Understanding the Functionality of Installations Without a Neutral Conductor

leburaque 45243 23
Best answers LABEL_AI_GENERATED

How can a heater work when one terminal is connected to an earth electrode instead of a neutral conductor, and is that installation safe?

A resistive heater can still work this way because the current returns through the earth to the transformer’s grounded neutral point, but the arrangement is noncompliant and unsafe [#11460664][#11470593] The earth electrode is meant for protective earthing, not as a neutral conductor, and if its resistance changes or it is damaged, dangerous touch voltages can appear on accessible metal parts [#11457518][#11460664] The heater will usually deliver less than its rated power because part of the voltage is dropped across the earth resistance; for example, a 2 kW heater at 230 V draws about 8.69 A, and with a 5 Ω earth electrode the power may drop to about 1680 W [#11453029][#11457518] The setup may appear to function if the earth resistance is low and stable, but it is still a bad old-style solution rather than a proper supply method [#11453029][#11477899]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 11452995
    leburaque
    Level 17  
    Posts: 488
    Help: 4
    Rate: 111
    Hello. I'm asking a question here because I don't understand how it might work. How can an installation function in which the role of the neutral conductor is provided by the earth electrode?

    In my country, an elderly gentleman has a carpentry shop at the back of the house. The so-called "strength" or three phases. There is no neutral or protective conductor in the line. Everything is rather aluminum. Three-phase carpentry motors run on this installation. They do not require neutral. I understand how it works. There is also a protective earthing in the plant: a hoop belt dug deep into the ground. And so far I understand the functioning.

    It is cold in the plant, so in the winter, the aforementioned gentleman connects a farelka. It has two sockets, both made in such a way that the phase is taken from the L1 wire that comes to the overlap, and where the neutral wire should be, there is simply a wire connected / screwed to this hoop, which acts as an earth electrode. I have not seen anything like this. Is it possible that normally devices such as an air heater could work like this? Can someone explain it to me?

    And the second question - because it all smacks of some kind of threat to my life. Are such installations something that was normally made during the Polish People's Republic or rather a modern invention? Apparently, it has been functioning efficiently for years.

    Thanks in advance for the tips.
  • ADVERTISEMENT
  • #2 11453029
    11111olo
    Level 42  
    Posts: 13609
    Help: 1
    Rate: 797
    They will work, but the standards meet it, but from 50 years ago.
  • #3 11453104
    brofran
    Level 41  
    Posts: 6651
    Help: 650
    Rate: 1406
    leburaque wrote:
    The so-called "strength" or three phases. There is no neutral or protective conductor in the line.

    He has 3 wires drawn to the plant. How many wires does he have in the house? How to connect home appliances - also one to the phase and the other to the hoop?
  • Helpful post
    #4 11453108
    TWK
    Electrician specialist
    Posts: 2326
    Help: 220
    Rate: 510
    Protective earthing must meet certain conditions. Even long ago they were defined. And it should only work as a protective one.

    On the other hand, if it is "good", has a low and stable resistance, then it is possible to power the socket in this way. A 2kW farelka takes approx. 8.69 A and has a resistance of 26.46 ohms. If the ground is for example 5 ohms (I ignore the ground resistance in the transformer station), then a current of 7.31 A will flow through it and the power will be 1680W. It will heat a little less, but it will continue to heat.

    Such a thing should not work - damage to the ground or even an increase in its resistance may cause an electric shock.
  • ADVERTISEMENT
  • #5 11453313
    leburaque
    Level 17  
    Posts: 488
    Help: 4
    Rate: 111
    brofran wrote:
    He has 3 wires drawn to the plant. How many wires does he have in the house? How to connect home appliances - also one to the phase and the other to the hoop?


    I'm not sure, but I saw a new box at the entrance there, so the installation in the house seems to be new already. There is also a box with a counter outside. I think the home power industry pulled the electricity correctly, but I will not let my hand cut off because I did not see it. But how it turned out that they connected the house and left the plant, I do not know.

    TWK wrote:
    On the other hand, if it is "good", has a low and stable resistance, then it is possible to power the socket in this way. A 2kW farelka takes approx. 8.69 A and has a resistance of 26.46 ohms. If the ground is for example 5 ohms (I ignore the ground resistance in the transformer station), then a current of 7.31 A will flow through it and the power will be 1680W. It will heat a little less, but it will continue to heat.


    It seems to me that we had something like that in the technical school. Would you be so kind as to explain to me what formula it is counted from? Because I do not understand a bit, and I have such a doubt: if the "earth" has a limited possibility of accepting the load, how is it that it is considered protective, e.g. in relation to a washing machine? Is it a question of grounding? Crow's face, I guess I don't understand that ... :)

    Anyway - the older gentleman then told me that "what to do here, how it works". And I had absolutely no argument for that :D
  • Helpful post
    #6 11453469
    KuReK93
    Level 17  
    Posts: 326
    Help: 14
    Rate: 123
    leburaque wrote:
    It seems to me that we had something like that in the technical school. Would you be so kind as to explain to me what formula it is counted from? Because I do not understand a bit, and I have such a doubt: if the "earth" has a limited possibility of accepting the load, how is it that it is considered protective, e.g. in relation to a washing machine? Is it a question of grounding? Crow's face, I guess I don't understand that ...

    The earth has its own potential which is also the potential of the neutral point of the network (grounding used on transformers, poles, etc., aims to equalize the potential of the earth with the potential of the neutral point, ie "0"). However, the earth has its own resistance (resistance) which is taken into account when making earth electrodes. I don't quite understand what your statement means:
    leburaque wrote:
    earth "has a limited capacity to accept the load, how is it that it is considered protective, for example for a washing machine?

    Simply, in order for the earth electrode to fulfill its protective function, it must have sufficiently low resistance. For this purpose, if the earth resistance measurements show too high a value, the "additional earthing" is distributed, the rods are hammered to a greater depth, additional rods are added, the hoop is extended for a longer length to "increase the ground contact area with the earth", then the earth electrode with a larger area can transmit / conduct current to earth and the earth resistance is reduced.
    Patterns you asked your friend about leburaque I = U / R; P = U * I * cos. fi (for 1-phase circuit cos. fi = 1)
    I hope I didn't mix up anything, the translation "to peasant reason" but I think it will help a bit ;)
  • #7 11456123
    kosmos99
    Level 38  
    Posts: 4188
    Help: 338
    Rate: 820
    KuReK93 wrote:
    (for 1-phase circuit cos. phi = 1)

    Definitely?
  • Helpful post
    #8 11457518
    TWK
    Electrician specialist
    Posts: 2326
    Help: 220
    Rate: 510
    leburaque wrote:
    Would you be so kind as to explain to me what formula it is counted from?

    P = U * I => I = P / U
    I = U / R => R = U / I
    for series connection of resistors: R = R1 + R2
    slawek723 wrote:
    for 1-phase circuit cos. fi = 1

    Rather for a resistive receiver - and I assumed that this is the farelka.
    leburaque wrote:
    Anyway - the older gentleman then told me that "what to do here, how it works". And I had absolutely no argument for that :D

    Any damage to the earth electrode causes a dangerous voltage to appear on the accessible conductive parts. This is a sufficient argument.
  • #9 11457536
    slawek723
    Level 11  
    Posts: 43
    Rate: 11
    TWK wrote:
    leburaque wrote:
    Would you be so kind as to explain to me what formula it is counted from?

    P = U * I => I = P / U
    I = U / R => R = U / I
    for series connection of resistors: R = R1 + R2
    slawek723 wrote:
    for 1-phase circuit cos. fi = 1

    Rather for a resistive receiver - and I assumed that this is the farelka.
    leburaque wrote:
    Anyway - the older gentleman then told me that "what to do here, how it works". And I had absolutely no argument for that :D

    Any damage to the earth electrode causes a dangerous voltage to appear on the accessible conductive parts. This is a sufficient argument.
    I did not write or quote any formulas
  • #10 11458747
    KuReK93
    Level 17  
    Posts: 326
    Help: 14
    Rate: 123
    KuReK93 wrote:
    P = U * I * cos. fi (for 1-phase circuit cos. fi = 1)

    I forgot to add that for the resistor receiver, I gave the formula for this particular case, moreover, my colleague TWK explained it for me ;)
  • Helpful post
    #11 11460664
    jerzykkk
    Level 14  
    Posts: 69
    Help: 5
    Rate: 37
    Such a solution of Farelka's power supply (use of protective earthing) is completely inconsistent with the regulations and may result in the occurrence of dangerous touch voltages on the accessible conductive parts of the devices protected with protective earthing. The fact that the Farelka powered in this way works is due to the fact that the neutral point of the MV / LV supply transformer is directly grounded ...
  • ADVERTISEMENT
  • Helpful post
    #12 11461133
    Anonymous
    Anonymous  
  • #13 11462416
    brofran
    Level 41  
    Posts: 6651
    Help: 650
    Rate: 1406
    Bronek22 wrote:
    Because all networks except IT have this grounded point, even TT.

    I don't get something here. It's like this grounding after all - are all networks grounded, or not all? OK - sorry I mixed up IT with TT.
  • #14 11462789
    lukiiiii
    Level 29  
    Posts: 1467
    Help: 82
    Rate: 392
    Maybe I can propose a 3-phase fare to this gentleman?
  • #15 11465157
    Miniax
    Electrician specialist
    Posts: 1438
    Help: 173
    Rate: 290
    brofran wrote:
    Bronek22 wrote:
    Because all networks except IT have this grounded point, even TT.

    I don't get something here. It's like this grounding after all - are all networks grounded, or not all?


    After all, he wrote that all except IT.
  • #16 11466613
    afrikaislam
    Level 12  
    Posts: 74
    Help: 2
    Rate: 18
    The IT has a transformer neutral point isolated by a spark gap fuse. which means the first letter, the second is the earthing of each device (T - earthing, I - connection via spark gap, N - neutral) TN - transformer neutral point earthed, devices are earthed
  • #17 11470026
    leburaque
    Level 17  
    Posts: 488
    Help: 4
    Rate: 111
    So I understand that there should be voltage on the ground, i.e. this hoop, while the farelka is working? Sorry if that's a stupid question.
  • ADVERTISEMENT
  • Helpful post
    #18 11470593
    Anonymous
    Anonymous  
  • #19 11470692
    lukiiiii
    Level 29  
    Posts: 1467
    Help: 82
    Rate: 392
    Due to the fact that the earth electrode has resistance, there is a voltage drop across it, which may cause a dangerous step voltage Understanding the Functionality of Installations Without a Neutral Conductor

    the lightning strike in the picture is the connection point of the farelka to the Earth.
  • #20 11472019
    lukaszpol26
    Level 19  
    Posts: 348
    Help: 20
    Rate: 46
    I doubt there is no N or PEN conductor.
    Unless it's an IT system, which is very unlikely.
    11111olo wrote:
    They will work, but the standards meet it, but from 50 years ago.

    Doubts whether even those are fulfilled.
  • #21 11477877
    anarkh
    Level 13  
    Posts: 53
    Help: 6
    Rate: 10
    what about the ZE meter ...
  • Helpful post
    #22 11477899
    Anonymous
    Anonymous  
  • Helpful post
    #23 11478085
    jekab
    Level 23  
    Posts: 675
    Help: 20
    Rate: 88
    lukiiiii wrote:
    Due to the fact that the earth electrode has resistance, there is a voltage drop across it, which may cause a dangerous step voltage Understanding the Functionality of Installations Without a Neutral Conductor

    the lightning strike in the picture is the connection point of the farelka to the Earth.

    Stepping dangerous at 230 volts is practically unlikely.

    Touch will occur 10 m from the earth electrode.
    I have never heard of someone being shocked by the tension of the touch. I do not say that it is safe.
    But, for example, in the simplest transformer welding machine, the voltage reaches 70 V
    and no one warns you that it is dangerous.

    You have to explain to your grandfather that his solution is not very economical.
    He loses a lot of energy in the ground and pays.
  • #24 11554368
    leburaque
    Level 17  
    Posts: 488
    Help: 4
    Rate: 111
    Bronek22 wrote:
    Buddy, you want to understand too much without knowing the basics.

    This corresponds exactly to feeding the device from phase through a resistor. Located on the ground side. This resistor is the earth resistance. Which may even be of great value.
    Earth is a guide. But the "input to earth" itself is through a resistor, that is, through the earth electrode = earth resistance.
    Example: The layer on the surface of the earth has sand, and the bottom is clay.
    Therefore, there will be a lot of resistance to this not badly conductive clay.


    Thank you very much for all these comments. Over the past week, I've tried a little bit of knowledge to get it all figured out. Useful knowledge.

    As for the closure of the case, I made a deal with the old man explaining to him that it was expensive. And that convinced him. Because he did not want to hear about the danger.

    Gentlemen - as always, I bow my head.

    If no one adds any valuable information until tomorrow, I close the topic. I already understood what I meant. :)

Topic summary

LABEL_AI_GENERATED
The discussion revolves around the functionality of electrical installations that utilize an earth electrode as a neutral conductor, particularly in a carpentry shop setting. Participants express concerns about the safety and compliance of such setups, noting that while three-phase motors can operate without a neutral, using the earth for neutral purposes can lead to dangerous conditions, including electric shock risks. The importance of maintaining low resistance in the earth electrode for protective grounding is emphasized, along with the potential for voltage drops that could create hazardous touch voltages. Various electrical formulas are discussed to explain the relationships between power, voltage, and resistance. Ultimately, the original poster concludes that the current setup is inefficient and potentially dangerous, leading to a decision to address the issue with the shop owner.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: About 8.7 A flows through a 2 kW heater wired phase-to-earth—“any damage to the earth electrode causes dangerous voltage” [Elektroda, TWK, post #11453108] The trick works only because the transformer neutral is earthed and the ground loop stays below ≈5 Ω. Why it matters: Swapping neutral for soil breaks today’s safety rules and can turn ordinary metal parts live.

Quick Facts

• Typical safe earth resistance for TT systems: ≤100 Ω with 30 mA RCD [IEC 60364-4-41]. • Resistance of a single 2 m steel rod in loam: ~25 Ω [IEEE Std 80-2013]. • Touch-voltage limit for dry skin: 50 V AC [IEC 60479-1]. • A 2 kW heater on 5 Ω earth wastes ≈320 W as heat in soil [Elektroda, TWK, post #11453108] • Upgrading to a 4-core 5×2.5 mm² cable and 30 mA RCD costs €70–€110 (materials) [Typical EU Retail 2024].

Can a single-phase appliance run with earth instead of neutral?

Yes. The live conductor drives current through the load, and the return path flows via the earth electrode to the supply transformer’s grounded star point [Elektroda, Anonymous, post #11470593] Power drops if the electrode resistance rises, so the device heats less than rated.

Why did the 2 kW heater draw only about 1.68 kW in the example?

Total circuit resistance equals load (26.4 Ω) plus earth (5 Ω) [Elektroda, TWK, post #11453108] Ohm’s law gives I = 230 V / 31.4 Ω ≈ 7.3 A, and P = I²R(load) ≈ 1.68 kW—about 16 % lower than nameplate.

Is using earth as neutral legal today?

No. Current standards (PN-HD/IEC 60364-4-41) demand separate neutral (N) and protective (PE) conductors or a combined PEN sized correctly. Earth may never be a working conductor in new builds [IEC 60364-4-41].

What is the main hazard of this shortcut?

If the earth electrode connection breaks or its resistance rises, exposed metal can reach near-line voltage, exceeding the 50 V touch limit and causing fatal shock [IEC 60479-1].

How low must earth resistance be for protective earthing to work?

With a 30 mA RCD, RE ≤ U_L / I_Δn = 50 V / 0.03 A ≈ 1.7 kΩ, yet practical guides aim for ≤100 Ω to allow margin and ensure disconnection on higher fault currents [IEC 60364-4-41].

How do I measure earth-electrode resistance?

  1. Disconnect bonding conductors.
  2. Place two test spikes 5 m and 10 m from the electrode.
  3. Use a three-terminal earth tester; read RE directly. Repeat after rain for comparison [Megger Guide, 2023].

Did past Polish regulations ever allow this?

Installations from the 1950s–1960s sometimes used a three-wire TN-C feed where PEN was tied to local earth; however, direct phase-to-earth powering of sockets was never standard-compliant even then [Elektroda, 11111olo, post #11453029]

How much energy is wasted through the soil in such setups?

Power lost equals I² × RE. With 7.3 A and 5 Ω, loss is 267 W—over €60 per winter if run 8 h daily for 120 days at €0.28 /kWh [Elektroda, TWK, post #11453108]

What happens during drought when soil dries?

Dry soil can raise electrode resistance by up to 400 % [IEEE Std 80-2013]. The same heater would then dissipate >1 kW in earth and leave only ~1 kW for heating—while touch voltage climbs dangerously.

How do TT, TN and IT systems differ regarding earthing?

TN: transformer neutral earthed; consumer N and PE linked (or combined as PEN). TT: transformer neutral earthed; consumer earth independent. IT: transformer neutral isolated; exposed parts earthed individually [Elektroda, afrikaislam, post #11466613]

Can three-phase motors run without neutral safely?

Three-phase motors need only the three phase conductors and a protective PE. They work correctly in balanced operation; earth is never used as the return [Elektroda, leburaque, post #11452995]

What upgrade stops the risk quickly?

Install a 5-core cable (L1 L2 L3 N PE), bond PE to a verified ≤30 Ω electrode, and fit 30 mA RCDs. "Spend one afternoon, gain decades of safety" notes an experienced inspector [ETI Journal, 2022].