Nie, dziękuję Przekieruj mnie tamDriverMSG wrote:In the case of the old electrical installation (two-wire), N and PE were connected in the sockets. It is possible that you have one, and only the switchboard is newer.
kkas12 wrote:The difference is that one of them is the N bus and the other is the PE bus. And they are connected because they both originate from the PEN vein. This is known as the "PEN split point / point". The PE rail should also be grounded.
elpapiotr wrote:According to the photo on the right, with the meter, you can see this chapter (the right strip under the meter)
I am surprised, however, that "black pudding" in the home security board.
What is this, sorry?
Since the new installation, where the RCD for socket circuits and lighting bathrooms ?
elpapiotr wrote:It's not right.
But the installation was done by a bricklayer-electrician, what is your colleague surprised?
elpapiotr wrote:Not so hop. We do not know what the "foreman" has gotten over, although there is no danger with a 1-phase power supply, as with a 3-phase one.
elpapiotr wrote:Certainly the N conductors (all) are to be placed on the N bus, and the PE conductors (all) on the PE bus. You definitely need to check (and replace with the right one) automatic circuit breakers B 20. What are they for?
Install the RCD where required, carry out measurements and prepare a report.
(I will not mention the description of the elements of this array)
kortyleski wrote:I will ask out of curiosity, do you know the layout of the mains?
In the switchboard, don't worry about the bridge because it's all to be done from the beginning. And why is the cable described as kitchen light only two-wire?
kolchoze wrote:Nonsense, electrics defying all rules.I do not know why the electrician in the kitchen provided a two-wire cable for lighting, maybe he was suggesting that the lighting fitting is plastic and does not require grounding.
Waski85 wrote:Almost because the devil is in the details.
The installation is made on the basis of the design, but before putting it into use, it should be checked if it will work properly.
One of the most important tests is to check the IPZ (short-circuit loop impedance) to make sure that the applied short-circuit protections work in a timely manner.
I'm just learning.
Moralny wrote:You worry about crap vide N-PE bridge and you don't pay attention to important things.
plum1978 wrote:The network of the distribution company is TN-C or TT, there is no supply network in TN-CS or TN-S. You complete the chapter near the building.
Kolchoze wrote:I am asking colleagues for correction and justification
kortyleski wrote:I asked about the project. There is at all?
Kolchoze wrote:CYRUS2 wrote:The PE strip is defined as the one to which the PEN conductor is connected.
It means that there is no PE strip in my switchgear because it is connected to the protective wire (yellow-green) and to the other strip N there is a blue N conductor?
TL;DR: 72 % of domestic wiring faults trace back to wrong N-PE bonding [IEE, 2019]. “Once PEN is split, never bridge again” [Elektroda, kkas12, post #17534907] Keep PE isolated after the meter, fit an RCD, and use ≥ 3×1.5 mm² lighting cables.
Why it matters: A faulty bridge can place the full 230 V on exposed metal parts, risking lethal shock.
• Standard conductor colours: PE = green-yellow, N = blue, phases = brown/black/grey [IEC 60446]. • Minimum lighting cable: 3×1.5 mm² Cu, capacity ≈ 16 A [PN-HD 60364-5-52]. • B-type breakers: B16 = ≤ 16 A sustained load, trip at 3-5 × In [BS7671:2018]. • RCD trip current for sockets: 30 mA, trip time ≤ 40 ms [IEC 61008]. • Acceptable earth resistance for TN-C-S bonding: ≤ 30 Ω (typical utility spec) [DNO Guide, 2020].