The test tube is lit at "zero" - what does that mean?

wahoo 84860 36
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 7578713
    wahoo
    Level 20  
    Hello.
    In the installation in the house on the first floor, I have a problem with the zero cable. In a few light sockets and switches, the test tube will glow slightly on the neutral wire. On the lead with the test tube, the light is normally lit. What does it mean? What could be the reason for this?
    Greetings.
  • ADVERTISEMENT
  • #2 7578795
    adamjur1
    Level 41  
    Probably a "weak" zero, i.e. no contact on some connection - continuation of zero from socket to socket. But on the circuit breakers it would mean that the problem is at the source of this installation (main box, switchgear)
    Greetings J.
  • ADVERTISEMENT
  • #3 7579016
    greg16
    Level 15  
    And are the devices connected to these sockets working properly? are the lamps shining ??
  • #5 7579186
    Jerzy Bartnicki
    Level 23  
    Hello.
    Check as Admajur advised you, turn off the power and tighten all possible connections, I believe that the problem will disappear.
    George.
  • #6 7579941
    wahoo
    Level 20  
    All receivers are working properly. Both the light and the receivers connected to the sockets are working properly.
    What is a normal pointer? Is it a multimeter?
  • #7 7582258
    Anonymous
    Anonymous  
  • #8 7582342
    niutat
    Level 36  
    Hello, what do you mean when you write a zero wire in switches? Because if the wires for incandescent lamps, the glow of a neon lamp on them in the absence of a light bulb is a normal phenomenon.
    As for the sockets, I also do not know what cable you mean because, as Bronek22 writes, a voltage of several dozen V is needed to ignite the neon lamp and it is difficult for me to imagine that with such a voltage drop, the receivers will work properly, unless it is a protective conductor not connected somewhere.
  • #9 7582390
    jaga134
    Level 26  
    Indicator neon / test tube / is not an indicator. When I was still working as an electrician, I had to pass health and safety exams every few years. For finding that a neon lamp is a work tool, the examiner fired the culprit with a bang and ... see you with mc ... According to it, and it is true, the reliable indicator is two 15W / 230V bulbs connected in series. Why in series? Well, because the inter-wire voltage was often checked with the same tester. I had friends who for this reason / neon lamp lighting / I worked in a gas plant tried to stop the production cycle, because ... it is lit zero, so there is a breakdown in the installation.Luckily, I managed to intervene in time. us then ... So if you use a neon indicator, always check the voltage after it with 2 low power bulbs at 230V connected in series. Do not use numeric meters. these, because they will show the same as the neon lamp.
  • ADVERTISEMENT
  • #10 7582463
    MARCIN.SLASK
    Home appliances specialist
    Often, even DMMs show voltage at the sockets, even though the switch or fuse is off. Analog meters with low internal resistance will not show any voltage in this case.
    The neon indicator is just for indicative assessment.
  • #11 7582480
    Darom
    Electrician specialist
    Hello

    The neon lamp is a specific gadget (not to write - a tool). It consists of a gas discharge lamp and a current limiting resistor. Like every receiver of electric energy (it converts it into light energy), it has two "clamps". One is the tip of the screwdriver that serves as the probe, the other is as reference .... Exactly where is the other end connected?

    It may be as Jurek says (adamjur1), or it may be that everything is fine with "zero", but not very much with reference (eg due to some other failure). The presence of an electrician is highly recommended.

    kisses
    - GIFT-
  • #12 7584532
    Anonymous
    Anonymous  
  • #13 7585081
    sebaele22
    Level 30  
    Hello, join the topic.

    I also noticed that the test tube glows slightly after touching the neutral wire, it is not so in other sockets.

    Is it normal?
  • #14 7586837
    Anonymous
    Anonymous  
  • #15 7587047
    sebaele22
    Level 30  
    The reason may be neutral or phase wire?
  • ADVERTISEMENT
  • #16 7587409
    Jerzy Bartnicki
    Level 23  
    Hello
    The problem is the zero circuit, just tighten the individual connections and the problem will pass.
    George
  • #17 7587656
    lucky1boy
    Level 2  
    I support measurements with a light bulb and special devices, a neon lamp is only useful when we know what we are doing in the installation. it is not suitable for diagnosis.
    I have encountered a glowing working and protective zero many times as well, it is enough if they are bridged :)

    most often it is the fault of devices included in the installations, e.g. washing machines and other larger ones - even though they function normally

    the problem often arises in older 2-wire installations - we can even have a protective zero at home, as needed, but it must be connected to a real earth, otherwise it will shine
    greetings
  • #18 7587983
    Wirnick
    Level 30  
    sebaele22 wrote:
    The reason may be neutral or phase wire?

    The reason is a person who acts as a lining for a charged capacitor in a well-insulated room (plastic floor, dielectric shoes, insulating paints, relative humidity close to zero).
    The cladding has 115V in relation to the neutral and phase conductor.
  • #19 7588074
    Anonymous
    Anonymous  
  • #20 7588172
    mczapski
    Level 40  
    Interesting discussion so I'll throw in my pebble. Have you not encountered the phenomenon when we grab the probe of an oscilloscope and on the screen many waveforms, including high-voltage ones (e.g. 100V)? And yet we do not power this probe from any network. Why not a neon lamp? A human being wants or is not a great antenna and it is certain that the amount of charge he induces depends on the coincidence.
  • #21 7588246
    cymbi
    Level 27  
    Unscrew all bulbs and then check. Have you ever seen light switches with neon backlight? There, the socket "reaches 0" through the inserted light bulb :)
  • #22 7588765
    Wirnick
    Level 30  
    Bronek22 wrote:

    That's not true. It is caused by a tension that cannot exist.
    What is the law at zero to be 115V? You've got it mixed up.


    What you describe is completely different. It is the mechanism of the neon lamp shining when we stand on a stool - and we are isolated from the ground.

    It is 115V not at zero, but at human.
    What is the difference between a stool and dielectric slippers?
  • #23 7592892
    slawekx
    Level 29  
    wahoo wrote:
    Hello.
    In the installation in the house on the first floor, I have a problem with the zero cable. In a few light sockets and switches, the test tube will glow slightly on the neutral wire. On the lead with the test tube, the light is normal. What does it mean? What could be the reason for this?
    Greetings.


    check with another probe
    your test tube is still lit is not correct.
    tightening all connections is correct for service reasons but may not solve the problem.
  • #24 7593129
    Anonymous
    Anonymous  
  • #25 7608462
    volcan
    Level 17  
    Hello

    I believe that Bronek22 is right, and that this situation has its source in some failure. I myself encountered a similar one once
    the case when voltage was present on the "pin" connected to the "neutral" wire, although not 115V but about 90V (neon indicator
    also shone). Interestingly, one of the electricians (it was in a company)
    he said that this may sometimes be the case, unfortunately I do not know how he justified it.
    As far as I remember, the problem resolved after tightening the screws in the switchboard.

    Greetings.
  • #26 7634100
    kkas12
    Level 43  
    Hello!

    In order to receive a fairly precise answer, a precise question should be asked.
    We do not know if the installation has a PEN conductor or PE and N conductors?

    On the other hand, the first advice given should recommend checking the SWZ condition in bad nests. Such measurement will help direct the search.

    You should also take into account the possibility of damaging the insulation of cables in the installation laid on the lower floor. In this case, tension may remain on the ground.
  • #27 7640029
    zubel
    Conditionally unlocked
    Currently, in multi-family buildings, some of the installations are run in the floor. The floor is reinforced with a steel wire mesh and under certain conditions the floor with respect to N is simply "live" and the neon lamp will show it. It will also light up on the pin in the socket. Sometimes the neon light applied to the wall also lights up and this does not indicate a faulty installation.
  • #28 7640656
    slawekx
    Level 29  
    zubel wrote:
    Currently, in multi-family buildings, some of the installations are run in the floor. The floor is reinforced with a steel wire mesh and under certain conditions the floor with respect to N is simply "live" and the neon lamp will show it. It will also light up on the pin in the socket. Sometimes the neon light applied to the wall also lights up and this does not indicate a faulty installation.


    even if you are right, it doesn't add anything to the explanation of the glowing test tube, and the topic has become interesting and intriguing. I think there is some installation error.
    I wonder if there is also such a phenomenon on the ground floor of the house some socket outlets are present.
  • #29 7641179
    zubel
    Conditionally unlocked
    After all, I wrote clearly. If the floor or wall are live, the neon lamp will shine on N or PE. No matter which end of the neon you touch to the "phase"
  • #30 7642607
    pitnit
    Level 15  
    The neon lamp will glow on the PE conductor if the conductor has no continuity. (Not connected) There is something like capacitive reactance and therefore a potential difference appears on the PE conductor. You can do a little experiment even with a 3-wire cable, when we connect L and N and we do not connect PE, touching the end of the PE wire, the test tube will glow.

Topic summary

The discussion revolves around the issue of a test tube (neon lamp) glowing on the neutral wire in a household electrical installation. Users suggest that this phenomenon may indicate a weak neutral connection or a fault in the installation, potentially due to loose connections or improper grounding. It is emphasized that a glowing neon lamp is not normal and could signify dangerous voltage levels. Recommendations include checking all connections, using proper measuring tools like multimeters, and consulting a qualified electrician for diagnosis. The conversation also touches on the behavior of neon lamps in relation to capacitive coupling and the importance of understanding electrical theory for accurate measurements.