Immergas EOLO Star 23 kW: Encountering Error 03 After Resolving Error 11, Fan Not Starting

sp3qyg 64193 26
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 8811298
    sp3qyg
    Level 12  
    Hello !
    The fault occurred during the evening shower.
    Error 11 came first.
    I'll turn him on
    And he is now error 03 (orange)
    And I'm green because there is no such error in the manual (it's 01.02 then 04).
    The chimney is clean, the fan is not jammed, the pressure switch tubes are clean (if you puff, it clicks normally).
    Who has any idea what's next?

    When the cw tap is unscrewed, the fan does not start (no voltage on the contacts), but I have already lost my mind whether it starts before or after the ignition



    Thanks in advance for your help
  • ADVERTISEMENT
  • #2 8882661
    Gobimen
    Level 12  
    Probably the motherboard

    It can be fixed.
  • #3 8883076
    zybie
    Level 30  
    Start the pressure switch on the fan probably stuck
  • ADVERTISEMENT
  • #4 8886326
    mariachi27
    Level 1  
    hello, maybe this will help someone...

    same problem as colleague (error 11 on display)

    scheming, undressing, peeking and what?

    it turns out that the stove gets too little air for gas combustion (closed chamber).

    it happened because I installed an anemostat behind the air intake and twisted it too much.

    after increasing the air supply, the problem disappeared.

    Regards
    mariachi27
  • #5 8886454
    MarudaP
    Level 21  
    There is something about it. My air intake was almost completely icy. I had to clean up.
  • #6 12458718
    piter771
    Level 2  
    for me it turned out that error 11 was due to the fact that water (rain) got into the fan from the chimney
  • #7 12493237
    bastianik
    Level 2  
    Water got into the fan and it wouldn't spin? was there an error 11 despite the fact that the fan was spinning?
  • #8 12493400
    piter771
    Level 2  
    after disassembly, it turned out that it did not even fire because even the burners were flooded, after drying I fired it and everything still works :)
  • #9 12748915
    Bubisss
    Level 1  
    WELCOME, I'm joining this thread because I have error 10 (blinking yellow) I tried to fill the installation with this small round black plug but it doesn't work, (the pressure does not rise) My stove is immergas eolo star 23Kw
  • #10 12778177
    dominik_ryka
    Level 14  
    Bubisss wrote:
    WELCOME, I'm joining this thread because I have error 10 (blinking yellow) I tried to fill the installation with this small round black plug but it doesn't work, (the pressure does not rise) My stove is immergas eolo star 23Kw

    Either the pressure sensor has failed or (at worst) the electronic board.
  • ADVERTISEMENT
  • #11 12958410
    ja26
    Level 11  
    Hello everyone, I have a question for users of the eolo star boiler with a closed combustion chamber, what are your opinions about the boiler, what is your winter combustion?
  • #12 13205851
    PagerOwski
    Level 12  
    Dude, I have a stove like that. In my case, it heats about 60 m2 - the temperature is constantly set at 22.5 degrees. I have a comprehensive contract (i.e. heating the apartment, hot water and a gas hob). My worst 2 months cost PLN 970, although they were very frosty. My annual cost is less than $4,000. I would like to point out, however, that I do not have a hall in the apartment yet and when leaving the apartment a lot of cold air attacks the apartment.
  • #13 13207268
    ja26
    Level 11  
    Hello friend, I have 75 meters to heat, I also have a gas stove and this stove. My bills for the whole year are PLN 2600. I heat on the day 21-22 at night 19 degrees. At the beginning I was in the tariff in 2.1 but that my consumption is above 1200 meters per year until I was transferred to the tariff in 3.6 where transmission fees etc. cost about PLN 120 for 2 months, and in the tariff in 2.1 there was a fee for 2 months about PLN 50. Apart from the fact that in the tariff in 3.6 gas is slightly cheaper than in the tariff in 2.1. for now. I also have a tybox 810 wireless sensor and so far I don't think I pay much.
  • #14 13242356
    PagerOwski
    Level 12  
    The annual settlement came and the forecast for the next year - the projected cost is something around PLN 3,200. I need to build a hall quickly.

    Ps buddy above and how do you set the water temperature? I have 46 degrees (and as I wrote earlier, the temperature in the house is 22.5 all the time) - my wife often opens the windows to ventilate the whole apartment (so this should also be taken into account - with the temperatures that are currently prevailing, after less than 30 minutes the temperature in the house drops to about 20 degrees, so the stove starts up on a regular basis later)
  • #15 13245990
    ja26
    Level 11  
    I have a water temperature of 50 degrees on the stove. If you have PLN 3200 per year, what is your gas consumption per year. Because something doesn't suit me here. You pay a fixed amount every 2 months throughout the year, right? Because I also had bills forecasted, but my consumption was quite high, i.e. over 1200m per year and they transferred me to the tariff in 3.6 and wages every 2 months as much as I use up as much wages.
  • #16 13248132
    PagerOwski
    Level 12  
    Sorry buddy, I was wrong now we received the forecast for PLN 2,600 because we had an overpayment, so the first invoice to pay is March for the amount of PLN 520 (for 2 months).
  • #17 18483717
    SzukaczForumowy
    Level 2  
    1 question about the cost spoiled the thread a bit, and the subject is an error.
    Does anyone else have this five?
    I get error 03 from time to time. Twice in a row when c. water was flowing on the shower valve half open. Could it be the heat exchanger overheating?
  • ADVERTISEMENT
  • #18 19723156
    Schnaider
    Level 10  
    Hello gentlemen,
    On Sunday morning, error 03 was displayed and the stove stopped working.
    According to the manual, fan error.
    I disassembled the fan myself, cleaned it and oiled it with WD40, because it was heard that the bearing was slowly seizing up.
    After all, the stove after connecting and turning on the fan after 10-15s showed error 03 and the fan ended. There was no ignition. The fan worked fast at first, then a little slower.
    Chimney checked, air supply all unobstructed, etc.

    SOLUTION:
    The next day, the installer Immergas was called.
    The first step is to check the fan voltage and diagnose: the device is not expelling.
    Replaced with a new one (he had it with him).
    Immediately after replacement and connecting to electricity, the stove starts with a hoof.
    Everything as it should be.
    It's just for those looking for help as I have solved the problem 03.
    I will only add that the fan was already 8 years old.
  • #19 19964916
    dzimus
    Level 12  
    Schnaider wrote:
    Hello gentlemen,
    On Sunday morning, error 03 was displayed and the stove stopped working.
    According to the manual, fan error.
    I disassembled the fan myself, cleaned it and oiled it with WD40, because it was heard that the bearing was slowly seizing up.
    After all, the stove after connecting and turning on the fan after 10-15s showed error 03 and the fan ended. There was no ignition. The fan worked fast at first, then a little slower.
    Chimney checked, air supply all unobstructed, etc.

    SOLUTION:
    The next day, the installer Immergas was called.
    The first step is to check the fan voltage and diagnose: the device is not expelling.
    Replaced with a new one (he had it with him).
    Immediately after replacement and connecting to electricity, the stove starts with a hoof.
    Everything as it should be.
    It's just for those looking for help as I have solved the problem 03.
    I will only add that the fan was already 8 years old.


    ‐-----------------------------------
    I confirm. Replacing the bushings with bearings solved the problem for me. The windmill must be pumping otherwise 11 and 03 will pop up on a regular basis. The electronics in these boilers do not break down. 14 years old and walks like gold. Everything original except the bearings in the fan.
  • #20 20081692
    snooki
    Level 15  
    Hello, yesterday error 11 popped up on my stove - which is associated with the lack of hot water in the tap. I read on the forum information that probably the fan or pressure switch will burn. I dismantled the stove to check the exact model of the pressure switch. I put it together and checked if the fan turns on. Unfortunately, the fan did not move when the hot water was turned on. I checked it with a meter and there is no voltage going to it. There was also no voltage at the plug on the board to which the wires going to the fan are connected. The relay normally ticks as if it were switching on but the current does not release. Then only error 03 started to appear. I managed to borrow a board from the same furnace and only the furnace started working. I also noticed that at the plug from which the wires to the fan go, both are swollen. The other wires are OK.
    So in my case the problem lies somewhere in the electronics on the board and not in replacing the fan.

    By the way, I'm curious if maybe the relay is failing?
  • #21 20473928
    dzimus
    Level 12  
    Buddy, move this pressure switch to the right of the pump, it did not touch me. After replacing the board, you could just move france.
  • #22 20985039
    dagaa00
    Level 1  

    Nike Star stove. For some time, errors 03 and 11 began to appear. I called a service technician, he inspected the furnace, cleaned everything, and the next day the errors appeared again. The service technician came again, this time he replaced the fan and the pressure switch (that`s what it`s called :) ). For a few days the stove worked without any problems, then after 4 days error 11 started appearing again. Additionally, when using water, hot water suddenly stops flowing for about 1.5 minutes. ice water flows, then warm water starts flowing again. Does anyone have an idea what else could be causing the error?
  • #23 20985326
    zales.vip
    Level 31  
    You probably have EOLO STAR and not NIKE STAR.
    But to answer:
    The reason may be:
    1. Chimney - blockage of one of the chimney flues (oxygen or exhaust gases).
    2. Breakage of the hose from the fan to the pressure switch.
    3. Fault on the motherboard.
    4. Of course, there is also the pressure switch itself - once it happened to me that the new one was defective.
    5. Fan - if it is new, it may be installed incorrectly
    6. Clogged choke in the fan
  • #24 21120626
    elekam2
    Level 2  
    Hello,
    I'm having a problem with error 11, Immergas EOLO STAR.
    In my case it looks like an electronics problem, but I don't know how I can check it exactly.
    I am an electrician, not an electronics technician, but with your help it might be possible to diagnose specifically what the problem is.
    I have checked the patency of the hoses from the pressure switch and the fan itself (they look ok).
    There is no voltage coming from the board to the fan.
    Attached is a video of what happens when I turn the hot water off.


    .
  • #25 21120641
    zales.vip
    Level 31  
    Replace the relays. And preferably the capacitors at once.
    All electrolytes.
    Replace all components 1:1 with EXACTLY the same ones.
    If you are not proficient in soldering, contact an electronics technician.
    The Immergas circuit board is a little fragile and it is easy to chip the tracks.
  • #26 21120678
    elekam2
    Level 2  
    Thank you for your quick response.
    But that doesn't solve the problem of the cooker not working on Sundays ;-(
    I am sending a picture of the board.
    PS. You can hear the relay ticking after turning on the hot water.
    I don't think I'm going to do it myself, even though I'm good at soldering, it's a time-consuming task to gather parts etc.
    I'm pressed for time, so I can either buy new or reconditioned electronics. (How much does it cost to remanufacture such electronics?)

    Close-up of an Immergas boiler circuit board with visible wiring and components. Image of an electronic circuit board with a display showing a temperature of 21°C. .
    I would like to be sure that this is the fault of the board and not some other component of the cooker. That's why I asked for help in diagnosis.
  • #27 21121124
    zales.vip
    Level 31  
    The relay "ticks" but if you open it and look at the contacts you will understand.

Topic summary

The discussion revolves around the Immergas EOLO Star 23 kW boiler, specifically addressing the transition from Error 11 to Error 03, with the fan failing to start. Users report various potential causes and solutions, including issues with the motherboard, pressure switch, and fan. Some users suggest that insufficient air supply or water ingress into the fan may lead to these errors. Solutions proposed include cleaning or replacing the fan, checking the pressure switch, and ensuring proper voltage supply. One user successfully resolved Error 03 by replacing the fan after diagnosing the issue with the help of a technician. Others emphasize the importance of checking the electronic board and relays for faults.