I will add that the cable is laid loose without a conduit, and I have to prepare this part of the floor for screeds.
I will add that the cable is laid loose without a conduit, and I have to prepare this part of the floor for screeds.
Greggy77 wrote:Because in the house design I have a ring earth electrode and a lightning rod (not done yet)
WojcikW wrote:what partnership are you talking about?
WojcikW wrote:And most importantly, has your colleague seen the project?
opornik7 wrote:Take the best photo or scan and post it on the forum because it's hard to judge the situation from your words.
Greggy77 wrote:whether this wire should be connected outside the building with the hoop iron in the nearest control joint or insert the hoop iron and connect it to the GSW.
opornik7 wrote:The ring earth electrode is the best solution for lightning protection in any facility, old or new.WojcikW wrote:what partnership are you talking about?
Designing the ring earth electrode on the new facility is a mess for me. I'm writing about this and I can't understand...
WojcikW wrote:Seriously. And what do you think?
WojcikW wrote:The foundation earth electrode is not the best earth electrode for a lightning protection system. As I wrote, the ring earth electrode is the best. The ring earth electrode does not exclude the foundation earth electrode, on the contrary, in the case of the building's lightning protection system, both earth electrodes should be used: the ring earth electrode for the lightning protection system and the foundation earth electrode for the power system. Ring and foundation earth electrodes should be connected in GSW. It is also permissible to connect both earth electrodes in the ground.
Greggy77 wrote:There is no foundation earth in the project.
Greggy77 wrote:The team ", which was making the foundation, if they were to make a foundation grounding, they would definitely botch it.
Greggy77 wrote:You belong to those who believe that the foundation earth electrode is done by a steel fixer, a tiler in bathrooms and kitchens, and a plasterer in rooms.There is no foundation earth in the project. The "team" that made the foundation, if they were to make a foundation earth electrode, they would definitely botch it...
retrofood wrote:I even think that the foundation earth electrode is not suitable as an earth electrode for a lightning protection system. Anyone who has not seen a chimney blown apart by lightning and electrical installation not connected anywhere, torn out of the plaster, is not aware of the forces to which the foundation will be subjected in the event of a lightning strike.WojcikW wrote:The foundation earth electrode is not the best earth electrode for a lightning protection system. As I wrote, the ring earth electrode is the best. The ring earth electrode does not exclude the foundation earth electrode, on the contrary, in the case of the building's lightning protection system, both earth electrodes should be used: the ring earth electrode for the lightning protection system and the foundation earth electrode for the power system. Ring and foundation earth electrodes should be connected in GSW. It is also permissible to connect both earth electrodes in the ground.
My comment for readers:
This is a private opinion Colleague, professional literature and scientists say otherwise, however, since there is freedom of expression, holding such views is not punishable.
WojcikW wrote:I even think that the foundation earth electrode is not suitable as an earth electrode for a lightning protection system. Anyone who has not seen a chimney blown apart by lightning and electrical installation not connected anywhere, torn out of the plaster, is not aware of the forces to which the foundation will be subjected in the event of a lightning strike.
WojcikW wrote:Anyone who has not seen a chimney blown apart by lightning and electrical installation not connected anywhere, torn out of the plaster, is not aware of the forces to which the foundation will be subjected in the event of a lightning strike.
TWK wrote:Is the message helpful? + -1 -
WojcikW wrote:I even think that the foundation earth electrode is not suitable as an earth electrode for a lightning protection system. Anyone who has not seen a chimney blown apart by lightning and electrical installation not connected anywhere, torn out of the plaster, is not aware of the forces to which the foundation will be subjected in the event of a lightning strike.
TWK wrote:Is the message helpful? + -1 -
emigrant wrote:Unfortunately, the phenomenon of lightning is more complicated and resistive resistance is not everything. We make static measurements and lightning is not only a dynamic phenomenon, but also has a wave nature. We do not know until the end what will be the wave impedance of the path we will make to the ground. In the measurements, the current flows to the ground like a duck's foot, through a layer of concrete, which has a large surface area. In fact, dynamic and wave phenomena can cause, for example, 90% of the lightning current to pass through concrete with a small area, causing the temperature in this place to increase to, for example, 500°C. In addition to thermal phenomena, there are also electrodynamic forces. It is these forces that pull the electrical wires out of the plaster. Much can be written about it.WojcikW wrote:Anyone who has not seen a chimney blown apart by lightning and electrical installation not connected anywhere, torn out of the plaster, is not aware of the forces to which the foundation will be subjected in the event of a lightning strike.
Hmm, but the surge current from the ground discharge and its destruction will only be at the point of its impact (vertical or horizontal fuse) there may be some destruction. For example, it pulls out the air terminals from the fastenings. So I don't know how the foundation can be destroyed, it's already a long way to go as soon as the lightning current is discharged.
In addition, where there are poor sandy soils, only the foundation earth electrode can go down even below 5?.
I happen to have a ring earth electrode, but as an electrician in the fall, he checked the resistance of my earth electrode (7.3 ?using the technical method, he said that he had previously made a foundation earth electrode, they lowered the resistance to 2?.
There is a video on youtube somewhere, I don't remember if it's DEHNa or some research institute in Germany, how the lightning protection system is properly made, there is no potential difference, everything done with art is to lead the lightning to the ground, it's like water running off a duck. There was even no sparking, which is common when the lightning protection system is poorly made. Sparking is probably due to the potential difference.
emigrant wrote:The foundation is copper?It may not be complicated, but it's not entirely unexplored. The test was at 2 million volts and 200kA. As far as I know, 200kA ground discharges do not occur in Poland and even 100kA is a rarity. Hmm, 500 degrees already in the foundation earth electrode? Yes, if we discharge the lightning current with small cross-sections, let it be 2.5-4mm^2, it may even lead to an explosion / evaporation of copper ...
WojcikW wrote:I wrote about concrete and my colleague about copper....In fact, dynamic and wave phenomena can cause, for example, 90% of the lightning current to pass through concrete with a small area, causing the temperature to rise to, for example, 500°C in this place...
WojcikW wrote:In fact, dynamic and wave phenomena can cause, for example, 90% of the lightning current to pass through concrete with a small area, causing the temperature in this place to increase to, for example, 500°C. In addition to thermal phenomena, there are also electrodynamic forces. It is these forces that pull the electrical wires out of the plaster. Much can be written about it.
Quote:Lightning discharge currents have much higher values and are therefore able to break down electrically weak contacts between rebars, reducing their resistance. With low resistance and short flow times of lightning surge currents, thermal effects are not dangerous for foundations.
WojcikW wrote:In fact, dynamic and wave phenomena can cause, for example, 90% of the lightning current to pass through concrete with a small area, causing the temperature in this place to increase to, for example, 500°C.
Darom wrote:I'm not that person, I didn't attend the ILPC seminars.I must admit that if I am not mistaken about the person, I had the opportunity to meet my friend WojcikW. They may be a bit presumptuous in conversation, but they are knowledgeable about the subject. He attended ILPC seminars...
WojcikW wrote:The foundation earth electrode is not the best earth electrode for a lightning protection system. As I wrote, the ring earth electrode is the best. The ring earth electrode does not exclude the foundation earth electrode, on the contrary, in the case of the building's lightning protection system, both earth electrodes should be used: the ring earth electrode for the lightning protection system and the foundation earth electrode for the power system. Ring and foundation earth electrodes should be connected in GSW. It is also permissible to connect both earth electrodes in the ground.
TL;DR: Field tests show foundation electrodes lower earthing resistance by 30-50 % compared with ring strips [DEHN, 2020]; “a properly made foundation earth electrode has practically unlimited durability” [Elektroda, retrofood, post #14738987] Always bond PE, GSW and electrode per EN 62305-3 to avoid flash-over. Why it matters: Correct routing now prevents costly rewiring and protects life during a 200 kA strike.
• EN 62305-3 Type B allows either ring or foundation electrode; ≥80 % of conductor must contact soil [EN 62305-3:2009]. • Minimum down-conductor cross-section: 50 mm² steel or 16 mm² Cu [PN-HD 60364-5-54:2011]. • Typical earth resistance target for residential LPS: ≤10 Ω; <5 Ω preferred for surge devices [IEC TS 60728-11]. • Hot-dip-galvanized strip corrodes ~0.13 mm/year in wet soil; full perforation can occur in 8-12 years [TU München, 2019]. • Average retrofit cost of external ring electrode: €12-18 per m including excavation [BDB, 2022].