Choosing the Right PE Protective Cable for Home Switchboard Earthing Connection
sebtr 81724 18
What cable should I use to connect an external earth electrode to the PE busbar in a home switchboard, and can I bury that PE conductor in the ground?
Do not bury a flexible PE cable like LGY or a copper conductor in the ground; in the ground use a galvanized earth strip/loop (bednarka), and then connect it above ground to the PE rail with LGYżo 16 mm² or larger [#10144932][#10145189][#10146230][#10146398] The thread recommends bringing the galvanized loop/strip into the building and terminating it on the PE/GSW bar, rather than running the protective conductor underground [#10146230][#10148329] If the building has no basement, the loop can be brought to the earthing bar through a wall penetration or similar route, but the underground part should be the earthing electrode itself, not the LGY wire [#10148166][#10148329] Several replies also stress that the earth electrode must meet technical requirements and its resistance should be measured, because a few pins and a loop at about 1 m depth do not automatically guarantee a good earth [#10144791]
  • #1 10144733
    sebtr
    Rate: 15
    I have a question how to use the PE cable to connect the earthing pin (outside the building) to the busbar of the home switchboard.
    The connection is made of a YKY 5x10 mm2 cable.
    I want to do grounding additionally, because I am not convinced by this piece of flat bar (rod) in the ground in the ZE cabinet.
    I want to make a grounding with a few pins and a hoop at a depth of about 1m.
    But I don't know if I have to buy some YKY and use 1 wire as PE, or maybe there are typical cables for grounding.
  • #2 10144791
    darek_wp
    Help: 119
    Rate: 193
    Start by presenting the connection conditions (network type, installation parameters). It is not really necessary to ground the N and PE split point. And if you want to do grounding, first of all, let it meet the technical conditions enabling it to work because
    sebtr wrote:
    earthing with a few pins and a hoop at a depth of about 1m
    it is not yet a guarantee of adequate grounding resistance.
  • #3 10144799
    sebtr
    Rate: 15
    the system is TNC and I have to switch to TNS. The connection of N with PE with a piece of rod (1m) in the ground was made in the ZE cabinet. For me, the most important thing is safety and I am going to connect several RCDs in the house. Measurements will of course be taken. I am only interested in whether it is possible to buy a PE cable for laying in the ground
  • #4 10144932
    karolq
    Help: 44
    Rate: 131
    You leave the ground with a galvanized hoop and then LGYżo from 16 mm ^ 2 and above is used for this purpose.
  • #5 10144967
    sebtr
    Rate: 15
    But the LGYżo cable from 16 mm ^ 2 cannot be placed in the ground!
    I will have a length of cable about 2 meters from the distribution board and then 2 meters in the ground to the pin with the hoop
  • #6 10145189
    zbich70
    Help: 1171
    Rate: 6666
    Read again my colleague Karolq's post. You put a hoop in the ground, and connect it to the LgYżo wire above.
  • #7 10145203
    sebtr
    Rate: 15
    I only have the entrance to the building underground and therefore this cable will be about 2 meters in the ground.
  • #8 10145211
    filip.s
    Help: 50
    Rate: 85
    Then you enter the building with a rope.
  • #9 10145212
    kkas12
    Help: 1076
    Rate: 4312
    So what technical conditions are we talking about?
    And what are the guarantees of an appropriate ground resistance?
    Why do you call a single strand a cable?
    And why should it not be placed in the ground?
  • #10 10145256
    sebtr
    Rate: 15
    a hoop for a residential building? I have big doubts
    On the other hand, stranded, cable in the ground is exposed to difficult conditions.
    I could not find the YKY 1x16 protective cable in the specification (colors). I wonder if anyone had a similar problem
  • #12 10146230
    greg16
    Help: 9
    Rate: 37
    My friend . The protective grounding at the facility is absolutely necessary. You introduce the cooperage into the basement and connect it to the PE rail.
    Buddy darek_wp - there is no question of grounding the separation point anywhere. From what the author of the post writes, the installation in TN-S enters the facility and the colleague additionally grounds the PE wire. I rather advise against connecting the LGY cable underground.
  • #13 10146398
    kkas12
    Help: 1076
    Rate: 4312
    Of course, copper cables should not be laid in the ground as well. And you can't even think about combining them.
    However, the basic question for the author of the thread:
    What is the purpose of splitting the PEN in a junction remote from the object?
    Why is there no foundation earth electrode (if it is a new building, of course)?
  • #14 10146745
    jarecki 86
    Electrician specialist
    Help: 127
    Rate: 294
    When it comes to a new building, I advise you to get out of your head with some high heels.
    In accordance with the applicable rules of technical knowledge and the construction design, it should be carried out (as mentioned in col. kkas12 ) foundation earth electrode.
    If it is not there, then in order to equip the building with proper equipotentialization, it is necessary to dig a rim, not to mention its earthing value in the case of using overvoltage protection.
  • #15 10147268
    elpapiotr
    Help: 1015
    Rate: 3530
    I don't understand what the dispute is about. About the name?
    After all, there is the name "protective conductor"
    Bezel clearly writes about it
    And it's all in PN-HD 60364-5-54: 2010 Electrical installations in building structures. Selection and assembly of electrical equipment.
  • #16 10148166
    sebtr
    Rate: 15
    A colleague of kkas12 wrote that:
    Probably a colleague wondered why ZE performs the PEN distribution and wants the recipient to have TN-S in the contract. It is probably mainly about securing the measuring system and the position in the meter cabinet.
    This earth electrode (short flat bar, rod under the box) is not suitable as an earth electrode. I agree that the best earth electrode is undoubtedly the foundation earth electrode, but unfortunately, most people forget about the implementation of the foundation earth electrode at the construction stage. Now, when it is time to make the correct earth electrode, I have to bury the hoop under the connection (YKY 5x10mm2 cable) and lead it to the building. The problem is how to bring the hoop to a building without a basement. Making an additional Lgy connection box is a solution, but I'm wondering where to put a box that is undoubtedly disfiguring. Another solution is to lead the hoop to the clamp of the earthing bar to the bar, but this requires additional forging in the wall.
  • #17 10148216
    elpapiotr
    Help: 1015
    Rate: 3530
    What does forgetting mean and what does most mean?
    If someone is building for himself WITHOUT any building supervision, it is to himself.
    If a construction manager was employed by the investor and he did not ensure it, the manager should be dismissed without remuneration.
    It performs independent functions, so that he knows himself, that he knows what he writes in paragraph 184 of the Regulation of the Minister of Infrastructure on technical conditions,
    which buildings and their location should correspond to of April 12, 2002 (Journal of Laws No. 75, item 690).
    Miwhoo
    Electric installations specialist
    Help: 128
    Rate: 316
    For doubters, I present photos of the BEDNARKA approach to the interior of the building [single-family house]:
    Ending of the hoop with GSW rail [the same building]:
    If I searched, I would probably find more photos. The fact that few people have such installations does not mean that they are done wrong ...
    @ele_pp the fact is that even the supervision does not remember about the foundation earth electrode, which is the easiest way to make, no matter if artificial or natural, and few people visit the electrician before the shell is closed ...
    What are the regulations, everyone knows what they are reflected in reality, you know ... since there are no earth electrodes even on the projects ...
  • #19 10148370
    sebtr
    Rate: 15
    I close the topic
The discussion revolves around the proper use of PE (Protective Earth) cables for connecting the earthing pin to the busbar of a home switchboard. The user expresses concerns about the adequacy of existing grounding methods and seeks advice on whether to use a YKY 5x10 mm² cable or if there are specific cables designed for grounding. Responses highlight the importance of grounding systems, particularly the transition from TNC to TNS systems, and the necessity of ensuring proper grounding resistance. Various cable types are mentioned, including LGYżo and YKY, with caution advised against using certain cables underground due to environmental conditions. The conversation also touches on the significance of foundation earth electrodes and the common oversight of their installation during construction.