Setting Orifice in Purmo Steel Radiators (1997): Valve Adjustment, Number Scale & Boiler Position

cyryl70 116362 11
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 8599499
    cyryl70
    Level 11  
    Hello.
    I have problems with the radiators. It's about setting the orifices on the valves.
    I have Purmo steel radiators from 1997.
    I don't know how this orifice is positioned?
    What to relate to?
    Is there any scale according to which the orifice is adjusted?
    What do the numbers 1,2,3,4,5,6,7 mean and what is N?
    What is the best way to position the radiator farthest from the boiler and the closest?
    Please help.
  • ADVERTISEMENT
  • #2 8600092
    Anonymous
    Anonymous  
  • #3 8600630
    cyryl70
    Level 11  
    ok but what to refer to when adjusting the orifice? is there any graduation? throttling, i.e. on the smallest settings, e.g. 1.2 yes?
  • ADVERTISEMENT
  • #4 8600644
    Anonymous
    Anonymous  
  • #5 8601191
    cyryl70
    Level 11  
    at what time or so? dot? ie a recess or a hole right? is it in the same place on every valve? I have 7 radiators I am most interested in the temperature, including 7 - smoke because I mainly live there 1 - boiler room 2 kitchen 3 - bathroom 4 - hall 5 - room 6 - room and 7 - room where it is to be warmest You can set it like this: 1 - 1, 2 - 2, 3 - 3, 4 - 4, 5 - 5, 6 - 6, 7 - 7? Assuming that the heaters closest to the furnace should be choked and not farthest away. Room No. 7 is the farthest from the furnace and it should be the warmest there.
  • ADVERTISEMENT
  • #7 8605252
    cyryl70
    Level 11  
    is this orifice in the same place in each head? what to do to make the last radiator heat the most? I try to set up but nothing. This radiator is the farthest from the stove
  • #8 8605388
    zybie
    Level 30  
    maybe it is not the fault of bad closure, but a difficult flow, for example a dirty filter on the central heating return
  • #9 8630539
    Zbigniew Rusek
    Level 38  
    cyryl70 wrote:
    is this orifice in the same place in each head? what to do to make the last radiator heat the most? I try to set up but nothing. This radiator is the farthest from the stove

    You need to set it for a higher flow (especially when "farthest from the boiler" means the highest floor of the building). On the last floor, you can successfully set the highest digit, and maybe even "N", but it's probably not necessary.
    Tip. The setting "1" is not recommended even closest to the boiler and on the lowest floor, because in such "blockage" the valve may "silt up" and stop heating altogether. It is worth remembering that when there were no thermostatic valves and radiators were traditionally covered, the most common causes of non-heating (or very poor heating) were air or fouling of the orifice (especially when the opening was very small and the radiator was closed for a long time).
  • #10 9229014
    greg_1983
    Level 10  
    I have a question - I have a gas stove installed in my apartment (4 rooms with radiators. From the nearest stove: bathroom, small room, kitchen, large room). What is the best way to set the orifice parameters in the radiators? (apartment not too big ~ 48m). Does it make sense to change something (I have 'N' set to all [except for the bathroom one - I don't know there, because I haven't checked]).
    because I wonder ... isn't it better to just set 'N' everywhere and control the temperature on the stove and the 'main' knob on the radiators? (all radiators are properly heated with the 'N' setting)

    One more violation of 3.1.13 and I will draw the consequences. Please correct previous posts!
    mod.serwisant73
  • ADVERTISEMENT
  • #11 9231917
    zybie
    Level 30  
    Colleague GREG you are theoretically right, but with too large differences in the distance, the pump-heater will not work properly. After all, like everything in this world, water is also easy and shortens its path.
  • #12 11323942
    pdarek2
    Level 13  
    Or maybe your heads will not tear off, as "Guest" said, but you will make sure that in a multi-family apartment they will be freezing and you will feel comfortable. I work in such a company and I still have to look for people like you if in a multi-family, because you can shoot your own at will as in previous posts
    1 closer to the furnace and not finite at the end.

    3.1.13. It is forbidden to publish entries that violate the spelling rules of the Polish language, careless and incomprehensible.
    mod.serwisant73

Topic summary

The discussion revolves around adjusting the orifices on Purmo steel radiators from 1997, specifically focusing on valve settings and their relation to radiator performance. Users inquire about the meaning of the numerical scale (1-7 and N) on the valves, which indicates flow regulation, with "1" representing the lowest flow and "N" indicating no throttling. It is suggested that the orifice settings should be adjusted based on the radiator's distance from the boiler, with closer radiators requiring lower flow settings. A dot on the valve body serves as a reference point for adjustments. Users also discuss potential issues affecting radiator heating, such as dirty filters and the importance of ensuring proper flow to the farthest radiator. Recommendations include setting higher flow rates for radiators located on upper floors and avoiding the lowest setting to prevent valve blockage.