VIESSMANN VITODENS 200-w: Resolving Error F4 - Damaged Burner Automatic (Replacement & Repair)
grzeg0 100793 11
What causes the F4 fault on a Viessmann Vitodens 200-W, and can the burner control unit be repaired or replaced?
F4 on this boiler is often caused by a dirty or worn ionization electrode rather than the entire burner automation, and the electrode may be cleaned first but is often replaced if the problem returns [#9107245] [#9108991] Cleaning the metal part of the ionization electrode and the whole electrode block restored operation in the thread, at least temporarily [#9107245] [#9110490] Service should also check the gasket, chimney/flue system, electrical connections, gas settings/measurements, exhaust-gas analysis, and perform calibration or a reset if needed [#9108991] [#9127053] One reply notes that the burner control unit/main board itself is the boiler automation and can cost about PLN 1,500, but the thread points first to the electrode as the more likely fault [#9102486] [#9108991]
  • #1 9102231
    grzeg0
    Help: 22
    Rate: 164
    Hello forum members. I have a boiler as in the subject, so the F4 fault has appeared for some time. It shows me as damaged BURNER AUTOMATIC. And the question is which element it is and whether it can be repaired or replaced with a new one. I attach a photo. Thank you in advance.
  • #2 9102486
    wawrzeczko_t
    Heating systems specialist
    Help: 199
    Rate: 1033
    The burner control unit is the boiler automatics (electronic main board) which costs about PLN 1,500.
  • #3 9102650
    grzeg0
    Help: 22
    Rate: 164
    Is that the only possibility? Because I wonder that the boiler works after the reset, the error is displayed after a few days, and when it is cold, it works for up to two weeks. It seems to me that when it is turned on often, nothing happens to it.
    wawrzeczko_t
    Help: 199
    Rate: 1033
    piracik
    Help: 557
    Rate: 1977
    Unscrew the ionization electrode (detail C in the photo) and clean its metal part.
    Perhaps it would be worth calling the service for the annual technical inspection.
  • #6 9107498
    grzeg0
    Help: 22
    Rate: 164
    The technical inspection was five months ago. I'll clean the electrode and let me know. Thanks :D
    Ionization electrode wear as primary F4 fault cause
    #7 9108991
    dejure
    Rate: 13
    This fault is most likely caused by the wear of the ionization electrode.
    this element is responsible for flame control and optimal combustion - unfortunately it is immersed in the flame and wears out due to slow burnout, losing its properties. This vulnerability will only get worse
    The gas fittings dosing gas into the combustion chamber or the unsealing of the flue gas conduit may also be responsible for this error.
    I suggest calling a service that will visually check the electrode, check the level of the so-called ionization current and performs exhaust gas analysis to verify the correctness of the combustion process. Cleaning the electrode may only help temporarily or not at all.
    Most likely, the ionization electrode will be replaced and, depending on the type of boiler and the year of construction, the so-called code plug.
  • #8 9109040
    piracik
    Help: 557
    Rate: 1977
    Can you explain why this coding plug is replaced?
  • #9 9110490
    grzeg0
    Help: 22
    Rate: 164
    Yesterday I cleaned the ionization electrode and the whole electrode block. It works for now.
  • #10 9113361
    dejure
    Rate: 13
    The coding plug is actually a small chip on which important information is stored about the type of boiler, parameterization of the combustion process in which the ionization electrode is actively involved, read by the automation.
    According to my information, at the moment Viessmann makes electrodes made of two metals, and thus, there will be different values of the ionization current, which are stored in this chip.
    Replacing the ionization electrode with a new one and leaving the old plug on may not really eliminate the problem.
    But this will be judged by the service technician by looking at the serial number of the device and the software number on the plug in the automation,
    LeeRoz
    Rate: 61
    The electrode is one of the causes that can cause F4. When the errors you wrote appear, you should first check many things, the gasket, the chimney system, perform manual calibration, maybe reset the plug or maybe a master reset, check the electrical connections, perform gas measurements, perform exhaust gas analysis and some other important things that you do not need to do yourself. measuring devices you are not checking for yourself.
  • #12 9144809
    grzeg0
    Help: 22
    Rate: 164
    Thank you very much for your comprehensive answers. After cleaning everything works (:
The discussion revolves around the F4 error code on the Viessmann Vitodens 200-w boiler, indicating a damaged burner automatic. Forum members suggest that the issue may stem from the ionization electrode, which is crucial for flame control and can wear out over time. Cleaning the electrode is recommended as a temporary solution, but replacement may be necessary if the problem persists. Additionally, the coding plug associated with the ionization electrode may need to be replaced to ensure proper functionality. Other potential causes include gas fittings and flue gas conduit issues. A thorough inspection by a service technician is advised to diagnose and resolve the problem effectively.