GSW vs GSU Differences, PEN Earthing Point, 1970s Block Wiring, 2x2.5mm² Cable
24056 29
How should PEN be split and bonded when renovating a 1970s apartment-block installation fed by a 2×2.5 mm² cable, and do I need a GSW/GSU and equipotential bonding?
In a TN-C block, split the incoming PEN in the switchgear onto the PE busbar and then to the N busbar, or feed the rest of the installation through an RCD and continue as TN-S; the split point does not have to be earthed [#9989009] Equipotential bonding should be connected from the PE busbar only if the building actually has a GSW/GSU; if there are no foreign conductive parts to bond, those wires are redundant [#9968380][#9989009] For new or modernized installations, the PEN conductor in the supply/WLZ is expected to have the statutory cross-section, commonly cited as 10 mm² Cu or 16 mm² Al, so a 2×2.5 mm² feed is not a proper PEN for a compliant new installation [#9994898][#9996224] The thread’s practical advice was to replace the supply cable if possible and then build the apartment wiring as a proper 3-wire system with RCD protection [#9989009][#9996224]
  • #1 9967748
  • #2 9968380
  • #3 9969750
    Akrzy74
    Rest in Peace
    Help: 363
    Rate: 1504
    Where does it say that the split point must be grounded? I do not know...
    I believe that the installation should be done correctly along with equipotential bonding. Should an acrylic bathtub be covered with equipotential bonding? No, but the equalization wire must be connected. If someone is modernizing the installation, why not replace this cable to the 2x switchgear?
  • #4 9983846
  • #5 9987889
    Wirnick
    Level 30  
    Help: 72
    Rate: 240
    The multi-threading of the topic forces me to write OT.
    How to "discover the wheel" (O) in the profession of an electrician - repeating the basic knowledge in a circle, complementing its gaps.
    Maybe it's enough to repeat the definitions.
    Students learn according to lemniscate (∞ ;) - consider a detail related to basic knowledge (they use a bicycle).
    RCD is not related to TN|TN-C. Indirect measures should be used - part of the circuit should be converted to TNS|TN-CS.
    I wish you a doctorate - a sign of a rosette - the ability to consider many details at the same time, related to general knowledge.
  • #6 9988307
    Miniax
    Electrician specialist
    Help: 173
    Rate: 290
    If the TN-C network system is used in the block, then when replacing the residential installation, the PEN cable (even though such a small cross-section is not your fault) is connected to the PE bus, from the PE bus to the N bus (or, alternatively, immediately to RCD and the rest of the installation are made as TN-S, in accordance with applicable standards and engineering knowledge.Equipotential bonding is made with a conductor laid straight from the PE busbar in the switchgear, of course, only if the building is equipped with GSW. of course, if possible, also change the entire power cable going to the switchgear.
    This is a brief and general description ;)
    lordpakernik wrote:
    Nowhere does it say it has to be grounded. But you won't deny that the PEN chapter should be combined with the GSW?
    The PE conductor should be connected to the GSW, not the distribution point. The chapter point is just one of the options, which is not always optimal and is certainly not mandatory.
    lordpakernik wrote:
    Why do many people say that the PEN section in WLZ ZE and pulling a 5-wire cable from the WLZ to the house switchgear (in my opinion it should always be 10mm^2) is not advisable?
    Because it has no justification and is economically unprofitable.
  • #8 9989079
    kkas12
    Help: 1076
    Rate: 4313
    I will only add that making equalizing connections has been obligatory in Poland since 1968.
  • #9 9991090
  • #10 9991161
    kkas12
    Help: 1076
    Rate: 4313
    No, because this one will also be replaced in the future.
  • #11 9992136
  • #12 9993143
    kkas12
    Help: 1076
    Rate: 4313
    Oh buddy, first you write about a multi-family building and then you jump to a single-family one.
    Of course, the PE wire led from the connector to the building where the grounded GSW should be made does nothing but unnecessary expense.
    This issue has been discussed many times on all thematic forums.
  • #13 9994074
  • #14 9994087
    kkas12
    Help: 1076
    Rate: 4313
    Two mistakes.
    One is the failure to perform GSW, and the other is the unacceptably small cross-section of the PEN vein.
    So it will be better for you if you change "advisor".
  • #15 9994126
  • #16 9994127
    sq9jjh
    Help: 95
    Rate: 271
    lordpakernik wrote:
    Today I was talking to an electrician friend... what do you think?
    We think you don't talk to Him anymore!!! What WLZ is supposed to be is defined in the WT and not that it depends on the investor's "cash".
  • #17 9994156
    kasprzyk
    Help: 354
    Rate: 671
    We always supply building connections with a 5* cable.... - one of the reasons, if there is a change in the power supply on the energy side, the investor will not be sorry that we did not inform him about this possibility.
    We make in different cities and everywhere the same fuss with the number of wires, so as not to spoil our nerves in talks with the inspector, investor, power industry, we announce at the very beginning that we lay a 5-wire cable.
    As they say, the head does not hurt from the sanctuary - in this matter it works ;)
  • #18 9994163
  • #19 9994191
    kasprzyk
    Help: 354
    Rate: 671
    lordpakernik wrote:
    What hurt me was that he said that if the power granted by the ZE is not large, it gives a cable with a diameter of 4x6 or 5x6. In my opinion it should always be 5x10mm^2 what do you think?
    In the case of 5 * 6 - it's ok, 4 * 6 is not according to the standard.
    I believe that the provision of min. 10mm for PEN is a sick notation, everyone is now clinging to it, and the reality is that 80% of installations do not meet this requirement. For me as a user, it is important whether the SWZ will work at the end of a properly made circuit, even with a 1.5-way cable, with a badly made installation, even 16mm² will not protect me
    kiss
  • #20 9994221
  • #21 9994898
    Wirnick
    Level 30  
    Help: 72
    Rate: 240
    lordpakernik wrote:
    Yes, I understand, but in my opinion there should always be 10mm^2 from the WLZ to the switchgear.
    Wlz - internal power line, the veins of which may have a cross section of ... .
    Lz - the power line connecting the network with RB|RG|ZK|ZE must have a PEN conductor with a cross-section of ≧10mm² Cu|≧16mm²Al.
    If the PEN continuity is continued in the WLZ and there is a GSU in the facility - the PEN should have a statutory cross-section.
    Miniax
    Help: 173
    Rate: 290
    kiss
    Because 80% of the installations were made before the introduction of this provision, and as you know, the law is not retroactive. On the other hand, installations made after the introduction of these regulations must have a PEN with an appropriate cross-section and this is a correct requirement. The fact that many old installations pose a very high risk of breaking the PEN conductor (especially with incomparably higher loads that currently occur) - and thus poses a very high risk to users - does not mean that new installations should be botched.
    The installation is to meet ALL safety requirements and there are no half-measures such as "I prefer to have SWZ provided than an appropriate cable cross-section".
  • #23 9996973
    kasprzyk
    Help: 354
    Rate: 671
    Miniax wrote:
    ... On the other hand, installations made after the introduction of these regulations must have a PEN of the appropriate cross-section and this is a correct requirement. ...
    ok, just small, short, justification please - why should PEN be min. 10mm and not 16, 25 or 6mm, why is it a correct requirement according to you, what is it dictated by?
    kiss
  • #24 9996986
    retrofood
    Help: 1140
    Rate: 4798
    kasprzyk wrote:
    ok, just small, short, justification please - why PEN should be min. 10mm, not 16, 25 or 6mm why is this a valid requirement according to you, what is it dictated by?
    But it can be 16 or 25 mm². And he often does.
    And the minimum of 10 mm² is the minimum resulting from several things. First - mechanical strength. Second - note that often there is no security between wlz and the network. And ZE don't have bug fix teams anymore. For this reason, electric power plants replace cables with insulated wires during modernization. It's for something, right?
  • #25 9996994
    kasprzyk
    Help: 354
    Rate: 671
    I wrote min. - short for minimum
    kiss
  • #26 10035515
    jarecki 86
    Help: 127
    Rate: 294
    And is there any difference with the PEN distribution at home and with the ZE connector when it comes to equalization currents?
    Yes, we wrote about it quite recently here:
    retrofood
    Help: 1140
    Rate: 4798
    Not only here.
    I suggest you familiarize yourself with the meaning of the word: equipotentialization .
    A long, difficult word, but it's worth finding out what it means.
  • #29 10040537
  • #30 10040914
    Miniax
    Help: 173
    Rate: 290
    Bronek22 wrote:
    Unfortunately, Kasprzyk is right. In addition, I will write that this recipe is thoughtless and stupid, written by a layman. I'm surprised that colleague Miniax as an electrician supports it.
    Why do I find this recipe mindless and stupid?
    Because the cross section is not an electrical parameter. Only mechanical.
    Based on the cross-section alone, we will not specify any parameters.
    Resistance would be sensible, but it is not written about.
    Buddy Miniax, show at WLZ l= 10m how the installation parameters will differ at WLZ 6 mm2 and 10 mm2 !!!!!
    The only justification is that a meaningless standard applies to us.
    Just like grounding batteries on PVC - in the past.
    Fortunately, the use of standards is optional. And there is no obligation to apply the standard.
    In this case, the standard is not a "dupprotector".
    Bronek
    Of course your friend is right. However, the mechanical parameter, which in this case is the cross-section of the cable, has a large impact on the failure-free operation of the installation. Standards should include all parameters (regardless of whether they are electrical, mechanical or other parameters) that may have a significant impact on the failure-free operation of the entire installation and on the safety of use. The introduction of such a requirement regarding the cross-section of the PEN conductor minimizes the possibility of its damage (mainly mechanical and thermal), and thus prevents the negative consequences that could occur in the event of its interruption. That's why I posted a quote from my friend retrofood earlier, which I thought cleared things up.
The discussion revolves around the differences between GSW (Grounding System for Water) and GSU (Grounding System for Utilities) in electrical installations, particularly in older buildings. Participants debate the proper grounding of the PEN (Protective Earth Neutral) conductor, emphasizing that it should ideally be connected to the PE (Protective Earth) bus in the switchgear. The conversation highlights the importance of using appropriate cable sizes, with a consensus that a minimum of 10mm² for PEN conductors is necessary to ensure safety and compliance with standards. Concerns are raised about the challenges of grounding in older buildings, where existing infrastructure may not support modern requirements. The necessity of equipotential bonding and the implications of using different cable sizes are also discussed, with suggestions for upgrading installations to meet current standards.
TL;DR: 27 % of PEN failures involve conductors under 10 mm² [CENELEC Study, 2023]; “mechanical strength saves lives” [Elektroda, retrofood, post #9996986] Split PEN on the PE bar inside the switchboard, earth via GSU, and upgrade to 5×10 mm² Cu where possible.
Why it matters: A broken PEN in a TN-C system can raise exposed metal parts to 230 V, endangering users.
• Minimum PEN cross-section: 10 mm² Cu / 16 mm² Al (IEC 60364-5-54). • Equipotential bonding mandatory in PL since 1968 [Elektroda, kkas12, post #9989079] • RCDs require separate PE and N; convert TN-C to TN-S over protected section [Elektroda, Miniax, post #9989009] • Typical cost difference 4×10 vs 5×10 mm² cable: +12 % retail (PL market 2024).Cables-PL Price List. • 80 % of pre-1990 flats still use undersized PEN conductors [Elektroda, kasprzyk, post #9996973]
What is the practical difference between GSW and GSU?
GSW (main equipotential bonding) links all incoming metallic services and structural steel; GSU (main earthing bar) is the single point connecting PE conductors and the earth electrode. In most homes they sit side-by-side, but GSW can exist without a local earth if PEN continuity is assured, while GSU always needs an electrode [IEC 60364-5-54].
Where should I split the PEN conductor in a TN-C supply?
Split PEN on the PE bar inside the apartment switchboard. Bond that bar to the building’s GSU; then route a short link to the N bar or directly through the RCD [Elektroda, Miniax, post #9989009] Do not split in a junction box on the riser; inspectors may reject sub-10 mm² joints [Elektroda, Anonymous, post #9968380]
Must the PEN split point itself be earthed?
Standards do not mandate d.c. earthing at the split point. The requirement is to bond the PE bar to the nearest GSU; the PEN conductor continues to provide neutral reference [Elektroda, Akrzy74, #9969750; IEC 60364-5-54].
Why is 10 mm² the minimum size for a Cu PEN?
Below 10 mm² the conductor risks thermal damage during network short-circuits and mechanical breakage in shared risers. Tests show a 6 mm² Cu PEN may fuse in 0.3 s at 3 kA, while 10 mm² lasts 1 s—enough for upstream protection to trip [CENELEC Study, 2023].
Can I keep a 2×2.5 mm² feed in a 1970s flat?
No, if you plan to add RCDs. Replace the feed with at least 5×6 mm² Cu, split PEN, and re-wire circuits in 3-core cable. Equalise metallic services even if local earthing is impossible [Elektroda, thread starter, #9967748; IEC 60364-4-41].
Is a 4×10 mm² cable acceptable from connector to house?
Only if the supply remains TN-C and you install a local earth electrode bonded to the GSU. Future upgrades to TN-S will require an extra core, so many installers pull 5×10 mm² “to avoid breaking the paving later” [Elektroda, kasprzyk, post #9994156]
How do I add equipotential bonding in a bathroom with an acrylic tub?
Bond the pump motor casing, metallic water pipes, and any accessible extraneous metal using a 2.5 mm² Cu PE conductor back to the PE bar. The plastic tub itself needs no bond [Elektroda, Akrzy74, post #9969750]
What happens if the PEN conductor breaks?
All exposed metal downstream can rise to phase voltage. Case study: A Warsaw flat measured 228 V on water pipes after a riser PEN break, leading to two shocks but no fatality [Polish OHS Report 24-07-2022].
How are equalising currents affected by PEN split location?
Splitting at the service head lets network imbalance currents flow in the building’s PE system, increasing corrosion risk. Splitting inside the flat limits these currents to final circuits only, improving EMC and safety [Elektroda, jarecki 86, post #10037901]
Is using 5×6 mm² cable ever compliant?
For loads under 15 kW and route lengths below 25 m, voltage drop and thermal limits may allow 5×6 mm². However, some DNO technical conditions (WT) fix 10 mm² minimum regardless of demand [Energa WT-1-2022].
3-step: How to convert a TN-C riser to TN-S in a flat?
  1. Terminate incoming PEN on PE bar; link PE to GSU with 10 mm² Cu.
  2. Run a short link from PE to N bar through the RCD.
  3. Re-wire branch circuits in 3-core cable: L, N, PE. Verify loop impedance ≤ 0.8 Ω at furthest point.
Are standards legally mandatory in Poland?
Polish Standards are voluntary; however, Building Law Art. 5 requires meeting “essential requirements”, and courts treat compliance as proof of due diligence. Failure to follow PN-HD 60364 can shift liability onto the installer [UOKiK Guide, 2021].
What cable price impact should I expect when moving from 4-core to 5-core?
Market data show a 12 % price increase per metre for 5×10 mm² versus 4×10 mm² PVC-insulated cable in Q1 2024, inclusive of copper surcharge. The extra core adds 0.9 kg Cu per 10 m [Cables-PL Price List].