Vitodens 100 F1 Error: Flue Gas Temperature High After Service Checks—What Next?

Vitodens 37806 31
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 13001028
    Vitodens
    Level 9  
    As in the topic, the error F1 appeared - too high temperature of exhaust gas. Service called and:
    - burner checked
    - exchanger cleaned
    - exchanger descaled and flushed
    - pump checked
    - chimney checked - draught is
    - CO2 in normal.
    Nothing helped, still flue gas temperature too high and F1.
    What else can be done, checked?

    PS Installation probably froze last winter, now (November) worked 3 weeks without problems.
  • ADVERTISEMENT
  • #2 13004587
    piracik
    VIP Meritorious for electroda.pl
    What exhaust temperature came out on the exhaust analysis?

    Added after 5 [minutes]:

    The flue gas temperature should be close to the temperature on the boiler.
    Up to 10*C may be higher than that on the boiler.
    If on the flue gas analysis the temperature was within this range then the flue gas temperature sensor should be replaced.
  • #3 13004675
    Vitodens
    Level 9  
    The exhaust gas temperature on analysis reached 130-140 0C, so it's not the exhaust gas temperature sensor.
  • #4 13004963
    piracik
    VIP Meritorious for electroda.pl
    Vitodens wrote:
    What else can be done, check?


    Diligently vent the boiler.
  • #5 13004978
    Vitodens
    Level 9  
    The boiler was vented, the pump also. Will try again.
  • #6 13005023
    piracik
    VIP Meritorious for electroda.pl
    On the exchanger you have such a white faucet. With a radiator vent key you can unscrew it.
    Place some hose on it if there is none and let some water out in a few cycles.
    You can do this on the boiler pump on.
  • ADVERTISEMENT
  • #7 13007547
    Anonymous
    Anonymous  
  • #8 13015691
    Vitodens
    Level 9  
    Venting did not help - I did twice.

    As I wrote earlier exchanger decalcified, flushed, chimney checked "draught" good - so it's not that.

    As ideas run out we will try to put in the second exchanger and see if that helps.
  • #9 13015869
    Anonymous
    Anonymous  
  • ADVERTISEMENT
  • #10 13015876
    Vitodens
    Level 9  
    I don't have one, but the SERVICEMAN "is supposed to have one."
  • #11 13015905
    Anonymous
    Anonymous  
  • #12 13015988
    Vitodens
    Level 9  
    The exchanger is from a dismantled boiler.
    The draught in the flue was measured above the boiler (two holes in the outlet pipe) with a sensor with which CO2, flue gas temperature, O2, etc. were also measured.
  • #13 13019307
    Nargo
    Level 22  
    Check the filter before the boiler yet. A simple fault and it can mess up a lot :) .
  • #14 13019310
    Vitodens
    Level 9  
    The filter in front of the boiler clean.
  • #15 13079341
    swornegacie
    Level 12  
    And how is the problem solved?
  • #16 13079961
    saskia
    Level 39  
    Are the radiators heating correctly?
    How was the pump checked?
  • #17 13080170
    Vitodens
    Level 9  
    The problem is not solved.

    When the furnace is running (set to minimum temperature), all radiators are heating.

    The pump was replaced with a new one.
  • #18 13081898
    saskia
    Level 39  
    I suspect that you have very long and too thin risers, and the last radiator is quite far from the boiler.
    If the installation froze early, it is most likely that any impurities such as scale, rust, etc. were crushed and detached to the inner surfaces of the installation.
    You must check all flows on the entire system, but it would be best to flush it under pressure from the mains, in the opposite direction to the CH flow.
    Of course, you would have to disconnect the boiler before doing so.
  • #19 13086939
    Vitodens
    Level 9  
    Maybe I will try to flush, but if the installation was obstructed and the water was "slow" flowing then the water temperature on the stove would rise very quickly, and nothing like that happens. Unless I am deducing wrong?
  • #20 13087139
    saskia
    Level 39  
    At a minimum temp. radiators give off heat more slowly (less "gravitational pull" in the radiators) and then it spreads to all radiators more evenly.
    If the temperature is high, the first radiators give off a lot of heat and then there is a greater "draught" on them, so that further radiators do not heat up as quickly as the first.
  • #21 13087699
    piracik
    VIP Meritorious for electroda.pl
    Vitodens wrote:
    the temperature of the water on the furnace would rise very quickly, and nothing like that happens.

    saskia wrote:
    With this, the temperature of such a short circuit rises quickly and the boiler overheats.


    In my opinion, the problem does not lie in too little circulation.
    Where are you mate?
  • #22 13087751
    saskia
    Level 39  
    Me, or the author of the topic? :-) .
  • #23 13088439
    piracik
    VIP Meritorious for electroda.pl
    saskia wrote:
    I, or the subject author? :-)



    Good :-)

    If the distance was within reason, I would love to see such a cauldron what someone has already at it fell :D


    Vitodens wrote:
    we'll try putting in a second exchanger and see if that helps



    Have you done a test on another exchanger?

    Now it still occurred to me.
    If the exchanger froze then it may also have deformed quality.
    If it deformed then the gaps between the coils of the pipe may have increased making the exhaust gas flow faster giving less heat to the exchanger.

    The temperature on the boiler in such a case would reach a low temperature and the temperature of the flue gas would be very high.

    I think this theory is very likely.

    Vitodens 100 F1 Error: Flue Gas Temperature High After Service Checks—What Next? .
  • ADVERTISEMENT
  • #24 13090553
    Vitodens
    Level 9  
    piracik wrote:
    If the distance would be within reason



    Mlawa - a little far away

    piracik wrote:
    Have you tested on another exchanger?


    Unfortunately no, it's hard to get a new exchanger without paying for it.

    piracik wrote:
    If it deformed then the gaps between the coils of the pipe may have widened



    The gaps we checked, only in two places are minimally above normal.
  • #25 13090845
    piracik
    VIP Meritorious for electroda.pl
    Vitodens wrote:
    only in two places are minimally above the norm.


    For.
  • #26 13122973
    dario0
    Level 16  
    There is no way that the coils of the heat exchanger, then it would push the alu side rings and gaskets - so there would be condensate or flue gases.
    It is impossible that the temperature of exhaust gases in this boiler reached 140 degrees.
    Or no flow or faulty gas fittings and let too much gas through, but this should come out in the analysis of exhaust.
  • #27 13123432
    piracik
    VIP Meritorious for electroda.pl
    You see seemingly the possibility of such a thing, and yet the temperature is there.
    To make the gaps larger does not have to push the rings. It is enough that some are widened and others narrowed.
    Or, for example, the diameter of the coils will change.
  • #28 13123861
    dario0
    Level 16  
    There is no such possibility. !
  • #29 13123890
    piracik
    VIP Meritorious for electroda.pl
    So what is the cause of this fault?
  • #30 13129485
    _uki_
    Level 11  
    check the nozzles, whether they are sized for the gas you have in the network (or cylinder), the gas pressure after the gas block, the amount of gas burned at max/min power. air vents, birds in the chimney, etc.


    at worst, the motherboard
  • Topic summary

    The discussion revolves around the F1 error in the Vitodens 100 boiler, indicating excessively high exhaust gas temperatures. Despite multiple service checks—including burner inspection, exchanger cleaning, descaling, pump verification, and chimney draught assessment—the issue persists. Users suggest potential causes such as inadequate heat collection due to flow issues, possible deformation of the heat exchanger from freezing, and the need to check gas nozzles and pressure. The author considers replacing the heat exchanger and contemplates purchasing a new boiler for warranty and spare parts assurance.