Integra 32 - message "There was a tamper, call service"

obreb 42272 13
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 10731982
    obreb
    Level 11  
    Hello,
    New control panel, freshly installed Integra 32.
    Configuration via DLOADX, after the configuration is completed, the control panel housing is closed. The message "There was a tamper, call service" on the keypad
    Service code + # - keypad message "Tamper information cleared"
    After a while, "There was a sabotage, call the service" appears again. Several attempts to review events. No failure in the system and the same inscription "There was a sabotage, call the service" for several days. Or maybe someone has encountered such a problem in this headquarters?
    How to clear the message? Maybe some option in the system?

    .................................................. ..........................
    Announcement

    Also read:
    Satel Integra - system configuration - selected issues Selected and most interesting topics regarding the configuration of the Satel Integra system
    Outputs (programmable and not only) of control panels
    How the control panel alarm outputs work
    Connecting any detector to any alarm control panel - guide
    How to connect the siren to the alarm control panel - guide
    Types of Integra control panel outputs that we use in home automation

    CO furnace - integration with alarm (e.g. Satel Integra)
    ETHM 1 Plus / Integra Control. Selected Issues.


    We invite you to read the other guides, highlighted topics, articles in the field of security systems such as intercoms, gate and barrier automation, alarm systems, cameras, access control:
    Security Systems Tutorials


    If you do not find the answer to your question in the above-mentioned topics, please visit the forum:
    Security systems


    We also encourage you to visit the General Guides section, where you will find materials from other forum sections, including those for people starting their adventure with electronics:
    General Tutorials
  • ADVERTISEMENT
  • #2 10732087
    suworow
    VIP Meritorious for electroda.pl
    obreb wrote:
    Maybe some option in the system

    Carefully look for the disabling of this message in the system options (in the manual you will find it without any problem). However, it clears this message by entering the service mode, but if the tamper continues, this message will return after exiting the service mode.
    greetings
  • ADVERTISEMENT
  • #3 10732157
    obreb
    Level 11  
    But if there was a tamper, a yellow LED on the keyboard and some failure message should be on. Meanwhile, everything is fine. The LED is off and the system armed the system without any problems.
  • #4 10732375
    Anonymous
    Level 1  
  • #5 10732397
    obreb
    Level 11  
    I do not know ??? I did not fumble at the keyboard, apart from the operation.
  • #6 10733446
    humek
    Level 32  
    Do you have any expanders E or other there? if they do not have a sensor used, e.g. (microswitch) connected to the TMP terminals, these terminals should be shorted with a wire bridge. In the DLOADX program, you can view the violated zones.
  • ADVERTISEMENT
  • #7 10734510
    ankowalcz
    Level 11  
    Check which line indicates tamper, maybe there are inappropriate detector resistors, e.g. 2EOL and 2.2k resistors, if violated, there will be a tamper, the second cause is e.g. a small jump of the housing tamper contact (bend the plate off)
  • #8 10735467
    obreb
    Level 11  
    Should the manipulator not indicate a fault with a yellow indicator light?
    I have expanders connected, but as I wrote earlier, the system is in service-mode - failures do NOT show any failure.
    I think there is one more thing that should be done. Changing anything in service mode and saving to Flash memory ....?
    If the enclosure tamper contact is not depressed, the loud tamper alarm is set - the same with the rest of the system components. The control panel is arming and working properly. No failure.
  • #9 10735515
    humek
    Level 32  
    The yellow LED on the encoder will show failures and not violated inputs. I will emphasize once again what I wrote before !!! CHECK IN DLOADX in the tab state of violation zones. In this tab you will see everything. Changing and saving to flash memory is a must.
  • #10 10735808
    obreb
    Level 11  
    I can also check the status of the inputs via the keypad, I don't need to connect to the control panel - TRUE ????
  • ADVERTISEMENT
  • #11 10738135
    maolat
    Level 13  
    You can check the status of the inputs by long pressing the 1 key, as long as you have activated this function in the control panel (Data -> Structure and hardware -> Hardware -> Keypads -> State inspections)
  • #12 10747128
    humek
    Level 32  
    Don't be afraid of the computer! connect the cable to the control panel and run the DLOADX program and the tab for viewing inputs and outputs will be easier because you can observe both inputs and outputs. You can also use the keyboard, as the colleague wrote above, but you only have the status of inputs. If you are in the installation phase, starting the system, it is better to check everything using the preview tab of the status of inputs and outputs of the Dloadx program than to tap the keyboard. The program will cover everything at once.
  • #13 10765529
    dj_volt
    Level 26  
    You can solve the problem without a computer - look for the "Message after tamper alarm" option in the Service Mode and uncheck :-)
  • #14 11125275
    obreb
    Level 11  
    Problem solved. Cause - tamper contact of the housing.

    Moderated By sharp:

    Since the problem is solved, I close the topic.

Topic summary

The discussion revolves around a newly installed Integra 32 control panel displaying the message "There was a tamper, call service." Users suggest checking system options in DLOADX to disable the message, but note that it may reappear if the tamper condition persists. Possible causes include a 24-hour tamper zone violation or improper contact with the keyboard tamper. Users recommend verifying the status of tamper inputs through DLOADX or the keypad, ensuring proper connections, and checking for any issues with detector resistors. Ultimately, the problem was resolved by addressing the housing tamper contact.