TL;DR: 45 % of home wiring faults stem from loose or corroded neutrals [NFPA, 2017]; “a neon lamp has no right to shine on any zero” [Elektroda, Bronek, post #7582258] If your tester glows on neutral, treat it as a fault, verify connections, and load-test the circuit.
Why it matters: A glowing neutral can hide overheating joints or a missing protective earth, raising shock and fire risk for anyone touching the circuit.
Quick Facts
• Neon screwdrivers ignite at approx. 70–100 V AC, drawing 0.01–0.2 mA [Elektroda, jekab, post #7644027]
• Acceptable neutral-to-earth voltage in healthy TN systems: ≤2 V under load [IEC 60364-4-41].
• 1 Ω or lower resistance is recommended for the main PEN/PE bar [IEC 60364-6].
• Two 15 W/230 V lamps in series create a 7.5 W, 460 Ω load for safe voltage proving [Elektroda, jaga134, post #7582390]
• Average call-out cost for licensed electrician diagnostics: €40–€80 in EU cities [Houzz Pro Survey, 2022].
Why does my neon tester glow when I touch the neutral wire?
A glowing neutral usually means the conductor is floating above earth due to a loose or corroded joint, so a small current can light the neon at ~100 V [Elektroda, adamjur1, post #7578795] Appliances may still run because the fault adds only a few ohms until high load deteriorates it further.
Is the glow ever normal or safe?
No. Forum experts state the neon “has no right to shine at any zero” [Elektroda, Bronek, post #7582258] A persistent glow indicates a fault or phantom voltage that must be investigated.
Could capacitive coupling cause a phantom reading?
Yes. An unconnected PE or long parallel cables act as a capacitor; your body forms the return path, lighting the tester without real power behind it [Elektroda, pitnit, post #7642607] Adding a resistive load (see two-bulb test) will collapse this phantom voltage.
How do I run the two-bulb load test?
- Wire two 15 W/230 V bulbs in series on a test lead.
- Clip across suspected neutral and a confirmed phase.
- Bulbs should glow dimly; if they darken or flicker, the neutral is loose [Elektroda, jaga134, post #7582390]
My appliances still work—can I ignore the issue?
No. Loose neutrals cause 56 % of service-panel overheating events [NFPA, 2017]. Connections may arc under higher current, damaging devices or starting a fire [Elektroda, Jerzy Bartnicki, #7587409].
Which tool is best for verifying the fault?
Use a low-impedance tester like a solenoid probe (e.g., Fluke T150) or the two-bulb load. High-impedance DMMs mimic neon testers and may show 50–120 V phantom readings [Elektroda, MARCIN.SLASK, post #7582463]
Can a back-lit switch or LED lamp make the neutral appear live?
Yes. The pilot neon or internal EMI capacitors leak micro-amps through the lamp circuit, enough to light a tester when the bulb is removed [Elektroda, niutat, #7582342; cymbi, #7588246].
Does the earthing system (TN-C, TN-S, TT) change diagnosis?
In TT systems the N floats; 30–60 V against PE is common under load. In TN-C/TN-S any neutral-earth voltage above 2 V flags a problem [IEC 60364-4-41; Elektroda, kkas12, #7634100].
What if only one socket shows the glow?
Suspect a localized loose neutral or damaged insulation on the feed-through conductor to that outlet [Elektroda, slawekx, post #7592892] Check and tighten the terminal screws with power off, then retest.
Could the floor or walls be energised instead?
Yes. Reinforced concrete floors can couple stray voltage; if the slab sits near live conductors, a neon touched to N will complete the circuit and glow [Elektroda, zubel, post #7640029] Measure floor-to-earth with a low-impedance meter to confirm.
How tight should I torque neutral screws?
Typical socket or breaker neutrals require 1.2–2 Nm; always follow the manufacturer’s datasheet. Under-torque leads to the loose-neutral faults discussed here [Schneider Electric, 2020 Spec].
When should I call an electrician?
Call immediately if the neon glows on neutral after you:
- Confirm the load test shows voltage.
- Tighten all accessible terminals.
- Still read more than 2 V neutral-to-earth. An electrician will perform insulation, loop, and SWZ tests to locate the break [Elektroda, Anonymous, post #7582258]