Nie, dziękuję Przekieruj mnie tamQuote:Is the pipe brazed or crimped?
In both cases - apart from threaded connections, the pipe can be built in, and it can even be plastered over.
Quote:Relevant standards on this subject will be provided by RIGIPS or KNAUF
Quote:Before the leak test, did you indicate to the inspector that you wanted to install the pipe? If so, an appropriate entry should be made in the acceptance and inspection report of the installation. Unless it is not required by Polish law.
waldekel wrote:
(...) on the remaining above-ground storeys, it is allowed to run them also in chases covered with unsealed screens or filled - after prior installation tightness test - with easily removable plaster that does not cause corrosion of the pipes. Filling of grooves in which copper pipes are led is prohibited.
Quote:And how does the recipe apply to copper pipes covered with a jacket or thermal insulation?
Quote:Filling of grooves in which copper pipes are led is prohibited.
krisi3 wrote:One tube is a problem, and probably ?22 or ?18.
unitral wrote:Is the pipe brazed or crimped?
krisi3 wrote:And with today's plumbing technology, I don't see any problem with placing the pipe under the ceiling, and it doesn't have to be 10 cm above the table top and along the wall.
krisi3 wrote:And in the first post, my friend assured that the tightness was checked and here we have the answer why it is not worth hiding gas pipes.
unitral wrote:Since he wasn't doing the pressure test, he wasn't doing it at all.
Such an installation should not be commissioned and approved, and a protocol is issued after the pressure test.
unitral wrote:You can plaster your welded steel pipes, just make a plan (handwritten and attach it to your apartment papers) if any changes are needed in the future ...
unitral wrote:... The stove has to be moved because the bathroom volume is less than 8m3.
MM2X wrote:... The previous tenant made the "modernization" (lowering the ceiling + other ...) at the cost of over 2 m3. The kitchen is connected with the hall, but even without it it is over 8 m3.
unitral wrote:Nonsense on your bill.
What is pipe lagging for?
TL;DR: Methane becomes explosive at 4–16 % volume [Elektroda, waldekel, post #9021657]; “The unsealed screen is, among others, the GK board” [Elektroda, unitral, post #9021041] Polish §165.2 lets above-ground gas pipes hide behind removable drywall when joints are welded/crimped and a recorded pressure test is done.
Why it matters: You can keep kitchens neat without risking an unseen gas pocket.
• §165.2 Journal of Laws 75/2002: copper pipes may sit behind an unsealed screen; filling grooves is banned [Elektroda, waldekel, post #9020850] • Explosive range of methane: 4 %–16 % in air [Elektroda, waldekel, post #9021657] • Mandatory tightness test: 0.05 MPa for 30 min or 5 kPa for 15 min [Elektroda, MM2X, post #9030791] • Typical design fee for flat gas retrofit: approx. 300–600 PLN [PSGG, 2023]. • Minimum room volume for open-flue heater: 8 m³; closed-flue: 6.5 m³ [Elektroda, mirrzo, post #9030830]