short PE with N, will the switch switch off? Perhaps the sensitivity of the switch is important here and one will turn off and the other will not?
  • ADVERTISEMENT
  • #2 7563136
    basstec
    Level 34  
    Posts: 2597
    Help: 144
    Rate: 178
    Not necessarily. Differential works on the principle of the difference between the incoming and the returning current. If there is a differential device connected to only one outlet and this outlet is not loaded, it will not disconnect because there is no potential difference. If the receiver is connected and turned on, making a short circuit between pe and somehow part of the current flows to full and the difference between what influences through L and returns through N because some of it escapes in PE.
  • ADVERTISEMENT
  • #3 7563271
    Anonymous
    Anonymous  
  • #4 7563364
    Łukasz-O
    Admin of electroenergetics
    Posts: 21789
    Help: 654
    Rate: 4292
    maryjandx wrote:


    I know how the differential works and I also know that if the yellow-green wire short-circuits the blue wire, the differential will turn off if it is functional.


    You probably don't quite know how the differential works, or you don't understand what your colleague basstec wrote.
    I will repeat again, the RCD will not work after N and PE short-circuited, if the given circuit is not loaded.
  • ADVERTISEMENT
  • #5 7563428
    pavulon
    Level 21  
    Posts: 526
    Help: 34
    Rate: 73
    Łukasz-O wrote:
    maryjandx wrote:


    I know how the differential works and I also know that if the yellow-green wire short-circuits the blue wire, the differential will turn off if it is functional.


    You probably don't quite know how the differential works, or you don't understand what your colleague basstec wrote.
    I will repeat again, the RCD will not work after N and PE short-circuited, if the given circuit is not loaded.


    The circuit does not have to be loaded after the RCD, it is enough that there is a different load in a given "area", relatively close to the RCD, and then a short circuit N to PE will trip. After all, the N conductor is a work conductor and if there is a current, there is a voltage drop, if the voltage is sufficient to flow the RCD tripping current, it will release, if not, it will not.
  • #6 7563496
    krzysiek7
    Moderator of Electricians group
    Posts: 4880
    Help: 678
    Rate: 1953
    I join the moderator. If the circuit is not loaded, no current flows, and if no current is flowing, there is no differential current, so the differential has no reason to switch off. My friend maryjandx , I suggest reading a bit.
  • #7 7563548
    niutat
    Level 36  
    Posts: 3247
    Help: 288
    Rate: 758
    And I will join my colleague Pavulon, the loaded N may have a voltage in relation to PE that is so high that their short circuit after the differential will cause it to work through the equalizing current in the N path of the differential. It has happened to me several times.
    Of course, such a case is possible when the differential is powered by other circuits than the one on which we are experimenting.
  • #8 7563744
    krzysiek7
    Moderator of Electricians group
    Posts: 4880
    Help: 678
    Rate: 1953
    My friend New Year's Eve maybe make up your mind. You write that you join your friend pavulon and you actually confirm the words moderator . :D
  • #9 7564325
    greg16
    Level 15  
    Posts: 137
    Help: 9
    Rate: 37
    Now I will add something from myself. The differential does not need to be biased to work. In the case of an N-PE short-circuit, a current flow through the N line may also occur behind an unloaded differential. Why ? because N may be at a potential other than PE because there are voltage drops across it. Of course, it also depends on where the point of division into PE and N is
  • #10 7564411
    pavulon
    Level 21  
    Posts: 526
    Help: 34
    Rate: 73
    Well done, I can see that greg16 He also knows "what's going on", I go to the workshop and quickly construct a small installation and capture the experience of triggering the rcd without load at shorted PE to N on a video and I will provide a link tomorrow morning.
  • #11 7564496
    tomek_tkkj
    Level 12  
    Posts: 15
    Help: 1
    Rate: 4
    greg16 wrote:
    Now I will add something from myself. The differential does not need to be biased to work. In the case of an N-PE short-circuit, a current flow through the N line may also occur behind an unloaded differential. Why ? because N may be at a potential other than PE because there are voltage drops across it. Of course, it also depends on where the point of division into PE and N is

    Colleague greg 16 is right as long as we are talking about a TNC-S network. There is no dividing point in TNS networks (and these are mainly built now) ...
    The socket in question is powered from the 1st phase, and this circuit is supplied from the 3-phase circuit, i.e. both have a common N conductor. is equal to 0 V, but has a certain potential (i.e. the N conductor is connected to a certain potential). If we close N and PE (with a potential equal to 0), we close the circuit and the flow of current (and only 30mA is enough to operate). If we had a symmetrically loaded (and this is almost never the case) 3-phase network, the differential would not work.
  • #12 7564516
    blaszczok
    Level 13  
    Posts: 115
    Rate: 15
    Hello. I just wanted to share some practical comments. The differential was without any load, the N wire was 5cm long and the PEN maybe 10cm and it was also triggered. So that you can see from this example the typical operation of the potential difference. Best regards, Michał.
  • #13 7564536
    greg16
    Level 15  
    Posts: 137
    Help: 9
    Rate: 37
    Of course I know :) I'm not saying that this will always happen, but it can. Many factors will influence it. One of them is the fact that the loaded N conductor may have a higher potential than the PE conductor because there is a voltage drop on it, but it is and it is enough for 30mA to flow. If someone does not believe it does not have to. And who has any knowledge of electrical engineering should know.
  • #14 7565281
    Łukasz-O
    Admin of electroenergetics
    Posts: 21789
    Help: 654
    Rate: 4292
    Naturally, it would really depend on the type of network and information where the distribution is, RCD and socket, etc. - my mistake. I considered the split circuit directly before the RCD.
  • ADVERTISEMENT
  • #15 7565969
    Anonymous
    Anonymous  
  • #16 7566033
    aklim
    Level 14  
    Posts: 106
    Help: 6
    Rate: 12
    Just make an experience. Short PN and N with a milliammeter, the current through the milliammeter is the difference of the current through the differential.
  • #17 7567386
    niutat
    Level 36  
    Posts: 3247
    Help: 288
    Rate: 758
    krzysiek7 wrote:
    My friend New Year's Eve maybe make up your mind. You write that you join your friend pavulon and you actually confirm the words moderator . :D

    I meant the unloaded circuit in which we are doing the experiment, not the entire installation.
    I had to deal with such cases and the differential worked even though the circuit was turned off by a fuse.
  • #18 7567395
    Anonymous
    Anonymous  
  • #19 7568138
    Wirnick
    Level 30  
    Posts: 1774
    Help: 72
    Rate: 240
    maryjandx wrote:
    For the differential to work properly, you need a specific grounding, otherwise it will bang.

    For the correct operation of the RCD, it must be turned on in accordance with the diagram on its housing or in the installation manual. The task is to measure the residual current in active conductors and switch off the current in active conductors when the nominal value of the residual current is exceeded.
    Switching off (tripping) is caused by errors or damage to the circuits.
    Installation errors were presented.
    In addition to the prophylactic differential current paths (PE conductor), there may be random paths (flame ion flow, foundation, ...).

Topic summary

LABEL_AI_GENERATED
The discussion revolves around the behavior of a 30mA residual current device (RCD) when a short circuit occurs between the neutral (N) and protective earth (PE) wires on an unloaded socket. Participants clarify that if the circuit is not loaded, the RCD may not trip because there is no potential difference to detect. However, if there is a load on the circuit or nearby circuits, the RCD could potentially trip due to voltage drops in the N conductor. The effectiveness of the RCD is influenced by the network type (TNC-S vs. TNS) and the presence of other loads in the area. Several users share practical experiences and emphasize the importance of understanding the electrical network layout and the conditions under which the RCD operates.
AI summary based on the discussion. May contain errors.