Maximum Power for 16 mm2 Cable Over 8 Meters with 28kW 1-Phase Heaters and Appliances

Grzegorz_n 82572 8
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 8644640
    Grzegorz_n
    Level 15  
    I warmly welcome :)

    Please help oriented :)

    What is the maximum power to load a 16 mm2 cable with a length of 8 meters, assuming that 28 kW are 1F heaters, the rest are "common" household appliances (washing machine, fridge, kettle, several computers, sockets with devices with low power consumption)

    I know, the data is not very precise, but I don't know what to write, so if the question is asked, I'll fill it in.

    Thank you in advance for your help :)


    greetings :)
    Gregory :)
  • ADVERTISEMENT
  • #2 8644648
    slawekx
    Level 29  
    28 kW is the radiator power for sure?
  • ADVERTISEMENT
  • #3 8644732
    Miwhoo
    Electric installations specialist
    Single or three-phase power supply?
  • #4 8645032
    karolq
    Level 22  
    Grzegorz_n wrote:
    I warmly welcome :)
    28 kW
    Gregory :)


    I think 2.8 kW, because 28 kW at home is not feasible even on 3 phases :) Pre-meter protection would have to be 50A!

    In a 1-phase system, you will not load 16mm ^ 2 to the maximum, because the protection will not give you. I do not know about other power plants, but we have a 1-phase fuse max. 25A.

    I assume this is copper.
    As for the maximum load:
    Maximum Power for 16 mm2 Cable Over 8 Meters with 28kW 1-Phase Heaters and Appliances
  • #5 8645071
    Grzegorz_n
    Level 15  
    slawekx wrote:
    28 kW is the radiator power for sure?

    This is the total sum of heaters that will work in the room, each of 2000W / 230V

    Miwhoo wrote:
    Single or three-phase power supply?

    3F power supply, but each radiator has a separate circuit and the phases will be evenly loaded on each of the circuits.


    YDY 5x16mm2 cable
    This is an 8 m long section of cable that will connect the meter with the indoor switchgear. WLZ has sufficient stock.
  • ADVERTISEMENT
  • #6 8645082
    karolq
    Level 22  
    And what security do you have in the building?
  • ADVERTISEMENT
  • #7 8645092
    Grzegorz_n
    Level 15  
    karolq wrote:
    And what security do you have in the building?

    I do not have it yet, in the sense that I will apply for an additional power allocation and depending on how much I will apply, I will have such security.

    That is why I would like to know how much power I can put on the cable.

    By the way...
    I need tables where I can look at the cable cross-section and see what power, what current, etc. or, for example, what protections are used for different power values or the load in A, how many kW. In general, I am interested in a collection of such conversion tables for various electrical applications. Where to look for it?
  • #8 8645191
    slawekx
    Level 29  
    Specify - here I refer to the author of the topic - the type of stoves you want to power. That is, brand and power.
    In addition, you ask for details that you already know well because you have already done a similar installation.
    https://www.elektroda.pl/rtvforum/topic1255422.html
    Is it the same?
  • #9 8645213
    retrofood
    VIP Meritorious for electroda.pl
    The author of the topic disregards any comments from experienced electricians. He only asks because he wants to do as he thinks and only looks for acceptance of his ideas. Violates point 11 of the forum regulations, not presenting the whole situation for analysis, but sipping his problems, which makes the posts artificially "punched". I close the topic so that someone looking for similar solutions would not be guided by his theories ..

Topic summary

The discussion revolves around determining the maximum power load for a 16 mm² cable over a length of 8 meters, particularly in the context of powering 28 kW heaters and various household appliances. Participants question the feasibility of 28 kW in a residential setting, suggesting that such a load would require significant protection (e.g., 50A for three-phase systems). The conversation highlights the importance of knowing the type of power supply (single or three-phase) and the specific appliances to be powered. The author seeks guidance on power allocation and requests tables for cable specifications and protection ratings. Concerns are raised about the author's approach to the topic, with some suggesting a lack of thoroughness in presenting the situation for analysis.